Old 05-02-2014, 06:39 PM   #1
Senior Member
 
Join Date: Nov 2012
Location: Home is where I park it
Posts: 1,503
Thermostat Gremlins

This morning I switched on my heat pump. It came on, but after a few minutes it automatically cut out and the furnace cut in. It switched back and forth 2 or 3 times all by itself.

The display was flipping between HP and FURN about once per second.

Anyone else had this happen??

Boowho??
boowho is offline   Reply With Quote
Old 05-02-2014, 06:52 PM   #2
Senior Member
 
tmmar's Avatar
 
Join Date: Apr 2008
Location: Long Island (Nassau County), NY
Posts: 4,352
Bill,
I have not had this happen to me.
Did you try doing a reset on the thermostat? Here's the procedure.

Make sure the thermostat is in the OFF condition.
Simultaneously press and hold the MODE and ZONE buttons.
The LCD should display “IniT” and all available zones.
Release the MODE and ZONE buttons.
Press the ON/OFF button to exit system set up.
The furnace ON/OFF temperature differential should be set at this time.

Might want to give this a try.
Tom
__________________
Tom and Margaret
2014 Berkshire 390bh-60

tmmar is offline   Reply With Quote
Old 05-02-2014, 06:59 PM   #3
Senior Member
 
Join Date: Nov 2012
Location: Home is where I park it
Posts: 1,503
Quote:
Originally Posted by tmmar View Post
Bill,
I have not had this happen to me.
Did you try doing a reset on the thermostat? Here's the procedure.

Make sure the thermostat is in the OFF condition.
Simultaneously press and hold the MODE and ZONE buttons.
The LCD should display “IniT” and all available zones.
Release the MODE and ZONE buttons.
Press the ON/OFF button to exit system set up.
The furnace ON/OFF temperature differential should be set at this time.

Might want to give this a try.
Tom
Thanks Tom.... I WILL give it a try.

Boowho??
boowho is offline   Reply With Quote
Old 05-03-2014, 11:04 AM   #4
Senior Member
 
gasman94's Avatar
 
Join Date: Oct 2012
Location: Southwestern Mi
Posts: 1,242
Are you guys getting both a/c units to use the heat pump?

Rich
gasman94 is offline   Reply With Quote
Old 05-03-2014, 11:11 AM   #5
Senior Member
 
tmmar's Avatar
 
Join Date: Apr 2008
Location: Long Island (Nassau County), NY
Posts: 4,352
Rich,
Only one of my a/c's is a heat pump the other is a/c only.
Tom
__________________
Tom and Margaret
2014 Berkshire 390bh-60

tmmar is offline   Reply With Quote
Old 05-03-2014, 11:41 AM   #6
Senior Member
 
gasman94's Avatar
 
Join Date: Oct 2012
Location: Southwestern Mi
Posts: 1,242
Quote:
Originally Posted by tmmar View Post
Rich,
Only one of my a/c's is a heat pump the other is a/c only.
Tom



Thanks Tom. I thought that I read on a previous post some time ago that there was a way to turn on the heat pump to the a/c unit in the bedroom. Both units appear to be the same. They also told me at the factory that only one is operable.
gasman94 is offline   Reply With Quote
Old 05-03-2014, 02:19 PM   #7
Berkshire 390QS
 
NO3putt's Avatar
 
Join Date: Feb 2011
Location: Colorado
Posts: 1,489
Both of mine are ac and heat pump.
__________________
2011: 54 days, 2012: 218 days, 2013: 175 days, 2014: 196 days
2015: 188 days, 2016: 72 days, 2017: 185 days: 2018 182 days
2019: 156 days (2009 Berkshire, 390QS, and toad)
NO3putt is offline   Reply With Quote
Old 05-03-2014, 02:50 PM   #8
Senior Member
 
tmmar's Avatar
 
Join Date: Apr 2008
Location: Long Island (Nassau County), NY
Posts: 4,352
Rich,
If you remove the grill that holds the a/c filter, if you look around you can see the model number. If you look that model number up it you should be able to see if it has heat pump ability. If it does, you would need to go up on the roof and remove the shroud. There is an aluminum covered box on the passenger side. Remove the cover and you will see a circuit board. There is a series of dip switches on the board. You need to set to the dip switch marked 'heat pump' to the 'on' position to enable the heat pump. After that is done, you would need to reboot the thermostat as I described above to recognize the units new settings.
Good luck,
Tom
__________________
Tom and Margaret
2014 Berkshire 390bh-60

tmmar is offline   Reply With Quote
Old 05-03-2014, 04:03 PM   #9
Senior Member
 
gasman94's Avatar
 
Join Date: Oct 2012
Location: Southwestern Mi
Posts: 1,242
Thanks Tom. I also have a '14, so I probably have the same setup. I will check, however.
gasman94 is offline   Reply With Quote
Old 05-03-2014, 07:39 PM   #10
Senior Member
 
Todouble's Avatar
 
Join Date: Nov 2013
Posts: 849
How cold is it outside? Heat pumps are only good in these RV prob down to 35ish. It may work off an outdoor air temp sensor and below a set point auto switch to gas furnace. Just a thought. Or this could be the case and you have a faulty sensor thinking it's lower than it is and trying to switch to propane
Todouble is offline   Reply With Quote
Old 05-03-2014, 09:48 PM   #11
Senior Member
 
JTN8's Avatar
 
Join Date: May 2013
Location: Virginia
Posts: 619
My 14 has two 15k heat pumps but I special ordered it that way, with that being said, I've used them in temps in the low 30's to high 20's and they both continued to work.

Jason
JTN8 is offline   Reply With Quote
Old 05-03-2014, 10:46 PM   #12
Senior Member
 
Join Date: Nov 2012
Location: Home is where I park it
Posts: 1,503
Quote:
Originally Posted by Todouble View Post
How cold is it outside? Heat pumps are only good in these RV prob down to 35ish. It may work off an outdoor air temp sensor and below a set point auto switch to gas furnace. Just a thought. Or this could be the case and you have a faulty sensor thinking it's lower than it is and trying to switch to propane
You may be right..... I WAS in the coldest environment I've been in since buying the coach. I will have to study up though, I did not think the whole heating system (thermo, furnace, HP) was that "smart".

Boowho??
boowho is offline   Reply With Quote
Old 05-04-2014, 05:42 AM   #13
Senior Member
 
Todouble's Avatar
 
Join Date: Nov 2013
Posts: 849
The heat pumps really can't keep up by themselves when it's 30 degrees or below outside. At this point they start staging up the electric heat strips. You may or may not have that so in your case I'm thinking it switched over to propane. This is how my home system is and I really don't know if this is your setup, just sharing my thoughts. Goodluck
Todouble is offline   Reply With Quote
Old 05-04-2014, 08:53 AM   #14
Senior Member
 
tmmar's Avatar
 
Join Date: Apr 2008
Location: Long Island (Nassau County), NY
Posts: 4,352
When I have used the heat pump in temps below about 40 it would after a while freeze up (I think) and when that happened, they compressor would cycle off until it defrosted, and then cycle back on. The gas furnace never came on by itself. It only goes on when I switch the thermostat to furnace.
__________________
Tom and Margaret
2014 Berkshire 390bh-60

tmmar is offline   Reply With Quote
Old 05-04-2014, 09:39 AM   #15
2011 Berkshire 390BH
 
Superchief's Avatar
 
Join Date: Aug 2011
Location: Lancaster, NY
Posts: 1,063
Same experience as Tmmar. I have found anything below 44 degrees, the heat pump doesn't put out heat and laborers.
__________________
Craig



Finally completed all State visits in August 2011 with a trip to North Dakota.
Superchief is offline   Reply With Quote
Old 05-04-2014, 09:43 AM   #16
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Todouble is correct, when your condenser coil freezes and gets ice on it either you have a sensor on it or you have a board inside that will put it in defrost either every 30, 60 0r 90 minutes. If you do not have heat strips then it should bring on your propane furnace during the defrost cycle. The compressor will not shut off your reversing valve will switch the flow of freon to A/C but will shut off your condenser fan motor. That whats defrost the coil. I don't know what stat you have but if it has a emergency heat switch on it, that also will bring on your propane furnace. If it is working right you should see a puff of steam outside when it switches back and your Condenser fan comes back on in heat mode. Thats pretty much the basics on how they are supposed to operate. You will still feel cold air at the ceiling registers but the furnace should compensate that.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 05-04-2014, 12:03 PM   #17
Senior Member
 
tmmar's Avatar
 
Join Date: Apr 2008
Location: Long Island (Nassau County), NY
Posts: 4,352
gljurczyk,
The a/c's that are installed in our coaches do not have heat strips in them and the furnace does not come on during the defrost cycle. Also, the thermostat does not have an emergency heat switch. There is defrost sensor in the a/c that handles the defrosting when it ices up. This is my second Berkshire so I am very familiar with the operation of the a/c's.
__________________
Tom and Margaret
2014 Berkshire 390bh-60

tmmar is offline   Reply With Quote
Old 05-04-2014, 12:38 PM   #18
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Quote:
Originally Posted by tmmar View Post
gljurczyk,
The a/c's that are installed in our coaches do not have heat strips in them and the furnace does not come on during the defrost cycle. Also, the thermostat does not have an emergency heat switch. There is defrost sensor in the a/c that handles the defrosting when it ices up This is my second Berkshire so I am very familiar with the operation of the a/c's.
Didn't mean to ruin your day, I glad you know what the problem is then. I'm also sure you know how to trace the short. Have a nice day, hope you get it working.I was suggesting this to BOOWHO the OP, or by the way the compressor doesn't shut off during defrost mode.not quite sure what would defrost the Condenser coil if the the compressor shuts off and didn't reverse to cooling cycle as I stated. But I guess anything is possible.....
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 05-04-2014, 01:41 PM   #19
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Boowho, If I were you I would be asking why during defrost mode your unit is not switching over to LP Furnace during your defrost cycle as tmmar has said. If you read up on the RV forum they all have auto switch over. A different stat can do that once you go into defrost. The question is why FR sets up there MH this way. they also have lock outs that are settable to say that you might not be comfortable at 35 degrees outside compared to 40 degrees lock out. To me 35 degrees ambient air temp you will not get more then 60/ 65 degree air coming into the unit. To me that is a cold draft. Hope you get your problem fixed. But just think soon you will have all summer to work on your problem good luck and happy travels.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 10-03-2014, 02:06 PM   #20
Junior Member
 
Join Date: Oct 2014
Posts: 1
Exclamation furnace and a/c mix up?? Please help before winter cold comes!

The overhead fans in my trailer continue to blow cold air after the lower ones have stopped blowing hot air. The thermostat is set to furnace at 60 degrees.
The trailer is almost a year old and this phenomenon started in September when I turned the temperature up to 60 expecting the system to kick on and heat the place up and then stop after the temperature had been reached.

Any ideas where to begin looking for what's wrong? Is there a sensor somewhere I need to clean?
dalgal2014 is offline   Reply With Quote
Reply

Tags
thermostat


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 10:09 PM.