Old 01-19-2013, 12:28 PM   #11
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,337
Quote:
Originally Posted by Charliemomoney View Post
i have no problem with the overhead unit, or the heat strip application ,it cycles with the thermostat fine, just the furnace, i did consider the sail switch, but haven't replaced it yet.. thanks
Upper left hand of frf web page next to USER CP "files" section.

Turbs
__________________

__________________
TURBS is offline   Reply With Quote
Old 01-19-2013, 12:33 PM   #12
Owner/Operator
 
RodeoGeorge's Avatar
 
Join Date: Dec 2012
Location: Chino Valley, AZ
Posts: 671
The most frequent cause of the problem that you are describing is the Limit Switch.

The purpose of the Sail Switch is to prevent the burner from igniting if there is not sufficient air flow, or to shut the burner off if the airflow drops below the required CFM. Your burner is igniting.

The Limit Switch is just that. The device that limits the temperature of the chamber to a safe level. If the Limit Switch is not returning to the normal (open on some furnaces, closed on others) state, the furnace will not cycle back on until shut completely off and turned back on.

RodeoGeorge
__________________

__________________
RodeoGeorge is offline   Reply With Quote
Old 01-19-2013, 02:20 PM   #13
Junior Member
 
Join Date: Dec 2012
Posts: 13
I had a similar issue on my Roo 19. I am not sure if furnace is the same model. Documentation is packed away in trailer for the winter. My problem was with the sail switch. Seems like Suburban was having an issue with some sail switches getting stuck open. The control board must sense an open switch when it was not supposed to be and goes in lockout mode. turning thermostat off and back on resets the furnace. The fix for mine was that the service center was instructed by Suburban to trim sail switch. At least that is what I was told they did. Worked fine after that.
__________________
IllinoisCamper is offline   Reply With Quote
Old 01-19-2013, 02:35 PM   #14
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 21,168
Quote:
Originally Posted by wa3pnt View Post
The most frequent cause of the problem that you are describing is the Limit Switch.

The purpose of the Sail Switch is to prevent the burner from igniting if there is not sufficient air flow, or to shut the burner off if the airflow drops below the required CFM. Your burner is igniting.

The Limit Switch is just that. The device that limits the temperature of the chamber to a safe level. If the Limit Switch is not returning to the normal (open on some furnaces, closed on others) state, the furnace will not cycle back on until shut completely off and turned back on.

RodeoGeorge
This sounds like the best answer to me...
__________________

__________________

Lou and Laura with Bella - German Short Hair Pointer
2008 GMC Sierra 2500HD Crewcab SB Allison Duramax
2010 Flagstaff 8526RLWS - Superglide 3300
HAM CALLSIGN - KC3FFW
Herk7769 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 03:33 AM.