Too much load is my guess.. But to which breaker - the one in your unit or the shore power one? A GFI will only (should only) trip when it detects a leakage current of over 5 mA to ground, not during an overload condition...
If you replaced the receptacle, are you sure the "Line" and "Load" are connected properly? Did you verify your breakers are good? Only a visual or did you use a meter? Need some of these answered before we can assist from the couch..