08-28-2013, 08:50 AM
|
#1
|
Senior Member
Join Date: Jul 2010
Location: Waynesville
Posts: 14,428
|
30 Amp Trip
How much 110+ power can you use in your unit before a Breaker trips? This would be at the Same time. Youroo!!
|
|
|
08-28-2013, 08:58 AM
|
#2
|
Moderator Emeritus
Join Date: Sep 2007
Location: Ontario, Canada
Posts: 4,327
|
I have a digital readout of the amps load from my hard-wired surge protector and have seen 32-33A displayed. I then shut something off as I know a trip will follow if left a while.
Dave
__________________
Nights camped in 2013 - 55, 2014 - 105, 2015 - 63
|
|
|
08-28-2013, 09:35 AM
|
#3
|
Site Team - Lou
Join Date: Oct 2009
Location: South Eastern PA
Posts: 23,269
|
HowStuffWorks "Basic Circuit Breaker Design"
There are two types of breakers. MOST inexpensive ones use a bi-metallic strip that needs to get hot enough to bend away from the contact to trip the switch to the "tripped" position.
Since the "quickness" of the trip depends on how much heat is being produced, a small overload can take several minutes to heat the strip enough to release the switch. The higher the overload current the quicker it will trip.
Some breakers use an electromagnet to pull the trip lever. Once the overload current reaches a point where the magnet is strong enough, the circuit will open.
Even with the electromagnet style, there are tolerances (say 30 amps + 1 amp). The circuit may open early or late depending on where the actual current flow needed to trip it falls.
__________________
Lou & Freya the wonder dog
2008 GMC Sierra 3000HD Allison Duramax
2019 Flagstaff 8529FL
|
|
|
08-28-2013, 10:04 AM
|
#4
|
Phat Phrog Stunt Team
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
|
Quote:
Originally Posted by youroo
How much 110+ power can you use in your unit before a Breaker trips? This would be at the Same time. Youroo!!
|
Why u ask ?
|
|
|
08-28-2013, 10:08 AM
|
#5
|
Senior Member
Join Date: Nov 2012
Location: X
Posts: 2,781
|
Maybe you're asking "power", normally measured in watts? That would be about 120x30= 3600 watts.
|
|
|
08-28-2013, 10:11 AM
|
#6
|
Site Team - Lou
Join Date: Oct 2009
Location: South Eastern PA
Posts: 23,269
|
Depending on what is going on in the camper at the time, I have seen my AC amperage meter spike above 30 amps (31 or 32) several times over the last few months without tripping the post or camper main breaker. Since the spike never lasts more than a few seconds (typically a hair curler in use when the AC kicked on) the breakers hold.
__________________
Lou & Freya the wonder dog
2008 GMC Sierra 3000HD Allison Duramax
2019 Flagstaff 8529FL
|
|
|
08-28-2013, 03:10 PM
|
#7
|
Senior Member
Join Date: Jul 2010
Location: Waynesville
Posts: 14,428
|
Quote:
Originally Posted by f1100turbo
Why u ask ?
|
Just seems to be several members say they can use (ALL)-MW-A/C-W/H-Coffee Maker-Hair Dryer- and not trip a Breaker! I don't buy it. Youroo!!
|
|
|
08-28-2013, 03:17 PM
|
#8
|
Senior Member
Join Date: Apr 2011
Posts: 313
|
Quote:
Originally Posted by youroo
Just seems to be several members say they can use (ALL)-MW-A/C-W/H-Coffee Maker-Hair Dryer- and not trip a Breaker! I don't buy it. Youroo!!
|
I think some of it could be A lot of those items cycle. A/c Compressor not always running and when it is its relatively low amperage (10-15) its the kick in that's hard, and most of the time breakers will handle a fairly large start load. Some coffee pots hot plate cycle with temp, microwaves cycle.
I have run A/C, coffee pot and hair dryer at same time.
|
|
|
08-28-2013, 03:24 PM
|
#9
|
Senior Member
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
|
Quote:
Originally Posted by herk7769
HowStuffWorks "Basic Circuit Breaker Design"
There are two types of breakers. MOST inexpensive ones use a bi-metallic strip that needs to get hot enough to bend away from the contact to trip the switch to the "tripped" position.
Since the "quickness" of the trip depends on how much heat is being produced, a small overload can take several minutes to heat the strip enough to release the switch. The higher the overload current the quicker it will trip.
Some breakers use an electromagnet to pull the trip lever. Once the overload current reaches a point where the magnet is strong enough, the circuit will open.
Even with the electromagnet style, there are tolerances (say 30 amps + 1 amp). The circuit may open early or late depending on where the actual current flow needed to trip it falls.
|
Herk, I just sit and wounder how you have all this information. What you posted is exactly true. A breaker will hold up to 10% over the rating for a short period of time such as a surge, but will trip if if it is longer then seconds. That is why you size a breaker for start up amps like your A/C when it comes on. With saying that it will only hold for seconds until the motor gets out of the start wind and into the run amps. You just constantly amaze me with your post.......
__________________
Coachmen M/H
Concord
2018 / 300 DSC
|
|
|
08-28-2013, 03:34 PM
|
#10
|
Senior Member
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
|
Quote:
Originally Posted by youroo
How much 110+ power can you use in your unit before a Breaker trips? This would be at the Same time. Youroo!!
|
Youroo, It will depend what you have on and using at the time there is number of post on what the amp draw is on different 110V Appliances. Then you have to think about the amp draw that you plug into the electrical sockets and is running at the time. Would I have my microwave running with my A/C and my wife drying her hair? The answer is no it would trip a 30 amp breaker every time. I would hope the trailer tripped before the pedestal.........
__________________
Coachmen M/H
Concord
2018 / 300 DSC
|
|
|
08-28-2013, 03:43 PM
|
#11
|
Site Team - Lou
Join Date: Oct 2009
Location: South Eastern PA
Posts: 23,269
|
Quote:
Originally Posted by youroo
Just seems to be several members say they can use (ALL)-MW-A/C-W/H-Coffee Maker-Hair Dryer- and not trip a Breaker! I don't buy it. Youroo!!
|
This is possible with 50 amp service (not 30 amp service).
__________________
Lou & Freya the wonder dog
2008 GMC Sierra 3000HD Allison Duramax
2019 Flagstaff 8529FL
|
|
|
08-28-2013, 04:32 PM
|
#12
|
Senior Member
Join Date: Jul 2010
Location: Waynesville
Posts: 14,428
|
Quote:
Originally Posted by herk7769
This is possible with 50 amp service (not 30 amp service).
|
Seems like (2) members just posted about not being able to run their Fire places and Micro at the same time,and they are (50) AMP. Youroo!!
|
|
|
08-28-2013, 05:17 PM
|
#13
|
Site Team - Lou
Join Date: Oct 2009
Location: South Eastern PA
Posts: 23,269
|
Quote:
Originally Posted by youroo
Seems like (2) members just posted about not being able to run their Fire places and Micro at the same time,and they are (50) AMP. Youroo!!
|
Oh, NOT being able to...
That is correct. The fireplace (depending on model) is either 1500 watt or 2000 watts. The Microwave is 1100 watts (with an induction load - startup current - for the magnetron).
Just those two items ALONE can exceed 30 amps. In my camper there is a wall switch that selects one or the other and never both at the same time.
Microwave and air conditioner is "dicey" as the sum of the amperages depends on whether the compressor/fan is peaking at the same time as the magnetron. It may work sometimes and not others.
__________________
Lou & Freya the wonder dog
2008 GMC Sierra 3000HD Allison Duramax
2019 Flagstaff 8529FL
|
|
|
08-28-2013, 05:29 PM
|
#14
|
Site Team
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,933
|
Quote:
Originally Posted by youroo
Seems like (2) members just posted about not being able to run their Fire places and Micro at the same time,and they are (50) AMP. Youroo!!
|
Any chance the fireplace and microwave are on the same subcircuit? Was it the main breaker tripping or a smaller breaker inside the RV panel tripping?
__________________
2011 Flagstaff 831 RLBSS
A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
|
|
|
08-28-2013, 06:07 PM
|
#15
|
Senior Member
Join Date: Nov 2012
Location: X
Posts: 2,781
|
Quote:
Originally Posted by wmtire
Any chance the fireplace and microwave are on the same subcircuit? Was it the main breaker tripping or a smaller breaker inside the RV panel tripping?
|
They're talking about the case where there is a switch to allow only one of the two to run. Nothing is tripping.
Also, I don't see youroo's post that is being quoted anymore so I suspect he edited it. I don't think we have any evidence that this is happening in a 50-amp service RV. (They shouldn't have wired it that way if it is.)
I believe this is the original thread being referred to: http://www.forestriverforums.com/for...ver-21966.html
|
|
|
08-28-2013, 07:23 PM
|
#16
|
Senior Member
Join Date: Dec 2011
Posts: 3,570
|
Quote:
Originally Posted by BarryD0706
They're talking about the case where there is a switch to allow only one of the two to run. Nothing is tripping.
Also, I don't see youroo's post that is being quoted anymore so I suspect he edited it. I don't think we have any evidence that this is happening in a 50-amp service RV. (They shouldn't have wired it that way if it is.)
I believe this is the original thread being referred to: http://www.forestriverforums.com/for...ver-21966.html
|
Barry can't be fur certain, but I believe I remember at least two posts where people claimed they run tons of loads on a 30 amp cord. One even claimed it's cause the equip only draws full current part of the tiime. (not really). This I would guess in the last two weeks is maybe what Youroo is referring to.
|
|
|
08-28-2013, 08:42 PM
|
#17
|
Senior Member
Join Date: Nov 2012
Location: X
Posts: 2,781
|
Actually Youroo has brought up both topics (posts 7 & 12). Very confusing isn't it! ;-)
|
|
|
08-28-2013, 11:45 PM
|
#18
|
Senior Member
Join Date: Jul 2010
Location: Waynesville
Posts: 14,428
|
Quote:
Originally Posted by VinceU
Barry can't be fur certain, but I believe I remember at least two posts where people claimed they run tons of loads on a 30 amp cord. One even claimed it's cause the equip only draws full current part of the tiime. (not really). This I would guess in the last two weeks is maybe what Youroo is referring to.
|
You are correct. Youroo!!
|
|
|
08-28-2013, 11:49 PM
|
#19
|
Senior Member
Join Date: Jul 2010
Location: Waynesville
Posts: 14,428
|
Quote:
Originally Posted by BarryD0706
Actually Youroo has brought up both topics (posts 7 & 12). Very confusing isn't it! ;-)
|
Post # 12 was in reply to Herks post. I was talking about (30A) then (50A) somhow got into the Fight? Youroo!!
|
|
|
|