Furnace Problem - Rockwood

Hello, I'm new here and arent sure I'm in the right place , feel free to redirect me. I bought a 2013 rockwood 5th wheel in Nov '12. I love it. However.... Iwas in Oliver BC over Xmas and got held up there w/ some health issues for a while. As a result I used my furnace a lot. Normally Im much further south. Now this is sold as a polar pack...but..at -10C I had to use 2 electric heaters to keep it at 21C. Country RV inPenticton replaced some elecronic boards 2x.I think they burned out because the furnace runs 24/7 trying to keep up. Took it in to the shop and they said that was just the way it is.If you are kind enough to reply please ignore the obvious , this is my 3rd 5thW and the others pumped out 5x the heat. Iwould appreciate any thoughts.
jacksb is offline   Reply With Quote
Old 07-27-2013, 09:02 PM   #2
Moderator Emeritus
 
Dave_Monica's Avatar
 
Join Date: Sep 2007
Location: Ontario, Canada
Posts: 4,327
If I understand correctly, you're having to run 2 electric heaters in addition to the furnace to keep the inside temp at 21C while the outside is -10C. We have done a fair amount of camping at temp of -1 to -4C but not keeping the inside temp that high. With the colder temperature I'm not surprised that you need the furnace running a lot. Is the furnace vent air hot? Is the furnace cycling on/off?

Dave
__________________


Nights camped in 2013 - 55, 2014 - 105, 2015 - 63
Dave_Monica is offline   Reply With Quote
Old 07-28-2013, 04:50 PM   #3
Junior Member
 
Join Date: Jul 2013
Posts: 4
Quote:
Originally Posted by Dave_Monica View Post
If I understand correctly, you're having to run 2 electric heaters in addition to the furnace to keep the inside temp at 21C while the outside is -10C. We have done a fair amount of camping at temp of -1 to -4C but not keeping the inside temp that high. With the colder temperature I'm not surprised that you need the furnace running a lot. Is the furnace vent air hot? Is the furnace cycling on/off?

Dave
The outside vent seems to pump about 10x the heat outside as inside. Inside , tho you can here the fan come on low it is almost like no fan at all in the register right above the furnace and little to no heat comes through the other vents.If the electric heater (s) can maintain the temperature , yes it cycles off. The furnace appears to have no hi fan. This is with a skirt and insul in the vents. I used my old Komfort at -25C and didnt have the problem(now that was a bad year)
jacksb is offline   Reply With Quote
Old 07-28-2013, 04:51 PM   #4
Junior Member
 
Join Date: Jul 2013
Posts: 4
Quote:
Originally Posted by jacksb View Post
The outside vent seems to pump about 10x the heat outside as inside. Inside , tho you can here the fan come on low it is almost like no fan at all in the register right above the furnace and little to no heat comes through the other vents.If the electric heater (s) can maintain the temperature , yes it cycles off. The furnace appears to have no hi fan. This is with a skirt and insul in the vents. I used my old Komfort at -25C and didnt have the problem(now that was a bad year)
Bye the way thanks for answering so quickly
jacksb is offline   Reply With Quote
Old 07-28-2013, 07:55 PM   #5
Moderator Emeritus
 
Dave_Monica's Avatar
 
Join Date: Sep 2007
Location: Ontario, Canada
Posts: 4,327
Quote:
Originally Posted by jacksb View Post
The outside vent seems to pump about 10x the heat outside as inside. Inside , tho you can here the fan come on low it is almost like no fan at all in the register right above the furnace and little to no heat comes through the other vents.If the electric heater (s) can maintain the temperature , yes it cycles off. The furnace appears to have no hi fan. This is with a skirt and insul in the vents. I used my old Komfort at -25C and didnt have the problem(now that was a bad year)
I believe that they use only a single speed fan for the furnace...mine is the same. Sounds like it's time to remove the return air/access panel and see if the ducts are properly connected to the furnace and ensure that there's no restriction on the intake side.

Dave
__________________


Nights camped in 2013 - 55, 2014 - 105, 2015 - 63
Dave_Monica is offline   Reply With Quote
Old 07-29-2013, 07:45 PM   #6
Junior Member
 
Join Date: Jul 2013
Posts: 4
yup did that, the problem is that for a forced air furnace there is just no forced air.Its like the fan forces all the air outside and inside there's only rising heat. Put it on last night at 10C and it stayed on all night temp went to 16c inside. Trying to find someone here who does FR warranty work (prince george) , no luck so far. Im a little skeptical about the place in Penticton "its suppose to be like that" . I dont think so. Do other people w/ these units get adequite heat?
jacksb is offline   Reply With Quote
Old 07-29-2013, 07:58 PM   #7
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 23,269
Some info. The fans are on a common shaft motor. There is an "inside fan" on one end and an "outside fan" (for the combustion air) on the other. There is just the single motor.

Fan speed is determined by battery voltage. Low voltage = low fan (and higher than normal exhaust temperatures).

It can also be slowed by lack of lubrication, bug nests in the outside fan cage, and overheating motor. If the motor slows enough the sail switch will not close and the furnace will not run at all.

Air velocity at the outlet is a function of the duct work. Crushed hoses, disconnected hoses, separated plenum can cause lack of airflow from an otherwise perfectly health heater.
Attached Thumbnails
Click image for larger version

Name:	Suburban Furnace 001.jpg
Views:	449
Size:	64.8 KB
ID:	36479  
Attached Files
File Type: pdf suburbantech.pdf (804.8 KB, 50 views)
__________________
Lou & Freya the wonder dog
2008 GMC Sierra 3000HD Allison Duramax
2019 Flagstaff 8529FL
Herk7769 is offline   Reply With Quote
Old 07-29-2013, 08:12 PM   #8
Moderator Emeritus
 
Dave_Monica's Avatar
 
Join Date: Sep 2007
Location: Ontario, Canada
Posts: 4,327
The sail switch to ensure airflow before opening the gas valve, is it only on the combustion side? Is it possible that the fan for the room airflow is loose on the shaft and not delivering proper airflow?

Dave
__________________


Nights camped in 2013 - 55, 2014 - 105, 2015 - 63
Dave_Monica is offline   Reply With Quote
Old 07-29-2013, 10:19 PM   #9
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 23,269
Quote:
Originally Posted by Dave_Monica View Post
The sail switch to ensure airflow before opening the gas valve, is it only on the combustion side? Is it possible that the fan for the room airflow is loose on the shaft and not delivering proper airflow?

Dave

I believe the sail switch is on the room side. I would think the blower has to be on to cool the combustion chamber (that is how the house side air gets hot).

This is why I think it is a distribution problem and not a furnace problem. My guess is a torn or disconnected heat duct.
__________________
Lou & Freya the wonder dog
2008 GMC Sierra 3000HD Allison Duramax
2019 Flagstaff 8529FL
Herk7769 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 08:30 PM.