Drawing 35 amps on a 30amp circuit

I had the fridge, 15k A/C and the microwave going all on a 30 amp conneciton. I checked the Progressive Industries EMS - PT30X for usage and was drawing 35 amps. Glad it all worked
__________________

Mike and JoAnne
Montana Summer / Arizona Winter
2016 Prism 24G /2002 HitchHiker 38LKTG
ACME EZTowing a 2015 Chevy Sonic RS Hatchback
AudiDudi is offline   Reply With Quote
Old 08-11-2018, 08:42 PM   #2
Senior Member
 
Bluepill's Avatar
 
Join Date: Jun 2015
Location: Pensacola, FL
Posts: 1,645
National Electrical Code recommendation is to run no more that 80% of circuit capacity on a continuous basis. That's 24 amps. Short bursts, like A/C startup, are OK to exceed this amount.
__________________
2019 Coachmen Freedom Express 192RBS
2015 T12RBST Flagstaff Hardside

Disclaimer: The actual value of my "Two Cents" of advice varies just like a bitcoin.
Bluepill is offline   Reply With Quote
Old 08-11-2018, 09:47 PM   #3
Senior Member
 
AudiDudi's Avatar
 
Join Date: May 2017
Location: Western Montana
Posts: 883
Quote:
Originally Posted by Bluepill View Post
National Electrical Code recommendation is to run no more that 80% of circuit capacity on a continuous basis. That's 24 amps. Short bursts, like A/C startup, are OK to exceed this amount.

I was surprised the main breaker didn't trip. The A/C was running constant as it was almost 100 deg.
__________________

Mike and JoAnne
Montana Summer / Arizona Winter
2016 Prism 24G /2002 HitchHiker 38LKTG
ACME EZTowing a 2015 Chevy Sonic RS Hatchback
AudiDudi is offline   Reply With Quote
Old 08-12-2018, 02:31 PM   #4
Senior Member
 
Join Date: Nov 2016
Posts: 156
Like Bluepill said...I wouldn’t trust a 30A breaker that carried 35A for more than a second, (maybe 2) to protect anything.
__________________
Dave W AKA "Toyman"
Well modified Forester C 2551
Why ?...Why not ?
Toyman is offline   Reply With Quote
Old 08-12-2018, 02:41 PM   #5
Senior Member
 
Join Date: Jan 2017
Posts: 3,290
I doubt you were drawing 35 A, continuously - your AC unit running, your microwave, and your fridge, if the compressor is actually on when the other two items are running, still wouldn’t exceed 30 A.

I can run both of my 13.5ac’s, fridge, computers, TV, receiver, and some floor fans, all on 30amp service. : )
__________________
The Turners...
'07 Rockwood Signature Ultralight...
two Campers and two Electric cars : )
formerFR is offline   Reply With Quote
Old 08-12-2018, 03:32 PM   #6
llr
Senior Member
 
Join Date: Feb 2017
Location: SW Ohio
Posts: 1,694
Unless breakers have gotten much better recently it is not surprising.
I worked in the R&D area of a company that made panels and breakers, not my area but I talked to people in that area.

It was common to carry a 50% overage indefinitely and a 100% overage for a number of minutes. Occasionally they would melt together then never trip.
A short circuit would trip almost instantly.
__________________
2024 Artic Wolf 3018 Suite 5th Wheel
Prior TT Grand Design 2800BH TT 2021 - sold 4/24
Prior TT 2017 Flagstaff 831CLBSS Classic Ultra lite - SOLD 5/21
TV 2024 F350 DRW Lariat Ultimate
Prior TV 2017 F150 6.5' bed 3.5 Eco-boost Max tow 1800lbs payload - sold 4/24
llr is offline   Reply With Quote
Old 08-12-2018, 03:51 PM   #7
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
Residential circuit breakers trip two different ways depending on the type of overload. They have a bimetallic strip that heats up and bends to trip the breaker. The higher the overload, the quicker it trips. In slightly overloaded conditions they may hold for a while, but will eventually trip.

In short circuits they have a mechanism that will trip the breaker immediately.

So it's possible that it could have seen 35 amps for a little while (A/C Compressor startup) and not tripped.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 08-12-2018, 04:41 PM   #8
Senior Member
 
Join Date: Jan 2017
Posts: 3,290
our experiences, in all our time, miles, and places we've traveled to and stopped at, is that there is nothing 'for certain', whether it's power related, water, sewer, or anything else... but, we've realized that every rv park and campground can have some issues, sometimes voltage, sometimes a 'trigger happy' Shore Power breaker, and sometimes even 'non standard' wiring.... don't ask me how I know(Alaska, but I'll say no more!)
: )

you can find a breaker that might be 'less' sensitive than it might be designed for, but those are hard to determine since nothing is telling you that it's 'going wrong'... while others have an overly 'sensitive' breaker, and you think it's YOUR coach, when it's just the breaker.
__________________
The Turners...
'07 Rockwood Signature Ultralight...
two Campers and two Electric cars : )
formerFR is offline   Reply With Quote
Old 08-13-2018, 10:31 AM   #9
Always Learning
 
ependydad's Avatar
 
Join Date: Nov 2011
Location: Four Corners, FL
Posts: 21,891
I happened to read a thread on here recently for the same issue ("http://www.forestriverforums.com/for...-a-164111.html"). In it, user HONDAMAN174 reported that Progessive Industries reported that the amps display on the EMS is an estimate and seems to show high by about 1/3.
__________________
Officially a SOB with a 2022 Jayco Precept 36C
Checkout my site for RVing tips, tricks, and info | Was a Fulltime Family for 5 years, now we're part-timing on long trips
ependydad is offline   Reply With Quote
Old 08-13-2018, 10:57 AM   #10
Senior Member
 
Join Date: Apr 2016
Location: Port Charlotte Fl/Hinsdale Ma
Posts: 4,823
The only true amp reading comes from a clamp around the wire amp probe. All others a faked estimates. Close but no cigar. Remember. Volts go down, amps go up. Just because you can overload a breaker doesn't mean it ok to do it. Something is going to fail. When it does, bad things happen.
cavie is offline   Reply With Quote
Old 08-13-2018, 11:04 AM   #11
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
Actually the only true amp reading comes from a calibrated donut or shunt and meter movement. Too much application error in a clamp-on. Though it's the best method most consumers or even technicians have and it's much better than anything else.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 08-13-2018, 01:50 PM   #12
Senior Member
 
rlh1957's Avatar
 
Join Date: May 2017
Location: Southeast
Posts: 1,047
Something more was running than that to draw 35 amps. And if it really was 35 amps you should have an electrician check that main breaker or the pedestal breaker as well as find out everything that is running. Start shutting breakers. Checking inverter converter draw.

I maxed out my rig just to see where it would blow... the 30Amp shore power always kicks first.
__________________
2018 Forest River Rockwood Roo
24WS

2019 Ford SD F-350 SRW Lariat
Tow & Gooseneck Prep
FX4 Off Road (4X4)
rlh1957 is offline   Reply With Quote
Old 08-13-2018, 02:52 PM   #13
Senior Member
 
bubbles's Avatar
 
Join Date: Dec 2012
Posts: 7,652
I believe circuit breakers are tested to a time based 135% must open.
bubbles is offline   Reply With Quote
Old 08-13-2018, 04:15 PM   #14
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,621
Breaker specifications

Quote:
Originally Posted by Toyman View Post
Like Bluepill said...I wouldn’t trust a 30A breaker that carried 35A for more than a second, (maybe 2) to protect anything.
I actually specified breakers one year. They are typically specified to trip within one hour at 10% overload and within milliseconds at much higher currents.

I'm not a bit surprised that the OP could pull 35 amps through a 30 amp breaker, not do I believe anything is defective.

Larry
Larry-NC is offline   Reply With Quote
Old 08-13-2018, 06:26 PM   #15
Senior Member
 
AudiDudi's Avatar
 
Join Date: May 2017
Location: Western Montana
Posts: 883
Quote:
Originally Posted by Bama Rambler View Post
Actually the only true amp reading comes from a calibrated donut or shunt and meter movement. Too much application error in a clamp-on. Though it's the best method most consumers or even technicians have and it's much better than anything else.
Agree re: shunt/donut. The microwave was only running for a minute. 15k A/C on full time, laptop plugged in, fridge on AC, 2 small fans running and the TV was likely on. The only reason I checked the EMS was I figured I was likely close to maxxing out on a 30amp circuit.

I have no idea how PI measures/estimates amps being drawn. Voltage was reading 126. I was just surprised to see 34-35amps.
__________________

Mike and JoAnne
Montana Summer / Arizona Winter
2016 Prism 24G /2002 HitchHiker 38LKTG
ACME EZTowing a 2015 Chevy Sonic RS Hatchback
AudiDudi is offline   Reply With Quote
Old 08-13-2018, 06:56 PM   #16
Senior Member
 
Join Date: Jun 2015
Location: Payson, AZ
Posts: 3,874
there was another post a few weeks ago where somebody was drawing in excess of 30 amps on a PI EMS. he called them and got the response that the amp usage displayed on their EMS units was an 'approximation'.
__________________
2015 cardinal model 3825fl
2015 dodge ram 3500 dually
CHICKDOE is offline   Reply With Quote
Old 08-13-2018, 07:07 PM   #17
Member
 
Join Date: Jul 2018
Posts: 86
I blow my 30 amp breaker regularly. In order to run the air conditioner which is on almost 24/7 and the microwave on the same time, I have to unplug the hot water heater or I blow the 30 amp circuit breaker.

I'm thinking up upgrading to 50 amp service. I will run a 30 amp line out of one of the 50 amp service lines to the existing box and use the remaining capacity for electric heaters, heat strips, and other stuff I need to keep stuff from freezing overnight during the winter months.
Ilovemywife is offline   Reply With Quote
Old 08-13-2018, 07:43 PM   #18
Senior Member
 
AudiDudi's Avatar
 
Join Date: May 2017
Location: Western Montana
Posts: 883
Quote:
Originally Posted by Ilovemywife View Post
I blow my 30 amp breaker regularly. In order to run the air conditioner which is on almost 24/7 and the microwave on the same time, I have to unplug the hot water heater or I blow the 30 amp circuit breaker.<snip>
.

My water heater is propane only. I'd guess that is why it's only a 30amp motor home. Although, my old 30 amp 97 HR Alumascape TT had electric HW heater, microwave and 15k A/C. I never tried to run all 3 at the same time.
__________________

Mike and JoAnne
Montana Summer / Arizona Winter
2016 Prism 24G /2002 HitchHiker 38LKTG
ACME EZTowing a 2015 Chevy Sonic RS Hatchback
AudiDudi is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 02:56 AM.