12v Inverter in Battery Compartment

Looking to install my new Projecta INTELLI-WAVE INVERTER(12V) IP600 model(600watts output) with remote meter in my new Coachmen Apex 22QBS.
I am looking for places to install but limited inside the TT/Caravan, one place i want to install is in the rear carrier box which is aluminium but installed in here is the house battery, it says not to install the inverter in the same compartment as the batteries as the gasses from the house batteries could ignite, if I fitted fully sealed RV deep cycle batteries then there would be no gasses to ignite, this sounds quite safe to me what do you think chaps.
savi18 is offline   Reply With Quote
Old 03-11-2015, 07:19 PM   #2
Senior Member
 
Join Date: Feb 2015
Posts: 105
Are you an Electrical Engineer ?
Do you want to go BOOM ?
If the answer to both is NO then I would do what the directions / warnings say.
Is it worth the risk?
Bamamax is offline   Reply With Quote
Old 03-11-2015, 08:17 PM   #3
Member
 
jaibyrd's Avatar
 
Join Date: Feb 2015
Location: NH
Posts: 84
Not worth the risk. Should anything happen, you may have issues on an insurance claim due to the decision to install in a space the MFG clearly said not to.
__________________
Snyder Family - Pelham, NH
2015 Sunseeker 3170DS
jaibyrd is offline   Reply With Quote
Old 03-11-2015, 08:41 PM   #4
Senior Member
 
Join Date: Jul 2013
Posts: 240
As I understand it, sealed batteries can release hydrogen. Normally, gases are retained within the battery. If the pressure exceeds a certain level, it will open a pressure release valve and hydrogen will escape.

I'm not an electrical engineer. My comment is based upon research I've done in trying to decide where to install an inverter in my Lexington 235.
00buck is online now   Reply With Quote
Old 03-11-2015, 09:13 PM   #5
Senior Member
 
Join Date: Dec 2012
Posts: 1,255
If you are talking about AGM's then you shouldn't have a problem as long as you allow for adequate air spaces. Even in the rare chance that an AGM will off-gas it is such a miniscule amount and quickly dissipates. Adding a 1/2" air exchange hole near the top of the compartment.. or several smaller holes, it shouldn't be a problem.

My setup is not at all uncommon. My batteries are stored in the underbed storage area.. along with my solar controller and inverter/charger. To be 'safe', you might want to try and install your inverter as low as possible (Hydrogen rises).
rana is offline   Reply With Quote
Old 03-11-2015, 09:44 PM   #6
Senior Member
 
Blackhat6mike's Avatar
 
Join Date: Dec 2014
Location: St Simons Island, GA
Posts: 1,234
IMHO, you need to rethink the size if your inverter as 600 watts won't power even your coffee pot. I tried 3,000 watts and even that was not enough. Went to 5,000 watts and I'm a happy camper.
I also installed a 12vdc muffin fan, like in a computer, to vent out the hydrogen gasses to the outside of the unit. Those gasses will corrode anything metal, not to mention your lungs. The fan also keeps the inverter cooled down.
Also, the inverter needs to be as close as possible to the batts with BIG cables. Lots of 12vdc amps to feed the inverter and your batts will not last long.
__________________
Aviator Wright Flyer #1919
Army Pathfinder Vietnam, 3 tours
DAV, MOPH, VFW, NRA, 1stCav. ABN
Blackhat6mike is offline   Reply With Quote
Old 03-11-2015, 10:54 PM   #7
Senior Member
 
GreenImp's Avatar
 
Join Date: Jul 2013
Location: Oregon
Posts: 716
Send a message via MSN to GreenImp
The user manual for my Xantrex ProSine 3.0 inverter states "Do not install the inverter/charger in the same compartment as vented (non-sealed) batteries or in any compartment capable of storing flammable liquids such as gasoline", leading me to believe that sealed batteries would be fine.

IMO, Simply venting the carrier box would be fine too (should have vents at the top AND near the bottom to allow air flow).

Another possible option that would be cheaper than new sealed batteries would be to install a sealed battery box within your carrier and vent it to the outside. Many if not most trailers are done at the factory this way.
__________________
'04 GMC Sierra 2500HD, CCSB, D/A, MaxBrake, B&W Companion, Retrax Pro, AR Power Steps
2021 Solitude 310GK w/FBP
1969 Camaro RS/SS Convertible
Dad's old 1968 Empi Imp (recently recovered from under 21 years worth of boxes/dust)
GreenImp is offline   Reply With Quote
Old 03-12-2015, 12:22 AM   #8
Member
 
Join Date: Jan 2015
Location: Mosgiel NZ
Posts: 81
Quote:
Originally Posted by 00buck View Post
As I understand it, sealed batteries can release hydrogen. Normally, gases are retained within the battery. If the pressure exceeds a certain level, it will open a pressure release valve and hydrogen will escape.

I'm not an electrical engineer. My comment is based upon research I've done in trying to decide where to install an inverter in my Lexington 235.
This is what I have researched,
Valve-Regulated Lead-Acid or VRLA, including AGM and Gel
(Absorbed Glass Mat) battery designs, can be substituted in
virtually any flooded lead-acid battery application (in conjunction
with well-regulated charging). Their unique features and
benefits deliver an ideal solution for many applications where
traditional flooded batteries would not deliver the best results
How it works
A VRLA battery utilizes a one-way, pressure-relief valve
system to achieve a “recombinant” technology. This means
that the oxygen normally produced on the positive plate is
absorbed by the negative plate. This suppresses the production
of hydrogen at the negative plate. Water (H
2O) is produced
instead, retaining the moisture within the battery.
It never
needs watering, and should never be opened
as this would
expose the battery to excess oxygen from the air. In addition to
damaging the battery, opening it also voids the warranty.
The difference between VRLA and traditional
flooded batteries
Flooded electrolyte batteries do not have special one-way,
pressure-relief valves, as they do not work on the recombination
principle. Instead, flooded designs utilize a vent to
allow gas to escape. They contain liquid electrolyte that can
spill and cause corrosion if tipped or punctured. They
should not be used near sensitive electronic equipment.
They can only be installed “upright.”
So what it says above is Flooding sealed batteries have a vent to
let the gases out but the VRLA don't so 100% sealed and no gases can escape, this is why these VRLA batteries can be installed upside down if needed, so this still makes me think I can install only the VRLA(GEL or AGM) batteries in my rear box but not flooded ones, does this change your views, Cheers

savi18 is offline   Reply With Quote
Old 03-12-2015, 05:58 AM   #9
CCRVOC
 
Ramblin Recks's Avatar
 
Join Date: Jan 2012
Location: Where ever we are parked
Posts: 516
Inverters come with lots of warnings. Besides of which you speak, mine also says not to mount on a combustible surface as the inverter gets too hot...
__________________
2012 Dodge 3500, SLT Big Horn,CC,DRW,Cummins HO, EB, 4x4, 3:73, Retrax Pro, Q20, TST507, Garmin RV760, Sleek 4g
2014 Cedar Creek, 36CKTS, 1000w Solar, TriStar MPPT 60, Magnum 2000w, PI EMS, WiFi Ranger Elite, Sleek 4g, Wingard DTV Traveler
Retired Army in 1995, and now retired in 2016
Ramblin Recks is offline   Reply With Quote
Old 03-12-2015, 07:39 AM   #10
Senior Member
 
mark0224's Avatar
 
Join Date: Oct 2013
Posts: 1,443
Good Info I have an 800 watt inverter I was planning on using in a similar manner for small electrical items during setup or for lighting for late day setup.
__________________
Think about things before you do them make life easier not harder.
mark0224 is offline   Reply With Quote
Old 03-12-2015, 07:24 PM   #11
Member
 
Join Date: May 2013
Posts: 30
Inverter fires are far too common

Speaking from first hand experience I can tell you that many "over the counter" inverters have been known to catch fire. Mine was turned on with a very light load and started to burn. Thank goodness we were in the coach at the time and put it out with a fire extinguisher. Morale of the story - Buy a good quality inverter with good ratings from other users.
Also note the cheaper inverters do not produce what is known as a "pure sine wave" so they may not power a phone charger or other electronics that need a pure sine wave power supply.
Do your research and you will save yourself a lot of potential grief.
GlennFC is offline   Reply With Quote
Old 03-12-2015, 11:07 PM   #12
Member
 
Join Date: Jan 2015
Location: Mosgiel NZ
Posts: 81
Quote:
Originally Posted by GlennFC View Post
Speaking from first hand experience I can tell you that many "over the counter" inverters have been known to catch fire. Mine was turned on with a very light load and started to burn. Thank goodness we were in the coach at the time and put it out with a fire extinguisher. Morale of the story - Buy a good quality inverter with good ratings from other users.
Also note the cheaper inverters do not produce what is known as a "pure sine wave" so they may not power a phone charger or other electronics that need a pure sine wave power supply.
Do your research and you will save yourself a lot of potential grief.
Your right in saying buy a well known Inverter, the one I bought is the Rolls Royce of Inverters, quite expensive but has excellent reviews I think they are made in Australia and definitely not made in China, this is the link if anyone wants to have a look http://www.projecta.com.au/Products/Inverters.aspx

I did buy a Chinese Inverter 4 years ago 2000 watt, lasted 1 month and stopped working did not get a refund, so as you say the way to go is look at review's like I did and you will sleep well at night,
savi18 is offline   Reply With Quote
Old 03-13-2015, 10:31 AM   #13
Left Coast
 
Join Date: Dec 2014
Location: vancouver,washington
Posts: 15,649
Send a message via Yahoo to bob caldwell
could there be a problem with a 50 herz. output?
bob caldwell is offline   Reply With Quote
Old 03-13-2015, 10:53 AM   #14
Junior Member
 
Join Date: May 2012
Location: Texas
Posts: 19
Inverter

My new 2015 Cedar Creek Silverback inverter from the factory is installed above the two batteries in the battery compartment,Hmm what to do?
ktex is offline   Reply With Quote
Old 03-13-2015, 01:01 PM   #15
Member
 
Join Date: Jan 2015
Location: Mosgiel NZ
Posts: 81
Quote:
Originally Posted by bob caldwell View Post
could there be a problem with a 50 herz. output?
Over here in New Zealand and Australia the power supply runs at 50Mhz,(230/240v not sure what the States are is it 60Mhz??
Also I think the UK is 50Mhz as well.
savi18 is offline   Reply With Quote
Old 03-13-2015, 04:19 PM   #16
Left Coast
 
Join Date: Dec 2014
Location: vancouver,washington
Posts: 15,649
Send a message via Yahoo to bob caldwell
sorry, i just looked at your 1st post and you are on the 50 side of the world. it's 60 in US.
bob caldwell is offline   Reply With Quote
Reply

Tags
battery, inverter

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 07:45 AM.