Old 01-04-2016, 09:11 AM   #11
Junior Member
Join Date: Nov 2013
Posts: 5
This is a picture of the wiring behind the furnace with the jump wire he added
Attached Thumbnails
Click image for larger version

Name:	IMG_0561.JPG
Views:	58
Size:	177.8 KB
ID:	97241  

cabinmo is offline   Reply With Quote
Old 01-04-2016, 10:38 AM   #12
Head Rambler
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 3,283
The furnace wires are;
Red = +12V
Yel = -12V
The Blues are to and from the T-stat.
One of the Blues is hooked to +12V through the valve switch.

You can test the T-stat by unhooking the blue wires and checking continuity through them. They should be shorted when the stat calls for heat and open when it isn't calling for heat.

If that checks out, check what happens if you leave the red and yellow wires hooked up and disconnect the blue wires. The unit shouldn't run. If it does then I suspect the internal hookup of the blue wires is wrong.

Salem 29RKSS Pushing a 2500 Mega-Cab CTD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 01-04-2016, 11:02 AM   #13
Jack of All Trades
RJHuser's Avatar
Join Date: Oct 2010
Location: Urbana, Ohio
Posts: 237
Check the blue with white tape-green-small red and the blue-small white. You might have the small red and small white mixed up.

Which is "the jump wire he added"?

Check the wiring per page 31 of the service manual below.

Rick & Debbie; Brandy, Dexter R.I.P., & Fritz R.I.P. (The Doxie "Kids")
2015 Jayco Pinnacle 36RSQS 5'er
2011 Rockwood Windjammer 3001W (Traded)

2013 Chevy Silverado 3500HD LTZ, 6.6L Diesel Dually; B&W Goose Neck and Companion 5'er hitch
RJHuser is online now   Reply With Quote
Old 01-04-2016, 11:35 AM   #14
Senior Member
Join Date: Jan 2015
Location: West Michigan
Posts: 278
Originally Posted by cabinmo View Post
This is a picture of the wiring behind the furnace with the jump wire he added
Hi at the furnace disconnect the white wire from the blue wire furnace should stops. If it dose reconnect white and blue wire at furnace then remove thermostat from wall and disconnect the white wire from the thermostat furnace should stop. If it dose then thermostat has failed and needs to be replaced. If it don't the cable with the red and white wire with the brown jacket to the thermostat has shorted at some point. If this has happened I would look for the damaged part in the furnace compartment. It dose not take much to pinch the wires together damaging the wire insulation and shorting them.

hope this helps Tim

TimVWulp is offline   Reply With Quote

furnace, suburban

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

» Virginia Campgrounds

Reviews provided by is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities

Copyright 2002-2015 Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 10:26 PM.