Old 08-03-2014, 06:57 PM   #31
fast murray's Avatar
The fact that you can plug in with all the breakers off in the coach makes you want to say the problem is right in the electrical panel of the coach. Make sure the neutral and grounding conductor aren't tied together in there. It would be interesting to test between the grounding prong and the neutral prong of your RV cord and see if there's any resistance between the two. There should be none. I'd also take that meter with the main off and make sure you're getting power to the line side of the main breaker and that the GFCI isn't tripping before you think it is. It's amazing the advice that RV dealerships will hand out. Removing the GFCI from your garage is not the answer. It's like listening to the electrical guy in Menards, bad idea!
2004 Wildcat 28BH
2012 Ram 2500 CCSB 6.7CTD
fast murray is offline   Reply With Quote
Old 08-03-2014, 07:15 PM   #32
Originally Posted by Krazymace View Post
So what's my cure? Appreciate all your info. Good stuff!
Inspection: no conductive material (copper wire, plug prongs) should be able to get wet.
Measurement: with power code disconnected from that GFCI outlet, measure between each conductor with an ohm meter. Anything connection between any two conductors that is near to or less than 20,000 ohms is a fault. A meter can help narrow down the search for that fault.
Testing: when everything is dry and the GFCI does not trip, then use a garden hose to slow wet different locations until the GFCI trips. You need not worry much about being electrocuted becaues the GFCI should trip before you can be shocked. As soon as a wet spot trips the GFCI, then you have a suspect location.
And finally, if the cable has a hole or crack, then moisture may have gotten inside. Getting inside of a cable dry before sealing it can be challenging. One popular solution was to put the break into a sealed container with rice. Over a week, rice may draw out that moisture.
One correction. Neutral and safety ground wire should not be connected anywhere until both meet at the pole. Or in this case, at the main breaker box in the house. If neutral and ground are shorted together in the coach breaker box, then that would explain a house GFCI trip and no coach GFCI trips.
westom is offline   Reply With Quote
Old 08-04-2014, 11:10 AM   #33
Freds342's Avatar
Everyone keeps forgetting the fact that the garage breaker doesn't pop when the 50-A cable is plugged in and the mains are open.
That shows us that the problem is after the main, NOT in the cable.
2005 Georgetown 342DS XL, Full Banks Package
2005 Liberty Renegade 4X Toad
1989 Wrangler Sahara Toad
1984 19.5' Beachcraft i/o 5.o liter, 4-bbl (and you thought your Moho sucked gas!)
D/W Carole and Maggie the Teacup Lab (Black Chihuahua)
Freds342 is offline   Reply With Quote
Old 08-04-2014, 03:27 PM   #34
Krazymace's Avatar
It actually does. I adapt my 50 amp down to a 30 amp extension cord and then adapt it down to a 20 amp GFI outlet. The second I plug into 20 amp, my garage GFI pops. If I plug directly into 30 am, which I have in my RV storage barn, I have no issues in my coach. I realize I have no 30 amp GFI protection.
Krazymace is offline   Reply With Quote
Old 08-05-2014, 11:38 AM   #35
Freds342's Avatar
I guess your post #7 confused me. It stated that as soon as you turned the main breaker in the MoHo on it tripped.
Old 08-05-2014, 05:54 PM   #36
bend302's Avatar
When you solve this problem, please post the results. I really don't understand electricity that well and would like to hear the fault and the fix.
Bill
Life is a journey, not a destination.
2005 Georgetown 359ts
Bill & Virginia, Kentucky
Nights camped in 2011...78 , 2012...73,
Nights camped in 2013...123, 2014 ...101
bend302 is offline   Reply With Quote
Old 08-05-2014, 10:04 PM   #37
Reason for tripping is layman simple. For every electron going to an RV (ie on black wire), a same electron must be returning to the house (ie on a white wire). A GFCI measures that current. For 20,000 milliamps, if five milliamps are unaccounted for, then a human life is at risk. So the GFCI cuts off current.
A GFCI measures current going out and current coming back. If not same, then current is going somewhere else; might harm a human. So a GFCI trips. A GFCI is that simple.
Old 10-03-2014, 07:57 PM   #38
Krazymace's Avatar
Brought my MH back from dealer today. Leaving on a trip tomorrow. I cannot connect to a GFI or non GFI circuit. If I connect to a GFI outside my house, the House/garage GFI trips. If I connect to a non GFI, it trips the breaker on my house electrical panel. Nothing in on in the MH. Help!!
Old 10-04-2014, 01:30 AM   #39
Indymule's Avatar
If it's tripping the breaker on a non GFI circuit the instant you plug in, you have a direct short somewhere. I would take it back to the dealer
Jay & Maria - Camp Dog Joplin
2018 Cedar Creek Champagne 38EL
2017 Ford F350 Crewcab Dually Diesel
Ham Callsign K9NDY
Indymule is offline   Reply With Quote