Old 08-06-2013, 08:58 AM   #1
Member
 
Join Date: Jul 2013
Posts: 94
Genset Question

On our new 3011DS I was finally able to start the generator and have it stay running. I understand that this is not unusual for a new gen. I have about an hour on it and when trying to start the AC it surges and then quits. It has done this 4 or 5 times. Any suggestions??? Nothing else is on, ie microwave.

Thanks
DennyH is offline   Reply With Quote
Old 08-06-2013, 12:27 PM   #2
Commercial Member
 
Join Date: Nov 2007
Location: Bristol, IN
Posts: 18,971
If you're at altitude, then there is an adjustment that needs to be made. At sea level I wonder if it is a fuel pump issue...I've been seeing a lot of those lately.
__________________
If "Search this Forum" does not yield answers, please post questions as a "New Thread" (instead of asking privately) so others can benefit from the answers.

Subscribe for "How To" videos and updates https://www.youtube.com/c/DynamaxRVs/

Sales-Service-Parts https://dynamaxcorp.com/contact-us
bclemens is offline   Reply With Quote
Old 08-06-2013, 01:17 PM   #3
Member
 
Join Date: Jul 2013
Posts: 94
I am in Middle Tennessee so altitude is not much of an issue(700ft) I will investigate the fuel pump issue further. Thanks!!
DennyH is offline   Reply With Quote
Old 08-06-2013, 07:23 PM   #4
Senior Member
 
Join Date: Feb 2013
Location: iowa
Posts: 285
read the manual and follow the break in instructions you might be putting to much load on to soon.
lbrunning is offline   Reply With Quote
Old 08-07-2013, 01:10 PM   #5
Commercial Member
 
Join Date: Nov 2007
Location: Bristol, IN
Posts: 18,971
I don't know. I'm in a 3010 here at the Goshen Rally. Brand new new from the plant...fired up the gen, turned on the air. Been working great for two days now. Although I have nothing else on at all.
__________________
If "Search this Forum" does not yield answers, please post questions as a "New Thread" (instead of asking privately) so others can benefit from the answers.

Subscribe for "How To" videos and updates https://www.youtube.com/c/DynamaxRVs/

Sales-Service-Parts https://dynamaxcorp.com/contact-us
bclemens is offline   Reply With Quote
Old 08-07-2013, 05:56 PM   #6
Member
 
Join Date: Jul 2013
Posts: 94
Thanks for the input, but I still am not able to start the AC. Even when I go from Lo Fan only to Hi then back to Lo the gen quits. Taking the MH to an authorized Cummins/Onan repair station next week.
DennyH is offline   Reply With Quote
Old 08-11-2013, 05:33 PM   #7
Tinkerer and Putterer
 
Join Date: Mar 2013
Posts: 401
I'm wondering if there is a restriction in the exhaust causing the stall. Pulling the plugs on the exhaust used to clean out the spark arrestor would uncork things.
HappyGuy is offline   Reply With Quote
Old 08-14-2013, 10:03 PM   #8
Senior Member
 
Join Date: Jul 2013
Location: Baton Rouge
Posts: 497
I agree with bclemens on it being the fuel pump. Mine fizzled out doing exactly what you described at the dealer on the day of our orientation. The generator ran fine the week before when we touring the unit.

There is a problem Onan has with the fuel pumps on these gensets (according to some research I did). It took less than 15 minutes for the shop to replace my fuel pump but I am afraid that it may happen again. I've read that some folks have had them changed several times.

Bobby
bgilly is offline   Reply With Quote
Old 08-15-2013, 09:13 AM   #9
Member
 
Join Date: Jul 2013
Posts: 94
I took the MH to an Authorized Cummins/Onas repair center yesterday(fortunately only 20 minutes from my house) and the first thing the mechanic did was look at the fuel pump. He verified it was built between October 2012 and April 2013 and said he was replacing it. I will get the MH back on Monday and let everyone knows what he found.

Thanks for the input!!!
DennyH is offline   Reply With Quote
Old 08-16-2013, 01:40 PM   #10
Senior Member
 
Join Date: May 2013
Posts: 254
I wonder if there is a serial number range that applies to the Onan fuel pumps. Also, what replacement pump is being installed? Some have commented that their replacements failed.
__________________
Tim

2013 Forester #3051SF
2009 Toyoda Tacoma (toad)
2010 Newmar Dutchstar (Sold)
2011 Fleetwood Bounder (Sold)
trwmodela is offline   Reply With Quote
Old 08-16-2013, 03:08 PM   #11
Member
 
Join Date: Jul 2013
Posts: 94
Just received a call from the Cummins/Onan service center- Fuel pump replaced with a newer model and all is well!!! A/C starts and runs just fine. I will pick it up on Monday and if I can get any serial #'s I will pass them along.

Denny
DennyH is offline   Reply With Quote
Old 08-20-2013, 07:10 AM   #12
Member
 
Join Date: Jul 2013
Posts: 94
I guess I spoke too soon!! When I got the MH back home the same problem persists!!!! The gen does run much smoother but the A/C will not run. As soon as I switch the A/C on the gen quits. The guys at the Onan repair center put a load bank on the generator to simulate the the load and it passed so it does not appear to be a generator problem. I guess I have a different problem. Hmmmmmm! Very disgusted!
DennyH is offline   Reply With Quote
Old 08-20-2013, 07:32 AM   #13
Senior Member
 
Join Date: Apr 2011
Posts: 313
It still sounds like a generator problem. Even if there was an issue with the a/c pulling to much amperage, it would trip a breaker before shutting the genny down.
Acableguy06 is offline   Reply With Quote
Old 08-20-2013, 08:11 AM   #14
Senior Member
 
Join Date: Jul 2013
Location: Baton Rouge
Posts: 497
Quote:
Originally Posted by trwmodela View Post
I wonder if there is a serial number range that applies to the Onan fuel pumps. Also, what replacement pump is being installed? Some have commented that their replacements failed.
Mine was OEM. I don't know that Onan has a full grasp of what "lot" is affected. Some units do fine, some don't.
bgilly is offline   Reply With Quote
Old 08-20-2013, 08:34 AM   #15
Tinkerer and Putterer
 
Join Date: Mar 2013
Posts: 401
I know that a UPS in the computer world can often pass a simulated load test when the load is introduced gradually and fail when the same load is applied suddenly. I'm wondering if this is what is happening here. I know when I turn on my AC the lights brown out and the generator bogs down so I'm sure that the AC is pretty close to maxing out the surge capacity of our 4 kw Onan ultra quiet unit. Didn't have the same behavior from an older / louder Onan genset of the same rating. One thing I did do that helped smooth the operation of the generator and ease the strain from AC cut in was change the oil over to 5W30 synthetic in place of the 30W that came from the factory. The cost was minimal (10.00). The manual recommended the switch to get the broadest operating range and I noticed a difference in startup and load handling.

Another thing to try is to shut off everything, switch the fridge to gas, turn on the blower/AC fan, and then try the AC. If the genset handles the switch over then you are probably looking at a problem with the generators ability to handle sudden loads or possibly a bad / loose ground on the genset itself.
HappyGuy is offline   Reply With Quote
Old 08-20-2013, 08:55 AM   #16
Senior Member
 
Join Date: Nov 2012
Location: X
Posts: 2,781
Quote:
Originally Posted by Acableguy06 View Post
It still sounds like a generator problem. Even if there was an issue with the a/c pulling to much amperage, it would trip a breaker before shutting the genny down.
That is not the commonly reported experience.
BarryD0706 is offline   Reply With Quote
Old 08-20-2013, 09:23 AM   #17
Senior Member
 
Join Date: Jul 2013
Location: Baton Rouge
Posts: 497
Quote:
Originally Posted by DennyH View Post
I guess I spoke too soon!! When I got the MH back home the same problem persists!!!! The gen does run much smoother but the A/C will not run. As soon as I switch the A/C on the gen quits. The guys at the Onan repair center put a load bank on the generator to simulate the the load and it passed so it does not appear to be a generator problem. I guess I have a different problem. Hmmmmmm! Very disgusted!
Have you tried the air conditioner on shore power? Check it on shore power and check the amperage. It should hover around 15 amps with fan on high and compressor running.
Dometic states generator size required for these units is 3500 watt. The Onan 4000 is plenty.
Might check the voltage output of the generator. A loadbank doesn't care much about voltage but that Dometic A/C will.

Bobby
bgilly is offline   Reply With Quote
Old 08-20-2013, 09:25 AM   #18
Senior Member
 
Join Date: Apr 2011
Posts: 313
Quote:
Originally Posted by BarryD0706 View Post
That is not the commonly reported experience.
Ok, are the newer Onans set up to shut down on overload then?

In my experience with most generators on overload, the breaker on the genny should open before engine stalls due to running out of power. Unless the generator is severely over rated or to large of a gen end is put on a small motor. If an over load is shutting down an engine under load this would not be good on the voltage regulator either. Unless this is a function in the generator to just shut down with an overload.
Acableguy06 is offline   Reply With Quote
Old 08-20-2013, 09:51 AM   #19
Senior Member
 
John McClain's Avatar
 
Join Date: Jan 2013
Location: Ventura
Posts: 166
Is their a fault light blinking on the Gen start switch ?
__________________
F-250 . stealth 3210 solar pannels, fantastic fans. and life line batteries
John McClain is offline   Reply With Quote
Old 08-20-2013, 02:39 PM   #20
Member
 
Join Date: Jul 2013
Posts: 94
Lets see... Everything, including the A/C works on shore power. The generator runs fine on fan, both hi and lo, Microwave, etc. Just quits when A/C compressor comes on.
Another question- Where is the converter/charger on the 3011?? My house batteries are dead and will not charge over 11.93 volts.

Thanks
DennyH is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 05:36 AM.