I have seen youtube videos on this, but wandering if any Forest River Rvers have had this installed on their rv say with the dometic 15000 btu unit. I see that 2000 watt generator are suppose to be able to run the Ac with this installed. Anyone out there had it done. Or can anyone suggest size Inverter/generator need to run the 15000 btu unit.
ronthet is offline   Reply With Quote
Old 05-27-2018, 09:19 AM   #2
Senior Member
 
SeaDog's Avatar
 
Join Date: Jan 2016
Location: x
Posts: 12,423
The problem is not with running its with starting the AC compressor. The typical AC runs on about 10 amps or 1200 watts but can require up to three times that amount to start. So a generating system that can handle a momentary 3600 watt surge be in the range. I run 2 yamaha's 2000s in parallel and have no problems. I do have a hard start kit on my AC
__________________
Retired Navy
Jake my sidekick (yellow Lab) 10/04 - 05/20
2017 RAM 2500 CC 4X4 Cummins Diesel
2016 Flagstaff 26 FKWS
AF&AM & El Korah Shrine of Idaho
SeaDog is offline   Reply With Quote
Old 05-27-2018, 09:36 PM   #3
Senior Member
 
Join Date: Apr 2015
Location: Orlando
Posts: 778
I installed one on my 15k unit. Now able to run ac with generac 2k generators. Haven't tried one. As mentioned the starting current can be over 30 amps, probably closer to 40 for a 15k. A hard start capacitor does not reduce the start current.
Brewhedd is offline   Reply With Quote
Old 05-27-2018, 09:54 PM   #4
Senior Member
 
SailorSam20500's Avatar
 
Join Date: Jun 2016
Posts: 5,060
A search with term microair will pull up a number of threads where people discuss these. One member recently sold a couple that he removed from a trailer he sold. He plans to install new units on his new trailer after the AC warranty expires.
__________________
Al
I am starting to think, that I will never be old enough--------to know better.
Tolerance will reach such a level that intelligent people will be banned from thinking so as not to offend the imbeciles. Fyodor Mikhailovich Dostoevsky, Russian Novelist
S.E. Mich. Flagstaff 26FKWS / 2022 F-150 3.5 EcoBoost SCrew Propride
SailorSam20500 is offline   Reply With Quote
Old 05-28-2018, 10:11 AM   #5
Senior Member
 
SailorSam20500's Avatar
 
Join Date: Jun 2016
Posts: 5,060
Additionally, On the Airstream forum has a long thread where the Easy Starts get discussed. Go over there and read thru this one and some others on that site: Can Generators Run Both AC's While Boondocking.
__________________
Al
I am starting to think, that I will never be old enough--------to know better.
Tolerance will reach such a level that intelligent people will be banned from thinking so as not to offend the imbeciles. Fyodor Mikhailovich Dostoevsky, Russian Novelist
S.E. Mich. Flagstaff 26FKWS / 2022 F-150 3.5 EcoBoost SCrew Propride
SailorSam20500 is offline   Reply With Quote
Old 05-28-2018, 04:15 PM   #6
Junior Member
 
dcling's Avatar
 
Join Date: Apr 2017
Location: Fountain Hills, AZ
Posts: 17
Smile

Quote:
Originally Posted by Brewhedd View Post
I installed one on my 15k unit. Now able to run ac with generac 2k generators. Haven't tried one. As mentioned the starting current can be over 30 amps, probably closer to 40 for a 15k. A hard start capacitor does not reduce the start current.
I am able to run my 15k a/c unit on one generac 2k generator in normal mode.
__________________
2018 Rockwood Mini Lite 2104S
2014 Jeep GC 3.0 Diesel
dcling is offline   Reply With Quote
Old 05-28-2018, 06:13 PM   #7
Senior Member
 
Join Date: Apr 2015
Location: Orlando
Posts: 778
Quote:
Originally Posted by dcling View Post
I am able to run my 15k a/c unit on one generac 2k generator in normal mode.
I'll have to try that. I assume you have an IQ 2000. I am not impressed with them at all. When running both they start the ac fine. When they slow down after the ac startup surge to the running current they slow too much. This causes the ac blower to slow momentarily. Don't get why this happens.
Brewhedd is offline   Reply With Quote
Old 05-28-2018, 06:33 PM   #8
Denver, CO
 
garbonz's Avatar
 
Join Date: Jan 2013
Location: Denver, CO
Posts: 2,102
Micro airs are the next best thing to sliced bread. It greatly reduces the stress on the small generators whether they can start the AC or not. Really, they are awesome.
__________________
2017 Fuse 23T
garbonz is offline   Reply With Quote
Old 05-28-2018, 09:15 PM   #9
Senior Member
 
Join Date: Feb 2017
Location: Spartanburg, SC
Posts: 504
My Micro air worked well on my 13.5 ac with my Honda 2000i until I got into 90+ temps at higher altitudes.
jeffnick is offline   Reply With Quote
Old 05-29-2018, 10:12 AM   #10
Senior Member
 
SailorSam20500's Avatar
 
Join Date: Jun 2016
Posts: 5,060
Quote:
Originally Posted by jeffnick View Post
My Micro air worked well on my 13.5 ac with my Honda 2000i until I got into 90+ temps at higher altitudes.
Not particularly surprising. High altitude decreases the engines power, reducing power output.

Did you put high altitude jets on the generator to compensate?
__________________
Al
I am starting to think, that I will never be old enough--------to know better.
Tolerance will reach such a level that intelligent people will be banned from thinking so as not to offend the imbeciles. Fyodor Mikhailovich Dostoevsky, Russian Novelist
S.E. Mich. Flagstaff 26FKWS / 2022 F-150 3.5 EcoBoost SCrew Propride
SailorSam20500 is offline   Reply With Quote
Old 05-29-2018, 10:39 AM   #11
Senior Member
 
Join Date: Feb 2017
Location: Spartanburg, SC
Posts: 504
Quote:
Originally Posted by SailorSam20500 View Post
Not particularly surprising. High altitude decreases the engines power, reducing power output.

Did you put high altitude jets on the generator to compensate?
When doing cross country, this might mean changing jets every few days?
jeffnick is offline   Reply With Quote
Old 05-31-2018, 08:56 PM   #12
Senior Member
 
Join Date: Mar 2014
Posts: 3,095
What happens when you go up in altitude with a non-blown engine? The air pressure which pushes the air into the engine is significantly reduced (oxygen percentage in air does not change). The maximum air pressure inside the engine is about 20% lower at 6,000ft, and power generally drops about 25%. Inside the carburetor, the venturi effect is non-linear to begin with, so the fuel air ratio from the carb will change with altitude, resulting in the engine being richer at altitude. High altitude jets correct the fuel air ratio but do not increase the power out (except for the very slight increase from leaning the mixture).

The primary benefits of re-jetting and/or carb adjustments are easier starting and smoother idle. At higher RPMs, the rich mixture tends to foul your plugs and uses more gas than at optimum mixture. If you do re-jet, and forget to change the jets back when you come down, you are now running lean, and can damage the engine from being too lean and too hot.

In an ideal world, you advance ignition timing with altitude, too. The flame front does not travel as fast in the thinner air. Again, coming down you have to retard the timing back to its "normal" setting.

Electronic fuel injection optimizes the mixture for ambient pressure, but can't recover the power from the air pressure loss. The same with variable timing. The real cure is turbo- or super-charging to maintain the pressure into the engine.

Unless you are going up to 9K or 10K, re-jetting is seldom done unless you really want to optimize, and are staying at a given altitude for a while. If you are up at 9K+, you don't need air conditioning, so the generator running like crap (or not starting) isn't as much of an issue.

things I learned from flying carbureted aircraft and living at 7800ft
Fred W
2014 Rockwood A122 A-frame
2008 Hyundai Entourage minivan
camping Colorado and adjacent states one weekend at a time
pgandw is offline   Reply With Quote
Old 06-01-2018, 11:27 PM   #13
Senior Member
 
SailorSam20500's Avatar
 
Join Date: Jun 2016
Posts: 5,060
Thanks pgandw, I read forums to learn. Your post has upped my knowledge level. I've never understood what really happens as altitude increases in a NA engine. Just that many folks have said they rejet for high altitude. Now I think I know why and when it should be done along with the actual benefit of doing the work.
__________________
Al
I am starting to think, that I will never be old enough--------to know better.
Tolerance will reach such a level that intelligent people will be banned from thinking so as not to offend the imbeciles. Fyodor Mikhailovich Dostoevsky, Russian Novelist
S.E. Mich. Flagstaff 26FKWS / 2022 F-150 3.5 EcoBoost SCrew Propride
SailorSam20500 is offline   Reply With Quote
Old 06-01-2018, 11:54 PM   #14
Senior Member
 
Join Date: Nov 2017
Location: Northeast Ohio
Posts: 266
Quote:
Originally Posted by SeaDog View Post
The problem is not with running its with starting the AC compressor. The typical AC runs on about 10 amps or 1200 watts but can require up to three times that amount to start. So a generating system that can handle a momentary 3600 watt surge be in the range. I run 2 yamaha's 2000s in parallel and have no problems. I do have a hard start kit on my AC
I just installed one on my Coleman Mach 13500 unit and am successfully running the AC with my new Predator 2000 inverter.

There are two conditions to overcome: startup (inrush) current and running current. The Easy Start addresses the inrush current by reducing it in my unit from about 40 amps down to 17 amps, allowing a very small generator to start the compressor.

Running current is most assuredly way above 10 amps as stated above, especially for a 15,000 btu unit. My 13,500 btu unit runs at 13.5 amps on an 80 degree day and would be slightly higher on a hot day. My Predator is able to sustain this load, but requires all other 120v loads to be shut off (converter, etc.). Bottom line, make sure the generator you choose is capable of producing sustained wattage sufficient to run the AC, and realize the Micro Air Easy Start only addresses the startup inrush current, which it does very well.
My17Ram is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 03:59 PM.