I'm going to try to charge the systems before I bite the bullet on new units. I need to review all my paperwork to see exactly which units are on my travel trailer. I figured they were 15K units, however I may be wrong since I have two.
__________________
2010 Forest River 323FK
2008 2500 HD - Duramax - DPF Delete and cool duals
2012 Corvette GS
SCThunderBolt is offline   Reply With Quote
Old 01-31-2016, 10:56 AM   #22
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
One is probably a 15k "living room" and a 13.5k in the bedroom.


2015 Columbus 320RS
2008 2500HD Duramax
2015 nights camped "34"
TURBS is offline   Reply With Quote
Old 01-31-2016, 11:00 AM   #23
Junior Member
 
fincher's Avatar
 
Join Date: Mar 2013
Posts: 28
I have been having the same problem with ours since we bought it. I have complained about it to Forest River since we got it 3 years ago. They do not stand behind it. They told me that since our camper was prepped and wired for the 2nd AC unit that needs to be installed. Nothing said that the AC unit might be faulty.

TURBS I am going to add the 2nd AC unit myself but I've been trying to figure out if I should go with a ducted or non ducted? Also I want to know if you can install a thermostat on the wall or you have to just go with the switches on the unit? I have a fifth wheel and the switches would be out of reach.
fincher is offline   Reply With Quote
Old 01-31-2016, 11:29 AM   #24
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Go ducted.
If it's wired for second a/c it should have a dual climate thermostat.

You'll also need the cccII dual climate control module.
http://www.pplmotorhomes.com/parts/c...H7RxoCetXw_wcB

Hopefully it'll start warming up some and I can start installing mine.
I'll likely start a thread in doing so.



2015 Columbus 320RS
2008 2500HD Duramax
2015 nights camped "34"
TURBS is offline   Reply With Quote
Old 01-31-2016, 01:19 PM   #25
Junior Member
 
fincher's Avatar
 
Join Date: Mar 2013
Posts: 28
Super! Thanks
fincher is offline   Reply With Quote
Old 01-31-2016, 06:00 PM   #26
Junior Member
 
SCThunderBolt's Avatar
 
Join Date: Feb 2015
Location: Spring Texas
Posts: 26
TURBS, I found this on Youtube. Would something like this work?

__________________
2010 Forest River 323FK
2008 2500 HD - Duramax - DPF Delete and cool duals
2012 Corvette GS
SCThunderBolt is offline   Reply With Quote
Old 01-31-2016, 06:40 PM   #27
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
I don't see why not!



2015 Columbus 320RS
2008 2500HD Duramax
2015 nights camped "34"
TURBS is offline   Reply With Quote
Old 01-31-2016, 07:22 PM   #28
Junior Member
 
SCThunderBolt's Avatar
 
Join Date: Feb 2015
Location: Spring Texas
Posts: 26
Thanks. I'm going to dig into this a little deeper.
__________________
2010 Forest River 323FK
2008 2500 HD - Duramax - DPF Delete and cool duals
2012 Corvette GS
SCThunderBolt is offline   Reply With Quote
Old 02-01-2016, 06:53 AM   #29
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Those work well, but they have a tendency to leak. It is best to have someone solder them in. Also To get back to the correct charge if your doing it yourself it's best to read the name plate. It will tell you the exact charge needed. As an example it might say 28 oz or so. That is the correct amount to put in. you might have to dump the charge and then recharge the system to the name plate. Then you will not be over or under charged. Hope that helps you out. If you have a tech do it with the soldered in ones make sure he pulls a vacuum on the system, because you will get air in it and it has to be evacuated. You will NOT get air in the system with the one shown.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 02-01-2016, 08:26 AM   #30
Junior Member
 
SCThunderBolt's Avatar
 
Join Date: Feb 2015
Location: Spring Texas
Posts: 26
Thanks. My plan is to get a technician to solder one in before I go with the saddle valve.
__________________
2010 Forest River 323FK
2008 2500 HD - Duramax - DPF Delete and cool duals
2012 Corvette GS
SCThunderBolt is offline   Reply With Quote
Old 02-01-2016, 10:20 AM   #31
Junior Member
 
SCThunderBolt's Avatar
 
Join Date: Feb 2015
Location: Spring Texas
Posts: 26
I've been doing more research. It appears regular basic maintenance is required. Since owning my travel trailer 3 years now I have never cleaned the coils and filters. Since my units are working this seems like a good place to start. =)
__________________
2010 Forest River 323FK
2008 2500 HD - Duramax - DPF Delete and cool duals
2012 Corvette GS
SCThunderBolt is offline   Reply With Quote
Old 02-02-2016, 06:02 AM   #32
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Quote:
Originally Posted by SCThunderBolt View Post
I've been doing more research. It appears regular basic maintenance is required. Since owning my travel trailer 3 years now I have never cleaned the coils and filters. Since my units are working this seems like a good place to start. =)
Yep Very good place to start, don't use any harsh chemicals on your coils, and don't forget the drain pan...
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 02-03-2016, 12:19 AM   #33
Senior Member
 
Join Date: Jan 2016
Location: Phoenix, Arizona
Posts: 306
Being an HVAC contractor in Phoenix, I'd wash the outdoor coil to start. Maybe dirty enough to cycle the compressor off on high pressure and over heat during the day and work fine at cooler temps at night. Medium pressure from a garden hose is good enough. That's about all the maintenance a homeowner would be able to do besides keeping the indoor air filter clean. Also, as long as it is a copper line and not aluminum, a tech can sweat on a saddle valve while under pressure and see if the charge is low. If it is low, a leak should be located. If no leak is found the unit could be evacuated and recharged. Depending on how long the charge last, you could make a decision on looking deeper for a leak or just to replace it...just my 2 cents
bob dirt is offline   Reply With Quote
Old 02-03-2016, 06:05 PM   #34
Junior Member
 
SCThunderBolt's Avatar
 
Join Date: Feb 2015
Location: Spring Texas
Posts: 26
Thanks fellas. I appreciate the feedback!
__________________
2010 Forest River 323FK
2008 2500 HD - Duramax - DPF Delete and cool duals
2012 Corvette GS
SCThunderBolt is offline   Reply With Quote
Old 02-06-2016, 10:40 PM   #35
Senior Member
 
MNtraveler's Avatar
 
Join Date: Oct 2015
Posts: 2,404
<~However while at the RV dealer the rear AC unit stopped working and they removed it and replaced it with a new unit.~>

That's funny but only in the most evil sense of the word. That it happened right at the dealership is so fitting. Glad they fixed it for you!


Land of 10,000 Lakes
2016 Forester MBS 2401R
__________________
2016 FR Forester 2401R
Towing 2014 Honda CR-V
MNtraveler is offline   Reply With Quote
Old 02-08-2016, 11:22 AM   #36
Senior Member
 
VinceU's Avatar
 
Join Date: Dec 2011
Posts: 3,570
Quote:
Originally Posted by MNtraveler View Post
<~However while at the RV dealer the rear AC unit stopped working and they removed it and replaced it with a new unit.~>

That's funny but only in the most evil sense of the word. That it happened right at the dealership is so fitting. Glad they fixed it for you!


Land of 10,000 Lakes
2016 Forester MBS 2401R

Refer to post 4, Dometic having mfg problems and often elect to change.
VinceU is offline   Reply With Quote
Old 02-10-2016, 07:13 PM   #37
Senior Member
 
Join Date: Dec 2010
Location: East Berlin
Posts: 734
I would like to comment on adding the AC ports to a non working unit. Unless it is specifically spelled out that no repairs can be completed on the unit such as adding freon. Providing the repairs are completed by a trained technician, the manufacturer can not just void the warranty.

The Magnuson-Moss Warranty Act was passed just for this reason. All to often the manufacturer will use this cancellation of warranty claim if you have a repair made or you do something to improve how something functions.

If you have a unit under warranty you should know this act it will get you results especially if someone says we will void your warranty. Quoting that act to a warranty claim person makes them stutter.
Rich5117 is offline   Reply With Quote
Old 03-23-2016, 09:45 PM   #38
Senior Member
 
Thurman's Avatar
 
Join Date: Aug 2011
Location: Albany, GA.
Posts: 1,359
My 2 cents worth: NO I am not an A/C certified repair person. I have worked on auto A/C's and domestic refrigerators with a highly skilled A/C person. Placing a "tap valve aka bullet valve" is not the answer. IF one would want to place a valve for testing refrigerant pressures then one would need to add the solder-in brass valves on both the suction and supply side lines. Placing one valve on the suction can, and will, give you incorrect pressure readings. It is important to know what the pressures on both the supply side and suction side are doing. I have never seen one of those two piece valves be placed on a line and not leak withing six (6) months at the most. Windex sprayed onto the valve will confirm this somewhere around four (4) months. One of the most important things one can do for a unit that has apparently lost it's refrigerant is to have a vacuum drawn on the unit. IF there is a leak which would allow the refrigerant to leak out--then moisture can leak in. You just cannot properly charge a system with one of the DIY kits IF the system has moisture within it. Drawing vacuum is the only way to remove the moisture. A vacuum pump is not cheap and they don't sell them at Wally-World either--for a reason. Then you get into: "How long has the system not been working?" This is a need to know question because most times that the refrigerant leaks the special oil for the compressor leaks out also. Then one will have to know how to add just the correct amount of compressor oil to the system before adding the new refrigerant. It actually can get complicated to properly prepare a system for charging and doing the charge itself.
Thurman is offline   Reply With Quote
Old 03-24-2016, 04:34 AM   #39
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Quote:
Originally Posted by bob dirt View Post
Being an HVAC contractor in Phoenix, I'd wash the outdoor coil to start. Maybe dirty enough to cycle the compressor off on high pressure and over heat during the day and work fine at cooler temps at night. Medium pressure from a garden hose is good enough. That's about all the maintenance a homeowner would be able to do besides keeping the indoor air filter clean. Also, as long as it is a copper line and not aluminum, a tech can sweat on a saddle valve while under pressure and see if the charge is low. If it is low, a leak should be located. If no leak is found the unit could be evacuated and recharged. Depending on how long the charge last, you could make a decision on looking deeper for a leak or just to replace it...just my 2 cents
Bob dirt, just a question for you on the new Freon used. You stated that you would beable to pierce a copper line while it still held freon in it and solder in a valve. I know with the old freon r-22 that would not work. Don't know with the new freon it's been that long since my time working on units. Also I remember alum coils and lines when they first came out. We use to solder alum coils or lines for repair, I know they used to make a kit to do that. Is any of this stuff still around or have we just become a throw away society. I know for a fact if I pressure tested a system and found a leak at a fitting I had to blow out the lines before I could resolder a fitting, so you have my curiosity up, that's all. That was before all this EPA crap. They were just changing the r-12 and r-22 band, that's how long it's been. Thanks for your answer and information...
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 03-24-2016, 08:47 AM   #40
Senior Member
 
Join Date: Jan 2016
Location: Phoenix, Arizona
Posts: 306
New freon....that's funny. It's been around for a long time now (R410A)

I've soldered temp taps on R-22 system a lot in the past. Some of the new units (residential) back then came sealed. You couldn't troubleshoot them well without knowing pressures. Bad valves on compressor could seem like low charge without knowing more. The new R-410A runs a lot higher pressure than 22. The only things I see sealed nowadays are the small cabinet units for telecommunications, RV's, etc. All the new high efficiency stuff is charged by weight and checked by sub-cooling stamped on the name plate. This process is more time consuming AND is a pita. Anyhow, we don't leave temporary taps in the lines, they are just used for trouble shooting.
btw, the EPA has made us "pump out" systems for over 20 years now...

Another thing, most of the indoor coils now are aluminum and there is no repairing them
__________________
2016 Forester 2401WS MBS
Life is short...eat the cookie
bob dirt is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 10:08 AM.