Quote:
Originally Posted by brianneal View Post
......so "JD-ford-hd" are you saying since no AC is flowing to the coach when the generator is running it's because the coach batteries are bad? Advice??? Like the last post said, it works sometimes and others it doesnt??
Try this to see if low house battery voltage is the problem.
1. Start the "truck" engine, let it run a few minutes to charge the chassis battery.
2. Hold the "boost" rocker switch on the dash while simultaneously pressing the generator start switch.

If the generator starts up and you hear the microwave beep(that's what I listen for), you know the generator is "genning".....!! I have not convinced myself that low voltage alone would keep the generator from working. My feeble mind thinks that if there is enough voltage to turn the generator over AND start it, then that should also be enough to "flash" the armature as well.
__________________

__________________
"IF IT AINT GOT A MOTOR, I AINT INTERESTED"
jd-ford-hd is offline   Reply With Quote
Old 06-14-2011, 05:57 PM   #12
Senior Member
 
jd-ford-hd's Avatar
 
Join Date: Aug 2009
Location: Middle Tennessee
Posts: 160
Would be nice to know what brand genset everyone posting here has. Mine is a Generac Guardian 6500. Lets see if this problem is brand related.
__________________

__________________
"IF IT AINT GOT A MOTOR, I AINT INTERESTED"
jd-ford-hd is offline   Reply With Quote
Old 06-22-2011, 10:56 AM   #13
Junior Member
 
Join Date: Jun 2011
Posts: 3
Anything new on this problem? I also have the same problem. I am going to try to check to see if power is going to the transfer switch, as this could be a problem if your vehicle has one.
__________________
dontechen is offline   Reply With Quote
Old 06-23-2011, 05:22 PM   #14
Junior Member
 
Join Date: Feb 2009
Posts: 9
Quote:
Originally Posted by jd-ford-hd View Post
Try this to see if low house battery voltage is the problem.
1. Start the "truck" engine, let it run a few minutes to charge the chassis battery.
2. Hold the "boost" rocker switch on the dash while simultaneously pressing the generator start switch.

If the generator starts up and you hear the microwave beep(that's what I listen for), you know the generator is "genning".....!! I have not convinced myself that low voltage alone would keep the generator from working. My feeble mind thinks that if there is enough voltage to turn the generator over AND start it, then that should also be enough to "flash" the armature as well.
jd-ford-hd

I just picked up my RV this afternoon. I tried what you said with holding down the rocker switch to see if it was low power on the coach batteries, but that didn't work either unfortunately (and it starts right up without any issue). Any other suggestions? I used to be able to fire it up when I drove down the road to kick on the AC for the passengers in the back; used to work fine. I have a Guardian generator, unsure of the model number.
__________________
brianneal is offline   Reply With Quote
Old 06-23-2011, 06:14 PM   #15
Senior Member
 
jd-ford-hd's Avatar
 
Join Date: Aug 2009
Location: Middle Tennessee
Posts: 160
Almost scared to guess what your problem is. I had this problem crop up again this spring. Got my trusty Fluke multimeter and went at it. Had plenty of voltage in my house batteries. This time not only would my generator work sometimes at startup and sometimes not, it also would run for 10 to 45 minutes and shut down abruptly. FINALLY,, I found that the fuel pump (electric) was stopping. So I put a new electric pump on and "presto", my generator is running perfectly at every startup and does not stop..!! I can post all the diagnostic procedures with pics if you are so inclined to do this yourself but with a three year warranty from Generac I suggest letting an authorized service center do it IF you have one close AND you trust them..! EVERYTHING is so voltage dependent on these RVs nowadays. My diagnosis was the defective fuel pump was drawing too much voltage from the circuitry and that "field boost" was not initiating at startup which meant no AC current was generated even though the engine was running. Pheww....!!!
__________________
"IF IT AINT GOT A MOTOR, I AINT INTERESTED"
jd-ford-hd is offline   Reply With Quote
Old 06-25-2011, 05:11 PM   #16
Junior Member
 
Join Date: Jun 2011
Posts: 1
I have a 2007 370XL and had similar issues with no power to my coach through the transfer switch, which has resulted in replacing the auto transfer switch or components thereof on three occasions.

Symptom - no power when coach has been plugged into shore power

1) verify whether coach will power off of the genset
A) if so shut off the genset and check shore power for 220v
110 V Across each leg of circuit at the shore power input
of theTransfer Switch
B) if voltage is present but coach still won't power up,
Chances are you have a faulty transfer switch
C) if no voltage or only 110 on one leg of power, check your
Power Source

Symptom - no power from genset is running

1) Verify whether coach will power up from shore power
A) if so disconnect shore power and power up genset and
Check for 220v, 110 V Across each leg of circuit at the
Genset power input of theTransfer Switch
B) if voltage is present but coach still won't power up,
Chances are you have a faulty transfer switch
C) if no voltage or only 110 on one leg of power, check
Genset breakers

I have had to replace my transfer switch on three different occasions, twice I replaced the entire assembly and once I got away with just replacing the time delay circuit board. This last time, I replaced the factory installed unit with a progressive Dynamics PD52.
__________________
Fulltimer is offline   Reply With Quote
Old 06-25-2011, 07:51 PM   #17
Senior Member
 
jd-ford-hd's Avatar
 
Join Date: Aug 2009
Location: Middle Tennessee
Posts: 160
Good advice Fulltimer, for those who have the transfer switch. Brianneal and myself both have the "old timey" way on ours. We have to manually plug in for generator or shore power. Hearing the problems you have had makes me glad I don't have the auto transfer....!!
__________________
"IF IT AINT GOT A MOTOR, I AINT INTERESTED"
jd-ford-hd is offline   Reply With Quote
Old 06-27-2011, 05:59 PM   #18
Junior Member
 
Join Date: Jun 2011
Posts: 3
no power from genset

I am still testing (waiting a few days, then starting and waiting to see if the generator will power the coach) I do have a transfer switch and found a possible loose connection on the two white neutral wires coming out of the generator at the first junction box. Since then It has not happened, but I am still concerned though, because I was using a utility trailer over an extended period of time and the same thing would happen on a regular basis. This trailer had no transfer switch, but it did have the same generac guardian 6500 genset that I have in my moho. Has anyone taken thier genset in for service or talked to a generac generator service guy?
__________________
dontechen is offline   Reply With Quote
Old 06-27-2011, 10:06 PM   #19
Senior Member
 
jd-ford-hd's Avatar
 
Join Date: Aug 2009
Location: Middle Tennessee
Posts: 160
I called Generac and got nowhere. They simply do not do technical assistance over the phone. I talked to my closest authorized service center which is Camping World. The phone call convinced me that I knew as much as their generator "specialist". Just like all the other warrantable issues I have experienced, I will fix it myself...!
__________________
"IF IT AINT GOT A MOTOR, I AINT INTERESTED"
jd-ford-hd is offline   Reply With Quote
Old 07-06-2011, 04:41 PM   #20
Junior Member
 
Join Date: Jun 2011
Posts: 3
I was able to duplicate the problem again. No power to transfer switch. I called my local service guy who I have confidence in. He said that this will happen if it takes the generator a long time to start, he called it fuel flash, he said there is a time out. My generator has been hard to start, even though, I have changed everything. He said that my problem was probably due to carb. varnish, because my generator has only 300 hours in 5 years. I am going to take it in to him soon and will let you know what happens.
__________________

__________________
dontechen is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 08:42 AM.