Old 12-02-2015, 10:23 PM   #11
Junior Member
 
Join Date: Sep 2015
Posts: 25
Quote:
Originally Posted by DSQR View Post
Be careful - when you plug this type of device into a 50A receptacle on the power post, each hot leg is protected by a 50A breaker in the post. Your 30A cord and plug is now protected by a 50A breaker. The 30A main breaker in your TT will interrupt current only in the case of overloads on the TT-side of this 30A breaker. A fault upstream - between the TT 30A main breaker and the cord's plug - can result in a 30A cord carrying more current than it is rated for. Overheated cord, plug and cord terminations, melted insulation, cord burning setting fire to TT.
I think you point makes sense if you're not using an EMS.

But the EMS should protect everything downstream from the output connection of the EMS (e.g. everything you listed), yes? The EMS provides protection for high/low voltage, surge (current), frequency, open ground, open neutral, polarity, and accidental 240V.

Bob
__________________

__________________
2016 Rockwood 2715VS Ultra-V "Voyager" (commissioned 9/18/2015)
2013 Toyota Tundra 5.7L "Delta Flyer"
CavalierBob is offline   Reply With Quote
Old 12-03-2015, 07:29 AM   #12
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,337
Quote:
Originally Posted by CavalierBob View Post
I think you point makes sense if you're not using an EMS.

But the EMS should protect everything downstream from the output connection of the EMS (e.g. everything you listed), yes? The EMS provides protection for high/low voltage, surge (current), frequency, open ground, open neutral, polarity, and accidental 240V.

Bob
Yep!
__________________

__________________
TURBS is offline   Reply With Quote
Old 12-03-2015, 09:58 AM   #13
Future Roo 23IKSS Owner
 
elundquist's Avatar
 
Join Date: Feb 2015
Location: Gypsum, CO
Posts: 189
Dog Bone and EMS Protector

If anyone plugs their RV into a 50A outlet, DogBone or not, should have the RV electrical system rated for 50A service from the shore power plug all the way to the RV panel board.

I think DSQR is talking about the circuit from the point of the pedestal outlet to the main breaker at the RV converter.

The issue would be if there was a fault in the shore power cord and/ or the wiring from the shore power cord to the main breaker.

In my post below on DIY option one should have/use a shore power cord with a wire gauge for 50A and 50A rated twist lock connectors.

DO NOT use the 30A versions!

When I originally typed that post I was thinking of my planed setup where I am using a 50A wire gauge shore power cord.

But later before submitting the post ,without thinking, I went back and edited so it would make since in connecting to the 30A twist lock outlet on my Honda generator. In my planned setup I am going to need another pigtail to connect the shore power cord to the generator!

If you plug your RV into a 50A protected outlet you should make sure the circuit from the RV panel board/ converter to the shore plug end is rated for 50A!

Do not use 30A connectors on a cord if you going to plug into the 50A outlet. If you are going to plug into a 50A outlet make sure the shore power cord is rated for 50A.


Erik Lundquist
iPhone 6S using Tapatalk
__________________
elundquist is offline   Reply With Quote
Old 12-03-2015, 10:18 AM   #14
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,337
Quote:
Originally Posted by elundquist View Post
If anyone plugs their RV into a 50A outlet, DogBone or not, should have the RV electrical system rated for 50A service from the shore power plug all the way to the RV panel board.




Erik Lundquist
iPhone 6S using Tapatalk
Why?
Your limited to your 30 amp breaker regardless. .
__________________
TURBS is offline   Reply With Quote
Old 12-03-2015, 10:38 AM   #15
Future Roo 23IKSS Owner
 
elundquist's Avatar
 
Join Date: Feb 2015
Location: Gypsum, CO
Posts: 189
Dog Bone and EMS Protector

Quote:
Originally Posted by TURBS View Post
Why?
Your limited to your 30 amp breaker regardless. .

The problem is there is a possibility of a fault before the 30A breaker in the RV, where the fault could draw 50A of power on the 30A shore power cord/plug.

The 30A shore plug/ cord is only being protected by the 50A breaker in the pedestal. It's true the 30A EMS/ Breaker will protect the shore power cord from going above 30A based on loads in the RV, but not if there is a fault before the 30A EMS/ breaker in the camper.

Say your plugged into the pedestal and something cuts into the shore power cord shorting between the hot leg and ground, the neutral, or the safety ground. The fault could draw up to 50A before the pedestal breaker trips. This 50A draw could be a problem on a 30A shore power cord/ plug.

The difference between a 50A and 30A shore power cord is the 50A has 4 wires (L1, L2, neutral, & safety ground) and the 30A has 3 wires (L1, neutral, & safety ground). The other difference is in the gauge of the wire.

I am working with a 3 wire cord with a wire gauge that's large enough for 50A, but you can't count on every cord being a wire gauge for 50A!

Erik Lundquist
iPhone 6S using Tapatalk
__________________
elundquist is offline   Reply With Quote
Old 12-03-2015, 10:51 AM   #16
Pickin' & Campin'
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 5,017
Quote:
Originally Posted by elundquist View Post
If you plug your RV into a 50A protected outlet you should make sure the circuit from the RV panel board/ converter to the shore plug end is rated for 50A!

Do not use 30A connectors on a 50A cord if you going to plug into the 50A outlet. If you are going to plug into a 50A outlet make sure the shore power cord is rated for 50A.
I agree to this in theory only.
Yes you will have a 30 amp shore cord between your rig and the 50 amp post connector that is then protected by a 50 amp breaker but everything inside the rig is limited to 30 amps by your rig's breaker box so the chances of overloading/shorting your 30 amp shore power cord are slim to none unless a bulldozer runs over it or something.

You could take a 50 amp shore power cable and cut the trailer side end off and install a 30 amp trailer side connector but that sure wouldn't be something I'd do.
__________________
_________________________________________
2016 Flagstaff 8529IKBS Diamond Package 5th Wheel
2017 Ford F-Series SCREW 4x4
TST Tire Monitor w/Repeater - Sinemate 3500w Gen.
Days Camped: '15=22 '16=46 '17=30
5picker is online now   Reply With Quote
Old 12-03-2015, 11:26 AM   #17
Usually Confused Member
 
emm-dee's Avatar
 
Join Date: Nov 2015
Location: Georgia
Posts: 1,610
There's four things that scare me...fire, angry wives, mules and electricity. All the talk in this thread is getting my attention.

My impression is that, generally, it's OK for me to use a dog-bone adapter to plug my 30 amp cord into a 50 amp output. The trailer CB would protect the trailer and if it did its job because of, say, a short at the female end of the cord (where it connects to trailer) then it's possible to have an overheat/fire in the actual 30 amp power cable.

In other words...be careful where one places the power cord. Electricity concerns me enough that when I hook up (even to my home 30 amp outlet) the first thing I do is turn off power at the breaker. Then, I attach the cord to the trailer followed by plugging the cord into the receptacle. After that, I activate the breaker.
__________________
At some point during every day you suddenly realize nothing else productive is going to happen the rest of that day. For me, it usually occurs around 9 am.

Vengeance 25V (the Harley needed a home)
emm-dee is online now   Reply With Quote
Old 12-03-2015, 11:28 AM   #18
Future Roo 23IKSS Owner
 
elundquist's Avatar
 
Join Date: Feb 2015
Location: Gypsum, CO
Posts: 189
I should clarify...

A 30A shore power cord can be a 8 gauge 3 wire cord or likely be a 10 gauge 3 wire cord.

A 50A shore power cord could be a 8 or 6 gauge 4 wire cord.

To use a 3 wire shore power cord to plug into a 50A circuit you should verify the wire gauge in the cord to make sure it's rated for 50A.

There is no need to use a standard RV 50A 4 wire cord for a 30A 120VAC RV service as you only need 3 wires.

Just verify your wire gauges are large enough for the connection/ load and use connectors rated for the application.






Erik Lundquist
iPhone 6S using Tapatalk
__________________
elundquist is offline   Reply With Quote
Old 12-03-2015, 12:26 PM   #19
Future Roo 23IKSS Owner
 
elundquist's Avatar
 
Join Date: Feb 2015
Location: Gypsum, CO
Posts: 189
Quote:
Originally Posted by emm-dee View Post
There's four things that scare me...fire, angry wives, mules and electricity. All the talk in this thread is getting my attention.

My impression is that, generally, it's OK for me to use a dog-bone adapter to plug my 30 amp cord into a 50 amp output. The trailer CB would protect the trailer and if it did its job because of, say, a short at the female end of the cord (where it connects to trailer) then it's possible to have an overheat/fire in the actual 30 amp power cable.

In other words...be careful where one places the power cord. Electricity concerns me enough that when I hook up (even to my home 30 amp outlet) the first thing I do is turn off power at the breaker. Then, I attach the cord to the trailer followed by plugging the cord into the receptacle. After that, I activate the breaker.

It should be everyone's SOP (standard operating procedure) to cut off the breaker before inserting or removing their RV shore power cord! It prevents arch pitting on the terminals at the pedestal socket and on your shore plug.


Erik Lundquist
iPhone 6S using Tapatalk
__________________
elundquist is offline   Reply With Quote
Old 12-03-2015, 12:39 PM   #20
Phat Phrog Stunt Crew
 
elind's Avatar
 
Join Date: May 2012
Location: Upper Penisula Michigan / Arizona
Posts: 2,481
I don't turn off the breaker before because the surge protector doesn't allow power to enter the RV for 128 seconds. So there is no arching in the plug to worry about.
__________________

__________________
Ed & Ruthann / Toby and Tucker
2014 GMC Sierra Crewcab 2500 Duramax
2014 Wildcat 327ck
2015 129 nites
2016 63 nites
elind is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 10:24 PM.