Quote:
Originally Posted by jstew
Ok I finally got a chance to get some of the install done slowly over the last few nights. I disconnected the shore power from the main breaker and ran it to my inverter ac in. I then ran the ac out from the inverter back to the main 30a breaker and also disconnected the factory converter from its breaker as I just wanted to be able to power everything. So when I connect shore power my inverter detects it and starts charging the batteries, but none of my ac devices power up, I checked the panel with a voltage tester and there is live power being fed to the panel. When I disconnect the shore power the inverter picks that up right away also.
Any ideas on why nothing on the ac side might be functioning? Did I miss something?
|
I might provide the best information you will find anywhere. Step one: When installing the Freedom X to power an entire coach, the output of the inverter must be connected to the 120V coach electrical panel. The “line” inverter output goes to the screw terminal of the main breaker (the main breaker is feeding the bus bar that all the branch circuit breakers are connected to) of the coach electrical panel. The “ground” inverter output goes to the ground bus bar of the coach electrical panel. And the “neutral” output of the inverter goes to the neutral bus bar of the coach electrical panel. Now output from the inverter, will power the coach.
Step two: Disconnect the converter from the coach electrical panel so it is no longer powered from the coach electrical panel.
Step three: Install a new electrical panel somewhere in the coach to reconnect the shore power cord to or the output from the generator transfer switch if a generator transfer switch is installed. Do not connect the shore power cord or generator output directly to the inverter 120V inputs. This new electrical panel must have two circuit breakers, a separate 30 and separate 15-amp circuit breaker may be used. The shore power cord “line” wire will connect to the line connection in the new electrical panel. The shore power neutral wire will connect to the neutral bus bar in the new electrical panel. And the shore power cord ground wire will be connected to the new electrical panel box (housing) with a green ground screw or a ground bus bar may be added if desired. DO NOT short the ground and neutral connections in this new electrical panel. Every electrical panel in an RV must be treated as a sub panel and all ground and neutral kept separate. When shorting of the ground and neutral conductors are required by electrical code for safety, the device its self, the generator or the inverter will make this connection internally. Never make it in an electrical panel in an RV.
Step four: Connect the output of the new 30-amp circuit breaker from the new electrical panel to the “line” input of the inverter and new 15 amp breaker (Homeline 30's are labeled to be double tapped). Connect a neutral wire from the new electrical panel neutral bus bar to the “neutral” input of the inverter. And connect a new wire from the ground screw of the new electrical panel to the “ground” input of the inverter. The inverter transfer switch is rated at 30 amps surge and 24 amp continuous and the inverter input must have over current protection!
Step five: Lift the neutral wire from the coach neutral bus bar for the converter. Connect and run two new wires from the coach electrical panel for the converter to the new electrical panel. The output of the 15-amp circuit breaker in the new electrical panel will be connected to the “line” of the converter. And a new wire from the neutral of the new electrical panel bus bar will be connected to the neutral wire of the converter. The converter ground can be left as is, as ground, is ground, is ground. Now when plugged into shore power, the converter will be powered through the new 15-amp circuit breaker and not the inverter. And when the inverter is powering the coach, the inverter will not power the converter.
I also moved my electric water heater to my new electrical panel so it wouldn’t accidently be powered by the inverter by connecting it to another 15-amp breaker in the new panel as the converter was done. I chose to replace my main breaker in my coach electrical panel with a 25-amp breaker to better protect the inverter transfer switch since I relocated 22 amps of current draw that would have been supplied by the coach electrical panel. The 25-amp breaker is fine for my AC and microwave. The internal inverter transfer switch is controlled by the inverter, yet it is really a separate device and needs to be treated as such. I also chose to use stranded THHN building wire run in liquid tight conduits rather than solid conductor non-metallic Romex cabling.
This only covers the 120V side of the Freedom X inverter. The low voltage 12V side must be handled as outlined in the Freedom X installation manual.