07-05-2012, 12:45 PM
Electrical Fire Averted......JIT
Yesterday (the 4th), I was working in the TT and unplugged the
battery charger for my cordless drill. Whoops, the plug was HOT.
The warning flag went up as this is a low current device (<1amp
@ 117VAC) that should not heat its cord. I figured that the plug
or outlet might have "crud". The plug was fine, but the outlet
showed scorch marks. Second warning flag; this is NOT good.
Went to remove the cover for a look and burned my finger on the
outlet. Holy S***, this is very NOT good!. Left it alone to cool for
about an hour. Returned and again to remove the cover plate.
Burned again! Holy cow, there was nothing plugged in and it is
still emulating a Toaster Oven. No breakers popped, so there
must be a high resistance "short" causing current flow. Opened
the main breaker and unplugged the TT (Belt & Suspenders guy!)
and returned an hour later.
Removed the outlet and found about 4" of wire with melted
insulation and VERY discolored. This thing was really *HOT*.
I had planned to leave it plugged in over night. That would
not be the July 4th "Fire Works" that I wanted to see.
Lesson learned: check ALL outlets from time to time.....
Be safe folks.
cheers,
johnd
2001 Cherokee CKT27X - 2005 Chev 3500
Sara, John & Crafty Canines - Coco and Cole
Medical research shows that men have a "biological clock" too. The older we get, the greater the NEED to drive a TRUCK!
07-05-2012, 12:55 PM
Good catch.
Doug
2011 Prime Time Tracer 3000BHS
2007 Ford Expedition
Reese Dual Cam HP Hitch
Nights Camped 2015-5 in TT
07-05-2012, 01:05 PM
I am wondering why it failed. Cheaply made, loose connections? Could you see any indication of why? Is it a recognizable brand name?
07-05-2012, 01:23 PM
Cheaply made,
Probably.
loose connections?
Didn't seem to be. When I removed it, all screws were TIGHT.
(Maybe due to corrosion, tho')
No and No.
Could have been just about anything as cause.
Since it's a decade old, some PO may have plugged
in something with a corroded plug, thus starting the
"heat cycle". Once some of the plastic get carbonized
enough, current can "leak" to the other terminal
and the future is FIRE. I think I was WELL on the way!
With the heating continuing with nothing attached, the
Death Spiral had certainly begun...........
Whew.
johnd
07-05-2012, 01:27 PM
Just answered a PM on this very topic!
That duplex is a 15 amp rated duplex used with a 20 amp circuit.
When using a 30 to 20 amp adapter, the connections inside the duplex are in overload.
A 20 amp rated duplex has a pin socket shaped like a "T" on it's side.
Using the iPhone and will post a photo when I can.
Lou & Freya the wonder dog
2019 Flagstaff 8529FL
07-05-2012, 02:48 PM
Indeed, it certainly is a 15A outlet, But NOT used on a 20A
circuit. In a miracle of production, FR actually got it right
with a 15A breaker.
Main = 30A
A/C = 20A
All else = 15A
I ding em good when they (often) screw up, but I credit them
when they (finally) do it right....
Yep, it sure do.
My best guess as to the Original cause is still probably misuse
by PO combined with cheap ***** outlet....YMMV
cheers,
johnd
07-05-2012, 03:29 PM
I need to apologize to the OP.
Using the iPhone I misunderstood where the outlet was. I had just gone through this in a PM and jumped to the conclusion it was the same issue.
Hard to read the tiny print. I need to get used to the iPad/iPhone app.
It was an older style duplex and threw me.
07-05-2012, 04:07 PM
None needed; we're all friends here. Some of us might
even have made a mistake once....Long ago, of course!
If your eyes are anything like mine, that's totally understandable......
And I plan to T_H_R_O_W it. Far, far away!!!!
Hope ya'll are enjoying the holidays,
johnd
07-05-2012, 04:49 PM
Were you running off shore power, or an internal inverter?
Glenn - KA2DTH
2007 Chevy Express 1500 AWD
2005 Surveyor SV-230
07-05-2012, 05:24 PM
Shore.
Don't even own a 3.6KW inverter.....Or even a 1.8KW one.....
cheer,
johnd
07-05-2012, 05:33 PM
Originally Posted by dnaraG_1M
Shore.
cheer,
johnd
OK, how would a 3600 or 1800W generator come into the conversation?
My concern would be a MSW inverter and a drill battery charger.
Glenn - KA2DTH
07-05-2012, 05:40 PM
I am surprised to see the wires wrapped around the terminal screws and not plugged into the back which usually causes problems like this. Good thing you caught it.
07-05-2012, 06:24 PM
120V x 30A = ???
120V x 15A = ???
Why would that be? As I said the charger draws less that 1Ampere.
I.E. Less that 120watts.
Whether the AC waveform would be a problem for the charger
would depend on the power supply in the charger. Some designs
would have a problem, some not. But, it's not relevant as I answered
the OP question that I was on shore power.....
PS, I never mentioned a GENERATOR. If you read it again, you
will see that I said INVERTER. That is what the OP asked about
and that is what I answered........
cheers,
johnd
07-05-2012, 06:32 PM
Amen to that. Both thoughts.
When I wire things, I just plain refuse to use the "push-in"
option and always use the screws. I don't know that a loose
connection was the original cause. They were tight when I
removed the outlet, but with all the heat generated corrosion
they may have "welded" tight. (Poor description, but maybe
you get the idea.
I cringe when I think of what might have happened in a few
more hours...........
cheers,
johnd
07-05-2012, 07:23 PM
Too old to be too smart
Good call on not using the push-in termination. It's fast, but just WRONG! "Professionals" use them all the time!
I see another wire on the other terminal, which indicates that this receptacle was in the middle of a "pigtailed" wiring arrangement, and it was possible to draw current somewhere beyond these connections as well.
It also looks to be on the neutral (white) wires, as well.
Ever notice the little "bridge" between these two terminals? They're pretty small if you're drawing a lot of current (like a microwave oven) somewhere downstream, and they will generate some heat if this is the case.
What else was running in the rig at the time that is also 110-volt powered? Is that receptacle "downstream" of this?
Who is the manufacturer of this one?
Pop
Terry 250RKS, perfect for the two of us and the pups.
2000 F-350 7.3L CC/LB 4WD Lariat 3.73's
07-05-2012, 07:56 PM
Yep.
Makes me ashamed to call myself a "Professional"!
Oh well, I'm retired; guess that makes me a Professional
HouseHubby to a working BOATY (Bride Of All These Years).
Exactly right. The TT has one string for non-GFI outlets
(where this one was) and another string for GFI outlets.
Both strings are breakered at 15A.
It was. You got D*** good eyes!!!
Yeah. One would hope that it was designed to handle the
current that the outlet was rated for.
But.............One would also hope to win the lottery.
This one "seems" to be mid-stream - that's just a resonable
guess. Nothing else was on the string. A small fan was on the
GFI string, but that don't count.....
Leviton.
Pop
I've seen this occasionally in house wiring, but the few cases
I know about had a more probable cause - damaged Plug or
outlet, - corrosion, etc.
This just is a "I don't know".
cheers,
johnd
07-05-2012, 08:11 PM
Of course, Leviton makes a few "grades" of duplex receptacles, and I'd bet this one was one of the cheaper, "bulk" ones. Still.....
This thread makes me want to go out and tear apart the 110-volt system and inspect EVERYTHING, then replace it all with "the good ones".
As I know you will do with this one.....
Happy "bullet" dodgin'!
Pop
07-05-2012, 08:40 PM
Given what I've seen in the rebuild of this TT, I'm totally sure that
the cheapest components were used......and abused by the installers.
Even the "quality" of my chinese tractor looks good compared
to this TT......So sad.
And the 12V wiring?????
Yeah. Six/seven months pounding on this ---- trailer & I
thought that I was about done.
Silly me.
Thank you for your kind wishes!
The same to you.
And all who visit here...........
Pop
cheers,
johnd
07-06-2012, 08:01 PM
Pop
Previously I answered your post as below:
But now..........
I am beginning more and more to think that I may have
been wrong about "nothing else" on the stream. I have
believed that the fridge was on a different string.
But as I pull the outlets for inspection and try to discover
where the wires go, I am beginning to think that the fridge
was, in fact, on this string. Gonna test that theory tomorrow
because it would be a good explaination for why the outlet
remained burning hot when I thought everything was unplugged.
I don't see anything else that could have caused current flow
with the charger unplugged. Tested the damaged outlet for
resistance from Hot to Neutral and found an "open" circuit
on all ohmmeter ranges - up to 200 Megohms. Gotta be
caused by something downstream.........As you suggested.
And the heating effects of the "jumper tab" could
surely explain how all this problem got started in the
1st place........
And, oh yes, the fridge was running on AC.
D'oh!!!
Thanks for kicking my brain into gear (sorta, kinda).
johnd
07-06-2012, 11:08 PM
John,
I believe ALL of us who are following your investigation of this "tragedy, avoided" will benefit from this when you are through.
What we learn may just save us not only similar grief, but maybe MUCH more!
Thanks for being so thorough with your follow-up. Some may have just replaced the duplex, and simply pressed on.
Pop