Fireplace heater trippin’ !?

So I’m plugged into 50A at campsite. When I turn on the electric fireplace, it runs for about 10-15min roughly and then it shuts itself off. But by ‘shutting itself off’ I mean it trips the breaker.

What gives?

This has happened now multiple times at multiple different camp sites. I’m always hooked up to 50A so this shouldn’t be an issue.
__________________
2019 34QS with no ladder!
Eagle5 is offline   Reply With Quote
Old 03-05-2019, 08:00 AM   #2
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
I'm not sure how they have it wired either a home run or if it is like mine it is tied in with the electric water heater, it transfer power by a relay, so when the water heater turns on it will turn off the fireplace. The water heater takes top priority. Now if you have it on a home run, it could be a couple simple things, first a loose wire at the breaker which will cause heat and trip the breaker, or it could just be a bad breaker, they do go bad..
Hope that helps you a little, a third thing could be pulling to many amps I would guess it's on a 15 amp breaker, you would need a amp probe to measure that draw.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 03-05-2019, 08:58 AM   #3
Senior Member
 
Join Date: Jan 2017
Posts: 3,290
...'which' breaker are you referring to?

- campground pedestal 50amp breaker?
- your own main panel's 50amp breaker?
- the main panel's individual breaker for the fireplace?
formerFR is offline   Reply With Quote
Old 03-05-2019, 09:10 AM   #4
Senior Member
 
Join Date: Jan 2017
Posts: 3,290
...this topic comes up quite often on these forums, as the confusion is generally one of 'why' does the fireplace not provide heat as long as it is switched ON.

The consensus is that a Fireplace is a secondary 'heat' source, maybe more for ambiance versus true coach heating, like the furnace. The factories therefore 'share' the fireplace with another 'heat' or large draw item, usually either the microwave or the water heater, since there is generally not enough 'room' in the main panel for another separate and individual breaker for just the fireplace.
Because these two 'large amperage' appliances can't operate at the same time on this single breaker, there will be a relay inline that turns it off while the other appliance is operating, keeping the breaker from tripping.

Annoying? yes, I would be too, but I suppose that once you realize what's going on, it makes more sense. If it's shared with the microwave, then it's probably easier to realize when it's happening, but when it's shared with the Electric Water Heater element, it's only effected with the water heater element turns on to reheat the water... but that's not something you readily 'see' happening, which makes it feel as though the fireplace is just 'shutting off' for no reason.

Some older rigs with this same configuration actually used a separate switch, a manual switch, that the owner would need to switch ON to use the fireplace, or second roof air conditioner, and switch OFF in order to use the microwave. The current-day internal relay basically does this 'for' the owner, but it can be a little confusing, at first.


This may not be your issue, as you could also have a loose wire at your fireplace breaker, making the wire 'arc' when it heats up, causing the breaker to trip.
Or, you could have a loose wire at your main 50amp breaker, or even the campground breaker, which amounts to the same problem.
formerFR is offline   Reply With Quote
Old 03-05-2019, 09:26 AM   #5
Senior Member
 
Join Date: Jan 2017
Posts: 3,290
...I'll also add another explanation of your Main electrical panel, at least for us with 50amp double-pole breaker (100 amps total) RV service...

Since the total service is actually 100amps of usable power from your rig, the two 50amp breaker are tied together with a common trip handle. Your main panel's 50amp breakers are designed exactly like the campground's 50amp breakers - exactly the same.

Because you actually are using two 120v lines coming into your coach, your Main panel splits this to serve two SIDES of your coach. Usually your main panel will have the 50amp breakers in the middle, with individual breakers on both the left and right sides. (some of us have a more custom breaker panel, with the 50amp main breakers at the left side, but that is because it is designed more like a home's breaker panel, only horizontally configured, versus vertical, and we have a built-in Inverter sub-panel, generally the breaker to the far right)

Since you have two SIDES, each with 50amps of available power, but a common trip handle between them, either side can trip the whole panel if it exceeds 50amps. The factory then tries to divide the typical power 'usage' equally on each 'side', generally having one roof air conditioner on the left side, and the other on the right. Also, the Battery Charger might be on the left, with the Water Heater on the right, etc., etc., so that each 'side' has somewhat of equal usage while items are being used at the same time.

Now, rigs with the additional FIREPLACE heater have to be concerned with this in the electrical wiring scheme. If the fireplace was on it's own separate breaker, the 'balance' between the two 50amp sides might tip too far, in favor of one side, possibly causing nuisance tripping of the individual breaker, or even the 50amp double-pole main breaker for the whole coach... the factory therefore 'shares' this appliance with another device, on the same breaker, but installing an inline relay so that neither can work at the same time.


FUN, ain't it!
__________________
The Turners...
'07 Rockwood Signature Ultralight...
two Campers and two Electric cars : )
formerFR is offline   Reply With Quote
Old 03-05-2019, 10:20 AM   #6
Senior Member
 
Eagle5's Avatar
 
Join Date: Sep 2018
Location: Myersville Maryland
Posts: 146
Fireplace heater trippin’ !?

Quote:
Originally Posted by formerFR View Post
...'which' breaker are you referring to?

- campground pedestal 50amp breaker?
- your own main panel's 50amp breaker?
- the main panel's individual breaker for the fireplace?


The 15A breaker that tripped is the one at the foot of the bed. I’d call that the main breaker box. The 15A breaker is labeled ‘fireplace’ and nothing else.


I don’t know if it’s wired as a dedicated circuit or not. Seems that the people that built this coach don’t know anything about it.


I try to think to myself what else the coach was doing at the time this happened. Since this has happened multiple times, I don’t remember the previous ones but this morning the only thing running at the time was ONE of the heat pumps on roof. That’s it. And the fireplace ran for about 10-15min tops then just cut out.

I don’t remember if the previous times it tripped if I had any Heat pumps going at the same time or other electrical suck items. I don’t think that should matter though. [emoji2955]
__________________
2019 34QS with no ladder!
Eagle5 is offline   Reply With Quote
Old 03-05-2019, 10:25 AM   #7
Senior Member
 
Join Date: Jan 2017
Posts: 3,290
I wouldn't necessarily reason that just because it only is labeled as 'fireplace' that it is the only thing on that circuit - you might also have a TV, or something else plugged into the same outlet, or the same circuit...

a tripped breaker is a result of too much heat within a wiring line that prompts the breaker to trip, a safety feature. If tripping is occurring, then the fireplace, with the heat ON I assume, is drawing too many amps for that circuit breaker, or other things are also being powered at the same time on that circuit.

Do you also have an individual breaker for the Microwave? and the Elec Water Heater?

(edit: also, trip your main breakers, pull the front panel of the electrical box,
and remove the 15a 'fireplace' breaker and check the tightness/connection of the outgoing wire - these are known to easily come 'untight' after a little usage from the factory)

it's a fun diagnosis, and annoying, but when you find the answer, it will become clear!
__________________
The Turners...
'07 Rockwood Signature Ultralight...
two Campers and two Electric cars : )
formerFR is offline   Reply With Quote
Old 03-05-2019, 10:30 AM   #8
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
An electric resistance heater that trips the breaker after running a few minutes is usually from the element heating up and sagging or warping a little, and touching the enclosure. That creates a short and trips the breaker.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is online now   Reply With Quote
Old 03-05-2019, 10:33 AM   #9
Senior Member
 
Eagle5's Avatar
 
Join Date: Sep 2018
Location: Myersville Maryland
Posts: 146
Quote:
Originally Posted by formerFR View Post

Do you also have an individual breaker for the Microwave? and the Elec Water Heater?

Here’s a pic of the breakers. And my water heater is the truma tankless which I believe is only fired by propane and has really no electricity usage to speak of. It clearly has an on/off switch and a little green ‘on’ light but it doesn’t use electricity to heat water

Click image for larger version

Name:	IMG_3888.jpg
Views:	119
Size:	414.8 KB
ID:	198140
__________________
2019 34QS with no ladder!
Eagle5 is offline   Reply With Quote
Old 03-05-2019, 11:16 AM   #10
Senior Member
 
Join Date: Jan 2017
Posts: 3,290
sounds like a loose wire at the breaker, then....
formerFR is offline   Reply With Quote
Old 03-05-2019, 11:47 AM   #11
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
I still think it is a loose wire at the breaker or a bad breaker, but think of mine, I don't know what FP you have but if it keeps doing it after 10 or 15 mins, it seems to be consistent did you check the timer on the FP. But even that wouldn't explane the tripping, we keep going back to that, that's where I would start, a new 12.00 breaker and a screw driver....
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 03-05-2019, 01:38 PM   #12
Senior Member
 
dan-nickie's Avatar
 
Join Date: Feb 2014
Location: Dallas TX
Posts: 1,675
Man I would also check for a loose wire at the breaker.

In the Berkshire, the fireplace is typically on its own Breaker.
__________________
Dan
2014 Berkshire 390RB-60
dan-nickie is offline   Reply With Quote
Old 03-05-2019, 03:02 PM   #13
Senior Member
 
Join Date: Dec 2015
Posts: 294
Quote:
Originally Posted by Eagle5 View Post
So I’m plugged into 50A at campsite. When I turn on the electric fireplace, it runs for about 10-15min roughly and then it shuts itself off. But by ‘shutting itself off’ I mean it trips the breaker.

What gives?

This has happened now multiple times at multiple different camp sites. I’m always hooked up to 50A so this shouldn’t be an issue.

When you do check that breaker, trace that cable and make sure all

the other wires (black,white and bare copper) are tight both at the breaker box and at the fireplace.



DonB
AFDON is offline   Reply With Quote
Old 03-05-2019, 04:35 PM   #14
Senior Member
 
Join Date: Apr 2016
Location: Cedar Creek Lake, TX
Posts: 3,484
It could be as simple as a weak breaker. Do you have an amp probe to check the actual amp draw on this circuit?
__________________
Cedar Creek Lake, Texas
2019 Keystone Loredo 290SRL
2019 Ram 2500 4x4 Cummins crew cab
Andersen hitch
CedarCreekWoody is offline   Reply With Quote
Old 03-05-2019, 10:01 PM   #15
Senior Member
 
Eagle5's Avatar
 
Join Date: Sep 2018
Location: Myersville Maryland
Posts: 146
Quote:
Originally Posted by dan-nickie View Post
Man I would also check for a loose wire at the breaker.

In the Berkshire, the fireplace is typically on its own Breaker.


So you guys know which brand/type breakers these take? Wasn’t sure if it’s a special brand or I could just snag one at Lowe’s? I figured I’d get a new breaker before I pull the existing one and check the wire.
__________________
2019 34QS with no ladder!
Eagle5 is offline   Reply With Quote
Old 03-05-2019, 11:57 PM   #16
Dragonship Captain
 
Oscarvan's Avatar
 
Join Date: Oct 2016
Location: Eastern PA, USA
Posts: 1,335
Quote:
Originally Posted by Bama Rambler View Post
An electric resistance heater that trips the breaker after running a few minutes is usually from the element heating up and sagging or warping a little, and touching the enclosure. That creates a short and trips the breaker.
This is good info.

On the Berkshires (this is a Berkshire page) the fireplace is on a dedicated circuit. There is nothing else on there.

So, based on those two piece of information I suggest that you:

1 Slide up and remove the bezel.
2 Remove the 4 screws and pull out the fireplace. It's one piece and will stand on it's own.
3 you will see that it has a regular cord and is plugged into a single outlet. Unplug it and take it outside to the pedestal. Now plug it into the pedestal 20A outlet directly and see what happens.
4 If it works just fine you have a bad breaker
5 If it trips the pedestal breaker the fireplace is bad.
__________________
2020 RAM 3500 DRW Long Horn. In the hunt for a Palomino TC, formerly a 2017 Berkshire 38A: https://dragonship.blog/
Oscarvan is offline   Reply With Quote
Old 03-06-2019, 09:59 AM   #17
Senior Member
 
Join Date: May 2014
Location: Halifax Nova Scotia Canada
Posts: 833
Inside the fireplace there is a temp breaker that will open if the temp gets too high...safety feature....Could also trip main breaker!!!
Jim in Halifax is offline   Reply With Quote
Old 03-06-2019, 07:44 PM   #18
Senior Member
 
Eagle5's Avatar
 
Join Date: Sep 2018
Location: Myersville Maryland
Posts: 146
Thanks for all the help and info guys. I called the company that reps for the GreyStone fireplace. They are called WAY INTERGLOBAL and they’re in Elkhart IN. Phone is *574-971-4490‬. That’s who you call for parts, warranty, etc.

They said my model has had some issues with circuit boards and that “could” be the problem. They are on backorder right now because of this. She said they are about 30days out. So she’s gonna send me one when they arrive. If it doesn’t solve the problem, they will send me a replacement unit.

Sounds way more likely than the breaker or anything else. We shall see. I’ll report back. But at least anyone with this similar issue can find this thread and the company’s contact info.
__________________
2019 34QS with no ladder!
Eagle5 is offline   Reply With Quote
Old 03-06-2019, 09:43 PM   #19
Dragonship Captain
 
Oscarvan's Avatar
 
Join Date: Oct 2016
Location: Eastern PA, USA
Posts: 1,335
I would still rule out the breaker by plugging it into another outlet. (it's free.... )
__________________
2020 RAM 3500 DRW Long Horn. In the hunt for a Palomino TC, formerly a 2017 Berkshire 38A: https://dragonship.blog/
Oscarvan is offline   Reply With Quote
Old 03-06-2019, 10:15 PM   #20
Just as confused as you
 
Scrapper's Avatar
 
Join Date: Aug 2013
Location: south central Wisconsin
Posts: 5,108
I have a Greystone fireplace in my TT and it will run for 10 to 30 minutes then shut off. It seems that the grill deflects the warm air from the fan towards the thermostat bulb. If I leave the top grill open it will run for hours.
__________________
Richard & Jill
2014 Flagstaff 832IKBS Classic Super Lite
2018 Silverado 1500 Crew Cab Z71 4WD All Star Edition
Camping since 1989, Seasonal since 2000.
Car Shredder Op/Tech, Scrap Metal Recycling - retired
Scrapper is offline   Reply With Quote
Reply

Tags
fireplace, heater


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 12:43 PM.