50 Amp Service has to be 240v

Since I'm not aware of any 240 volt requirements in an RV (such as for a clothes dryer outlet), I had been wondering if it was ok to just bring in two 120v, 50-amp circuits. It seems like nothing in the RV would know the difference.

I figured out why that is NOT an acceptable approach.

In summary, it's because the neutral wire in your RV isn't sized for 100 amps of current.

In order to maintain 50 amps or less in that neutral wire, it's necessary that the two circuits have opposite phase across that neutral. This means that when one circuit is moving electrons into the neutral, the loads on the other circuit are taking at least some of those electrons out of the neutral. Neglecting minor phase-shifts (which happen when motors are involved), if each circuit is drawing 30 amps, the current in the neutral wire back to the pedestal has zero amps. The worst-case current in the neutral occurs when one circuit is pulling 50 amps and the other is pulling 0 amps.

I just thought this was interesting. I wonder if any of the "surge protection" devices actually check that there is ~240v between line-1 and line-2, because that is really important! I think I'll find out.
BarryD0706 is offline   Reply With Quote
Old 02-24-2013, 01:41 PM   #2
Owner/Operator
 
RodeoGeorge's Avatar
 
Join Date: Dec 2012
Location: Chino Valley, AZ
Posts: 671
You are absolutely correct regarding the two phases opposing each other, and therefore reducing the neutral current.

That being said, consider the fact that when a 50A to 30A adapter is used, it place the same phase on both sides of the 50A plug. BUT, you are then limited to 30A max by the pedestal breaker.

Here's a chart that might help you determine what protection some of the most commonly used SPs have.

RV Surge Protector Comparison

RodeoGeorge
RodeoGeorge is offline   Reply With Quote
Old 02-24-2013, 01:50 PM   #3
Senior Member
 
Join Date: Nov 2012
Location: X
Posts: 2,781
Good point. I guess that answers the question as to whether the surge-protectors check for this: They can't (and allow adapters).
BarryD0706 is offline   Reply With Quote
Old 02-24-2013, 02:45 PM   #4
Denver, CO
 
garbonz's Avatar
 
Join Date: Jan 2013
Location: Denver, CO
Posts: 2,102
The progressive has to be bypassed in order to use 30 amp service.
__________________
2017 Fuse 23T
garbonz is offline   Reply With Quote
Old 02-24-2013, 03:09 PM   #5
Senior Member
 
Join Date: Nov 2012
Location: X
Posts: 2,781
Quote:
Originally Posted by garbonz View Post
The progressive has to be bypassed in order to use 30 amp service.
Really? From their web FAQ's:

"Can I use an adapter and maintain full protection?
Yes. An adapter can be used and the RV will maintain full surge protection."

I was going to find out from experience on Wednesday. Thanks for the heads-up.
BarryD0706 is offline   Reply With Quote
Old 02-27-2013, 08:51 PM   #6
Senior Member
 
Join Date: Nov 2012
Location: X
Posts: 2,781
The current EMS-HW50's don't need to be bypassed. They work just fine on a 30->50 adapter. I suspect Progressive would update yours if you asked.
BarryD0706 is offline   Reply With Quote
Old 02-28-2013, 08:55 AM   #7
Senior Member
 
Join Date: Nov 2012
Location: X
Posts: 2,781
I am now even more impressed with Progressive Industries.

On the day that I posted the original comments I also sent an email to Progressive Industries asking if they had a check to insure there were two phases (~240v) between the two lines.

When RodeoGeorge posted with the need for adapters to be supported, I sent another email, suggesting that they check for single phase AND total line currents over 35 amps (which works in both situations).

I received a reply (from the president of the company no less!) saying that they had a new design which addresses my concern, but that it wasn't ready yet. He offered to upgrade my unit if I was interested.

I call that excellent customer service!!
BarryD0706 is offline   Reply With Quote
Old 02-28-2013, 10:03 AM   #8
Senior Member
 
slide5r4fun's Avatar
 
Join Date: Apr 2012
Location: Texas
Posts: 298
Thanks for posting this info Barry, Garbonz and Wa3pnt! I'm researching a 50 amp hard wired surge protector and know nothing about electrical. We have 50 amp service in our 5'er but sometimes use sites with 30 amp so the info you posted answered one of my questions. Based on what I've read on this forum, Progressive Industries is the way to go.
__________________
Kevin & Janine
2019 F350 Lariat DRW
2020 Jayco Pinnacle 36KPTS
slide5r4fun is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 04:30 AM.