Old 02-14-2019, 12:26 AM   #1
Member
 
Join Date: Dec 2018
Posts: 33
Do I have a Generator or Trailer Issue???

So we changed from a Class C RV to a Travel Trailer and are on our first shakedown camping trip. We have a 2013 Forest River RockWood Mini Lite 2502S. Everything is working fine except when we use the generator (purchased new) and the Microwave together. When running the microwave the surge light on the generator constantly lights up when it is only supposed to light up when the load is first applied (This happens every time no matter what). When running the microwave the following has happened, three times the generator has turned off, twice, the circuit breaker for the microwave has tripped and once the circuit breaker for all the other appliances tripped while the microwave was running, sometimes it runs ok but the surge light is always on.

So on a whim I decided to connect my Progressive Industries SSP-30X Smart Surge protector to the generator to see if it recognizes any issues. Nope, Got a green light. So I hooked the trailer up to the generator with the Progressive Industries SSP-30X and have not had any issues running the Microwave since. No generator shutting off, No red surge light coming on, no breakers tripping, nothing.

What could be causing the issues without the surge protector?

Thanks

Dave S
__________________
2013 Rockwood Mini Lite 2502S
DMS1 is offline   Reply With Quote
Old 02-14-2019, 05:45 AM   #2
Senior Member
 
Join Date: Aug 2016
Posts: 1,834
Neutral/ground bonding?
aeblank is offline   Reply With Quote
Old 02-14-2019, 06:00 AM   #3
Senior Member
 
Join Date: Nov 2017
Location: Dayton Ohio
Posts: 3,567
Generator type?

Size?
tomkatb is offline   Reply With Quote
Old 02-14-2019, 08:46 AM   #4
Senior Member
 
Join Date: Jun 2015
Location: Payson, AZ
Posts: 3,862
the ems is not a factor. sounds like you are overloading the generator. what make / model of generator? what make / model microwave? you probably have other things on already using generator power when you turn the microwave on. most likely nothing wrong except overloading the generator. turn all the other stuff off and try just the microwave on the generator.
__________________
2015 cardinal model 3825fl
2015 dodge ram 3500 dually
CHICKDOE is offline   Reply With Quote
Old 02-14-2019, 09:50 AM   #5
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
As eluded to above, what genny do you have, and what all else was running (including the converter) while running the M/W?

My initial thought is that you were unplugged, so your battery(s) were low and the converter was drawing a lot of power trying to recharge it/them. Then you ran the microwave while that was happening and that loaded the genny to capacity or above.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 02-14-2019, 02:21 PM   #6
Member
 
Join Date: Dec 2018
Posts: 33
I have a Champion 3500-Watt Dual Fuel Inverter Generator.

Like I mentioned above, ever since I plugged in the PI Surge protector everything has been fine now for 48 hours.
__________________
2013 Rockwood Mini Lite 2502S
DMS1 is offline   Reply With Quote
Old 02-14-2019, 02:25 PM   #7
Member
 
Join Date: Jan 2019
Location: Rochester,IL
Posts: 57
your power usage is a little too high for your gen. when microwave kicks on the voltage probably drops causing the errors. The voltage surge suppressor is doing it's job by keeping the voltage levels from varying as much.

Ben
benfox49 is offline   Reply With Quote
Old 02-14-2019, 02:30 PM   #8
Senior Member
 
njfishing's Avatar
 
Join Date: Feb 2017
Posts: 927
I was going to suggest the same as many of you, that the OP was overloading the generator......

Then I noticed he said " So on a whim I decided to connect my Progressive Industries SSP-30X Smart Surge protector to the generator to see if it recognizes any issues. Nope, Got a green light. So I hooked the trailer up to the generator with the Progressive Industries SSP-30X and have not had any issues running the Microwave since. No generator shutting off, No red surge light coming on, no breakers tripping, nothing.

What could be causing the issues without the surge protector?"


So back to the OPs question why does his generator run fine when using the Smart Surge Protector??
__________________
Gerry Z
2018 Forest River Heritage Glen 272RL
2018 Ford F150 Lariat 3.5 Ecoboost Max Trailer Package
Curt Trutrack WDH
HD Roadmaster Active Suspension
3200 Firman Generator/Inverter
njfishing is offline   Reply With Quote
Old 02-14-2019, 02:49 PM   #9
Senior Member
 
Join Date: Apr 2017
Location: 8300 Feet - Rocky Mountains
Posts: 2,445
Any 1500 watt generator should run any microwave. All micros are built to run on a 15 amp household circuit...what you have in your camper.

In fact, that's my test to see if my generator is functioning properly. I setup the genny outside my home kitchen and run an extension cord to the over-the-range micro. If the large microwave won't run properly, the generator is bad.

With no other loads (VERY IMPORTANT) the RV microwave draws far less power than a home micro. It should be a piece of cake for your generator to run that micro.

NOW...if you want to be absolutely thorough, pull the plug on your RV micro, run a 12/3 extension cord straight to the generator, and give it a try. That will rule out problems in your trailer. Now plug that extension cord into a 15 amp (not 20 amp) circuit in your house (shore power) directly and see what happens to rule out problems with the micro itself. Chances are it's the generator.

Other factors: When I setup, I run a 100', 12/3 extension cord from my 1500 watt generator to my (adapted) shore power cable. At 100 feet, 12/3 will easily handle transient 15 amp loads...e.g. the microwave at startup. With that extension cord in line, however, I can't RELIABLY run a 1500 watt hair dryer. It will occasionally trip the overload breaker, and in the case of my generator (a Generac), the only way to reset it is to shut down the generator then restart it. It was March in the Rocky Mountains when this happened, so the furnace may have been running, too....in which case, that would be a pretty serious overload.
But I NEVER have trouble running the micro or an espresso machine - one at a time - on my generator.

You'll get a raft of crap when you try this, but I'd bring it back to the seller and demand a replacement or refund. Explain that it doesn't deliver the advertised power (won't run a microwave oven), and you're not about to deal with warranty repairs or the manufacturer's nonsense. The seller can do that. Note that on your paperwork, the documents explicitly state that the seller is not responsible once you add fuel and oil, but most (e.g. Home Depot, Harbor Freight, Costco, and so on) will, in fact, reluctantly take it back. I returned...just returned...my first one to Costco, and bought the next one at Home Depot.

ANY GENERATOR can fail to perform up to standard...including a Honda. Get a new one, and do the home micro test on it. If it works out of the box, it will likely give you years of trouble-free service after that.

Look into the Predator brand at Harbor Freight. Consumer Reports says they compare VERY favorably with Hondas for half the price. Champions are really good and inexpensive as well. But any single generator can be a dud. The inverter technology is the weak link in the chain. So if you have a Predator, just get another one. A close friend has a Honda and a Predator, and he loves the Predator...and it pairs with the Honda.
__________________
Jim & Renee
2020 Jayco Jay Feather X-213
previously 2014 Forest River/Rockwood HW 277
2006 Ram 1500 4WD Crew with Firestone Airbags
Every weekend boondocking in the National Forests or at Lake Vallecito.
jimmoore13 is offline   Reply With Quote
Old 02-14-2019, 04:21 PM   #10
Senior Member
 
Join Date: Jul 2017
Location: North of Seattle, WA
Posts: 17,285
Quote:
Originally Posted by jimmoore13 View Post
Any 1500 watt generator should run any microwave. All micros are built to run on a 15 amp household circuit...what you have in your camper.

In fact, that's my test to see if my generator is functioning properly. I setup the genny outside my home kitchen and run an extension cord to the over-the-range micro. If the large microwave won't run properly, the generator is bad.
Rather than running extension cords why not just plug in an electric heater and set on high. Most (at least both of my "ceramic" heaters) draw 1500 watts on high. If a 1500 w generator can't carry a 1500 watt heater without showing a fault then it's bad.

What I've found is that there are often other loads on the power input that are overlooked. As others have suggested the converter may be in the middle of charging a battery which is usually the case when first plugged in and the charge current is at it's max. My biggest oversight is the electric heater element in the water heater. Another overlooked load is the refrigerator which is always going to select "Electric" if plugged in unless you take it off "Auto".

Back to microwaves, they are like electric motors. They take more power to start up than they need to run. If generator is marginally sized they often struggle to run even the small microwaves.
__________________
"A wise man can change his mind. A fool never will." (Japanese Proverb)

"You only grow old when you run out of new things to do"

2018 Flagstaff Micro Lite 25BDS
2023 f-150 SCREW XLT 3.5 Ecoboost (The result of a $68,000 oil change)
TitanMike is offline   Reply With Quote
Old 02-14-2019, 04:27 PM   #11
Senior Member
 
Join Date: Mar 2014
Location: Saint Louis
Posts: 1,458
I think the answer is neither. Probably when he hook sup his generator his converotr is working overtime to charge batteries, and his Fridge is probably set to Auto. So when that Fridge compressor or the Convertor kicks on, he is overloading his Generator
__________________
2015 Ram 2500 4x4 6.4l with 2015 Sandpiper 25RLS
Wife, myself and 2 furry kids
Mountndream is offline   Reply With Quote
Old 02-14-2019, 07:41 PM   #12
Senior Member
 
Join Date: Jun 2015
Location: Payson, AZ
Posts: 3,862
there's some good information that has been given! a 30 amp trailer can use 3600 watts of power before breakers start to trip (120 volts x 30 amps). in my mind i equate a 3500 watt generator to be sized for a 30 amp trailer and being able to run all things just as if the trailer were on shore power. one thing that was mentioned was a 3500 dual fuel generator. is the generator running on gas or propane? propane is supposed to derate the generator some (10%). also, just for the hell of it, what is the elevation that the generator is being run at?

i still can't understand how the ems has any effect. it monitors voltage (not amperage) on the input leads and passes the power through if the voltage is within tolerances. it does not adjust or alter either voltage or amperage. to that effect it is really just a simple on/off switch in the incoming power line.

all the other sources of ac power usage that were mentioned should be turning off (refrigerator, water heater, converter) and then give the generator a test by running the microwave. i would fully agree that if it fails at this the generator is bad as the microwave will only use 1800 watts (120 volts x 15 amp circuit) at max!

again lots of pertinent information being given.
__________________
2015 cardinal model 3825fl
2015 dodge ram 3500 dually
CHICKDOE is offline   Reply With Quote
Old 02-16-2019, 02:12 PM   #13
Member
 
Rango's Avatar
 
Join Date: Apr 2016
Location: Tallahassee, Fl
Posts: 68
Most microwave ovens pulse the power on and off to control cooking power. These pulses cause transients on the incoming power (dirty power) and your generator does not like these transients. It appears that your particular microwave is noisier that others. The SSP-30X has a surge suppressor built in that clamps these transients to a level that your generator control circuits can tolerate.

Microwave overs are non-linear loads unlike electric heaters (linear loads) so your generator has to handle them differently. Your generator is fine and it has plenty of kW/kVA to handle your microwave and most other loads in your RV. Just keep using the Progressive Industries device or install a smaller one on the receptacle serving your microwave.
__________________
Bob and Kim
Macy
2015 GMC 2500HD Denali Duramax Diesel
2016 Cedar Creek 36CKTS

Rango is offline   Reply With Quote
Reply

Tags
generator, trailer

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 06:36 PM.