Generator issue documented with video

2013 3011DS generator issue: surges only when Dometic AC/Heat Pump compressor is used regardless of load. 3 videos showing voltage, freq, load and results.

VIDEO0037 on Vimeo
VIDEO0038 on Vimeo
VIDEO0039 on Vimeo
EXTremist is offline   Reply With Quote
Old 09-29-2014, 09:02 PM   #2
Member
 
Join Date: Mar 2013
Posts: 46
After watching my own videos again, the only difference I see the compressor is making is that it is dropping the output voltage of the generator by several volts.

Other facts: Generator has 155.5 hours on it, oil has been changed twice and the fuel pump was replaced under warranty as it would not start or run hardly at all when new.
EXTremist is offline   Reply With Quote
Old 09-29-2014, 09:18 PM   #3
Senior Member
 
VinceU's Avatar
 
Join Date: Dec 2011
Posts: 3,570
Quote:
Originally Posted by EXTremist View Post
2013 3011DS generator issue: surges only when Dometic AC/Heat Pump compressor is used regardless of load. 3 videos showing voltage, freq, load and results.

VIDEO0037 on Vimeo
VIDEO0038 on Vimeo
VIDEO0039 on Vimeo
Since the unit will deliver full load, can't be much wrong with engine or fuel system. The only difference I note is the A/C is "inductive load" where the water heater and space heater are resistive load. That may be a idea to provide to Dometic engineers or FR. Seems like somehow they are out of sync. causing way too much apparent power (false load).
VinceU is offline   Reply With Quote
Old 09-29-2014, 09:29 PM   #4
Member
 
Join Date: Mar 2013
Posts: 46
Thanks! I will study up on the differences between the two. Been a long time but I do have an electrical degree.
EXTremist is offline   Reply With Quote
Old 09-29-2014, 09:34 PM   #5
Senior Member
 
VinceU's Avatar
 
Join Date: Dec 2011
Posts: 3,570
Quote:
Originally Posted by EXTremist View Post
Thanks! I will study up on the differences between the two. Been a long time but I do have an electrical degree.
I guess unsaid, would appear the heat pump is the problem, but just guessing.
VinceU is offline   Reply With Quote
Old 09-29-2014, 10:09 PM   #6
Member
 
Join Date: Mar 2013
Posts: 46
The more I research at Flight Systems the more I lean towards a very slightly defective regulator. Spendy guess though.
EXTremist is offline   Reply With Quote
Old 09-30-2014, 10:41 AM   #7
Commercial Member
 
Join Date: Nov 2007
Location: Bristol, IN
Posts: 18,971
good video. Forwarded this on to Dometic.
__________________
If "Search this Forum" does not yield answers, please post questions as a "New Thread" (instead of asking privately) so others can benefit from the answers.

Subscribe for "How To" videos and updates https://www.youtube.com/c/DynamaxRVs/

Sales-Service-Parts https://dynamaxcorp.com/contact-us
bclemens is offline   Reply With Quote
Old 09-30-2014, 10:49 AM   #8
Senior Member
 
mud yapster's Avatar
 
Join Date: Aug 2014
Location: Texas
Posts: 1,162
Yes you should forward those videos to the gen guys, Dometics guys, and FR. Have you checked the capacitors on the roof A/C heatpump unit yet?
__________________
2014 Palomino Columbus 3650TH
435AH 12V VMax Charge Tanks, 520 watt Monocrystilline Solar Array, Morningstar MPPT TS-60 CC,Morningstar Remote,Cotek True Sine Wave Inverter,Cotek Remote Controller,50amp Progressive Hardwire Surge Protector
2015 Dodge 3500 6.7L 4X4
2011 CanAm Commander XT 1000
mud yapster is offline   Reply With Quote
Old 09-30-2014, 10:55 AM   #9
Commercial Member
 
Join Date: Nov 2007
Location: Bristol, IN
Posts: 18,971
EXTremist. Have you tested that just running the 15k A/C on high? is it just on heat pump low fan?
__________________
If "Search this Forum" does not yield answers, please post questions as a "New Thread" (instead of asking privately) so others can benefit from the answers.

Subscribe for "How To" videos and updates https://www.youtube.com/c/DynamaxRVs/

Sales-Service-Parts https://dynamaxcorp.com/contact-us
bclemens is offline   Reply With Quote
Old 09-30-2014, 09:21 PM   #10
Member
 
Join Date: Mar 2013
Posts: 46
Any use of the compressor either AC or heat pump low or high will cause the generator to surge. As I stated in the video, the AC running in the heat will cause the gen to die completely. Thanks.
EXTremist is offline   Reply With Quote
Old 09-30-2014, 10:27 PM   #11
Senior Member
 
Join Date: Jul 2013
Location: Baton Rouge
Posts: 497
I'm thinking generator - fuel aspiration or starving in the carburator/injector at near full load conditions. Have Onan place a load bank on the generator starting with resistive then trying reactive.

Also, note that altitude and extreme temps (85 degrees and above) affect the performance/output of the generator. The 4000 watt output rating is at 500 feet and 77 degrees F. according to my Onan rep.

Look at page 13 of the Onan manual for surging problems: http://www.cumminsonan.com/www/html/.../rv/F-1123.pdf

Dometic will tell you if it runs fine on shorepower - the problem lies with the generator. I've already been that route. In the end, they were right.

Bobby
bgilly is offline   Reply With Quote
Old 10-01-2014, 08:52 AM   #12
Commercial Member
 
Join Date: Nov 2007
Location: Bristol, IN
Posts: 18,971
Yes, but why does the gen run fine pulling 27 amps of normal draw...but surge when there is 12 amps of compressor draw? The starving makes no sense if it is a load issue...when its starving at a smaller load.

I'm sending a unit over to Dometic to test...see if they can replicate the situation this week.
__________________
If "Search this Forum" does not yield answers, please post questions as a "New Thread" (instead of asking privately) so others can benefit from the answers.

Subscribe for "How To" videos and updates https://www.youtube.com/c/DynamaxRVs/

Sales-Service-Parts https://dynamaxcorp.com/contact-us
bclemens is offline   Reply With Quote
Old 10-01-2014, 09:06 AM   #13
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Sounds to me " I'm no expert " that the governor on the gennie is "finicky" at the rpm when it starts to surge.

IMO there's an issue with the governor.

No issues light load
No issues heavy load

We had a generator that would do this only under certain load.
When I noticed at that "certain" rpm the governor spring vibrated so violently that it was making the governor "hunt" "surge".
We adjusted the governor and installed a new spring to find the issue dissappear.

My 2 pennies.

Turbs
TURBS is offline   Reply With Quote
Old 10-01-2014, 09:25 AM   #14
Senior Member
 
Join Date: Jul 2013
Location: Baton Rouge
Posts: 497
Quote:
Originally Posted by bclemens View Post
Yes, but why does the gen run fine pulling 27 amps of normal draw...but surge when there is 12 amps of compressor draw? The starving makes no sense if it is a load issue...when its starving at a smaller load.
It is a counter reaction of the generator/governor. Mine was doing the exact same thing - load banked the generator only and under reactive load bank the my generator surged. Cummins already replaced the fuel pump prior to the test. Cummins renewed the carburetor and it worked fine afterwards. Almost 15 hours on it since the work with a lot of it air conditioner load and has been fine.

Bobby
bgilly is offline   Reply With Quote
Old 10-02-2014, 09:51 PM   #15
Member
 
Join Date: Mar 2013
Posts: 46
Thanks all...sounds like I need to take it to Cummins again for as load bank test rather than guessing at it.
EXTremist is offline   Reply With Quote
Old 10-20-2014, 09:41 AM   #16
Senior Member
 
mud yapster's Avatar
 
Join Date: Aug 2014
Location: Texas
Posts: 1,162
Quote:
Originally Posted by EXTremist View Post
Thanks all...sounds like I need to take it to Cummins again for as load bank test rather than guessing at it.
Were you able to figure out what was wrong with it? This past weekend I boondocked to check all my stuff and the Cummins generator 5500 watt.
Saturday morning I fired up the genny to make coffee and to let it run to charge battery. I let it run for about 10 minutes to warm up and then I turned on the coffee maker, and then turned on the electric fireplace, the gen ran for about 5 minutes then surged and died. The only load was the coffee maker and electric fireplace. I checked everything and then went to restart it and it started back up, I then turned the coffee maker only back on and it ran for say 10 minutes and died again but it wasn't surging this time it just died. I looked things over again and restarted it and turned the coffee maker on again and it stayed running so I let it keep running for an hour to top off the battery. My gen has 7.4 hours on it now and on the wednesday before this I had run it for 2 hours with both A/C units on so I know it wasn't air in the fuel line and the gas in the tank is new. Well hope you got yours working now anyway. I'm going to run mine this evening under all different load configurations and see if it acts up anymore.
__________________
2014 Palomino Columbus 3650TH
435AH 12V VMax Charge Tanks, 520 watt Monocrystilline Solar Array, Morningstar MPPT TS-60 CC,Morningstar Remote,Cotek True Sine Wave Inverter,Cotek Remote Controller,50amp Progressive Hardwire Surge Protector
2015 Dodge 3500 6.7L 4X4
2011 CanAm Commander XT 1000
mud yapster is offline   Reply With Quote
Old 10-22-2014, 09:16 AM   #17
Senior Member
 
mud yapster's Avatar
 
Join Date: Aug 2014
Location: Texas
Posts: 1,162
Found my genny problem, I thought my fuel pump quit. It would run for a few minutes and quit with load or without. Fuel pump wasnt pumping hardly any fuel so I removed it and tryied to blow thru the fuel line with my air compressor at 20 psi no luck it was clogged. I found where the fuel lines run alone the under side back to the fuel tank about 45' of fuel line. I took it loose at the tank and tried blowing threw it again with no luck. Traced line along rv back to genny and found the fuel line brackets supporting the lines were crushing the fuel line in 2 seperate places. I fixed those brakets and got good flow. Tested pump again and perfect fuel flow from pump. Hooked it all back up to genny and working perfect now. My Cummins onan 5500 only has 7.4 hrs on it and runs better now that it ever did in the last 7 hrs. I don't know what smashed the brackets holding the fuel line but its fixed now. Something you might look at to fix yours. Oh mine also surged from this.
__________________
2014 Palomino Columbus 3650TH
435AH 12V VMax Charge Tanks, 520 watt Monocrystilline Solar Array, Morningstar MPPT TS-60 CC,Morningstar Remote,Cotek True Sine Wave Inverter,Cotek Remote Controller,50amp Progressive Hardwire Surge Protector
2015 Dodge 3500 6.7L 4X4
2011 CanAm Commander XT 1000
mud yapster is offline   Reply With Quote
Old 10-23-2014, 07:48 AM   #18
Senior Member
 
mud yapster's Avatar
 
Join Date: Aug 2014
Location: Texas
Posts: 1,162
Here is a pic of the brackets that run along the underbelly holding the fuel lines and 2 of them were crushed smashing off the fuel line. These bracket was the easier one to take a pic of but there are probable a dozen of these along the underbelly holding the fuel lines. I never could figure out what had smashed them I guess from the factory that way.

Click image for larger version

Name:	IMAG1730.jpg
Views:	137
Size:	209.0 KB
ID:	65195
__________________
2014 Palomino Columbus 3650TH
435AH 12V VMax Charge Tanks, 520 watt Monocrystilline Solar Array, Morningstar MPPT TS-60 CC,Morningstar Remote,Cotek True Sine Wave Inverter,Cotek Remote Controller,50amp Progressive Hardwire Surge Protector
2015 Dodge 3500 6.7L 4X4
2011 CanAm Commander XT 1000
mud yapster is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 12:22 AM.