50 amp line

You do not need 4/0 copper.
I hope you are not confusing 4 AWG with 4/0... 4/0 is way huge and way overkill. 4/0 copper would handle 150 amps in copper for 160 feet.

The calculator says for 50 amps at 160 feet you need #2 AWG copper.
You would need 1/0 in aluminum.

I hope you decide not to use copper.
In 20 years it is still not OK to have a fire. Even if you are gone and it is someone else's fire.
larryandamy is offline   Reply With Quote
Old 05-02-2017, 07:47 AM   #22
Senior Member
 
Join Date: Sep 2012
Posts: 361
Please read about AL wire, it takes special fittings/connections. Like several of the posts in the 70s Al wired homes had to be rewired - wouldn't pass electrical inspections.
__________________
DJsFolly
D. J. Schuler is offline   Reply With Quote
Old 05-08-2017, 08:10 PM   #23
Senior Member
 
Join Date: Sep 2014
Location: North of I-10 & South of I-94, but East of I-5 & West of I-95
Posts: 114
OK, so I got back from the property and looked at the install the electric company has completed.

* The meter loop pole has a Square D 200 amp breaker box attached, with a 200 amp main principle shut off, and 8 knockouts for circuits.
* Voltage reading is approximately 119 to 121 volts and 238 to 242 volts between the two hot leads (the fluctuation may be from my cheap Craftsman multimeter)
* I will install a 100 amp breaker at the 200 amp breaker box at the meter loop
* I will install an 80 amp sub-panel at the RV port
* I will connect the sub-panel to the main breaker box with aluminum 2/0,2/0,2/0 & #1, direct burial at a 2' depth, cable enclosed in conduit only at open air from ground to boxes. I will line the trench with P-Gravel for aided drainage
* I will install the 50 amp 14-50R camper plug with a 50 amp breaker at the sub-panel (14-50R plug is next to the sub-panel)
* The meter loop pole is a maximum 172' from the camper.
* I will terminate the aluminum ends with Noalox


Finial thoughts?
Thank you for everyone's help
2nd House is offline   Reply With Quote
Old 05-09-2017, 08:04 AM   #24
Senior Member
 
Join Date: Jun 2015
Location: Payson, AZ
Posts: 3,874
just a thought. you might want to consider installing a normal 110 volt outlet off the subpanel by the trailer. you could use it to power hand tools and other things when working on the trailer. I would think you could power it from one leg of the cable you are installing so it shouldn't require any additional cable to be run. but I am not an electrician so do not take this as gospel!
__________________
2015 cardinal model 3825fl
2015 dodge ram 3500 dually
CHICKDOE is offline   Reply With Quote
Old 05-09-2017, 08:59 AM   #25
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
Sounds like you have it covered. Just make sure that the feeder and panel breaker lugs will handle the 2/0 wire size, and are rated for use with aluminum wire (most are, but there are a few exceptions).

I agree with ChickDoe about adding a convenience receptacle at the pedestal.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 05-09-2017, 09:10 AM   #26
Senior Member
 
Iwannacamp's Avatar
 
Join Date: Aug 2013
Posts: 7,916
Quote:
Originally Posted by CHICKDOE View Post
just a thought. you might want to consider installing a normal 110 volt outlet off the subpanel by the trailer. you could use it to power hand tools and other things when working on the trailer. I would think you could power it from one leg of the cable you are installing so it shouldn't require any additional cable to be run. but I am not an electrician so do not take this as gospel!
No electrician here either, but I think that would entail a sub-panel and a 15/20 amp breaker which is a good idea.
__________________
2017 Puma 297RLSS
2005 Ram 2500 4X4 diesel SMOKER!!
I love puns, irony and tasteless jokes...
born in Texas.... live in Arkansas
Iwannacamp is offline   Reply With Quote
Old 05-09-2017, 09:33 AM   #27
Senior Member
 
Join Date: Jan 2015
Location: Englewood FL
Posts: 2,797
Actually, that is what a subpanel allows. You feed it with split phase and you can wire a 50 amp split phase outlet, a 30 amp single phase outlet and a 20 or 15 amp duplex outlet. Bear in mind that you will need a main breaker, a duplex for the 50 amp and a 30 and 15 or 20 for the regular outlet. No additional feed wiring required. That means you need a subpanel with the main and 4 breaker slots for the outlets.

All in all pretty simple.
__________________

2015 335DS
ScottBrownstein is offline   Reply With Quote
Old 05-12-2017, 02:11 PM   #28
Senior Member
 
Join Date: Sep 2014
Location: North of I-10 & South of I-94, but East of I-5 & West of I-95
Posts: 114
So the two problems I have are:

1. The main breaker box is a Square D Homeline box. The 100 amp breaker will only hold a 1/0 wire at best (and that is questionable). So, I'm told to use a split bolt (rated for aluminum and copper) and go from 2/0 to a #1 copper which will fit the 100 amp breaker.
2. How on earth I'm supposed to bend large cable at a 90 degree to go straight into the breaker is beyond me. It would be great if there were a 90 degree adapter.

Thanks
2nd House is offline   Reply With Quote
Old 05-12-2017, 02:42 PM   #29
Senior Member
 
Iwannacamp's Avatar
 
Join Date: Aug 2013
Posts: 7,916
50 amp Electrical per Line

Quote:
Originally Posted by 2nd House View Post
So the two problems I have are:



1. The main breaker box is a Square D Homeline box. The 100 amp breaker will only hold a 1/0 wire at best (and that is questionable). So, I'm told to use a split bolt (rated for aluminum and copper) and go from 2/0 to a #1 copper which will fit the 100 amp breaker.

2. How on earth I'm supposed to bend large cable at a 90 degree to go straight into the breaker is beyond me. It would be great if there were a 90 degree adapter.



Thanks


Can you come from the side of the box?? Is that allowed? I'm not up on code, but that may answer.

That breaker is rated for 2/0-4 ga.
__________________
2017 Puma 297RLSS
2005 Ram 2500 4X4 diesel SMOKER!!
I love puns, irony and tasteless jokes...
born in Texas.... live in Arkansas
Iwannacamp is offline   Reply With Quote
Old 05-12-2017, 06:26 PM   #30
Senior Member
 
Join Date: Sep 2014
Location: North of I-10 & South of I-94, but East of I-5 & West of I-95
Posts: 114
Quote:
Originally Posted by Iwannacamp View Post
Can you come from the side of the box?? Is that allowed? I'm not up on code, but that may answer.

That breaker is rated for 2/0-4 ga.
I thought about going in from the side this very day at work...just sort of popped into my head!
I'm going out there tomorrow Saturday and see if there is a knock out. if so, that may very well be the answer.
I was not aware that breaker would handle a 2/0 wire? Where did you get that information if I may be so bold.
2nd House is offline   Reply With Quote
Old 05-12-2017, 08:14 PM   #31
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
If you go to Square D's Homeline site and look at the individual breakers, it lists the specs for the breakers, which include the wire size range.

Here's a link to the 100 amp Homeline breaker. HOM2100 miniature circuit-breaker 120/240v 100a
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 05-13-2017, 09:39 PM   #32
Senior Member
 
Join Date: Sep 2014
Location: North of I-10 & South of I-94, but East of I-5 & West of I-95
Posts: 114
I got back into town this evening...so much for the idea of going in through the side. The only side knockouts are at the very bottom, and do not line up with the circuits.
2nd House is offline   Reply With Quote
Old 05-13-2017, 10:00 PM   #33
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,149
Is it illegal or against code to hole saw new holes in the proper area of the box? I've seen that done.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=90
5picker is offline   Reply With Quote
Old 05-13-2017, 10:21 PM   #34
Senior Member
 
Join Date: Sep 2014
Location: North of I-10 & South of I-94, but East of I-5 & West of I-95
Posts: 114
Quote:
Originally Posted by Bama Rambler View Post
If you go to Square D's Homeline site and look at the individual breakers, it lists the specs for the breakers, which include the wire size range.

Here's a link to the 100 amp Homeline breaker. HOM2100 miniature circuit-breaker 120/240v 100a
Wow...that is expensive.
2nd House is offline   Reply With Quote
Reply

Tags
50 amp, electric, electrical


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 05:26 AM.