50 Amp Coach Plug

Just got our RV back from being repaired. Funny thing: a post jumped out and hit the side of the RV while I was turning a fairly sharp corner.

One thing that had to be replaced was the 50 amp coach plug (i.e. the plug where the power cable plugs in to the coach). I have the other end of the power cord plugged in to a 15 amp plug in the garage. There is power to the 15 amp plug and power in the coach to the main breakers on the WFCO in the coach. I have a Fluke power sensing device so I know the power gets to the main breakers. There are smaller breakers on either side of the main house breakers. One side is hot and the other side is not. The microwave works, but the television, ceiling fan and fireplace do not.

Before the coach went in to be repaired, the television, ceiling fan and fireplace worked when plugged in to the house power. I can't honestly say that I ever tried the microwave before. I am going through a 15 amp to 30 amp adapter and then a 30 amp to 50 amp adapter.

My question is this: when they replaced the 50 amp coach plug, does it sound like they switched the hot wires? I really would like the television etc. to work. I don't need the microwave when we are at home because I can go inside to nuke something if I want it. Is the fix to swap the hot wires at the coach plug? If not, does anyone have any ideas (Herk, Turbs, anybody?)?

Thanks for your help.

Mike
__________________

__________________
Mike & Nena Strong
2013 Cedar Creek 36RE
2012 Chevy Silverado Crew Cab 3500HD Diesel 4WD
Nights camped '14: 51 '15: 134 '16: 149 '17: 171

N9ID is offline   Reply With Quote
Old 05-20-2013, 09:38 PM   #2
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,337
Mike,
I have to think they forgot to hook up one of your legs of incoming power.

I dnt think its possible for them to switch wires or it would trip your breaker where your plugged in to.

You might have to take receptical off the side of the camper.

Turbs
__________________

__________________
TURBS is offline   Reply With Quote
Old 05-20-2013, 09:40 PM   #3
Fulltime family RVer
 
ependydad's Avatar
 
Join Date: Nov 2011
Posts: 14,727
Sure sounds like something is wired wrong!
__________________
2012 Ram 3500 DRW/crew cab/long bed/4x4/4.10 gears pulling an early 2013 Sabre 36QBOK
Checkout my site for RVing tips, tricks, and info | My family and I have fulltimed since June 2015
ependydad is offline   Reply With Quote
Old 05-20-2013, 09:45 PM   #4
Senior Member
 
Join Date: Nov 2012
Location: X
Posts: 2,781
Be very careful with this. If you (or they) do it wrong, you can put 240v across your 120v circuits which will be a disaster. Everything needs to be checked very carefully. Don't just assume it's because they left a wire disconnected. They might have swapped wires as well.
__________________
BarryD0706 is offline   Reply With Quote
Old 05-20-2013, 10:34 PM   #5
Senior Member
 
Broadway Joe's Avatar
 
Join Date: Oct 2011
Location: Fort Worth
Posts: 636
Your coach electric system is two separate 120 volt systems, with a common neutral and common ground. It sounds like when the receptacle was replaced the two hot leads were swapped. If hooked up to 50 amp service everything will work fine, if hooked up to 30 amp your secondary circuit is now improperly hooked up.

If you are not comfortable working on electric systems or are not familiar with the 50 amp rv plug go back to your service center.
__________________
Broadway Joe is offline   Reply With Quote
Old 05-20-2013, 10:45 PM   #6
Senior Member
 
Join Date: Nov 2012
Location: X
Posts: 2,781
Quote:
Originally Posted by joenic53 View Post
Your coach electric system is two separate 120 volt systems, with a common neutral and common ground. It sounds like when the receptacle was replaced the two hot leads were swapped. If hooked up to 50 amp service everything will work fine, if hooked up to 30 amp your secondary circuit is now improperly hooked up.
Sorry, but that's not right. A 30->50 adapter puts power on both of the hot legs so swapping them wouldn't cause this problem. Also, as I said before, "assuming" that everything will work fine when plugged into a 50-amp outlet may cause a disaster.

(Furthermore, it's not "two separate 120 volt systems". It has to be a center-tapped 240 service or the neutral will melt.)
__________________
BarryD0706 is offline   Reply With Quote
Old 05-21-2013, 07:56 AM   #7
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 3,237
Quote:
Originally Posted by BarryD0706 View Post
Sorry, but that's not right. A 30->50 adapter puts power on both of the hot legs so swapping them wouldn't cause this problem. Also, as I said before, "assuming" that everything will work fine when plugged into a 50-amp outlet may cause a disaster.

(Furthermore, it's not "two separate 120 volt systems". It has to be a center-tapped 240 service or the neutral will melt.)
You are correct if the 30 to 50 amp adapter was purchased at a store and made for RV purposes. If it was a user made adapter, maybe only one hot leg was wired in the 50 female plug. Most likely as you said, the repaired done by the dealer is at fault and needs to be checked again for proper connections.

N9ID, I would not connect into a 50 amp pedestal/receptacle until this has been fixed otherwise 240 volts could be applied to your equipment.
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2008 F250 Lariat CC SB 6.8L V10 4.10 axle ratio (NITTO TERRA GRAPLER G2 LT275/65R20E)
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2011(21) 2012(36) 2013 (17) 2014 (18) 2015 (18) 2016 (36) 2017 (32)
fonzie is online now   Reply With Quote
Old 05-21-2013, 08:18 AM   #8
Senior Member
 
Join Date: Apr 2012
Location: USA
Posts: 105
Take it back and have them fix it correctly.
__________________
Top B is offline   Reply With Quote
Old 05-21-2013, 09:00 AM   #9
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,337
Quote:
Originally Posted by Top B View Post
Take it back and have them fix it correctly.
Yep!
__________________
TURBS is offline   Reply With Quote
Old 05-21-2013, 09:03 AM   #10
Senior Member
 
Join Date: Nov 2012
Location: X
Posts: 2,781
Two more little points.

I guess this is somewhat of a rare case, but wanted to point out that a Hardwired Surge Protector would be useful in this case, whereas a portable one at the pedestal would not.

Also, FYI, there is nothing wrong with switching around the two hot leads (Red & Black) on a 50-amp service. They are symmetrical and no circuit tester will ever be able to the the difference. (However, if there are color labels on the connections, they should be followed to avoid confusion.)
__________________

__________________
BarryD0706 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 10:16 AM.