This is a picture of the wiring behind the furnace with the jump wire he added
Attached Thumbnails
Click image for larger version

Name:	IMG_0561.JPG
Views:	69
Size:	177.8 KB
ID:	97241  
__________________

__________________
cabinmo is offline   Reply With Quote
Old 01-04-2016, 11:38 AM   #12
Head Rambler
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 4,322
The furnace wires are;
Red = +12V
Yel = -12V
The Blues are to and from the T-stat.
One of the Blues is hooked to +12V through the valve switch.

You can test the T-stat by unhooking the blue wires and checking continuity through them. They should be shorted when the stat calls for heat and open when it isn't calling for heat.

If that checks out, check what happens if you leave the red and yellow wires hooked up and disconnect the blue wires. The unit shouldn't run. If it does then I suspect the internal hookup of the blue wires is wrong.
__________________

__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 01-04-2016, 12:02 PM   #13
Jack of All Trades
 
RJHuser's Avatar
 
Join Date: Oct 2010
Location: Fletcher, Ohio
Posts: 265
Check the blue with white tape-green-small red and the blue-small white. You might have the small red and small white mixed up.

Which is "the jump wire he added"?

Check the wiring per page 31 of the service manual below.

http://www.bdub.net/manuals/Suburban_Service_Manual.pdf

Rick
__________________
Rick & Debbie; Brandy & Schnoodle (Dexter & Fritz R.I.P.) the Doxie "Kids"
2015 Jayco Pinnacle 36RSQS 5'er
2018 GMC Sierra Denali 3500HD, 6.6L Diesel Dually; B&W Companion 5'er hitch
ScanGauge, TST 507 TPMS
RJHuser is offline   Reply With Quote
Old 01-04-2016, 12:35 PM   #14
Senior Member
 
Join Date: Jan 2015
Location: West Michigan
Posts: 419
Quote:
Originally Posted by cabinmo View Post
This is a picture of the wiring behind the furnace with the jump wire he added
Hi at the furnace disconnect the white wire from the blue wire furnace should stops. If it dose reconnect white and blue wire at furnace then remove thermostat from wall and disconnect the white wire from the thermostat furnace should stop. If it dose then thermostat has failed and needs to be replaced. If it don't the cable with the red and white wire with the brown jacket to the thermostat has shorted at some point. If this has happened I would look for the damaged part in the furnace compartment. It dose not take much to pinch the wires together damaging the wire insulation and shorting them.

hope this helps Tim
__________________

__________________
TimVWulp is offline   Reply With Quote
Reply

Tags
furnace, suburban

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 03:12 PM.