Just got back from a trip this morning during which we camped in 40 deg nights. Started the front furnace in my 390RB and noticed it lights and runs for about 90 sec and then apparently hits a limit, shuts down the burner but the fan continues to run. The burner stays off for about 3 minutes, relights and repeats the cycle. As a result it never reaches the requested temperature and just continues to run in this manner. This furnace has some rather small ducts under the loveseat so I'm wondering if the ducting is restricting flow or if I have a bad limit switch?

Anyone else have this happening?
__________________

__________________
edgewant

2013 Berkshire 390RB-60
toad - 2002 Jeep Wrangler Sport
edgewant is offline   Reply With Quote
Old 04-03-2016, 07:57 PM   #2
Senior Member
 
15berkxl's Avatar
 
Join Date: Mar 2015
Location: Mishawaka
Posts: 576
I had a similar situation with my other MH I first checked to make sure the inlet is clear. I changed the limit with a new one and that should be your first act if the inlet is clear since it is also the less expensive. You can also check ductwork for restrictions but unless you have critters making a nest in them I would doubt the ducting is causing the cycling. When I called the manufacturer they told me the fan motor will slow down with time so if the new limit does not correct it them check the fan blower and clean it if it's dirty if it's not replace the motor.


Wayne
__________________

__________________
Wayne
15berkxl is offline   Reply With Quote
Old 04-04-2016, 08:24 AM   #3
Go Seahawks!
 
Subsailor's Avatar
 
Join Date: Nov 2015
Location: Pacific Northwest
Posts: 233
Edge, I haven't had the issue (yet), but please keep us posted about what you find. You and I have the same coach and I am interested in how it works out. Good luck and I hope it is an easy fix. -Glenn
__________________
Glenn and Darcy
2013 Berkshire 390RB
2013 Jeep Wrangler (toad)
Pacific Northwest
Subsailor is offline   Reply With Quote
Old 04-06-2016, 08:07 PM   #4
Senior Member
 
edgewant's Avatar
 
Join Date: Feb 2013
Location: Tennessee
Posts: 456
Tried the furnace with the two 4 in ducts disconnected from outlet vents. Cycle time improved from 90 sec on to150 sec on. So added another outlet vent, reconnected ducts and cycle time stayed at 150 sec on. Replaced limit switch, no change in time on. Blower seems to working fine but is probably the culprit. Also suspect propane regulator.


Sent from my iPhone using Forest River Forums

2013 Berkshire 390RB-60
Toad: 2002 Jeep Wrangler
__________________
edgewant

2013 Berkshire 390RB-60
toad - 2002 Jeep Wrangler Sport
edgewant is offline   Reply With Quote
Old 04-06-2016, 08:28 PM   #5
Senior Member
 
15berkxl's Avatar
 
Join Date: Mar 2015
Location: Mishawaka
Posts: 576
As a test when mine acted up I bypassed the limit temporarily to test it everything worked fine and put out heat. When I removed the bypass went back to its old ways.


Wayne
__________________
Wayne
15berkxl is offline   Reply With Quote
Old 04-06-2016, 10:47 PM   #6
Senior Member
 
edgewant's Avatar
 
Join Date: Feb 2013
Location: Tennessee
Posts: 456
Well I do think somebody at Forest River screwed up on the duct arrangement on the front furnace. They took two 4 in ducts and placed a flow splitter on each to split the flow into two 2 in ducts (for a total of four). That's a drop from 25.4 sq in of flow to 12.5 sq in. Talk about a flow restriction. I removed those splitters and added a plenum that supplys the four two in ducts under the loveseat and another standard 10" x 2" floor register that discharges beside the loveseat. That gets the flow area up to about 32 sq in which meets the Suburban recommended minimum of 25 sq in.

Even with those changes and a new limit switch my run time is only about 150 sec before it cycles.

I have also noticed that the flex ducts that deliver the heat on the front furnace have about 18 in of excess that can be removed thereby eliminating several kinks and bends. I'll shorten those in the near future.

Measured the brass elbow that enters the heat exchanger chamber (its the propane supply) with an infrared thermometer since there is significant airflow leakage at the elbow. The front furnace runs about 20 deg F hotter than the rear (same model furnace). So the blower is suspect. I may try measuring the current draw on the front and rear to see if that indicates a weak blower before I start removing the furnace and searching for the best price on a new blower.
__________________
edgewant

2013 Berkshire 390RB-60
toad - 2002 Jeep Wrangler Sport
edgewant is offline   Reply With Quote
Old 04-07-2016, 06:58 AM   #7
Senior Member
 
15berkxl's Avatar
 
Join Date: Mar 2015
Location: Mishawaka
Posts: 576
Quote:
Originally Posted by edgewant View Post
Well I do think somebody at Forest River screwed up on the duct arrangement on the front furnace. They took two 4 in ducts and placed a flow splitter on each to split the flow into two 2 in ducts (for a total of four). That's a drop from 25.4 sq in of flow to 12.5 sq in. Talk about a flow restriction. I removed those splitters and added a plenum that supplys the four two in ducts under the loveseat and another standard 10" x 2" floor register that discharges beside the loveseat. That gets the flow area up to about 32 sq in which meets the Suburban recommended minimum of 25 sq in.

Even with those changes and a new limit switch my run time is only about 150 sec before it cycles.

I have also noticed that the flex ducts that deliver the heat on the front furnace have about 18 in of excess that can be removed thereby eliminating several kinks and bends. I'll shorten those in the near future.

Measured the brass elbow that enters the heat exchanger chamber (its the propane supply) with an infrared thermometer since there is significant airflow leakage at the elbow. The front furnace runs about 20 deg F hotter than the rear (same model furnace). So the blower is suspect. I may try measuring the current draw on the front and rear to see if that indicates a weak blower before I start removing the furnace and searching for the best price on a new blower.

Sounds like you have a good action plan. I had similar concerns about my previous non FR unit as they had run more duct length then needed but when unit was new it ran great and did not cycle like it did when it got older so did that issue really matter? Did yours ever work okay or has it always cycled?


Wayne
__________________
Wayne
15berkxl is offline   Reply With Quote
Old 04-07-2016, 07:38 AM   #8
Senior Member
 
CAT-RN's Avatar
 
Join Date: Jul 2014
Posts: 6,144
Well my duct work on my front furnace was similar. They ran two 4" from the furnace then sized each into two 2". So now you have four 2". Then it really gets crazy. They attach all four 2" to a board directly under the L-sofa.

All four dump out together and can go nowhere!! Just under the sofa. TRAPPED there. Originally I would raise the sofa bottom up a couple inches and let some heat out.

Then I did away with the L-sofa and the 2" heat runs. Went to two 4" heat runs and installed them under a six inch cabinet on each end of the new couch I put in.

The new set up heats the front of the coach great now.

Russell
__________________
CAT-RN is offline   Reply With Quote
Old 06-22-2016, 10:34 AM   #9
Senior Member
 
edgewant's Avatar
 
Join Date: Feb 2013
Location: Tennessee
Posts: 456
Solved my problem. Changed motor and no improvement.

Added a third supply duct that discharges in the corner of the return. Doesn't really comply with Suburban recommendations but it works great. Furnace now operates until set point is reached. The added supply discharges plenty of air and doesn't interfere with return air.
__________________

__________________
edgewant

2013 Berkshire 390RB-60
toad - 2002 Jeep Wrangler Sport
edgewant is offline   Reply With Quote
Reply

Tags
furnace

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 11:22 PM.