Installing a power pedestal. Anyone familiar with electrical code?
I want shore power for the camper while Im at home. Im about to start installing either a power pedestal, or a box mounted on a post with at 30a outlet and a 20a gfci outlet next to my garage. I cant mount it to the garage itself as I have a sliding fence gate that rests against the garage and travels its entire length. You can read more about the gate here;
http://www.forestriverforums.com/forums/f68/cantilever-gate-and-gravel-pad-build-lots-of-pics-117631.html
Im thinking it's going to have to be independent of the garage and be mounted in front of the gate on a post or pedestal.
My question is, can I run wire through conduit over top of the concrete the gate is mounted to, from the garage to the pedestal under the gate? Or am I going to have to trench around the cement and bury it?
I obviously want to be code complaint, and I cant seem to find anything regarding running conduit over cement. Only minimum depths that conduit is supposed to be buried. Going under the cement isn't really an option, its 18" thick and anchored to the garage foundation with rebar.
__________________
021 Ram Rebel 1500
2017 Shamrock 233s
Waterloo, Iowa
|
|
|
07-11-2018, 01:35 PM
|
#2
|
Senior Member
Join Date: Jun 2016
Posts: 729
|
Can you come out of the wall just to the left of the concrete? If so you could come out of the wall there into a swept 90 if not a schduled 80 conduit can run across the top of the concrete will have to be fastened down in one place
__________________
2016 wildwood x-lite 241qbxl
being jurked down the road by the beast 2007 Dodge ram 2500
5.9 cummins g56 Trans southbend clutch and a smarty
|
|
|
07-11-2018, 02:20 PM
|
#3
|
Senior Member
Join Date: Dec 2015
Location: Iowa
Posts: 266
|
Quote:
Originally Posted by railroaderone
Can you come out of the wall just to the left of the concrete? If so you could come out of the wall there into a swept 90 if not a schduled 80 conduit can run across the top of the concrete will have to be fastened down in one place
|
Well, that's what Im getting at. It doesn't have to be to the left of the concrete. I want it to come out above the concrete and go between the two gate trolleys, under the gate to the pedestal. I have 4" of clearance between the gate panels and the siding on the garage. I should be able to fit a conduit in there. It would be a straight run. My question is, is it code compliant to run it over concrete or does it have to be buried?
__________________
021 Ram Rebel 1500
2017 Shamrock 233s
Waterloo, Iowa
|
|
|
07-11-2018, 02:38 PM
|
#4
|
Senior Member
Join Date: Jun 2012
Location: Southern NM
Posts: 9,561
|
Here is my take on these kind of questions: if you are really worried about code, then all your questions can be answered by the local government agency where you drew your permit.
If you are doing it yourself without a permit, and asking these kind of questions, you should rethink and perhaps hire a local licensed contractor to do the work correctly the first time.
__________________
Scott and Liz - Southern NM
2012 Wildcat Sterling 32RL - w/level up (best option ever)
2007 Chevy 2500HD Duramax
Reese Fifth Airborne Sidewinder
|
|
|
07-11-2018, 02:48 PM
|
#5
|
Senior Member
Join Date: Jan 2017
Location: In the south
Posts: 266
|
Is it code compliance or not. That depends where you reside each county has different code requirements. Where I am wires have to be buried using underground wire 2 foot deep. If above ground have to be in conduit metal or pvc type.
|
|
|
07-11-2018, 02:51 PM
|
#6
|
Pickin', Campin', Mason
Join Date: Aug 2015
Location: South Western PA
Posts: 19,144
|
Quote:
Originally Posted by NMWildcat
Here is my take on these kind of questions: if you are really worried about code, then all your questions can be answered by the local government agency where you drew your permit.
If you are doing it yourself without a permit, and asking these kind of questions, you should rethink and perhaps hire a local licensed contractor to do the work correctly the first time.
|
I agree.
Code is locale dependent.
What is OK here may not be there.
Check with your associated agency.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA
Days Camped ☼ '19=118 ☼ '20=116 ☼ '21=123 ☼ '22=134 ☼ '23=118☼ '24=90
|
|
|
07-11-2018, 03:21 PM
|
#7
|
Senior Member
Join Date: Jun 2016
Posts: 729
|
If in conduit and secured it meets the stricter version of the code
__________________
2016 wildwood x-lite 241qbxl
being jurked down the road by the beast 2007 Dodge ram 2500
5.9 cummins g56 Trans southbend clutch and a smarty
|
|
|
07-11-2018, 03:52 PM
|
#8
|
Site Team
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
|
Railroaderone is correct. If it's in conduit and secured it complies with the NEC.
I prefer rigid metal conduit to PVC It's a little harder to work with, but provides more protection against abuse. Especially since you're running on top of concrete.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
|
|
|
07-11-2018, 03:59 PM
|
#9
|
Site Team
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,933
|
Whoever does install the 30 amp outlet, make absolute sure they know it's 120 volts only. We keep a printable pdf file at this link that you can print out and hand to anyone who installs the 30 amp outlet.
http://www.forestriverforums.com/for...let-27223.html
We've had professionals and amateurs miswire these outlets for 240 volts and really damage RV's.
__________________
2011 Flagstaff 831 RLBSS
A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
|
|
|
07-11-2018, 07:38 PM
|
#10
|
Senior Member
Join Date: Dec 2015
Location: Iowa
Posts: 266
|
I'll be doing the work myself. I just ran a new 100a service to the garage last year, so I have plenty of room in the panel. Wiring it is not an issue. Mostly, I just wanted to get my ducks in a row. I can certainly ask the building dept. when I'm there pulling the permit but I'm not going to make it down there until the day I do the work. I need to have materials bought and prepared beforehand. Some of it will need to be ordered. If I lay the conduit over the cement, I'll be using galvanized. If I bury it, I prefer pvc, and I'll need more wire.
If this was a job I was doing at work, I wouldn't think twice about running it right over the cement. But industrial electrical and residential are in two different worlds. Residential requirements are far more strict, and we don't pull permits or have any thing inspected. It's not necessary.
__________________
021 Ram Rebel 1500
2017 Shamrock 233s
Waterloo, Iowa
|
|
|
07-12-2018, 12:52 PM
|
#11
|
Senior Member
Join Date: Jun 2015
Location: Valencia Pa
Posts: 602
|
Get an electrician.
|
|
|
07-12-2018, 02:19 PM
|
#12
|
Junior Member
Join Date: Apr 2017
Posts: 2
|
IF you can access the National Electric code, Article 551.80 (B) This explains the feeders to the pedestal must be protected from physical damage.
you can log onto NFPA.org and get free access to NFPA 70 (the electrical code).
Good Luck
|
|
|
07-12-2018, 02:50 PM
|
#13
|
Senior Member
Join Date: Jun 2012
Location: Southern NM
Posts: 9,561
|
Quote:
Originally Posted by inspecelec
IF you can access the National Electric code, Article 551.80 (B) This explains the feeders to the pedestal must be protected from physical damage.
you can log onto NFPA.org and get free access to NFPA 70 (the electrical code).
Good Luck
|
That's all good, but doesn't address any local requirements that usually go beyond NEC.
__________________
Scott and Liz - Southern NM
2012 Wildcat Sterling 32RL - w/level up (best option ever)
2007 Chevy 2500HD Duramax
Reese Fifth Airborne Sidewinder
|
|
|
07-12-2018, 04:01 PM
|
#14
|
Senior Member
Join Date: Apr 2016
Location: Cedar Creek Lake, TX
Posts: 3,484
|
Be aware that if you are required to pull a permit they often require a physical inspection before you can backfill the trench. I would call code enforcement with your questions. Some require the work be performed or certified by a licensed electrician.
__________________
Cedar Creek Lake, Texas
2019 Keystone Loredo 290SRL
2019 Ram 2500 4x4 Cummins crew cab
Andersen hitch
|
|
|
07-12-2018, 04:08 PM
|
#15
|
Senior Member
Join Date: Jul 2017
Location: North of Seattle, WA
Posts: 17,334
|
Quote:
Originally Posted by CedarCreekWoody
Be aware that if you are required to pull a permit they often require a physical inspection before you can backfill the trench. I would call code enforcement with your questions. Some require the work be performed or certified by a licensed electrician.
|
Around here a homeowner can do his own work, they just have to pull a "Safe Wiring" permit.
Have to do it yourself, can't have "Cousin Bob" or "Nate the Neighbor" do it.
The work get's inspected.
That said I'd wager that only 10% of the work like this done in my County gets either a permit or inspected.
__________________
"A wise man can change his mind. A fool never will." (Japanese Proverb)
"You only grow old when you run out of new things to do"
2018 Flagstaff Micro Lite 25BDS
2023 f-150 SCREW XLT 3.5 Ecoboost (The result of a $68,000 oil change )
|
|
|
07-12-2018, 04:13 PM
|
#16
|
Senior Member
Join Date: Dec 2014
Location: Minnesota
Posts: 116
|
You may want to consider the "trip factor" for any surface mounted conduit.
|
|
|
07-13-2018, 12:53 AM
|
#17
|
Senior Member
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,584
|
Silly question: Have you thought about mounting a box on/in the garage wall, ABOVE the sliding gate? You might need a step stool to use it, but it would be a clean, easy install.
Larry
|
|
|
07-13-2018, 12:54 AM
|
#18
|
Senior Member
Join Date: Jul 2018
Location: Long Island, NY
Posts: 603
|
To me it looks like you want to run it where it could possibly be considered a walkway, so that could be an issue, maybe a building code more than an electric code issue. The other issue is that, despite it being in conduit, it could still be considered susceptible to damage, if it is out in the open and could be run over by a vehicle, for instance. If it was running along a fence it might be a different story. I'd be interested to see what you find and to see the finished project.
__________________
Travel Trailer: 2004 Flagstaff 25LB
New Tow Vehicle: 2017 F-150 3.5 Ecoboost, supercrew short bed FX4 Lariat
Old Tow Vehicle: 2009 Silverado 2500HD 4x4 Ext. Cab Short Bed
Travel Pooch:Sophie the Sato - Cats: Rhody and Hazy
2018:22nights / 2019:31Nights / 2020:18Nights
|
|
|
07-13-2018, 08:47 AM
|
#19
|
Senior Member
Join Date: Jul 2017
Location: Suffolk, Va.
Posts: 1,413
|
I would bury it and put the pedestal near the plug on the RV. I hate wires laying on the ground.
__________________
Michael & Fran Dilday (Baxter & Honey 2 Labs)
'18 Cedar Creek Champagne 38EL - '17 Ford F350 Lariat DRW w/Reese hitch - TST 507 Color TPMS - Garmin RV 770 LMT GPS
|
|
|
07-13-2018, 08:59 AM
|
#20
|
Senior Member
Join Date: Jun 2013
Posts: 10,833
|
Quote:
Originally Posted by NMWildcat
Here is my take on these kind of questions: if you are really worried about code, then all your questions can be answered by the local government agency where you drew your permit.
If you are doing it yourself without a permit, and asking these kind of questions, you should rethink and perhaps hire a local licensed contractor to do the work correctly the first time.
|
This post wins the thread! Asking people on the internet electrical code is not very smart!
__________________
B and B
2022 Venture RV SportTrek STT 302 VRB Travel Trailer
2018 Heartland Landmark 365 Louisville 5th Wheel
2015 Heartland Bighorn 5th Wheel
2013 FR Rockwood 8289WS 5th Wheel
2012 FR Rockwood 2703 SS Travel Trailer
|
|
|
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|