Amp load on 120/240 circuits

I wanted to start this as a separate thread in order not to create confusion on a thread where someone has an electrical question about their own personal RV.

Several times I've seen the comment that when the two legs on a 50 amp 240 volt circuit are used as two separate 120 volt circuits that the neutral wire is only carrying the "imbalance" between the two loads. I've seen it stated that if the load on both circuits is the same then the load on the neutral wire is actually zero. I just have a difficult time wrapping my head around this concept. Wmtire has posted several excellent articles on this subject, but it just doesn't register in my head.

I just ran a test in my shop using a clamp on amp meter, reading on the cables in the sub panel box. I had a 10 amp load on L1 and a 12 amp load on L2, nothing running on 240 volts. Using the above logic of the neutral carrying only the imbalance I would expect a 2 amp reading on the neutral line. Or, using the logic that the amps add together I would expect a reading of 22 amps on the neutral. But, I found neither. Instead I got a reading around 11 amps, apparently an average of the two loads (which is what I would expect to find.)

I'm hoping that some of the real sparkys or electrical engineers can fill us in with some facts rather than our usual conjecture, as I am neither. Too often I see this discussion pop up on a thread by a new member and I think we really confuse them when it may have no connection to their issue.
__________________
Cedar Creek Lake, Texas
2019 Keystone Loredo 290SRL
2019 Ram 2500 4x4 Cummins crew cab
Andersen hitch
CedarCreekWoody is offline   Reply With Quote
Old 11-01-2017, 11:18 AM   #2
Senior Member
 
Bluepill's Avatar
 
Join Date: Jun 2015
Location: Pensacola, FL
Posts: 1,645
Google is your friend.

https://www.bluesea.com/resources/86

Unless all of your circuit loads are purely resistive, the neutral current will be other than the calculated difference between the 2 legs. This is due to phase shift created by inductive and capacitive elements in the loads.

Google "Power Factor" for more info. It is a complex, but interesting, study.
__________________
2019 Coachmen Freedom Express 192RBS
2015 T12RBST Flagstaff Hardside

Disclaimer: The actual value of my "Two Cents" of advice varies just like a bitcoin.
Bluepill is offline   Reply With Quote
Old 11-01-2017, 11:48 AM   #3
clr
Senior Member
 
Join Date: Jul 2014
Location: Hawkins, Texas
Posts: 1,243
The two legs are on different phases. AC power on the power line is 3 phase for many reasons but manly for industrial (very heavy ) power use and for ease of transmission. Each phase is 120 degrees out of phase, so you have 3 phases separated by 120 degrees. To get the math to work correctly you need to consider the phases of the currents. You are using DC current formulas that do not consider phase.
__________________
Chuck & Sandra
Engineer/Teacher
2010 F350 CC 6.4
2015 Prime Time Sanibel 3601
clr is offline   Reply With Quote
Old 11-01-2017, 12:00 PM   #4
Wrench Turnin Fool
 
Arctic Wolf's Avatar
 
Join Date: Sep 2017
Location: Pike and Montgomery counties PA
Posts: 688
The load on the neutral should be equal to the hot leg on a 120 volt circuit.
You can think of it this way...
The 240 volt circuit is like two 12 volt batteries in series... To get 12 volts you would draw from the positive terminal of one battery (L1) and the jumper between -&+(N) 24 volts would be +(L1) on one battery to -(L2) on the other battery
__________________
Not all who wander are lost...
But I usually am

2001 Coleman SantaFe pop up
Excited new owner of 2018 Arctic Wolf 315TBH8
Towing with a 2005 F-250 5.4 GASSER
Arctic Wolf is offline   Reply With Quote
Old 11-01-2017, 12:02 PM   #5
Wrench Turnin Fool
 
Arctic Wolf's Avatar
 
Join Date: Sep 2017
Location: Pike and Montgomery counties PA
Posts: 688
Quote:
Originally Posted by clr View Post
The two legs are on different phases. AC power on the power line is 3 phase for many reasons but manly for industrial (very heavy ) power use and for ease of transmission. Each phase is 120 degrees out of phase, so you have 3 phases separated by 120 degrees. To get the math to work correctly you need to consider the phases of the currents. You are using DC current formulas that do not consider phase.
You're going to really confuse this with the three phase.
I'm pretty sure for the sake of this discussion were only dealing with split phase.
The three phase comes about because the generator is basically a 3 "Cylinder" electron pump (that's a simple way to understand it anyway)
__________________
Not all who wander are lost...
But I usually am

2001 Coleman SantaFe pop up
Excited new owner of 2018 Arctic Wolf 315TBH8
Towing with a 2005 F-250 5.4 GASSER
Arctic Wolf is offline   Reply With Quote
Old 11-01-2017, 12:36 PM   #6
Senior Member
 
Join Date: Jan 2016
Location: Apollo, PA
Posts: 588
Try this link for an explanation:

http://www.samlexamerica.com/support...chCircuits.pdf
__________________

2017 Rockwood 2703WS - Sold
2015 Keystone Sprinter 333FWFLS
2017 F250, 6.2 Gas, 3.73 Axle, 2902 lb Payload
If women don't find you handsome, at least they should find you handy!
andymil is offline   Reply With Quote
Old 11-01-2017, 12:37 PM   #7
Senior Member
 
Join Date: Apr 2016
Location: Cedar Creek Lake, TX
Posts: 3,484
Quote:
Originally Posted by Bluepill View Post
Google is your friend..
He isn't very friendly if you can't figure out how to tell him what you want.

Interesting discussions, but confusing.
__________________
Cedar Creek Lake, Texas
2019 Keystone Loredo 290SRL
2019 Ram 2500 4x4 Cummins crew cab
Andersen hitch
CedarCreekWoody is offline   Reply With Quote
Old 11-01-2017, 12:41 PM   #8
Wrench Turnin Fool
 
Arctic Wolf's Avatar
 
Join Date: Sep 2017
Location: Pike and Montgomery counties PA
Posts: 688
Quote:
Originally Posted by andymil View Post
Excellent explanation
__________________
Not all who wander are lost...
But I usually am

2001 Coleman SantaFe pop up
Excited new owner of 2018 Arctic Wolf 315TBH8
Towing with a 2005 F-250 5.4 GASSER
Arctic Wolf is offline   Reply With Quote
Old 11-01-2017, 12:50 PM   #9
Senior Member
 
Join Date: Jan 2016
Location: Apollo, PA
Posts: 588
Woody, try the experiment with two 100 watt light bulbs.

My cousin had a problem with his garage. When we turned one light on, no light. When we turned a second light on, both lights lit (different circuits). Turning on a third light changed the balance and the brightness changed. I found the neutral wire feeding the garage broke at the weatherhead. With two equal resistive loads, there was no current in the neutral weather it was connected or not.
__________________

2017 Rockwood 2703WS - Sold
2015 Keystone Sprinter 333FWFLS
2017 F250, 6.2 Gas, 3.73 Axle, 2902 lb Payload
If women don't find you handsome, at least they should find you handy!
andymil is offline   Reply With Quote
Old 11-01-2017, 12:52 PM   #10
Wrench Turnin Fool
 
Arctic Wolf's Avatar
 
Join Date: Sep 2017
Location: Pike and Montgomery counties PA
Posts: 688
Only because they were acting as a series wired pair on 240 volts.
__________________
Not all who wander are lost...
But I usually am

2001 Coleman SantaFe pop up
Excited new owner of 2018 Arctic Wolf 315TBH8
Towing with a 2005 F-250 5.4 GASSER
Arctic Wolf is offline   Reply With Quote
Old 11-01-2017, 01:30 PM   #11
Broken Toe
 
Cowracer's Avatar
 
Join Date: Jan 2012
Location: Imperial (St. Louis) MO
Posts: 3,745
Quote:
Originally Posted by Bluepill View Post
Google is your friend.

https://www.bluesea.com/resources/86

Unless all of your circuit loads are purely resistive, the neutral current will be other than the calculated difference between the 2 legs. This is due to phase shift created by inductive and capacitive elements in the loads.

Google "Power Factor" for more info. It is a complex, but interesting, study.

I am an electrical engineer, and this link is exactly correct.

AC is a different beast than DC and harder to understand, but if you break it up into instantaneous slices of time, you can look at it somewhat like DC and than makes it easier to understand some things.

In a 220 system one 'hot' will be a positive voltage with respect to neutral and the other will be exactly the same voltage but negative with respect to neutral. Any current carried in the neutral from one 'hot' will be offset by any current carried in the neutral from the other 'hot' because they are 180 degrees out of phase . One hot's current will be flowing one way, the other hot's current will be flowing the other way. If they exactly the same, they cancel out. If one is 10 amps and the other is 8, then the 8 amp current will cancel out 8amps of current in the 10 amp side, netting only 2 amps current in the neutral.

Of course, that is over-simpified, but I hope that helps.

Tim
__________________
FROG Member MO-0008-571 Since 20124444444444My Project Blog: https://cowracer.blogspot.com/

"Camper" 2016
Rockwood Signature Ultralite 8329ss
"Casper" 2017 Ram 2500 Laramie Diesel
..ProPride 3P Hitch - "Yeah. It's worth it."
Cowracer is offline   Reply With Quote
Old 11-01-2017, 04:34 PM   #12
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,960
Quote:
Originally Posted by CedarCreekWoody View Post

I just ran a test in my shop using a clamp on amp meter, reading on the cables in the sub panel box. I had a 10 amp load on L1 and a 12 amp load on L2, nothing running on 240 volts. Using the above logic of the neutral carrying only the imbalance I would expect a 2 amp reading on the neutral line. Or, using the logic that the amps add together I would expect a reading of 22 amps on the neutral. But, I found neither. Instead I got a reading around 11 amps, apparently an average of the two loads (which is what I would expect to find.)
Anyway you could post pics of your clamp meter reading at each line with it connected?
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is offline   Reply With Quote
Old 11-01-2017, 04:37 PM   #13
Wrench Turnin Fool
 
Arctic Wolf's Avatar
 
Join Date: Sep 2017
Location: Pike and Montgomery counties PA
Posts: 688
I just ran a test in my shop using a clamp on amp meter, reading on the cables in the sub panel box. I had a 10 amp load on L1 and a 12 amp load on L2, nothing running on 240 volts. Using the above logic of the neutral carrying only the imbalance I would expect a 2 amp reading on the neutral line. Or, using the logic that the amps add together I would expect a reading of 22 amps on the neutral. But, I found neither. Instead I got a reading around 11 amps, apparently an average of the two loads (which is what I would expect to find.)[/QUOTE]

This makes sense, since the two phases are opposite of each other.
__________________
Not all who wander are lost...
But I usually am

2001 Coleman SantaFe pop up
Excited new owner of 2018 Arctic Wolf 315TBH8
Towing with a 2005 F-250 5.4 GASSER
Arctic Wolf is offline   Reply With Quote
Old 11-01-2017, 05:09 PM   #14
Senior Member
 
Join Date: Apr 2016
Location: Cedar Creek Lake, TX
Posts: 3,484
Quote:
Originally Posted by wmtire View Post
Anyway you could post pics of your clamp meter reading at each line with it connected?
I didn't take photos of the meter readings. The actual numbers were fractional amps of course, but round out to the numbers I posted. I'm not trying to start an argument as this really does not matter in our RVs as long as the proper size cabling is used. I just kept seeing a member asking a question about his particular sitation and this discussion would pop up in the responses when it really has no impact on his issue. Rather than continuing to confuse new members I thought perhaps a good airing in a separate thread would let people express their thoughts.

Have you ever checked this with your own meter?
__________________
Cedar Creek Lake, Texas
2019 Keystone Loredo 290SRL
2019 Ram 2500 4x4 Cummins crew cab
Andersen hitch
CedarCreekWoody is offline   Reply With Quote
Old 11-01-2017, 05:13 PM   #15
Senior Member
 
Join Date: Apr 2016
Location: Cedar Creek Lake, TX
Posts: 3,484
Quote:
Originally Posted by Arctic Wolf View Post
This makes sense, since the two phases are opposite of each other.
That's the way I saw it too, but does not seem to be what others are saying. Hence my curiously.
__________________
Cedar Creek Lake, Texas
2019 Keystone Loredo 290SRL
2019 Ram 2500 4x4 Cummins crew cab
Andersen hitch
CedarCreekWoody is offline   Reply With Quote
Old 11-01-2017, 05:14 PM   #16
Wrench Turnin Fool
 
Arctic Wolf's Avatar
 
Join Date: Sep 2017
Location: Pike and Montgomery counties PA
Posts: 688
Alternating current does some wired things
__________________
Not all who wander are lost...
But I usually am

2001 Coleman SantaFe pop up
Excited new owner of 2018 Arctic Wolf 315TBH8
Towing with a 2005 F-250 5.4 GASSER
Arctic Wolf is offline   Reply With Quote
Old 11-01-2017, 05:28 PM   #17
Senior Member
 
BandJCarm's Avatar
 
Join Date: Jun 2013
Location: Between Pickles Gap and Toad Suck, AR
Posts: 6,070
Quote:
Originally Posted by Arctic Wolf View Post
Alternating current does some wired things
If that was intended, you get nineteen extra points!!! LOL
__________________
"Next to prayer, fishing is the most personal relationship of man" Herbert Hoover
"American by Birth, Southern by the Grace of God"Lewis Grizzard

FROG AR-0019-242
2016 GMC Denali 3500Dually--2017 CC 36CKTS
BandJCarm is offline   Reply With Quote
Old 11-01-2017, 05:36 PM   #18
Senior Member
 
Bluepill's Avatar
 
Join Date: Jun 2015
Location: Pensacola, FL
Posts: 1,645
Try this analogy:

Two identical water pumps connected to a common pool (C). One is pumping INTO another pool (A) and the other is pumping FROM a third pool (B). (i.e. the pumps are exactly"Out of Phase").

In this example Pool C is the neutral line, A is Line 1, and B is Line 2

When both pumps are moving the exact same amount of water, the level in the common pool does not change because amount IN equals amount OUT. If one of the pumps moves less or more water, the level in the common pool will change at a rate equal to the difference between the flows, not the average of the two.

Note: this analogy cannot be used when considering only 240 Volt loads, as the phase relationships no longer are valid because the mid point connection at the transformer (the Neutral leg) is not referenced.

FWIW, this subject took me the better part of 2 semesters of EE to fully understand. If you get it the first time you read about it, please apply to MENSA.
__________________
2019 Coachmen Freedom Express 192RBS
2015 T12RBST Flagstaff Hardside

Disclaimer: The actual value of my "Two Cents" of advice varies just like a bitcoin.
Bluepill is offline   Reply With Quote
Old 11-01-2017, 06:28 PM   #19
Wrench Turnin Fool
 
Arctic Wolf's Avatar
 
Join Date: Sep 2017
Location: Pike and Montgomery counties PA
Posts: 688
Lol
__________________
Not all who wander are lost...
But I usually am

2001 Coleman SantaFe pop up
Excited new owner of 2018 Arctic Wolf 315TBH8
Towing with a 2005 F-250 5.4 GASSER
Arctic Wolf is offline   Reply With Quote
Old 11-03-2017, 11:41 AM   #20
Senior Member
 
Join Date: Apr 2016
Location: Cedar Creek Lake, TX
Posts: 3,484
Quote:
Originally Posted by wmtire View Post
Anyway you could post pics of your clamp meter reading at each line with it connected?
Bobby I re-ran the tests, this time taking photos. Same loads, drill press on L1 and shop vac and lights on L2. And, of course, the results were different. So I ran them again. Again different. Ran a third time with even more difference. I'm not sure what is causing the variance but it was obvious something was going on that I wasn't understanding. In any case this was never a matter of need, just one of curiosity, so I'm just going to accept that I don't understand some things about A/C current and leave it at that. No point in posting the photos.

Thanks to everyone for your input. I sorry that I'm not a better student.
__________________
Cedar Creek Lake, Texas
2019 Keystone Loredo 290SRL
2019 Ram 2500 4x4 Cummins crew cab
Andersen hitch
CedarCreekWoody is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 07:22 AM.