Suburban furnace not working Urgent help needed

2016 Sunseeker 3010ds. First time out in cold weather with this camper. Furnace will light and run for a couple minutes and then flame goes out The unit will try and relight but fails. Please help it is getting cold.
izzaboomer is offline   Reply With Quote
Old 11-26-2016, 01:19 PM   #2
Member
 
Join Date: Jun 2013
Posts: 93
Propane tank have propane and turned to on position? Battery disconnect in the on position?
lexstone is offline   Reply With Quote
Old 11-26-2016, 02:04 PM   #3
Senior Member
 
Evereddie's Avatar
 
Join Date: Feb 2013
Location: Pfafftown NC
Posts: 2,353
Check for bug nests in heater vent.
__________________
There are 10 types of people in the world.
Those that know binary, and those that don't.

2013:31 / 2014:51 / 2015:58 / 2016:37 / 2017:46
2018:16
Total 239
Evereddie is offline   Reply With Quote
Old 11-26-2016, 02:23 PM   #4
Site Team
 
Flybob's Avatar
 
Join Date: Oct 2014
Posts: 15,243
Also check heat ducts/vents. If they are partially blocked, the furnace will overheat and the over temp will shut it down. There are know instances of the flexible heat ducts being crushed by wiring or frame members.
__________________

2015 Freedom Express 248RBS
TV 2015 Silverado HD2500 Duramax
TST Tire Monitors
Honda 2000I + Companion
2 100W solar panels
Flybob is offline   Reply With Quote
Old 11-26-2016, 03:15 PM   #5
Member
 
Join Date: Apr 2016
Posts: 75
propane on battery disconect on no blocked vents. All comes on heater working great small boom and flame goes out. will not relight
izzaboomer is offline   Reply With Quote
Old 11-26-2016, 05:30 PM   #6
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,051
Light a burner on the stove and watch how it acts when the furnace starts. If the flame on the stove goes low or out, you have a propane supply issue.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2017 Ford F-Series SCREW 4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=64
5picker is offline   Reply With Quote
Old 11-27-2016, 01:30 PM   #7
Senior Member
 
Join Date: May 2014
Location: Ontario, Canada
Posts: 145
Send a message via Skype™ to stillontheroad
I had the same problem so I joined the RV Repair club for $6.00 (annual membership) today to access all of their on line videos. Black Friday/Cyber Monday deal. Just going to watch the video now.
stillontheroad is offline   Reply With Quote
Old 11-27-2016, 02:33 PM   #8
Member
 
Join Date: Apr 2016
Posts: 75
Trouble is I am at a campground with very limited reception. Do you remember what you did?
izzaboomer is offline   Reply With Quote
Old 11-27-2016, 03:02 PM   #9
Member
 
RudysWorld's Avatar
 
Join Date: Jan 2012
Location: Collierville, TN
Posts: 586
Maybe a mud dauber in exhaust or burn chamber, if not a propane problem.
__________________

Rudy - 10 year old long haired dachshund, RIP
2011 Georgetown 350TS
2013 Chevrolet Equinox toad
RudysWorld is offline   Reply With Quote
Old 11-27-2016, 05:13 PM   #10
Senior Member
 
Join Date: Jun 2016
Location: Mid Michigan
Posts: 1,098
Sticky regulator?
markb422 is offline   Reply With Quote
Old 11-27-2016, 05:51 PM   #11
Senior Member
 
Evereddie's Avatar
 
Join Date: Feb 2013
Location: Pfafftown NC
Posts: 2,353
Did you do the "turn on a stove burner and then the furnace" test?
__________________
There are 10 types of people in the world.
Those that know binary, and those that don't.

2013:31 / 2014:51 / 2015:58 / 2016:37 / 2017:46
2018:16
Total 239
Evereddie is offline   Reply With Quote
Old 11-27-2016, 08:32 PM   #12
Senior Member
 
Join Date: May 2014
Location: Ontario, Canada
Posts: 145
Send a message via Skype™ to stillontheroad
[QUOTE=izzaboomer;1370989]Trouble is I am at a campground with very limited reception.

I knew that there was propane because it would start then go out. Then I had to access the control board... On mine it was difficult to do because the only way to get at it was to slide the whole unit out on the inside (I have a 2012 8280 Rockwood fifth wheel and the furnace is located under the oven)..Now the problem ... I had to disconnect the propane and that can be a dangerous process...I would not recommend that. Depending on the year of your unit, there may be an access panel right where the furnace exhausts, If there is, take out the screws and you should be able to access the control panel. Near the control panel there should be a small box with a little flipper on it. It may be that the flipper is stuck.. This unit works as follows.. When your furnace fires up, the fan should start but if the chamber gets too hot the flipper will activate and shut down the flame... Hope this helps a little. http://www.forestriverforums.com/for...ies/crying.gif
stillontheroad is offline   Reply With Quote
Old 11-27-2016, 09:02 PM   #13
Senior Member
 
TimVWulp's Avatar
 
Join Date: Jan 2015
Location: West Michigan
Posts: 641
Quote:
Originally Posted by izzaboomer View Post
2016 Sunseeker 3010ds. First time out in cold weather with this camper. Furnace will light and run for a couple minutes and then flame goes out The unit will try and relight but fails. Please help it is getting cold.
4. Burner ignites, but goes off and into lockout:
a. Check to be certain that flame sensor is over slots in the main
burner and that the main burner flame is burning against the tip
of the flame sensor - adjust by bending sensor probe. NOTE:
Sensor probe should be in the inner blue cone of the burner
flame (approximately 1/4" t o 5/16" above burner).
b. Burner still goes off and into lockout - check wire connections
at flame sensor and at module board.
c. Wire connections OK - check continuity through flame sensor
wire.
d. Continuity of flame sensor wire OK - check with micro amp
meter in series with flame sensor and flame sensor wire to be
certain that the flame sensor is generating at least seven
micro amps within seven seconds after the burner is ignited.
Connect meter as follows: (+) to sensor wire, (-) to sensor
probe. Adjust position of sensor probe, check for carbon
deposits on sensor probe if reading is less than seven micro
amps.
e. Flame sensor circuit generating at least seven micro amps,
but burner still goes off and into lockout - replace module
board

http://www.forestriverforums.com/for...?do=file&id=67

Above is a link from the library in the green bar at the top of the page. open the link and down load it and open the down load. the information I coped above is on page 29 of this link.

A common problem with the flame rod in your home or RV furnace is that it corrodes with white rust or red rust. The rust acts as an insulator to the micro amps and needs to be removed. This can be cleaned off with steal wool or 400 grit sand paper or a new flame rod so the rod has good contact with the flame to pass the micro amps.

Hope This Helps Tim
TimVWulp is offline   Reply With Quote
Old 11-27-2016, 09:12 PM   #14
Senior Member
 
Bluepill's Avatar
 
Join Date: Jun 2015
Location: Pensacola, FL
Posts: 1,645
Good thread here also:


http://www.forestriverforums.com/for...tml#post327988
__________________
2019 Coachmen Freedom Express 192RBS
2015 T12RBST Flagstaff Hardside

Disclaimer: The actual value of my "Two Cents" of advice varies just like a bitcoin.
Bluepill is offline   Reply With Quote
Old 11-28-2016, 09:24 PM   #15
Senior Member
 
Join Date: May 2012
Posts: 869
Quote:
Originally Posted by izzaboomer View Post
propane on battery disconect on no blocked vents. All comes on heater working great small boom and flame goes out. will not relight
I'm suspicious of the "small boom" statement. You should never have this because the only way you get a small boom is a gas explosion. Gas explosions occur when propane spreads around the mixing tube instead of travelling through it. Propane exits an orifice, mixes with air then is transported to the burners. If some of the propane does not go to the burners, you can get the "small boom" when the gas concentration rises to the point where the burner flame ignites it. This explosion will probably shut down the burner, exactly what you are seeing.

You should verify that the tubing between the orifice and the burners is free of obstructions.

Phil
pmsherman is offline   Reply With Quote
Old 12-08-2016, 12:13 AM   #16
Senior Member
 
TimVWulp's Avatar
 
Join Date: Jan 2015
Location: West Michigan
Posts: 641
Quote:
Originally Posted by izzaboomer View Post
2016 Sunseeker 3010ds. First time out in cold weather with this camper. Furnace will light and run for a couple minutes and then flame goes out The unit will try and relight but fails. Please help it is getting cold.
Hi izzaboomer looks like I ran into the same problem you are or were having with intermittent furnace operation. The 2 sons came home to visit and took over living room. So I went out to the TT turned on the television and furnace. Furnace worked for the first hour and then started with the fun and games of not playing nice. IT would lite the burner and go out 3 time and then lock out. I cleaned the flame rod NO change! Check the furnace over for how bad it was going to be to pull the furnace so I could get to the control board. After looking it over I called the dealer he said to bring it in. Brought it there last Thursday and got it back on Wednesday (to day). Dealership replaced the control board under warranty from suburban less than 2 years old and now works like new.

Hope This Helps Tim
TimVWulp is offline   Reply With Quote
Old 12-08-2016, 08:54 AM   #17
Member
 
Join Date: Apr 2016
Posts: 75
Thanks guys for all the info. Turned out to be muddobbers. I had put screens on right after purchase so must have happened at dealership. Good luck proofing that. I ate the cost.
izzaboomer is offline   Reply With Quote
Reply

Tags
furnace, suburban

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 12:26 AM.