Howdy, I have 250' of 30 amp 8 gage,
Cord, my RL 26 is 30 amp. I'll be using about 200 ft of that cord, so if I adapt to a 50 plug at the pole, and I'm using a Progressive exterior surge protector, will I be alright?
Ernpick57 is offline   Reply With Quote
Old 09-05-2016, 07:28 PM   #2
Bluepill's Avatar
50 Amp is 4 wire, 30 Amp is 3 wire.
Exactly what are you trying to do? Just being able to plug into a 50 Amp outlet in order to feed a 30 amp RV?
2008 Itasca Meridian 37H
Old 09-05-2016, 10:21 PM   #3
Ernpick57's Avatar
Thanks, for 13 days, we camp about 200' away from the pole which has 30, 50, and 20 amp receptacles. I'm thinking, with the voltage drop per 100 ft, if I used a four wire to three adapter, I'd have more power. What do you think? I sure don't want to overload. The city cranks up the volts for this event. Lots of campers.
Old 09-06-2016, 03:24 PM   #4
Head Rambler
You're going to be cutting it really close, IF they keep the voltage up.
Plugging into a 50 amp adapter won't help you because the voltage is still going to be 120 volts.
200' of #8 awg at 120 volts & 30 amps will have a voltage drop of about 7.5 volts or about 6.5%.
Even if they bumped it to 130 volts, you're still looking at a 7.5 volt drop or almost 6%.
At 200' you really need at least a #6 wire size. That will give you about a 5 volt drop or 4%.
Salem 29RKSS Pushing a 2500 Mega-Cab CTD!
Gotta go campin!
Old 09-06-2016, 11:06 PM   #5
Bluepill's Avatar
Well, you can "Cheat" by using extra wires to compensate for a smaller gauge then is recommended for a specific distance run. BUT, you have to double ALL wires, not just the "Hot" line. That means two wires each for the Hot, the Neutral, and the ground. That is a total of 6 wires.
In the case that you describe, it would be possible for you to cut the 250' cable in half, then have a double run of 125'.
IMPORTANT: 50 amp 4 wire service is actually two legs of 120 volts each that CANNOT be tied together because the potential BETWEEN THE LEGS is actually 240 volts, just like a household service.
You also might consider an Autoformer voltage regulator. Info here:
https://www.amazon.com/30-Amp-3-600-...autoformer#Ask
50 amp