XLR Boost electrical

We recently purchased our 2nd Forest River RV. We have an XLR Boost 27QB with 30amp. We dry camp for motocross, so we are using two 2000w generators paralleled together. The generators will trip, go into over current, or not start at all while running the AC. We installed a hard start kit and that would allow the generators to run for a few hours max. Did some research and found out the AC is a Dometic Duo Therm 13,500 btu and requires a minimum 3500w (this doesn't make sense). Borrowed two 2000w generators paralleled to see if it was our generators but same issue. Borrowed a 3000w and it did the same thing. Looking at getting Briggs and Stratton 3000w and 2200w to parallel (which seems like overkill). We think there is an electrical issue. Please provide any recommendations.
Hirstius is offline   Reply With Quote
Old 07-24-2016, 01:42 AM   #2
Senior Member
 
Play Harder's Avatar
 
Join Date: Feb 2015
Posts: 510
I'm thinking something is wrong especially if those are 2 Honda 2000 I can run my 15btu on one Honda 2000 it got to be in full run mode not ECO - and no problems if I parallel 2 - I have 2 hands 2000ui and 4000 onen genset - I normally only carry 1 Honda 2000 with me dry camping because it is so much quieter than the built in onen

I'm thinking you have the electric water heater turned on - or other large draw item - turn off all other breakers except AC

When AC is on I can't run anything else - like microwave even w built in onen 4000 genset
Play Harder is offline   Reply With Quote
Old 07-24-2016, 06:28 AM   #3
Senior Member
 
B and B's Avatar
 
Join Date: Jun 2013
Posts: 10,833
Send a message via AIM to B and B
Hello Hirstius,

You need to look at real ratings on any Generator not the nameplate. A Honda 2,000 watt is only 1600 watts, they can make 2,000 watts but only for short time. Your combo is 3200 watts. I would assume by your description you are in a middle of hot field. As the temp goes up the AC has to draw more current to keep up . I have a 4,000 watt Powerhouse generator , fuel injected (cold weather operation), and this will run my 15k btu fine.
I would recommend if finance allow that you buy a 7,000 watt generator, Powerhouse/Lifan makes a Inverter style also Honda. You have a Toy Hauler so you can just wheel it in.
The other poster is correct, check other draws as well. If running on generator you need to be cautious of other load.
I would stay from mixed sizes for Paralleling, are the Briggs and Straton Inverter style? There are many Generac, Bolly, Brigs, Dometic, Powerouse that are the same generator with a different badge or features.
__________________
B and B
2022 Venture RV SportTrek STT 302 VRB Travel Trailer
2018 Heartland Landmark 365 Louisville 5th Wheel
2015 Heartland Bighorn 5th Wheel
2013 FR Rockwood 8289WS 5th Wheel
2012 FR Rockwood 2703 SS Travel Trailer
B and B is offline   Reply With Quote
Old 07-25-2016, 09:16 AM   #4
Senior Member
 
WolfWhistle's Avatar
 
Join Date: Apr 2012
Posts: 3,275
Quote:
Originally Posted by Hirstius View Post
We recently purchased our 2nd Forest River RV. We have an XLR Boost 27QB with 30amp. We dry camp for motocross, so we are using two 2000w generators paralleled together. The generators will trip, go into over current, or not start at all while running the AC. We installed a hard start kit and that would allow the generators to run for a few hours max. Did some research and found out the AC is a Dometic Duo Therm 13,500 btu and requires a minimum 3500w (this doesn't make sense). Borrowed two 2000w generators paralleled to see if it was our generators but same issue. Borrowed a 3000w and it did the same thing. Looking at getting Briggs and Stratton 3000w and 2200w to parallel (which seems like overkill). We think there is an electrical issue. Please provide any recommendations.
I have to wonder like NS if other 12volt things are on; or if you have another issue. Fridge and WH on gas, I can start and run my 13.5 Dometic with start assist capacitor, on a single EU2000i, but would never attempt to leave it on. Was just testing. With two in parallel should be easy-peasy. That AC should only need 16amps to run it and the gensets in parallel should be capable of 26A. How many amps were you pulling? WW
__________________
Hyper Lite was sold

2017 F-250 4x4 6.2L Gas
I can't fix everything, but I can make it so nobody else can
WolfWhistle is offline   Reply With Quote
Old 07-25-2016, 09:44 PM   #5
Junior Member
 
Join Date: Jul 2016
Posts: 2
Additional Information

Thank you for the information. The inverter generators we were running are Smarter Tools AP2000iq powered with Yamaha motor and they get paralleled 3600w surge, 3000w running, 30amp surge, 25amp running . Plus, we are at 5280 altitude and aware of derating. We figured 3000w less 20% for altitude = 2400w. We tried two Honda's and the 3000 was a Yamaha. Items that are usually on are fridge (auto switch-unable to switch to propane when on generator), pump, microwave is plugged in but not used, 2 tv's plugged in and 1 occasionally used, DVD/radio combo, occasionally Fantastic fan, happijack, water heater is on electric but not switched on unless we need it (will have to check on switching it to gas). The Briggs and Stratton are the inverter 3000 and 2200 combo pack that says they get 2600 and 1700 less 200w for paralleling = 4100w less 20% = 3280w. RV is currently at the dealer for warranty work, so they are checking the amps that the AC is pulling. Because we are using it at a motocross track, AC is a must on most days. It was 99 here the other day, so it’s pretty hot out there.
Hirstius is offline   Reply With Quote
Old 07-26-2016, 07:15 AM   #6
Senior Member
 
WolfWhistle's Avatar
 
Join Date: Apr 2012
Posts: 3,275
?My Domestic 6CF has auto but also has a gas button?
Some of appliances you mention have parasitic loads even if off. Your converter as well. I switch everything off absolutely not needed, when in a situation like you were experiencing. If you don't have one, you should get a good EMS such Progressive that protects as well as shows you current and volts (and Hz).
WW
__________________
Hyper Lite was sold

2017 F-250 4x4 6.2L Gas
I can't fix everything, but I can make it so nobody else can
WolfWhistle is offline   Reply With Quote
Old 07-31-2016, 08:56 PM   #7
Member
 
GSD_Gunner's Avatar
 
Join Date: Jan 2016
Location: NE Ohio
Posts: 77
I've got a 27QB and a Yamaha 3000iseb generator and haven't had the issues you speak of. Ran for 3.5 days straight over Memorial Day weekend and never crapped out. On our trailer, you don't have the option to knock the fridge down to gas only if there is electric applied. As others have said, make sure the electric water heater element is off and don't try to use the microwave with the AC on. Other wise, you may want to call the stealership for the electrical system if you can't rectify it on your own.
__________________
2017 XLR Boost 27QB pulled by a 2014 Ram 2500 Cummins
GSD_Gunner is offline   Reply With Quote
Old 08-17-2016, 06:26 PM   #8
Junior Member
 
Join Date: May 2016
Location: Canada
Posts: 21
Electric water heater?? I have done the before, forgot to turn it off and then next time I have gone camping into the bush with a smaller generator I kept tripping it. Took me some head scratching before a realized
Ian Stewart is offline   Reply With Quote
Old 07-16-2023, 07:22 AM   #9
Junior Member
 
Join Date: Jun 2023
Posts: 4
Quote:
Originally Posted by Hirstius View Post
We recently purchased our 2nd Forest River RV. We have an XLR Boost 27QB with 30amp. We dry camp for motocross, so we are using two 2000w generators paralleled together. The generators will trip, go into over current, or not start at all while running the AC. We installed a hard start kit and that would allow the generators to run for a few hours max. Did some research and found out the AC is a Dometic Duo Therm 13,500 btu and requires a minimum 3500w (this doesn't make sense). Borrowed two 2000w generators paralleled to see if it was our generators but same issue. Borrowed a 3000w and it did the same thing. Looking at getting Briggs and Stratton 3000w and 2200w to parallel (which seems like overkill). We think there is an electrical issue. Please provide any recommendations.
There are serious electrical issues as well as National Safety Recalls! I have a 2022 27LRLE. It was purchased “NEW” April 29, 2023 and within the first week-the wiring caught fire in the wall (*behind the microwave). Luckily, I reacted in time and used the extinguisher, opened all the doors/hatches and called the fire department. They had to remove/unbolt the microwave. I can’t use more than a kettle w/out the wires catching fire. The dealer & Forest River will not do anything about it! I even purchased an extended warranty from Campers Inn RV!
FreyjaRushing is offline   Reply With Quote
Old 07-16-2023, 08:37 AM   #10
Senior Member
 
Join Date: Apr 2022
Location: Tarpon Springs FL
Posts: 3,464
Just tested my hot water heater


Inside Turned....... OFF (propane / 12v)
Outside turn .........ON (120v switch)
Water is getting HOT


switch your water heater to OFF on the electric side

or 120v water heater breaker to OFF
__________________
Tarpon Springs FL
2022 Salem 24RLXL
Aussieguy is online now   Reply With Quote
Old 07-16-2023, 08:55 AM   #11
Senior Member
 
Join Date: Apr 2022
Location: Tarpon Springs FL
Posts: 3,464
PLUS air conditioner ..
look at modifying the A/C to get better air flow

Example videos
https://www.google.com/search?client...itioner+modify


DIY using foam and tape $30 from hardware store
rvairflow.com $170 foam insert


new style with limited availability $75

https://koolrv.com/collections/a-c-connect
__________________
Tarpon Springs FL
2022 Salem 24RLXL
Aussieguy is online now   Reply With Quote
Old 07-16-2023, 09:07 AM   #12
Junior Member
 
Join Date: Jun 2023
Posts: 4
Unfortunately… I have been duped by the dealer. This is a “New” purchase (April 29,2023) and I am supposedly the first owner. These issues were immediately, upon delivery. The Furrion hot water system throws E6 codes and there there are 2 gas leaks: one where it first comes into contact with the camper and the other at the port of entry with the water heater. It doesn’t help that my Furrion system(s) were poached and replaced (*w/out my knowledge).
Attached Thumbnails
Click image for larger version

Name:	IMG_1730.jpg
Views:	28
Size:	305.9 KB
ID:	290324   Click image for larger version

Name:	IMG_1728.jpg
Views:	28
Size:	404.9 KB
ID:	290325  
FreyjaRushing is offline   Reply With Quote
Reply

Tags
electric, electrical, xlr


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 04:41 PM.