Old 03-07-2015, 01:22 PM   #21
Senior Member
 
Join Date: Apr 2012
Location: Southeast Pa
Posts: 194
Please explain why.
__________________


"DON'T FORCE IT - GET A BIGGER HAMMER'
"Paul & Laurie"
2013 Columbus 340 RK
2013 F350 Dually 6.7 Diesel
Paul M is offline   Reply With Quote
Old 03-07-2015, 01:24 PM   #22
Senior Member
 
Join Date: Aug 2013
Location: Pincher Creek, AB
Posts: 860
Quote:
Originally Posted by Paul M View Post
ALL 50 Amp RV sources ARE 220 Volt. Thae fact is that the RV does NOT use 220 volt. The Busses in the distribution box are split, so each side gets 110 Volt. For this reason is why some people state that RV's are ONLY 110 Volt. So just for clarification, There IS 220 Volts coming into the RV but it is not utlized in that fashion.
Not to nit pick, but it's actually 120 and 240 volt... 110 volts stems from Edison's original DC distribution system, the last one of which was disconnected in November 2007...
__________________
Camped: 2024 (Days/Nights) - 4/3
2023 (D/N) - 34/27, 2022 (D/N) - 41/33, 2021 (D/N) - 37/29, 2020 (D/N): 58/49

TT: 2020 26' Hemisphere 26BHHL
TV: 2020 GMC 2500HD 4x4
glen1971 is offline   Reply With Quote
Old 03-07-2015, 01:27 PM   #23
Senior Member
 
Join Date: Apr 2012
Location: Southeast Pa
Posts: 194
Fair enough. But it may depend on who's system your on and what they have the AVC's set at.
__________________


"DON'T FORCE IT - GET A BIGGER HAMMER'
"Paul & Laurie"
2013 Columbus 340 RK
2013 F350 Dually 6.7 Diesel
Paul M is offline   Reply With Quote
Old 03-07-2015, 01:30 PM   #24
Mod free 5er
 
Join Date: Mar 2008
Location: Concord, NC
Posts: 24,702
Quote:
Originally Posted by Paul M View Post
Please explain why.
Why does a 240V 50A service fry a 50 rv plug? BombDoc and a lot of others have fried theirs by plugging into a 50A 250V receptacle like for a welder.
__________________
OldCoot is offline   Reply With Quote
Old 03-07-2015, 01:30 PM   #25
Senior Member
 
geotex1's Avatar
 
Join Date: Sep 2014
Posts: 735
NEMA 14-50R is wired the same (split phase) regardless of RV or residential use. In residential, it is actually the common receptacle for an electric range.
__________________
geotex1 is offline   Reply With Quote
Old 03-07-2015, 01:31 PM   #26
Senior Member
 
Join Date: Aug 2013
Location: Pincher Creek, AB
Posts: 860
Quote:
Originally Posted by Paul M View Post
Fair enough. But it may depend on who's system your on and what they have the AVC's set at.
What is an AVC?
__________________
Camped: 2024 (Days/Nights) - 4/3
2023 (D/N) - 34/27, 2022 (D/N) - 41/33, 2021 (D/N) - 37/29, 2020 (D/N): 58/49

TT: 2020 26' Hemisphere 26BHHL
TV: 2020 GMC 2500HD 4x4
glen1971 is offline   Reply With Quote
Old 03-07-2015, 01:39 PM   #27
Senior Member
 
Join Date: Apr 2012
Location: Southeast Pa
Posts: 194
Can't answer about bombdoc's situation ect. without seeing the wiring configuration. The fact of the matter is a multimeter does not lie. If you measure the voltage as described above you WILL get the results as shown above if the source is wired properly. If you notice at campground power pedistals there is a single pole breaker for the 15 / 20 amp receptacle amd a single pole for the 30 amp. But there is a double pole for the 50. Thus the two seperate legs / polarity's which make up the 220 / 240.
__________________


"DON'T FORCE IT - GET A BIGGER HAMMER'
"Paul & Laurie"
2013 Columbus 340 RK
2013 F350 Dually 6.7 Diesel
Paul M is offline   Reply With Quote
Old 03-07-2015, 01:41 PM   #28
Senior Member
 
geotex1's Avatar
 
Join Date: Sep 2014
Posts: 735
Quote:
Originally Posted by OldCoot View Post
Why does a 240V 50A service fry a 50 rv plug? BombDoc and a lot of others have fried theirs by plugging into a 50A 250V receptacle like for a welder.
Getting way off topic, but anyone with a welder on residential service is wired the same way - split phase with two 120V hot legs.

Their problem with their RV service was an open neutral or ground so guess what happens on the return path - you get 220 surging/backfeeding the intact ground or neutral!

Conversely, you very much can mis-wire a 30A.
__________________
geotex1 is offline   Reply With Quote
Old 03-07-2015, 01:43 PM   #29
Senior Member
 
Join Date: Apr 2012
Location: Southeast Pa
Posts: 194
AVC' are used in the power company's substations on the distribution transformers. Stands for Automatic Voltage Control. They control the operation of transformer tap changers, which move in response to system load. On heavy load days in the summer when supply's are limited a power authority may invoke a 5% voltage reduction, which helps the reactive resources on the system maintain levels. This is done by moving the settings on the AVC's.
__________________


"DON'T FORCE IT - GET A BIGGER HAMMER'
"Paul & Laurie"
2013 Columbus 340 RK
2013 F350 Dually 6.7 Diesel
Paul M is offline   Reply With Quote
Old 03-07-2015, 01:46 PM   #30
Senior Member
 
Join Date: Apr 2012
Location: Southeast Pa
Posts: 194
I do apoligize for getting off topic.
Back to the regularly scheduled program.
I would keep the appliances for parts. Better to be looking at it than for it.
__________________


"DON'T FORCE IT - GET A BIGGER HAMMER'
"Paul & Laurie"
2013 Columbus 340 RK
2013 F350 Dually 6.7 Diesel
Paul M is offline   Reply With Quote
Old 03-07-2015, 02:03 PM   #31
Senior Member
 
Join Date: Apr 2012
Location: Southeast Pa
Posts: 194
Quote:
Originally Posted by fonzie View Post
This is being done just before brown out occurs or load shedding occurs to reduce load on the system.
I believe it more of a resource to maintain the high voltage transmission system voltages within limits to prevent a voltage colaspe, which would lead to cascading outages. Lets face it, if the transmission system is not stable and starts to fail none of the rest of it matters.
__________________


"DON'T FORCE IT - GET A BIGGER HAMMER'
"Paul & Laurie"
2013 Columbus 340 RK
2013 F350 Dually 6.7 Diesel
Paul M is offline   Reply With Quote
Old 03-07-2015, 02:04 PM   #32
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Quote:
Originally Posted by Paul M View Post
AVC' are used in the power company's substations on the distribution transformers. Stands for Automatic Voltage Control. They control the operation of transformer tap changers, which move in response to system load. On heavy load days in the summer when supply's are limited a power authority may invoke a 5% voltage reduction, which helps the reactive resources on the system maintain levels. This is done by moving the settings on the AVC's.
This is why most if not all appliances have a plus or minus 10% built in to there equipment voltage requirement such as A/C compressors and such. Before you would get any low voltage or high voltage damage to the equipment. ...
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 03-07-2015, 02:14 PM   #33
Senior Member
 
Join Date: Aug 2013
Location: Pincher Creek, AB
Posts: 860
Quote:
Originally Posted by Paul M View Post
AVC' are used in the power company's substations on the distribution transformers. Stands for Automatic Voltage Control. They control the operation of transformer tap changers, which move in response to system load. On heavy load days in the summer when supply's are limited a power authority may invoke a 5% voltage reduction, which helps the reactive resources on the system maintain levels. This is done by moving the settings on the AVC's.

The nominal voltages are still 120/240 though... Typically, in the United States, the Utility is regulated to provide a voltage of 104.4-127.2 vac (120 volts -13% and +6%).. As the tap changer would be located in the substation, it would only effect the subs buss voltage, and they don't measure the end user voltage and are meant more for larger adjustments. Usually by switching capacitor banks and the use of voltage regulators on the utility side the distribution voltages are changed, but still within regulated tolerances.. It's a delicate balance so that the two aren't fighting each other, as you said earlier to avoid the collapse of a power grid..
__________________
Camped: 2024 (Days/Nights) - 4/3
2023 (D/N) - 34/27, 2022 (D/N) - 41/33, 2021 (D/N) - 37/29, 2020 (D/N): 58/49

TT: 2020 26' Hemisphere 26BHHL
TV: 2020 GMC 2500HD 4x4
glen1971 is offline   Reply With Quote
Old 03-07-2015, 02:15 PM   #34
Senior Member
 
Rvdixie's Avatar
 
Join Date: Feb 2015
Location: Zephyrhills, FL
Posts: 176
These are not warranty items so a return to the manufacturer is not in play.
__________________
Richard Charron
Zephyrhills, FL
2015 Ford F150 Eco Boost
2016 Coachmen Chaparral Lite 29MKS
Rvdixie is offline   Reply With Quote
Old 03-07-2015, 02:20 PM   #35
Member
 
Join Date: Jan 2015
Location: Poconos, PA
Posts: 79
Quote:
Originally Posted by OldCoot View Post
Pardon me, but I don't believe that is correct.

50 amp rv's are set up for 120/240 which means it needs a neutral.

A 50 amp welding outlet is 240 only (no neutral)

I believe when you use a 30 to 50 adapter it sends the single 30 amp leg (120 ) to both legs in the camper so everything will work , you just can't use everything at the same time..

Joe
meganjoe is offline   Reply With Quote
Old 03-07-2015, 02:20 PM   #36
Senior Member
 
geotex1's Avatar
 
Join Date: Sep 2014
Posts: 735
Quote:
Originally Posted by gljurczyk View Post
This is why most if not all appliances have a plus or minus 10% built in to there equipment voltage requirement such as A/C compressors and such. Before you would get any low voltage or high voltage damage to the equipment. ...
Yes sir!

Two pieces of advice for the OP after everything is repaired: 1) never, ever plug your rig into the pedestal - even a home one (!) - with the breaker on because the hot legs can make contact before both the ground and neutral do and the bad things happen (!); and, 2) get a Progressive Industries EMS-HW50C installed as soon as you can afford and not worry about things! You really don't want just a a surge protector, you want the voltage protection as well because as just quoted above around supply is not constant, and can dip or spike beyond the margin.
__________________
geotex1 is offline   Reply With Quote
Old 03-07-2015, 02:24 PM   #37
Senior Member
 
Join Date: Apr 2012
Location: Southeast Pa
Posts: 194
[QUOTE=glen1971;800647]The nominal voltages are still 120/240 though... Typically, in the United States, the Utility is regulated to provide a voltage of 104.4-127.2 vac (120 volts -13% and +6%).. As the tap changer would be located in the substation, it would only effect the subs buss voltage, and they don't measure the end user voltage and are meant more for larger adjustments. Usually by switching capacitor banks and the use of voltage regulators on the utility side the distribution voltages are changed, but still within regulated tolerances.. It's a delicate balance so that the two aren't fighting each other, as you said earlier to avoid the collapse of a power grid..[/QUOTE I agree with all of the above except that cap banks tend to raise the distribution volatge, thus making the tap lower. this is how the caps support the transmission voltage. Tends to force vars up the trans or at least minimize losses. the only plase a cap may help dist. voltage is at the end of a long dist. circuit. As we know Vars don't travel well.
__________________


"DON'T FORCE IT - GET A BIGGER HAMMER'
"Paul & Laurie"
2013 Columbus 340 RK
2013 F350 Dually 6.7 Diesel
Paul M is offline   Reply With Quote
Old 03-07-2015, 02:31 PM   #38
Senior Member
 
geotex1's Avatar
 
Join Date: Sep 2014
Posts: 735
Quote:
Originally Posted by meganjoe View Post
50 amp rv's are set up for 120/240 which means it needs a neutral.

A 50 amp welding outlet is 240 only (no neutral)

I believe when you use a 30 to 50 adapter it sends the single 30 amp leg (120 ) to both legs in the camper so everything will work , you just can't use everything at the same time..

Joe
You got it Joe. And a 240/50A welder would use a NEMA 6-50R 3 prong.

I'm pretty sure we geeks are confusing everyone now!
__________________
geotex1 is offline   Reply With Quote
Old 03-07-2015, 02:34 PM   #39
Senior Member
 
Join Date: Apr 2012
Location: Southeast Pa
Posts: 194
geotex1, Who you calling a geek ? lol
__________________


"DON'T FORCE IT - GET A BIGGER HAMMER'
"Paul & Laurie"
2013 Columbus 340 RK
2013 F350 Dually 6.7 Diesel
Paul M is offline   Reply With Quote
Old 03-07-2015, 02:43 PM   #40
Always Learning
 
ependydad's Avatar
 
Join Date: Nov 2011
Location: Four Corners, FL
Posts: 21,891
Quote:
Originally Posted by meganjoe View Post
50 amp rv's are set up for 120/240 which means it needs a neutral.

A 50 amp welding outlet is 240 only (no neutral)

I believe when you use a 30 to 50 adapter it sends the single 30 amp leg (120 ) to both legs in the camper so everything will work , you just can't use everything at the same time..

Joe

Thanks, Joe. That confirms what I thought I was reading.
__________________
Officially a SOB with a 2022 Jayco Precept 36C
Checkout my site for RVing tips, tricks, and info | Was a Fulltime Family for 5 years, now we're part-timing on long trips
ependydad is offline   Reply With Quote
Reply

Tags
led, power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 07:45 PM.