Old 02-16-2014, 07:52 PM   #61
B47
Senior Member
 
Join Date: Jan 2012
Location: Keller, Texas
Posts: 6,090
Quote:
Originally Posted by OldCoot View Post
The controversy is crazy IMO. Circuit breakers will work as switches on an rv water heater for no more than it is used as an inside switch and so what if it goes bad after 3 or 4 years of this, they only cost about $8. No big deal. Have used individual circuit breakers as switches on my 2 overhead electric heaters in the garage for 12 years and they are still functioning as designed.
To each their own. I'm not going to look it up, but I just wonder what local building codes say about using CB's in place of switches.

And yes I'm talking buildings/homes just as OC is here and not RV's.
B47 is offline   Reply With Quote
Old 02-16-2014, 09:56 PM   #62
Senior Member
 
Join Date: Jul 2010
Posts: 7,948
If you guys really think you need to need more information about 120 volt circuit breakers used as switched in your house please read.
Hope you non-electricians can comprehend the terminology.

Electrical Circuit Breakers
This is the first of a series of articles intended to supplement your knowledge beyond the immediate requirements of the NEC. The following is a listing of the topics covered in this article.
  • Circuit Breakers Defined
  • Circuit Breakers As Switches
  • Currents To Break
  • Excessive and Over Currents
  • Current and Temperature
  • Circuit Breakers As High Temperature Limit Switches
  • Ampacities Of Electrical Conductors
  • Shorts To Ground
  • Arcing Faults
  • Bolted Faults
  • Safety First, Always First
  • NEC Requirements For Circuit Breakers
This article begins by defining circuit breakers then begins to delve into some of the nice to know details about the relation ships of current, temperature, and ampacities of conductors. The subject of faults and the various types of faults is then covered. The topic of safety while next to last is highlighted as being the of first order importance. The final topic for this part is a brief listing of some of the more general requirements relating to circuit breakers. This series of articles will cover the types of circuit breakers that one will find in many types of facilities today. The beginning article begins to lay a foundation (a review for many) and progress to the higher amperage sizes introducing molded case, Insulated case, drawout ending with the most advanced of all the microprocessor based circuit protective devices that are becoming more common. I hope you find this information of value.
At the end of this newsletter, you will find means of providing Mr. Holt with your very valuable comments about this article. Please be sure to put your two cents worth in, as Mike and I think it is worth a lot more than that.

Part 1
Circuit Breakers Defined
The American National Standards Institute (ANSI) defines a circuit breaker as: “A mechanical switching device, capable of making, carrying and breaking currents under normal circuit conditions. Also capable of making and carrying for a specified time and breaking currents under specified abnormal circuit conditions, such as those of a short circuit” The NEC defines a circuit breaker as “a device designed to open and close a circuit by non-automatic means, and to open the circuit automatically on a predetermined overcurrent without damage to itself when properly applied within it’s rating.” While the ANSI and the NEC definitions describe the same family of devices, they do have some differences, the same is true with the actual circuit breakers them selves. They are much the same in general terms; however there are a number of significant differences between the many types of electrical circuit breakers installed in many types of facilities today.

Circuit Breakers As Switches
Both the ANSI and the NEC definitions acknowledge the potential for the legitimate use of circuit breakers as switches. Switches (pass, but do not consume electrical power) are considered as being control devices, thus one may also say that a breaker is a control device, or a controller.
To aid in the understanding of a fine point, I offer this comparative example. A gas valve and a steam pressure relief valve are both controllers, one the fuel to the burners that aids in the development steam pressure, and the pressure relief valve that opens on excessive pressure. Both are controllers, one operating (the gas valve) the other safety (the relief valve).
Likewise in a parallel manner; we say that a circuit breaker can control and protect an electrical circuit. An electrical relay is an example of an operating control; it opens and closes the circuit. Circuit breakers are not designed as replacements for relays, operating controls.
There is as you may intuitively have anticipated an exception. Some circuit breakers are manufactured for use in a specific type of application. When a circuit breaker is designed to also be routinely used as an on-off switch to control 277 volt florescent luminaires they are marked SWD, for switch duty. This does not mean that a switch duty breaker can be used to manually control a traffic signal light where it will be cycled 1,000 or more times per day. The point is; the listing for switch duty (SWD) does not mean a circuit breaker can be used as a high frequency cycling operating control, such as a relay that has a life span rated in tens, if not hundreds of thousands of duty cycles.
While circuit breakers can be legitimately and safely used as switches, the frequency and duration of such use is very limited. Routinely circuit breakers are manually operated for service-maintenance, and repair type activities. With the preceding enhancing our understanding; we can say that circuit breakers can legitimately be used as switches, generally they are not intended for prolonged frequent or repetitive manual breaking and making type control of electrical energy utilization equipment.

Currents To Break
For general consideration and our immediate purposes; the amounts of currents circuit breakers are required to open and close can be divided into the following three broad current amplitude groups.
The first and lowest being rated load or less. For example: a 60 amp low voltage molded case thermo-magnetic breaker must be able to open or close 48 amps (80% of its rating) or less.
Next up in current quantity, this same breaker must be able to open or close Overload currents. Overloads for our purposes can be understood by reference to the NEC requirements overload protection for motors. Thermal overloads are commonly sized for some 115% of the motor’s nameplate full load amps. A motor with a service factor of one, and a rated load of 10 amps would be overloaded when pulling 11.5 amps or more. Overload currents can for our immediate purposes be considered to be percentages increases above rated normal load current.
The third and highest current level grouping is Short Circuit Currents. Short circuit currents can be considered as being fifteen (15) or more times normal rated load currents. In summation, circuit breakers may be called upon to open or close a circuit within a current ranging from no current flow, to as much as twenty (20) times or more its rated current. For a 100 amp breaker that could 2,000 amps or more.
As will be covered later, this high value of short circuit current is routinely exceeded by circuit breakers today. This should not be considered as implying that all circuit breakers can open unlimited amounts of current, as will be covered later on, they can not.

Excessive and Over Currents
The National Electrical Code (NEC) defines excessive current as “any current in excess of the rated current of the equipment or the ampacity of a conductor.“
Overcurrent conditions are caused by defective conductors, equipment, or an excessive workload burden placed upon the utilization equipment. Fuses and circuit breakers provide a level of safety against overcurrent conditions in electrical circuits. We therefore routinely say that fuses and breakers are overcurrent protective devices (OCPD). That is they protect the circuit’s components from overcurrent. To minimize the length of this paper, only automatic circuit breaker type overcurrent protective devices will be covered.
A circuit breaker’s primary functions are to provide overcurrent protection, and Isolation from energized circuit components and un-energized circuit components. Breakers must perform these functions when properly applied without fail in all circumstances completely and safely, while protecting the electrical circuit against overcurrent induced damage between normal rated current and the breaking capacity of the breaker called Ampere Interrupting Capacity (AIC). Now that is a big job and an important job.
Modern breakers routinely do their job day in and day out with very little maintenance. Like all things that are made by man, they do have limits and they do fail. Hopefully this paper will help you to better understand and appreciate the task performed by those little black boxes.
Hopefully this papaerHopefull


Current and Temperature

The movement of electrons (electricity) in a conductor produces a rise in the temperature of the conductor. Excessive temperature rise (caused by an excessive amount of electron collisions with base material atoms) can result in the melting of the wires material (copper), if it is allowed to rise as high as 1,980 degrees F. For a point of reference, the NEC limits the operating temperature of XHHW type conductor insulation to no more than 194 degrees F. Thus it can be understood that long before the copper wire will begin to melt, the wires insulation material will have melted and burned up.
Our first priority therefore is the temperature of the conductor’s electrical insulating materials. Differing types of insulating materials have different maximum design operating temperatures.

Circuit Breakers As High Temperature Limit Switches

Electrical energy is transported throughout an electrical circuit by the conductive path provided by electrically insulated wires. The material that performs the insulation function in the circuit has a high temperature limit far below that of the copper wire. Circuit breakers are routinely sized to limit the possible damage to the insulation material and not the copper wire. This being the case we can say that a circuit breaker limits the temperature of the connected-protected wire’s insulation materials.

Ampacities Of Electrical Conductors

Just how hot an electrically insulated wire can get before its insulation melts, suffers damage or a decrease in electrical dielectric strength (the ability to perform as an electrical insulator) and other physical features are well-known facts. The various types of materials used as electrical insulation have been tested and the results listed in what are called ampacity tables in the NEC in article 310.16.
How long an installed conductor’s insulation material will last without overload, is yet another question. Research is underway to determine the life of an installed insulated conductor. No doubt when completed, it will point to many factors that have a negative impact upon the inservice life span of an insulated conductor. For now we can book a safe bet that voltage spikes, vibration, environmental factors such as temperature, UV light, aggressive vapors and fluids, and relative humidity will all be proven to shorten to some degree the life of modern plastic type electrical insulation materials.
I suspect that many of these same factors also have a negative impact upon circuit breakers. I do not know of any research that defines the service life of circuit breakers. Nor am I aware of any research underway seeking to determine the service life of circuit breakers. Considering the importance of the safety provided to people and property circuit breakers provide, it is a bit puzzling as to why such research has not already been undertaken.
For many years various types of materials have been used as electrical insulators. Today conductors are made using material for outer jacketing, and for filling in the gaps (indices) between bundled round conductors. These materials may or may not be considered to be electrical insulators. Some medium and high voltage cables are made using materials that are considered to be conductive, or semi-conductive.

Ampacities Of Electrical Conductors

A short circuit is an unintended path through which current can flow. Any time current flows in a path that is not the normal path, we say that the circuit is shorted. Shorts are further defined by the nature of the shorted connection. A direct short is commonly a phase-to-phase short, which is when two hot (un-grounded) wires make an unintended contact with each other; a phase-to-phase short circuit has been created.
A circuit breaker must be able to respond to a short circuit, which can present a large current flow in a short period of time. A short circuit unlike an overload (typically a percentage increase not multiples of rated load current) presents its self in a very short period of time and will typically be multiples of the loads normal operating current.
Breakers are tested to determine their ability to clear a short-circuit without damage to them self’s. With a phase-to-phase short, the breaker will be required to open the circuit at the circuits rated phase-to-phase voltage. This would be the case independent of the system being grounded or un-grounded, that is either wye or delta solidly grounded or un-grounded or resistance grounded.

Shorts To Ground
When an insulated hot wire, (un-grounded) un-intentionally makes electrical contact with an electrically conductive-grounded object, a ground fault is created. The words ground fault means that there is a defect in the wires electrical insulation, and the faulted wire has shorted to ground. Many times a phase-to-phase short will develop into a ground fault, and the other way around. Either a phase-to-phase short can produce a ground fault, or a ground fault can produce a phase-to-phase short. The fault can be in one, two or three wires insulation materials.
Ground fault type circuit (GFCI) breakers will not be covered in this paper. The short circuit, overload current limiting nature of these types of breakers however will be covered. It is only the ground fault or residual current feature of GFCI type breakers that is not covered in this paper. A ground fault can present a current flow that is limited only by the impedance of the circuit and the capacity of the energy source supplying the faulted circuit. Ground faults can occur rapidly and can be either of low impedance type consuming a significant amount of electrical energy or as an arcing type fault with little total energy consumed. Some breakers are not designed to respond to arcing type shorts to ground.
Most breakers today will respond to a short to ground that is of the low impedance type as the current levels are normally multiples of normal load currents to which the circuit breaker has been manufactured to sense and respond to.
When installed in a grounded type system, such as a center grounded wye system, only one half of the systems phase-to-phase voltage will be broken by the breaker on a ground type fault. With an un-grounded type system a ground fault on the first phase to ground connection does not result in any current flow as the system is not referenced to ground. Yet should a second ground fault develop, the breaker will be required to break phase to phase system rated voltage.
With resistance grounded systems, the impedance of the supply system’s ground and the circuit’s ground fault combine to determine the amount of current drawn. Further, more detailed pursuit of understanding of the various electrical system grounding (earthing) methods used in America is beyond the limiting scope of this paper.

Arcing Faults
When a loose connection is made in the faulted circuit, so loose that the current flow is non-continuous, it is called an arcing or arc fault. This type of circuit defect is much like a welder using a welding electrode to produces an electric arc. Arcing type faults are the most difficult to locate (due to conductor concealment in conduit or inside enclosed cavities of walls) and can be the cause of fires. This type of defect is the opposite of a bolted fault, the circuit impedance is higher and the connection is very irregular (high frequency). They may last for only a fraction of a second and then cool down and not flow current, or heat up again and produce an arc between the two conducting surfaces.
During the A-C cycle there are two times that the supply circuit voltage goes to zero volts, there are two times when the circuit’s electromotive pressure is zero and an arc cannot be produced. This zero volts time helps to increase the faulted circuits impedance. The higher impedance makes it more difficult for the arc to re-establish it’s self again. These types of faults produce heat in a very localized area, this is how they can start a fire and not trip a common thermal-magnetic circuit breaker, their energy level is so low and they last for such a short time, that they are typically not detected by a circuit breaker or a fuse.
In response to this unique type of circuit defect, an entirely new family of circuit protectors called arc fault circuit interrupter (AFCI) type circuit breakers has been under development over for the last ten years. Because of the unique nature (microcomputers) of these devices they will not be covered in this short paper. The common circuit breaker will not respond to the development of an arcing type fault due to the low total amount of thermal energy developed by the arc and the very high frequency of the arc. Perhaps one can liken an arcing fault as an embryonic electrical circuit defect, unlike the defect that has fully developed and matured into an adult electrical fault such as a bolted fault.

Bolted Faults
Occasionally a short will develop that has a firm solid connection to either a grounded conductive object or another hot wire, that it is said to be a bolted fault. We are saying that it was not a loose connection, that it was not wiggling around. A bolted fault offers a lesser impedance to the flow of current than does an arcing type fault.
A loose connection type of fault may produce enough heat as to melt or plasticize the conductor’s material and having cooled enough to then produce a joint so firm and secure as to be comparable to a welded fault. Then we would call it a bolted fault. Circuit breakers are typically calibrated as to be capable of responding to a bolted type fault as they result in sufficient current flow to cause either the thermal or the magnetic trip elements of open the circuit.

Safety First, Always First
The exact nature of electricity, that is it can not be detected with the eyes, ears, or the nose, yet if it is touched, it can kill, must be remembered at all times. Circuit breakers are very reliable components of an electrical system, however they are man made; and are subject to becoming defective. Proper lock-out-tag-out procedures must be followed when working on electrical circuits above 50 volts. Proper personnel protective equipment must be in serviceable condition and properly worn. Safety is a requirement, not an option of every electrical task, large or small, be it routine or emergency in nature. Always use the three-step method when checking for voltage.
Take good care of your electrical test meters, having them checked at least every three years for insulation strength and for calibration as listed in the instruction booklet, or once a year. While a switch may visually indicate that the contacts have opened, a meter must be used to confirm that no voltage remains in the equipment to be worked on. Many times more than one source of power is provided to a machine.
When working with others do not assume that they know how to operate your meter, and do not assume that you know how to operate their meter. Take the time necessary to learn how to properly operate the test instruments that you will be required to use. I know that it is temporarily embarrassing to admit that we do not know something, but being found dead on the job, I believe to be more permanently embarrassing.

NEC Requirements For Circuit Breakers
The National Electrical code has several requirements for circuit breakers (overcurrent protective devices). The following is a listing of some of them. Others can be found in the various specific articles, such as 430 covering motors.
1) Main, feeder and branch circuit breakers must be installed in a readily accessible location.
2) A working space as wide as the equipment, or at least three feet wide and thirty inches deep, or deep enough to allow any doors to be opened at a 90 degree angle be provided in front of the equipment housing a breaker.
3) That when the operating handle is in the up position that it’s center line be not more than 6 ft. 7 inches above the floor or working platform.
4) That it be installed so that it is secure on its mounting surface.
5) That when installed that the up position be on and that when the operating handle is moved down that this be the off position.
6) That the breaker be clearly marked as to its off and on positions.
7) That the breaker be clearly marked, such that after installation that the amperage rating is clearly visible.
8) That the operating handle be of a trip free design, that is it can not be blocked or kept from tripping due to some type of obstruction keeping the operating handle from moving to the off, or tripped position.
9) When wires are connected to a breaker that they be properly torqued to the breaker’s termination points.
10) The NEC has specific requirements for both AFC and GFCI type circuit protectors that are mostly applicable based upon specific locations.

There are specific product type requirements for breakers to be listed by a nationally recognized testing lab (NRTL) such as UL that we will not be covering in this short paper. That means detailed information relating to engineering type testing and things that the circuit breaker manufacture must know about are not covered.
In the next part of this article we will review additional information covering functions, types, components, voltage ratings, ampere ratings, ampere interrupting current (AIC), TESTING -listing OF circuit BREAKERS, NOT all “breakers” are rated the same, the electrical arc, effects of current flow, thermal energy, thermal trip element and some information about magnetic trip elements.
Iggy is offline   Reply With Quote
Old 02-16-2014, 11:15 PM   #63
Anacortesians
 
Join Date: Oct 2010
Location: Anacortes, WA
Posts: 1,166
Not sure why your rig doesn't have an inside switch. Our '02 does, on the panel just below the kitchen counter. Maybe FR dropped the feature to save $5!
__________________
Frank and Eileen
No longer RVers or FR owners
F and E Damp is offline   Reply With Quote
Old 02-17-2014, 11:04 AM   #64
Senior Member
 
Join Date: Jul 2012
Location: Western New York State
Posts: 1,923
F and E, I think you hit the nail on the head. Probably when Warren Buffet and his Berkshire Hathaway friends bought the company they saw an opportunity to make another buck off each Forest River sold.

Iggy, great information. May I surmise that the article says its fine to use the circuit breaker for the hot water heater as a switch?
__________________
sherman12 and The Fabulous Miss Barb
2014 SportsCoach Cross Country 360DL DP
Former 2011 Georgetown 330TS
Kia Sportage on MasterTow Dolly
sherman12 is offline   Reply With Quote
Old 02-17-2014, 02:14 PM   #65
Senior Member
 
mbtelguy's Avatar
 
Join Date: Jan 2010
Posts: 191
Iggy

I may have miss it but the source of the information you provided would be.nice.

Also it would appear that the article you provided does not rule out the use of the Water Heater CB as a switch, primarily because of it’s infrequent use.

The following is taken from the article provided:

“While circuit breakers can be legitimately and safely used as switches, the frequency and duration of such use is very limited. Routinely circuit breakers are manually operated for service-maintenance, and repair type activities. With the preceding enhancing our understanding; we can say that circuit breakers can legitimately be used as switches, generally they are not intended for prolonged frequent or repetitive manual breaking and making type control of electrical energy utilization equipment.”

Iggy I’m sure you would agree, that one of the results of an individual accepting advice/information provided on the internet as valid, no matter how well intentioned.,can be unnecessary costs. I think.getting an second“non-internet” opinion is a good idea.

Gary
mbtelguy is offline   Reply With Quote
Old 02-17-2014, 02:23 PM   #66
B47
Senior Member
 
Join Date: Jan 2012
Location: Keller, Texas
Posts: 6,090
Just wonder if anyone has checked their local building codes regarding the use of a CB in place of a switch (Post#61).
B47 is offline   Reply With Quote
Old 02-17-2014, 02:51 PM   #67
Senior Member
 
Join Date: Jul 2010
Posts: 7,948
Quote:
Originally Posted by mbtelguy View Post
Iggy

I may have miss it but the source of the information you provided would be.nice.

Also it would appear that the article you provided does not rule out the use of the Water Heater CB as a switch, primarily because of it’s infrequent use.

The following is taken from the article provided:

“While circuit breakers can be legitimately and safely used as switches, the frequency and duration of such use is very limited. Routinely circuit breakers are manually operated for service-maintenance, and repair type activities. With the preceding enhancing our understanding; we can say that circuit breakers can legitimately be used as switches, generally they are not intended for prolonged frequent or repetitive manual breaking and making type control of electrical energy utilization equipment.”

Iggy I’m sure you would agree, that one of the results of an individual accepting advice/information provided on the internet as valid, no matter how well intentioned.,can be unnecessary costs. I think.getting an second“non-internet” opinion is a good idea.

Gary
Quote:
Originally Posted by B47 View Post
Just wonder if anyone has checked their local building codes regarding the use of a CB in place of a switch (Post#61).


My source is the National Fire Safety Code which includes National Electric code. It is actually for buildings both commercial and residential but in all fairness doesn't include trailers or motorhomes. So the RV industry implements their own and that is why some rigs have RVIA sticker on the outside of the access door. In most cases it it equal to NEC building codes.
Attached Thumbnails
Click image for larger version

Name:	RVIA_sticker.jpg
Views:	137
Size:	49.5 KB
ID:	46375  
Iggy is offline   Reply With Quote
Old 02-17-2014, 03:35 PM   #68
Senior Member
 
Join Date: Jul 2012
Location: Western New York State
Posts: 1,923
Ok, just re-read Iggy's article and previous posts. Now I'm up to speed that the electricians on the forum seem in agreement that CB's "should not be used" as switches. Got it.
__________________
sherman12 and The Fabulous Miss Barb
2014 SportsCoach Cross Country 360DL DP
Former 2011 Georgetown 330TS
Kia Sportage on MasterTow Dolly
sherman12 is offline   Reply With Quote
Old 02-17-2014, 06:13 PM   #69
Senior Member
 
Join Date: Jun 2012
Posts: 10,907
Quote:
Ok, just re-read Iggy's article and previous posts. Now I'm up to speed that the electricians on the forum seem in agreement that CB's "should not be used" as switches. Got it.
That's not what I got out of it. I got that SOME folks on this forum think you shouldn't but many of us think it's OK if you aren't doing it every day.

So as I said before, you need to read as much as you can and then make up your own mind.
__________________
1988 Coleman Sequoia - popup (1987-2009) - outlasted 3 Dodge Grand Caravans!
2012 Roo19 - hybrid (2012-2015)

2016 Mini Lite 2503S - tt (2015 - ???)
2011 Traverse LT, 3.6L, FWD
2009 Silverado 1500 Ext Cab, 5.3L, 4x4, 3.73
2016 Silverado 2500HD Dbl Cab, 6.0L 4x4, 4.10
rockfordroo is offline   Reply With Quote
Old 02-17-2014, 06:21 PM   #70
Senior Member
 
BillMFl's Avatar
 
Join Date: Jan 2013
Posts: 498
I leave the hot water breaker in the on position as my default setting. I do turn it off when storing the coach and winterizing it. If we want hot water in a hurry, we also turn on the gas in combination with the electric, usually for fast recovery after the queen bee uses all the hot water for her morning shower. We never boondock and to save LP we use RV park electric for hot water and a space heater in the bedroom. Usually only run the furnace to take the chill off during the morning.
BillMFl is offline   Reply With Quote
Old 02-17-2014, 07:18 PM   #71
Senior Member
 
Join Date: Mar 2009
Location: Baltimore Md.
Posts: 122
Quote:
Originally Posted by Iggy View Post
My source is the National Fire Safety Code which includes National Electric code. It is actually for buildings both commercial and residential but in all fairness doesn't include trailers or motorhomes. So the RV industry implements their own and that is why some rigs have RVIA sticker on the outside of the access door. In most cases it it equal to NEC building codes.

The National Electric Code (NFPA 70) is written and published by the NFPA.
It includes Recreational Vehicles and Recreational Vehicle Parks. Article 551 covers RVs.
Articles 240.83(D),404.11 and 410.141(A) cover Circuit Breakers used as SWITCHES.
Cherokee39 is offline   Reply With Quote
Old 02-17-2014, 07:33 PM   #72
Mod free 5er
 
Join Date: Mar 2008
Location: Concord, NC
Posts: 24,702
My electric heaters in the garage have a rheostat that also turns the unit off, but once I get the desired setting, I leave it there for the winter and turn the units on/off with the circuit breakers. 12 yrs and still working great.

BTW, do the same with the 220v metal lathe, mig welder, tig welder and air compressor. If they are not being used, the circuit breakers are switched off, been doing this for over 40 yrs and never had to replace a breaker.
__________________
OldCoot is offline   Reply With Quote
Old 02-17-2014, 07:40 PM   #73
Average Joe
 
MrJoe's Avatar
 
Join Date: Jul 2013
Location: Mechanicsville, MD
Posts: 689
Nice job Iggy... Unbelievable that all this started with the flick of a switch

I'm not even getting into this one.
__________________
Joe and Karen
2014 Sunseeker 2450sf

Southern Maryland and Beyond!

MrJoe is offline   Reply With Quote
Old 02-17-2014, 07:41 PM   #74
Senior Member
 
Join Date: Mar 2009
Location: Baltimore Md.
Posts: 122
Member Manufacturer Compliance Standards

printer Print Page email Email Text



Home » Standards and Education » Standards » Member Manufacturer Compliance Standards

RVIA Member Manufacturers of Recreational Vehicles and Recreational Park Trailers agree to build their units to the following RVIA adopted standards.

Recreational Vehicles (RV)

2011 edition - NFPA 1192 Standard for RVs - Covers Plumbing, propane and Fire & Life Safety

2011 edition - ANSI/RVIA Standard for Low Voltage Systems in Conversion & RVS 12V Standard - Covers 12 Volt Electrical Systems

2011 edition - National Electrical Code (NEC) (See Article 551) - Covers 120V Electrical Systems

RVIA Handbook - A guide to ANSI/NFPA 1192 -Outlines enforcement positions based on the above standards that are used by RVIA inspectors during RV manufacturer member inspections

Recreational Park Trailers (RPT)

2009 edition - ANSI A119.5 Recreational Park Trailer Standard - Covers Fuel Systems, Fire & Life Safety, Plumbing and Construction Requirements

2011 edition - National Electrical Code (NEC) (See Article 552) - Covers 120V and 12V Electrical Systems


This information is from RVIA website.
Note the reference to NFPA 70 article 551 and 552 for park models.
You can believe what you want however when the printed codes and the manufactures specification sheets (Square D, Siemons, Cutler Hammer etc)
permit the use of a breaker as a switch I will use it as a switch. Keep in mind this is in an RV and not an airplane, helicopter, space shuttle or ocean going ship.
Cherokee39 is offline   Reply With Quote
Old 02-17-2014, 08:07 PM   #75
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
If I want to turn my water heater off on electric I flip the breaker. People keep saying about the electrical code. In my Rv I have 7 circuits on a 14 ga 15 amp breaker, you would never get away with that in a home under either the national code or your County Inspection. If you want to use the CB as a switch go ahead and do it. The worst thing that will happen is that it will become weak, at that time change it for 12.00 bucks. It is worst to put 7 circuits on a 15 amp 14 ga wire but they do it at FR on a 8289WS 5th wheel which is way more dangerous then flipping a breaker as a switch. Just my 2 cents worth. By the way that 7 circuit run also includes my Refer and TV on it and all my plugs outside and in the main area. That flips daily.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 02-17-2014, 08:16 PM   #76
Denver, CO
 
garbonz's Avatar
 
Join Date: Jan 2013
Location: Denver, CO
Posts: 2,102
I put an illuminated switch for the converter and for the hot water heater. That way I know when they are on, very cute.
__________________
2017 Fuse 23T
garbonz is offline   Reply With Quote
Old 02-17-2014, 10:48 PM   #77
Senior Member
 
Join Date: Jul 2010
Posts: 7,948
You know this thread has changed so much it is useless.
You guys would argue and disagree if I said the sun will rise tomorrow.
Iggy is offline   Reply With Quote
Old 02-17-2014, 10:58 PM   #78
Average Joe
 
MrJoe's Avatar
 
Join Date: Jul 2013
Location: Mechanicsville, MD
Posts: 689
Depends on what you mean by rise.
__________________
Joe and Karen
2014 Sunseeker 2450sf

Southern Maryland and Beyond!

MrJoe is offline   Reply With Quote
Old 02-17-2014, 11:23 PM   #79
B47
Senior Member
 
Join Date: Jan 2012
Location: Keller, Texas
Posts: 6,090
Quote:
Originally Posted by Iggy View Post
You know this thread has changed so much it is useless.
You guys would argue and disagree if I said the sun will rise tomorrow.
Depends on whether you say it will rise in the East or West.
B47 is offline   Reply With Quote
Old 02-18-2014, 10:19 AM   #80
Senior Member
 
Join Date: Jul 2012
Location: Western New York State
Posts: 1,923
Reminds me of what I tell my DW, the sunset in Key West is not the same as the sunset in Buffalo over lake Erie.

Sorry, way off topic.
__________________
sherman12 and The Fabulous Miss Barb
2014 SportsCoach Cross Country 360DL DP
Former 2011 Georgetown 330TS
Kia Sportage on MasterTow Dolly
sherman12 is offline   Reply With Quote
Reply

Tags
heater, hot water, water, water heater

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 08:10 PM.