Generator Issue?

2017 Georgetown 364. Picked up in April. My last 2 trips, driving down the road with generator running, both roof AC units running, after about 2 hours of non-stop driving, all 120v power in the coach goes away (AC units, refrigerator, microwave, TVs, everything). Generator never stops. No breakers are blown. As soon as I stop the coach and turn of just one, either one, of the roof AC units via the thermostat, all 120v power returns like nothing ever happened.

Thoughts?
Stymie71 is offline   Reply With Quote
Old 06-29-2016, 05:07 PM   #2
Member
 
Join Date: Apr 2016
Posts: 38
Other facts:

Doesn't do it just sitting still in a field or while camping and running solely on generator, at least not yet. Have camped 72 hours running on generator without issues.

Also, does not do this while on shore power. Again, at least not yet.
Stymie71 is offline   Reply With Quote
Old 06-30-2016, 01:20 PM   #3
Phat Phrog Stunt Team
 
AquaMan's Avatar
 
Join Date: Apr 2012
Location: Tipp City, OH
Posts: 7,154
Had/having same issue while while on our trip out west. What I've been able to deduce is that if losing power while generator is running, the transfer switch has kicked out or the breakers on the generator have kicked. I've had the generator completely stop also. This I'm thinking has to do with heat and or fuel vapor lock. It has been in the upper 90's and 100's most of the time. I have a couple people researching possible solutions. Not sure why the transfer switch won't kick back in when it kicks out though. It will if I turn generator off and back on.


Sent from my iPhone using Forest River Forums
__________________
2016 Georgetown 364TS
2017 Jeep Rubicon Recon toad
Nights Camped 2019 - 17
AquaMan is offline   Reply With Quote
Old 06-30-2016, 01:54 PM   #4
Senior Member
 
Dijoeboss's Avatar
 
Join Date: May 2013
Posts: 532
Generator Issue?

I have listed this issue in a thread "transfer switch won't stay engaged" I think is what it's called, no fix that I can find yet after battling it for 3 years.


2013 Georgetown XL 350
Bunkhouse
2002 F250 4X4 CC
2012 Jeep Liberty
Dijoeboss is offline   Reply With Quote
Old 06-30-2016, 02:15 PM   #5
Phat Phrog Stunt Team
 
AquaMan's Avatar
 
Join Date: Apr 2012
Location: Tipp City, OH
Posts: 7,154
Quote:
Originally Posted by Dijoeboss View Post
I have listed this issue in a thread "transfer switch won't stay engaged" I think is what it's called, no fix that I can find yet after battling it for 3 years.


2013 Georgetown XL 350
Bunkhouse
2002 F250 4X4 CC
2012 Jeep Liberty

The issue may not be the transfer switch but the generator itself. I think that may be my issue. I think the heat is causing the generator to skip a beat and allowing the switch to fall out and for some reason, not re-engaging. I had hard time getting the generator to start again when this happened. I think the fuel line vapor locked, because I had to prime it for a couple minutes to get the fuel line to fill (it will vibrate when not completely pressurized).


Sent from my iPhone using Forest River Forums
__________________
2016 Georgetown 364TS
2017 Jeep Rubicon Recon toad
Nights Camped 2019 - 17
AquaMan is offline   Reply With Quote
Old 06-30-2016, 04:22 PM   #6
Senior Member
 
Dijoeboss's Avatar
 
Join Date: May 2013
Posts: 532
Quote:
Originally Posted by AquaMan View Post
The issue may not be the transfer switch but the generator itself. I think that may be my issue. I think the heat is causing the generator to skip a beat and allowing the switch to fall out and for some reason, not re-engaging. I had hard time getting the generator to start again when this happened. I think the fuel line vapor locked, because I had to prime it for a couple minutes to get the fuel line to fill (it will vibrate when not completely pressurized).


Sent from my iPhone using Forest River Forums

If you come up with a fix, I'd love to hear about it, I've had no success with anything I've tried in 3 years. ( mines not the transfer switch, it's been replaced twice.) Cummins has looked at generator- no problem found, RV repair shop checked a/c amp draws etc. no problem found.


2013 Georgetown XL 350
Bunkhouse
2002 F250 4X4 CC
2012 Jeep Liberty
Dijoeboss is offline   Reply With Quote
Old 06-30-2016, 04:55 PM   #7
Phat Phrog Stunt Team
 
AquaMan's Avatar
 
Join Date: Apr 2012
Location: Tipp City, OH
Posts: 7,154
What's the weather like when this happens? Hot? Cold? Both?


Sent from my iPhone using Forest River Forums
__________________
2016 Georgetown 364TS
2017 Jeep Rubicon Recon toad
Nights Camped 2019 - 17
AquaMan is offline   Reply With Quote
Old 06-30-2016, 05:55 PM   #8
Member
 
Join Date: Apr 2016
Posts: 38
It has been blistering hot. But my generator has never died. And, only while actually driving. I sat in a field in nearly 100 heat for 3 days running on generator with no issue. Left the field on way home and at about the 2 hour mark the power went out, but the generator never quit.
__________________
________________________
2017 Georgetown 364
2011 Dodge Grand Caravan
Stymie71 is offline   Reply With Quote
Old 07-01-2016, 04:57 AM   #9
Senior Member
 
cjd10's Avatar
 
Join Date: Sep 2013
Location: Charleston SC
Posts: 585
Mine has done exactly what you describe. We also will spend a few days running the generator without issue but as soon I start driving it would happen. Only happened on hot days.
I switched from using 30W oil to Onamax 15W-40 oil. Make sure the oil level is full. Even a little bit low will cause this. On mine the oil was getting hot and sloshing around enough to cause the low oil sensor to momentarily shut down the generator and thus the transfer switch.
Since changing I have only had this happen once in the last year and that was when the oil was old and should have been changed proir to that trip.
__________________
2014 Georgetown 351DS

Charleston SC
1 Boston Terrier, 1 Frenchie, Two Siamese
Gonna miss you Toby, Sage, and Izzie. RIP
cjd10 is offline   Reply With Quote
Old 07-01-2016, 07:28 AM   #10
Member
 
Join Date: Apr 2016
Posts: 38
I haven't check oil level yet for sloshing. I'll check tonight. Thx.
__________________
________________________
2017 Georgetown 364
2011 Dodge Grand Caravan
Stymie71 is offline   Reply With Quote
Old 07-02-2016, 01:11 PM   #11
Phat Phrog Stunt Team
 
AquaMan's Avatar
 
Join Date: Apr 2012
Location: Tipp City, OH
Posts: 7,154
Just got home from our trip and ran the generator for 24 hours without a hiccup. But the temps were below 85. The only time I had issue was when temps were above 95 and as high as 107 in WY! My buddy who has 364 also was having transfer switch problems, but his would kick back in after a couple minutes and the generator stayed running. I'm still believing that my issue is vapor lock.


Sent from my iPhone using Forest River Forums
__________________
2016 Georgetown 364TS
2017 Jeep Rubicon Recon toad
Nights Camped 2019 - 17
AquaMan is offline   Reply With Quote
Old 07-02-2016, 05:08 PM   #12
Member
 
Join Date: Apr 2016
Posts: 38
I just drove 2 hours in 95+ heat. Stopped and listened outside RV when AC units quit. Generator still running. But, transfer switch makes a grinding noise every 10-15 seconds or so. And, when it does this the generator acts like a load is being turned on.

I checked oil level and it was fine. So, something is causing transfer switch to activate back and forth. And, that switch was very hot to the touch.

I am now camping on shore power without issue.
__________________
________________________
2017 Georgetown 364
2011 Dodge Grand Caravan
Stymie71 is offline   Reply With Quote
Old 07-02-2016, 07:25 PM   #13
Phat Phrog Stunt Team
 
AquaMan's Avatar
 
Join Date: Apr 2012
Location: Tipp City, OH
Posts: 7,154
Low voltage will make sounds like that in the transfer switch. Noticed this on a low voltage shore power situation. Could also be heat related.


Sent from my iPhone using Forest River Forums
__________________
2016 Georgetown 364TS
2017 Jeep Rubicon Recon toad
Nights Camped 2019 - 17
AquaMan is offline   Reply With Quote
Old 07-02-2016, 10:03 PM   #14
Senior Member
 
Dijoeboss's Avatar
 
Join Date: May 2013
Posts: 532
When the transfer switch drops out, for whatever reason, vapor lock, low voltage, etc. whatever loads are on- most likely the A/C's, the transfer switch can't RE-engage due to the load, so it thumps loudly as it tries to reengage and can't, so it kicks in/out rapidly. Turn the A/C units off, the transfer switch will reengage and allow the A/C unit(s) to be restarted. This issue seems to be worse when the temps are high. I've tried jumping across the transfer switch with wires to eliminate the transfer switch, the load will kill the generator, SO that didn't work. Everything I've tried- nothing in 3 years has resolved this issue.


2013 Georgetown XL 350
Bunkhouse
2002 F250 4X4 CC
2012 Jeep Liberty
Dijoeboss is offline   Reply With Quote
Old 07-03-2016, 05:16 PM   #15
Phat Phrog Stunt Team
 
AquaMan's Avatar
 
Join Date: Apr 2012
Location: Tipp City, OH
Posts: 7,154
Sounds as though your generator is too small for the load you are putting on it. Have your AC units checked for amp draw and possibly put on hard start capacitors and fan delays. This will help lower the amp draw.


Sent from my iPhone using Forest River Forums
__________________
2016 Georgetown 364TS
2017 Jeep Rubicon Recon toad
Nights Camped 2019 - 17
AquaMan is offline   Reply With Quote
Old 07-03-2016, 09:17 PM   #16
Member
 
Join Date: Apr 2016
Posts: 38
So, a brand spanking new RV comes with either a generator or a transfer switch that will not carry the load in hot weather, which is when you need the AC units the most? Sounds off.

Has anyone ever talked with FR about this issue?
__________________
________________________
2017 Georgetown 364
2011 Dodge Grand Caravan
Stymie71 is offline   Reply With Quote
Old 07-03-2016, 09:49 PM   #17
Senior Member
 
Bluepill's Avatar
 
Join Date: Jun 2015
Location: Pensacola, FL
Posts: 1,645
Hot weather creates lower-density air, which changes the air-fuel ratio of the gasoline-to-air mixture supplied to the genny's engine. This reduces the power that the engine can produce, and shows up mostly when the engine is working hard to produce its maximum power. The same thing happens as altitude goes higher. Electronic fuel injection can reduce this effect by sensing intake air temperature as well a altitude. If you have a carburator, no automatic adjustment is possible.

Bottom line is that you should try to limit the electrical load on your genny in hot weather and/or at altitudes above 5000 feet.

Tech info here:

http://www.dieselserviceandsupply.co...ut_Rating.aspx
__________________
2019 Coachmen Freedom Express 192RBS
2015 T12RBST Flagstaff Hardside

Disclaimer: The actual value of my "Two Cents" of advice varies just like a bitcoin.
Bluepill is offline   Reply With Quote
Old 07-04-2016, 12:17 AM   #18
Member
 
Join Date: Dec 2015
Posts: 96
This is the sound

https://vimeo.com/173312206
__________________
2016 364TS
Kevin M. is offline   Reply With Quote
Old 07-04-2016, 07:16 AM   #19
Senior Member
 
copsuno's Avatar
 
Join Date: Apr 2011
Location: Greer, SC
Posts: 277
I have a six year old coach, 5.5 kW gen, it will not handle both airs at same time. I recommend you drive with one air and see what happens. Biggest voltage draws in motor home are air and microwave/convection. Just a thought.
__________________
Logic will carry you from point A to point B. Imagination will carry you everywhere. "Albert Einstein". 2011 Georgetown 360, Bride of 45yrs, and 2014 Chev Equinox toad, what more could you ask for.
copsuno is offline   Reply With Quote
Old 07-04-2016, 08:56 AM   #20
Member
 
Join Date: Nov 2007
Posts: 52
Quote:
Originally Posted by Bluepill View Post
Hot weather creates lower-density air, which changes the air-fuel ratio of the gasoline-to-air mixture supplied to the genny's engine. This reduces the power that the engine can produce, and shows up mostly when the engine is working hard to produce its maximum power. The same thing happens as altitude goes higher. Electronic fuel injection can reduce this effect by sensing intake air temperature as well a altitude. If you have a carburator, no automatic adjustment is possible.

Bottom line is that you should try to limit the electrical load on your genny in hot weather and/or at altitudes above 5000 feet.

Tech info here:

Factors Affecting Power Generator Output Rating | Diesel Service
That's a great point regarding Density Altitude...isn't there an adjustment on the genny that can be made for use in higher elevations? For example, Phoenix already has a DA of 3500' at 6AM and should rise another 1000' with daytime heating.
__________________
2020 GT7 36K7 (on order and should be delivered soon)
2013 Georgetown 350 XL (sold)
2018 Ford Focus toad
chill960 is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 01:50 AM.