Old 01-16-2019, 08:28 AM   #1
Junior Member
 
Join Date: Jan 2019
Posts: 9
Furnace doesn't kick back on

The furnace in my camper will kick on and work perfectly 2 or 3 times and then it won't run again until you turn it off and then back on with the thermostat. The furnace is a suburban sf35f. I've replaced the thermostat and the control box in the ceiling. Any ideas? I'm thinking the module board.
Natesev is offline   Reply With Quote
Old 01-16-2019, 08:31 AM   #2
Senior Member
 
ejohnson1144's Avatar
 
Join Date: Aug 2017
Posts: 426
Quote:
Originally Posted by Natesev View Post
The furnace in my camper will kick on and work perfectly 2 or 3 times and then it won't run again until you turn it off and then back on with the thermostat. The furnace is a suburban sf35f. I've replaced the thermostat and the control box in the ceiling. Any ideas? I'm thinking the module board.
I would look at the time delay relay if it has one they seem to be chincy.
ejohnson1144 is offline   Reply With Quote
Old 01-16-2019, 11:20 AM   #3
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
The SF35F doesn't have the time delay relay, that's handled in the control module.

We've had the same symptoms you describe several times and it's usually the control module in the furnace that's the problem.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 01-16-2019, 11:32 AM   #4
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,143
Quote:
Originally Posted by Bama Rambler View Post
The SF35F doesn't have the time delay relay, that's handled in the control module.

We've had the same symptoms you describe several times and it's usually the control module in the furnace that's the problem.
Agreed. I've experienced the same.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=90
5picker is offline   Reply With Quote
Old 01-16-2019, 03:19 PM   #5
Member
 
Join Date: Nov 2015
Posts: 47
Furnace

Yep, had same thing and was the furnace panel. Replaced under warranty and problem solved
jrmorris is offline   Reply With Quote
Old 01-16-2019, 05:33 PM   #6
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,584
Not always the controller board

Quote:
Originally Posted by Bama Rambler View Post
The SF35F doesn't have the time delay relay, that's handled in the control module.

We've had the same symptoms you describe several times and it's usually the control module in the furnace that's the problem.
You can also have the "failure to ignite" which requires the "reset by off/on" caused by a pressure regulator that's going bad. I'm referring to the gadget that's connected to the propane tank(s). If the regulator is more than a few years old, that's a definite possibility. The water heater and range are pretty insensitive to propane pressure, but the Suburban furnace is very fussy.

Ask me how I know.

Larry
Larry-NC is offline   Reply With Quote
Old 01-16-2019, 06:12 PM   #7
Senior Member
 
TimVWulp's Avatar
 
Join Date: Jan 2015
Location: West Michigan
Posts: 641
If under warranty have the dealer replace with suburban made control board. If it is not go to amazon and get a dinosaur brand control board much better made product.

Hope this helps Tim
TimVWulp is offline   Reply With Quote
Old 01-16-2019, 07:01 PM   #8
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,584
Overstuffed wallets?

Quote:
Originally Posted by TimVWulp View Post
If under warranty have the dealer replace with suburban made control board. If it is not go to amazon and get a dinosaur brand control board much better made product.

Hope this helps Tim
You guys must have overstuffed wallets if you recommend replacing the control board without doing a little bit of troubleshooting. To start with, all you need is your ears.

There are several reasons that the furnace will fail to light on three attempts and go into "lockout." The control board is only one of them, and (IMHO) not the most likely.
  1. Furnace clogged with dust. Suburban recommends not using a filter (any obstruction) so the whole area gets clogged with dust. If there's not enough airflow, the "sail switch" will not close and the furnace won't even attempt to light. (I can envision people removing the furnace, cleaning everything, replacing a perfectly good control board, having the furnace work, and attributing the fix to the control board when it really was the cleaning.)
  2. Bad propane regulator. This happened to me. The furnace was reliable with the plenum cover off, would light every time. Put the cover on and it wouldn't light. I checked gap, spark, sail switch, high limit switch, and everything else. All was in order. Even though the Suburban manual tells you to check gas pressure FIRST, I had put it off because I had no gauge. Finally I took some scrap wood, spare Romex staples, and $3 of fittings from Lowes and built a gauge. Sure enough, the 14-year-old regulator was bad. Next time it will be the first thing I check.

Larry
Larry-NC is offline   Reply With Quote
Old 01-16-2019, 09:38 PM   #9
Junior Member
 
Join Date: Jan 2019
Posts: 9
Thanks for all the input, I did go ahead and order a new dinosaur board from Amazon so we'll see if this fixes it. Btw the regulator is new, had to put a new one on after I got this camper because the previous owner had it hooked to a residential propane tank so it has new regulator and hoses.
Natesev is offline   Reply With Quote
Old 01-16-2019, 09:55 PM   #10
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,584
Take off the grille

Quote:
Originally Posted by Natesev View Post
Thanks for all the input, I did go ahead and order a new dinosaur board from Amazon so we'll see if this fixes it. Btw the regulator is new, had to put a new one on after I got this camper because the previous owner had it hooked to a residential propane tank so it has new regulator and hoses.
To install the new board, you will first have to
  • Take off the grille: Probably four Robertson screws. You will be amazed at all the dust and gunk behind it. You might as well get out the vacuum and start cleaning as you go. There will be more.
  • Turn off the gas on all tanks. Then disconnect the gas line at the furnace.
  • There will be four wires going into the furnace. If there's a connector, unplug it. If not, the wires will be long enough to remove the furnace and work on it in place.
  • Remove the furnace front plenum cover. It's the only thing you can see. Probably one sheet metal screw at the top edge.
  • Vacuum some more.
  • At this point you could actually reassemble the furnace and see if cleaning it fixed it.
  • If not, remove the furnace anchor screw at the front bottom center, approximately just below where you removed the plenum cover screw.
  • Pull the furnace out. Vacuum some more.
  • At the back you will see the double-ended fan motor, two squirrel-cage blowers, and the control board. Vacuum the squirrel-cage blowers, then clean them with an old toothbrush, then vacuum again.
  • Change the controller board if you are really convinced that it's a problem.
  • With the furnace out, you will see the two tubes exiting outside for the firebox intake and exhaust. They should be perfectly clean. If not, clean them. Vacuum some more. It's not unusual for mud daubers to nest there and clog the tubes with mud, hard to get out.
  • Now the tricky part: If you are really good, you will be able to slide the furnace back into the plenum, engaging the two tubes from the firebox onto the two vent tubes. It's hard. If you cannot do it, you will have to remove the vent from the outside. After the furnace is back together, you will have to put the vent back on with new butyl tape.
  • Reconnect the wires and the gas line before putting the anchor screw in.
  • Install the plenum cover and grille.
  • Re-install the vent cover if you had to take it off.

Larry
Larry-NC is offline   Reply With Quote
Old 01-17-2019, 09:12 PM   #11
Senior Member
 
TimVWulp's Avatar
 
Join Date: Jan 2015
Location: West Michigan
Posts: 641
Forest River Forums - Downloads - Furnace - Suburban Operation (Various models)

I atached a link from the library at the the top of this page to work on suburban furnaces. There is a lot of information in the library on how to fix and maintain your RV.

Hope this helps Tim
TimVWulp is offline   Reply With Quote
Old 01-21-2019, 09:03 PM   #12
Junior Member
 
Join Date: Jan 2019
Posts: 9
I put the new board in the other day and it seems to have fixed the problem, it has been replaced before so we'll see. Thanks for all the help
Natesev is offline   Reply With Quote
Old 01-21-2019, 09:09 PM   #13
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,584
So how dirty was it inside?

Quote:
Originally Posted by Natesev View Post
I put the new board in the other day and it seems to have fixed the problem, it has been replaced before so we'll see. Thanks for all the help
So how dirty was it inside? Did you clean it much?

Larry
Larry-NC is offline   Reply With Quote
Old 01-21-2019, 09:31 PM   #14
Junior Member
 
Join Date: Jan 2019
Posts: 9
It actually wasn't dirty believe it or not, I did have the vacuum on stand by figuring it would need a little but it was good
Natesev is offline   Reply With Quote
Old 01-21-2019, 09:32 PM   #15
Junior Member
 
Join Date: Jan 2019
Posts: 9
Quote:
Originally Posted by TimVWulp View Post
Forest River Forums - Downloads - Furnace - Suburban Operation (Various models)

I atached a link from the library at the the top of this page to work on suburban furnaces. There is a lot of information in the library on how to fix and maintain your RV.

Hope this helps Tim
That is very handy thank you
Natesev is offline   Reply With Quote
Old 01-21-2019, 09:38 PM   #16
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,584
To be honest...

Quote:
Originally Posted by Natesev View Post
It actually wasn't dirty believe it or not, I did have the vacuum on stand by figuring it would need a little but it was good
To be honest, my experience has been limited to a trailer in which a very hairy, shedding dog resides.

Larry
Larry-NC is offline   Reply With Quote
Old 01-30-2019, 02:08 PM   #17
Junior Member
 
Join Date: Jan 2019
Posts: 9
Ok so the new board seemed to work for a while but now it's being dumb again, it works fine sometimes but not at all other times. I did notice when changing out the thermostat that came with the new relay box that the was a couple other wires not being used which leads me to believe this trailer had an analog thermostat. Any other ideas?
Natesev is offline   Reply With Quote
Old 01-30-2019, 02:44 PM   #18
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
What happens if you connect the thermostat wires at the furnace together while it's acting up, Does it work correctly then?

You could always add a furnace only thermostat somewhere.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 01-30-2019, 06:29 PM   #19
Junior Member
 
Join Date: Jan 2019
Posts: 9
I will give this a try
Natesev is offline   Reply With Quote
Old 01-30-2019, 09:56 PM   #20
Senior Member
 
TimVWulp's Avatar
 
Join Date: Jan 2015
Location: West Michigan
Posts: 641
Quote:
Originally Posted by Natesev View Post
Ok so the new board seemed to work for a while but now it's being dumb again, it works fine sometimes but not at all other times. I did notice when changing out the thermostat that came with the new relay box that the was a couple other wires not being used which leads me to believe this trailer had an analog thermostat. Any other ideas?
Hi sorry to hear that you are still having trouble. The furnace has 2 wires that go to the thermostat. At the thermostat they are generally red and white. The red wire is connected to the R terminal and white is on the W Terminal. R or red is 12 volts + and white or W is the 12 volts + back to the furnace to start it. Do not short across the R and W terminals as this may cause a short and burn out the heat anticipator resistor in the thermostat. Remove the wires from R and W on the thermostat and put them together. The furnace should start and fire up as long as they are together. I have seen several post where the thermostat switch was going bad or failed. When this happens the furnace will not start the furnace fan or go into lock out failure mode.

hope this helps Tim
TimVWulp is offline   Reply With Quote
Reply

Tags
furnace


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 08:37 AM.