Old 06-20-2017, 08:20 PM   #1
dgb
Member
 
Join Date: Feb 2017
Location: Paso Robles, CA
Posts: 30
Factory Gen Set will not handle both AC units

2017 Georgetown 329DS. Just stopped in Las Vegas (it was VERY warm outside). When trying to run both AC units at the same time using the generator, both air conditioners started and ran for a little while. Then, the auto transfer relay switch started making a buzzing sound when the 2nd (rear) air conditioner was cycling on. The front air conditioner then shut down completely.

The front AC unit is a Dometic 15K. The rear AC is a Dometic 13.5K. The generator is a Onan RV OG 5500. The Transfer Relay is a Progressive Dynamics Model PD52.

Seems like the generator should be large enough to handle both AC units running at the same time. The buzzing noise sounds like an overload situation. Could the Transfer Relay be the problem?

Has anyone experienced this?
__________________
2017 Georgetown 329 DSF
1999 Jeep Wrangler
2008 KTM 450 EXCR
dgb is offline   Reply With Quote
Old 06-20-2017, 08:45 PM   #2
Senior Member
 
chrisbailey13's Avatar
 
Join Date: Apr 2014
Posts: 514
One of the easiest work arounds I have found is to turn off the electric Water Heater. If I run out of hot water, I simply use the propane water heater elements.
Also, stagger when you turn on the AC Units. I typically turn on the larger unit first and let it run until I hear the compressor kick on, then I turn on the second smaller unit. what you don't want is both units kicking on the compressor at the same time, that surge will choke your GENSET.
__________________
2014 Georgetown XL 352QS
2013-2019 Days Camped-502
chrisbailey13 is offline   Reply With Quote
Old 06-20-2017, 08:48 PM   #3
Tim & Lisa Trempert
 
Join Date: Sep 2008
Posts: 458
No problem at all for the generator. Sounds like a transfer switch problem.
__________________
Tim & Lisa
2011 Georgetown 350
Trempert is offline   Reply With Quote
Old 06-20-2017, 09:06 PM   #4
Member
 
Join Date: Sep 2014
Location: Versailles,Kentucky
Posts: 42
I have had the same problem with my 2014, 328TS. It happens when we're tailgating in RV lot on a 90+ degree day and sun shining on the back storage compartment where the transfer switch is located. It has helped to open the storage doors on both sides to get ventilation and cool down the switch.
Donamac is offline   Reply With Quote
Old 06-20-2017, 09:07 PM   #5
Phat Phrog Stunt Team
 
AquaMan's Avatar
 
Join Date: Apr 2012
Location: Tipp City, OH
Posts: 7,154
When stopped in very warm (hot) conditions, I open the door to the generator and/or transfer switch to allow air to move around and not get trapped. I've had my generator vapor lock on very hot days (even while going down the road). The heat from the engine combined with the generator heat caused the problem. Hasn't been an issue since that one time. It was 103-105 degrees in SD last summer.
__________________
2016 Georgetown 364TS
2017 Jeep Rubicon Recon toad
Nights Camped 2019 - 17
AquaMan is offline   Reply With Quote
Old 06-20-2017, 10:38 PM   #6
Senior Member
 
Dijoeboss's Avatar
 
Join Date: May 2013
Posts: 532
I've been fighting this exact same problem since 2013, 18K miles later..... NO FIX !!!! I've added hard start capacitors to the A/C units, I've changed the transfer switch TWICE!! I've verified the oil level is good in the generator, I've had the A/C units amp draws checked by myself and an RV dealer, no problem there, I've had a Cummins dealer check the HZ level of the generator, all ok. Good luck with this, I would still love to hear any NEW ideas, but after 4 years, I'm not very hopeful.
Dijoeboss is offline   Reply With Quote
Old 06-21-2017, 10:00 AM   #7
dgb
Member
 
Join Date: Feb 2017
Location: Paso Robles, CA
Posts: 30
I tried it again when I got home (CA). Ran the front AC for a while, then turned on the rear one. They both ran without shutting off. The generator was running with a definite load. I checked the Transfer Switch in the back compartment. The switch box was definitely hot. Had a slight burning smell. I will open the box later today when it has cooled off and check for burnt wires. I failed to note that when I was running the system yesterday (Vegas), it was 120 degrees. When I ran the units at home it was only 95. The only other thing that draws power is the 120v fridge. I would think that the system was designed to handle the loads that the factory installed. I will report on what I find in the transfer switch.
__________________
2017 Georgetown 329 DSF
1999 Jeep Wrangler
2008 KTM 450 EXCR
dgb is offline   Reply With Quote
Old 06-21-2017, 12:29 PM   #8
Senior Member
 
Bluepill's Avatar
 
Join Date: Jun 2015
Location: Pensacola, FL
Posts: 1,645
1. Dometic calls for 5KW genny capacity for dual 15K BTU A/C units. That is just for the A/C with no other loads like reefer, water heater, converter/charger, etc.

2. Generators derate at high temps. Onan Manual states "1% power derate for every 10 degrees above 77". At 120 degrees you were down about 250 watts. They also derate for altitude.

3. You might consider a split system with a small portable genny to run loads other than the A/C units.
__________________
2019 Coachmen Freedom Express 192RBS
2015 T12RBST Flagstaff Hardside

Disclaimer: The actual value of my "Two Cents" of advice varies just like a bitcoin.
Bluepill is offline   Reply With Quote
Old 06-21-2017, 01:52 PM   #9
Senior Member
 
Join Date: Aug 2015
Location: Out West Somewhere
Posts: 163
IMO, it was the heat that caused your problem. First of all, your 5500 generator would put out approximately 45 amps in a normal operating environment. As was stated, the efficiency of generators decreases rapidly with temperature rises.

In my experience, the 13.5 and 15 K AC both use around 18 to 20 amps each while running. Under startup, the amps jump up really high. So running both AC units was using somewhere around 36 to 40 amps, leaving you with very few amps to handle the other loads. That, combined with the drop in generator efficiency, IMO is the source of your problem.

My Class A's had Onan's that handled both AC units with power to spare BUT they all had EMS units to control the usage. The really big diesels have up to 12K generators.
WayneLee is offline   Reply With Quote
Old 06-21-2017, 02:29 PM   #10
Phat Phrog Stunt Team
 
AquaMan's Avatar
 
Join Date: Apr 2012
Location: Tipp City, OH
Posts: 7,154
Quote:
Originally Posted by dgb View Post
I tried it again when I got home (CA). Ran the front AC for a while, then turned on the rear one. They both ran without shutting off. The generator was running with a definite load. I checked the Transfer Switch in the back compartment. The switch box was definitely hot. Had a slight burning smell. I will open the box later today when it has cooled off and check for burnt wires. I failed to note that when I was running the system yesterday (Vegas), it was 120 degrees. When I ran the units at home it was only 95. The only other thing that draws power is the 120v fridge. I would think that the system was designed to handle the loads that the factory installed. I will report on what I find in the transfer switch.
The heat is what is causing your problems. Like I had mentioned before, open your access doors to genny and transfer switch. I would check inside the transfer switch and make sure the lugs are tight also. I'm pretty sure I would melt at 120 degrees!
__________________
2016 Georgetown 364TS
2017 Jeep Rubicon Recon toad
Nights Camped 2019 - 17
AquaMan is offline   Reply With Quote
Old 06-21-2017, 10:14 PM   #11
Senior Member
 
Bayouownbeer's Avatar
 
Join Date: Jul 2010
Location: Chauvin LA
Posts: 254
Quote:
Originally Posted by AquaMan View Post
The heat is what is causing your problems. Like I had mentioned before, open your access doors to genny and transfer switch. I would check inside the transfer switch and make sure the lugs are tight also. I'm pretty sure I would melt at 120 degrees!
I had exc same issue. I turn off my water heaters and took the metal cover off the transfer switch. Yes the wires are exposed but only I should be digging in there. Seems to have helped
__________________
2017 Georgetown 364TS
Bayouownbeer is offline   Reply With Quote
Old 06-21-2017, 10:24 PM   #12
Senior Member
 
B and B's Avatar
 
Join Date: Jun 2013
Posts: 10,833
Send a message via AIM to B and B
Every TV RF Truck I used had the this same Onan Genset. We added large 10 inch fans in the bay doors to get the air moving.
B and B is offline   Reply With Quote
Reply

Tags
factory


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 05:19 PM.