A Technical HVAC Question

With any ducted forced air system; residential, commercial, RV, etc., why is it that when you close registers to try to gain more CFM from other registers left open, you are never able to get all of that air that you just stopped moving to come out of the registers you left open? But, if you have a damper close to the air handler/fan and you close it to stop flow to those same registers, most of that air is directed to the open registers. I know there are scientific reasons because when I was a teenager, I worked as a helper for a relative’s air balancing company, but I didn’t learn or retain much of this information. I know it has a little to do with air loss from joints, but I think it is mainly due to something related to static pressure. When we were balancing a building’s system, the main things I remember about getting the right amount of air to the right places was adjusting the fan speed by adjusting belt pulleys, then adjusting dampers. Only fine-tuning was done at the registers once the correct CFM was obtained for each branch or VAV box.

If I was to close every register in my RV except for one or two, I notice very little difference in air flow at the registers I have left open. Why is this? Why is a closed damper (I wish RVs had these), close to the air source more effective at redirecting air than just closing registers?

Bruce
__________________
2016 Rockwood Windjammer 3029W Diamond Edition
2015 Chevy 3500HD LTZ 6.0 Crew Cab 4x4 Long Bed 4.10:1 SRW
nomad297 is offline   Reply With Quote
Old 08-08-2019, 06:42 AM   #2
Site Team
 
KyDan's Avatar
 
Join Date: Mar 2008
Location: Louisville, KY
Posts: 10,525
My guess is the outlets you are leaving open are somewhat choked to begin with.
Far down the line, outlet not completely lined up with the trunk line that's molded into the styrofoam in the ceiling?
Also might have leakage elsewhere so the air is taking the path of least resistance.

I know my ceiling unit has mediocre flow in the bedroom ceiling but if I open the vents on the ceiling unit itself it will literally blow your hair around if you stand under it.
__________________
Peace!
Dan & Rita D
2017 Nissan Titan 5.6L King cab 4wd
2016 Evergreen Everlite 242RBS
29' empty nest model. Blue Ox WD hitch
(1 queen bed, large main cabin and huge bathroom)
Camping days 2010-53, 2011-47, 2012-41, 2013-41, 2014-31, 2015-40, 2016-44, 2017-63, 2018-75, 2019-32, 2020-41, 2021-49, 2022-43, 2023-66
KyDan is offline   Reply With Quote
Old 08-08-2019, 06:48 AM   #3
Senior Member
 
nomad297's Avatar
 
Join Date: Jul 2015
Posts: 7,053
Quote:
Originally Posted by KyDan View Post
My guess is the outlets you are leaving open are somewhat choked to begin with.
Far down the line, outlet not completely lined up with the trunk line that's molded into the styrofoam in the ceiling?
Also might have leakage elsewhere so the air is taking the path of least resistance.

I know my ceiling unit has mediocre flow in the bedroom ceiling but if I open the vents on the ceiling unit itself it will literally blow your hair around if you stand under it.
I’m certain everything you just said is very likely with an RV, but I know the same thing will happen with well-designed and well-sealed systems in all scenarios.

I’m just curious, and I know there are people here who are experts with this stuff.

Bruce
__________________
2016 Rockwood Windjammer 3029W Diamond Edition
2015 Chevy 3500HD LTZ 6.0 Crew Cab 4x4 Long Bed 4.10:1 SRW
nomad297 is offline   Reply With Quote
Old 08-08-2019, 07:20 AM   #4
Senior Member
 
Chuck_S's Avatar
 
Join Date: Aug 2018
Location: Richmond VA
Posts: 4,554
If the air velocity out of a single outlet (after the others are shut) doesn't increase you have a blockage in the ducts which are rather small anyway. Our ducted system has a shutter on the bottom for an "air shower" when standing directly underneath. Massive amount of air comes out. If I close all but one ceiling outlets on mine the air comes out of the remaining out at a higher velocity but not as much as the air shower.

-- Chuck
__________________
2006 Roo 23SS behind a 2017 Ford Expedition
Chuck_S is offline   Reply With Quote
Old 08-08-2019, 08:06 AM   #5
Senior Member
 
A32Deuce's Avatar
 
Join Date: Nov 2012
Location: Mount Laurel, New Jersey
Posts: 9,230
You would be surprised how much more air flow you get from the ceiling vents if you block off the channel going away from the last vent opening. I blocked the 4 last vents to keep the air from going into dead space. Much more air flow.
__________________
2012 SunSeeker 3100SS Toad-1962 Futura Average 100 + days camping
A32Deuce is offline   Reply With Quote
Old 08-08-2019, 08:53 AM   #6
Senior Member
 
Join Date: Nov 2017
Location: Dayton Ohio
Posts: 3,591
Your issue is your measuring device.

In the car world we refer to it as the butt Dyno! Not very accurate.

Your central fan produces so many cfm. If you measure every outlet and add them up you will come up with less than whatever the central unit supplies. That is duct imperfection losses.

The more you close the more loss thru leaks. Higher pressure in the system.

None of which your dyno can measure.

The better the design the less throttling thru diffusers the better.
tomkatb is offline   Reply With Quote
Old 08-08-2019, 02:55 PM   #7
2006 Tundra Surveyor 241
 
rwhit's Avatar
 
Join Date: Jul 2019
Location: Georgetown Texas
Posts: 73
I just happen to be a licensed HVAC contractor that has been doing this since 1982. This is what is called sick duct work in the commercial field. With out turning vanes all you are doing is creating back pressure in the duct work especially if you are trying to push air to the farthest vents which could actually cause damage to the duct and the A/C unit. I have the same issue in my trailer as there are no standards or codes for mobile HVAC. I have attach a fan in our bedroom to the vent that draws air out of the duct and actually over cools the bedroom now but it keeps the wife happy. I don’t have a real fix for it due to the inaccessibility of the duct work but the small 12 volt fan is working for me.
rwhit is offline   Reply With Quote
Old 08-08-2019, 04:00 PM   #8
Senior Member
 
nomad297's Avatar
 
Join Date: Jul 2015
Posts: 7,053
Quote:
Originally Posted by rwhit View Post
I just happen to be a licensed HVAC contractor that has been doing this since 1982. This is what is called sick duct work in the commercial field. With out turning vanes all you are doing is creating back pressure in the duct work especially if you are trying to push air to the farthest vents which could actually cause damage to the duct and the A/C unit. I have the same issue in my trailer as there are no standards or codes for mobile HVAC. I have attach a fan in our bedroom to the vent that draws air out of the duct and actually over cools the bedroom now but it keeps the wife happy. I don’t have a real fix for it due to the inaccessibility of the duct work but the small 12 volt fan is working for me.
Sort of like the difference between pushing or pulling fish tape around sharp corners. It’s much easier to pull it than it is to push it.

Bruce
__________________
2016 Rockwood Windjammer 3029W Diamond Edition
2015 Chevy 3500HD LTZ 6.0 Crew Cab 4x4 Long Bed 4.10:1 SRW
nomad297 is offline   Reply With Quote
Old 08-08-2019, 04:43 PM   #9
Senior Member
 
Bluepill's Avatar
 
Join Date: Jun 2015
Location: Pensacola, FL
Posts: 1,645
Squirrel Cage blowers quickly get less efficient as back pressure goes up. They are designed for high volume/low pressure use.
__________________
2019 Coachmen Freedom Express 192RBS
2015 T12RBST Flagstaff Hardside

Disclaimer: The actual value of my "Two Cents" of advice varies just like a bitcoin.
Bluepill is offline   Reply With Quote
Old 08-08-2019, 04:55 PM   #10
Senior Member
 
Thurman's Avatar
 
Join Date: Aug 2011
Location: Albany, GA.
Posts: 1,359
"rwhit's" explanation is a good one. I have past experience working with industrial HVAC applications and whit hot the nail on the head. I've seen large, 48" x48", duct work that we just could not get enough COM out of the end of the run although the engineer's calculations states we should have plenty. We've had to install booster fans within a duct run to get personnel happy.
__________________

Thurman is offline   Reply With Quote
Old 08-08-2019, 05:26 PM   #11
Senior Member
 
Join Date: Oct 2018
Posts: 161
Some RV systems have a SAIL switch to shut down if the flow is too low and you could damage a furnace!!!
wanderer44 is offline   Reply With Quote
Old 08-24-2019, 11:16 PM   #12
Junior Member
 
Join Date: Jan 2019
Posts: 9
Quote:
Originally Posted by rwhit View Post
I just happen to be a licensed HVAC contractor that has been doing this since 1982. This is what is called sick duct work in the commercial field. With out turning vanes all you are doing is creating back pressure in the duct work especially if you are trying to push air to the farthest vents which could actually cause damage to the duct and the A/C unit. I have the same issue in my trailer as there are no standards or codes for mobile HVAC. I have attach a fan in our bedroom to the vent that draws air out of the duct and actually over cools the bedroom now but it keeps the wife happy. I don’t have a real fix for it due to the inaccessibility of the duct work but the small 12 volt fan is working for me.


We have the same problem with our trailer. Not to mention that the ac just sucks. Would you mind giving me details on the type of fan you use? I’d like to put one in ours. Thanks so much!
__________________

Renee
Simi Valley, CA
2019 FR Evo Stealth T3250
Bibbidi_Bobbidi_Boo is offline   Reply With Quote
Old 08-27-2019, 07:35 AM   #13
Senior Member
 
Join Date: May 2019
Posts: 1,016
Because as you close registers you are trying to force more air through the other registers, which increases the air velocity and increases the static pressure in the duct system.

As the external static pressure of the system increases the design point on your fan curve moves to the left up the curve (known as the fan riding the curve in the HVAC industry) and the total airflow (CFM) reduces. If the static becomes great enough to move the operating point to the very left side of the curve the fan will spin without moving any air, this is referred to as fan "stall".
Attached Thumbnails
Click image for larger version

Name:	fan curve.jpg
Views:	52
Size:	103.1 KB
ID:	213533  
__________________
2019S Mod Thread
https://www.forestriverforums.com/fo...ad-184896.html

2020 Rockwood Mini Lite 2109S
2022 Ford F-350 Lariat, 4x4, CC, SRW, 7.3L
01tundra is offline   Reply With Quote
Old 08-27-2019, 07:56 AM   #14
Master of the obvious
 
Join Date: Sep 2009
Location: Massachusetts
Posts: 66
Following... I too would like to install a fan to pull air into bedroom.
__________________
Craig & Jennifer, plus 4 boys, a charcoal and a silver lab
Outside Boston, MA
2017 Coachman leprechaun 310BH
2018 Kia Optima Toad
bigdaddy is offline   Reply With Quote
Old 08-27-2019, 08:14 AM   #15
2006 Tundra Surveyor 241
 
rwhit's Avatar
 
Join Date: Jul 2019
Location: Georgetown Texas
Posts: 73
This is the fan I bought and wire tied to the vent. I got power from the ceiling light next to the vent
Attached Thumbnails
Click image for larger version

Name:	5C35233C-A9FA-4321-835E-B2B1723854D9.jpg
Views:	64
Size:	351.1 KB
ID:	213535  
rwhit is offline   Reply With Quote
Old 08-27-2019, 12:22 PM   #16
2006 Tundra Surveyor 241
 
rwhit's Avatar
 
Join Date: Jul 2019
Location: Georgetown Texas
Posts: 73
I totally agree with this but after being a trainer and customer service for years I try to make it where people outside of the trade can understand the explanation but you are right on point.
rwhit is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 05:14 PM.