Old 03-07-2014, 02:38 PM   #1
Back to Shasta Camping...
 
Join Date: Jan 2014
Location: Stony Creek VA
Posts: 52
Red face Electrical Problem Liklihood (Surge Suppression VS EMS)

First of all I want to thank all those that participate in this forum. It truly is a ocean of knowledge for all to benefit...

My question revolves around the liklihood of a problem which causes damage to my new FW. I have reviewed most (if not all) of posts here as well as other forums and truly believe that the progressive industries products are the best... I know that I will get either a PI surge suppressor or an EMS. My question revolves around the liklihood of damage caused to an rv... Is it more likely to occur due to a surge of power... or because of low or high power...

Money is as tight here in our house as it is anywhere else and I surely don't want to spend more than I need to... but I also don't want to overlook what might be a more common power issue that a spike/surge.

I appreciate your comments here as both the DW and I review these message on a daily basis...

DW believes that surge suppression is all we need... And if money were no object I think that either a Frank's or Hughes would be the all around ideal solution... However, as I said money is an issue and I believe the compromise of using an EMS is the better compromise...

Again, please let me know your thoughts on whether the surge suppression option would/could be the solution to 99+% of the issues/problems. I know this is talked about alot but I have not seen any discussion on the likelihood of any fault compared to the other...

Lastly, POLL above does not include option of not having any power proection at all as that is NOT an option for DW and I. At a minimum we will have a surge suppressor. (But we prefer to make the right decision ONCE.)

Happy Travels,

Bill n Diana
Bill n Diana is offline   Reply With Quote
Old 03-07-2014, 02:52 PM   #2
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
If you get the progressive or TRC they protect you from both. TRC are a little cheaper but only comes with a 2 year warranty. Either low voltage or a spike will cause the same damage. More then likely you will encounter low voltage more then a spike. Some CG have very old and low power lines and even alum. wire a drop of 10% below you Full loaded amps will fry your stuff up electronics. A spike will do the same thing but I would consider that high voltage it will jump up 10% or so. You are more likely to get a spike during an electrical storm. Progressives are warrenty for life but you do pay for it in the cost. Both work the same. Just make sure you get one with a time delay built in, VERY IMPORTANT....For when the power comes back on. Your a/c will need time to equalize pressure. or you will go off on internal over load. That's not good for a compressor. It will shorten the life of the compressor.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 03-07-2014, 03:28 PM   #3
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Ems all the way.



TURBS
Sabre owners united!
TURBS is offline   Reply With Quote
Old 03-07-2014, 03:32 PM   #4
Senior Member
 
Join Date: Oct 2013
Posts: 496
I agree that low voltage is most likely. We have a EMS on our 5er. If we see a fault code we can either move to a different site or switch over to battery power. Like was said above, make sure you get a time delay if you plan on heavy use of the A/C.
__________________
2001 Ford F250 7.3l converted to F350 specs
2014 Flagstaff 8528RKWS
2006 model year Border Collie
Mtelkman is offline   Reply With Quote
Old 03-07-2014, 03:50 PM   #5
Senior Member
 
jtstromsburg's Avatar
 
Join Date: Jul 2011
Location: Stromsburg, Nebraska
Posts: 1,682
PI EMS works for me. Saved us three times last season. Truthfully, jot sure if there would've been damage or not. One was when one hot on the 50a pole was bad and the others were low voltage.

Sent by me
__________________
Joel and Teresa
2016 Sabre 34TBOK
2006 GMC 3500 CC LB DRW 4X4
jtstromsburg is offline   Reply With Quote
Old 03-08-2014, 07:04 PM   #6
Back to Shasta Camping...
 
Join Date: Jan 2014
Location: Stony Creek VA
Posts: 52
Click Switch in A/C & Refrigerator ???

Thanks for the input thus far.. The DW has a friend who works in the A/C sales business... He has told her that non of this is needed because the A/C and the refrigerator both have click switches....

Does anyone know what a click switch is and can you describe it for me... I have my personal thoughts on this click switch thingy but i don't want to step out and possibly cause undue/unwarranted friction is this friendship....

Thanks for enlightening me on click switches...

Happy trails,

Bill and Diana
Bill n Diana is offline   Reply With Quote
Old 03-09-2014, 04:57 AM   #7
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Quote:
Originally Posted by Bill n Diana View Post
Thanks for the input thus far.. The DW has a friend who works in the A/C sales business... He has told her that non of this is needed because the A/C and the refrigerator both have click switches....

Does anyone know what a click switch is and can you describe it for me... I have my personal thoughts on this click switch thingy but i don't want to step out and possibly cause undue/unwarranted friction is this friendship....

Thanks for enlightening me on click switches...

Happy trails,

Bill and Diana
Okay I did HVAC for 20 years. A click switch is a set temp disk that is wired in, your FAU use's one for a temp over heat problem. You also have them on your water heater, Your a/c has one internally in the winding area. A click switch will not stop anything on low voltage, high voltage or a spike in power. It's used as a heat sensor. If your a/c is running during a brownout out or power failure and then then pops back on your a/c compressor will not start because the high and low side has not equalized yet. It go's into what is called lock rotor. You would not know until you felt hot air only. At that time the click switch will stop power to your windings until you shut it off and it cools to the point of auto reset. Your a/c has to be turned off for this to happen, A guess but maybe an hour or so depending on how long it was on before you discovered it and shut the unit off your fan would still work. As far as a refer, never heard of one except in the coil area that it is attached to, when the coil gets hot that is what makes your cooling fan comes on. All equipment has a variance of plus or minis 10% for voltage if you go higher or lower you will start to burn the unit up not even knowing that it is happening until one of the boards go out. I hope this helps and I think that is what he talking about. It will not stop surges, low or high voltage....Spikes in power burn out more appliances then anything else. You might get a surge of 160 volts that is where you have your problem even if it for 1 second. by the way a click disk will open from low voltage to the compressor due to the higher heat and it is trying to run. At least get a surge protector.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 03-09-2014, 05:38 AM   #8
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Let me add one more thing, click-on's come in temperature rated from 110 to 190 degrees mostly. They also come normally open like for the refer. when coil hits a set temp it closes and bring the fen on (if you have a fan, they mostly come in slides if that where your refer is located) the others are normally closed to let power pass. when there is a heating problem they open to break the circuit. Also your convertor is not protected at all.....
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 03-12-2014, 07:53 AM   #9
Back to Shasta Camping...
 
Join Date: Jan 2014
Location: Stony Creek VA
Posts: 52
Thumbs up Thanks and another follow-on question???

Again, thanks to this wonderful collective brain trust... The wife and I ordered and have recieved our portable PI 50 EMS unit. I had thought that the security collar would have been a more heavy duty material and am considering other means to add to security of this device.

Right now I think I can get several links of heavy duty chain wrapped around the power cord and use it to secure portable unit to power pole... But I am also thinking of whether it would be beneficial to both engrave and stencil our names on one or several of the large flat areas around or behind the face of the unit.

I welcome your thoughts and details on how you all might have added to security of the expensive tool to avoided the likelihood of dreaded discovery of inadequately secured highly regarded pilferable property gone missing.

Again thanks and Happy Trails.

Bill n Diana
__________________
His TV: 2014 RAM 3500 MC DRW 6.7 CTD AISIN
His RV: 2014 REDWOOD 38FL (House)
Her TV: 2013 RAM 1500 CC 5.7 Hemi
Her RV: 2010 VCross 20VFB (Camper)
--------------------------------------------------
Bill n Diana is offline   Reply With Quote
Old 03-12-2014, 08:46 AM   #10
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
I just wrap a plastic coated cable and lock around it. It will stop the average person but if a thief wants it, he will get it. I also installed a motion sensor light on that side. If that light comes on it will deter them atleast. Names engraved is not a bad idea incase you spot it somewhere but they all look the same. don't let that spoil your trips. There is really not that many being stolen. You could also by an alarm that would be set off if taken, use fish line so they can't see it to trip the alarm.They sell these little battery ones and leave it at the pole when they remove it it will set it off.......
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 03-31-2014, 06:59 AM   #11
Back to Shasta Camping...
 
Join Date: Jan 2014
Location: Stony Creek VA
Posts: 52
Securing PI 50Amp EMS

Folks,

Thanks to all your comments, your assistance has been great.

Next question on this topic though... This past weekend DW and I took Phoenix out for first outside of the driveway camping trip. I had lock, cable chain and everything to lock up the EMS. The power box though had the hasp like lip that stuck through the drop down cover... I looked at all of it and then decised that best option for me at this site was to just use the padlock and lock the power pole lid closed. DW thought it might not be the best idea but my rationale to better secure our EMS won out...

My question, what are your thoughts about locking the drop-down lid of the receptacle on the power pole? This particular camp site had a dedicated power pole for every site so there was no issue have to share a power pole with anyone else.

As always, thanks for your thoughts.

Happy Travels,

B n D
__________________
His TV: 2014 RAM 3500 MC DRW 6.7 CTD AISIN
His RV: 2014 REDWOOD 38FL (House)
Her TV: 2013 RAM 1500 CC 5.7 Hemi
Her RV: 2010 VCross 20VFB (Camper)
--------------------------------------------------
Bill n Diana is offline   Reply With Quote
Old 04-01-2014, 05:04 AM   #12
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
I don't see any problem with that at all. With saying that I have not heard of anyone stealing one either. Some of the old box's you won't be able to do that. I installed a scare light on that side with the motion detector on it. That would ward off someone that is trying to steal it. At least I hope. I put that on after my wifes bike was stolen one night. That was an $800.00 lost. oh by the way I see that you are from the great state of Virginia. COE camp grounds are now open here on the lake. If you have never been to my area give us a try, Here is a link to my Town all or most of the camp grounds are within 5 to 8 miles away on the water camping. [url]WWW.Clarksvilleva.org[/url] We have 3 live camaras set up on our town site shows the lake and downtown.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 04-01-2014, 06:26 AM   #13
Back to Shasta Camping...
 
Join Date: Jan 2014
Location: Stony Creek VA
Posts: 52
Kerr Lake

GK,

The wife and I camp a bit at some of the COE and state park CGs around Kerr Lake. We like Rudd's Creek the best... We are camping at Satterwhite over Memorial day weekend... And she told me we were camping at Occoneechee Park sometime this year but I forget when... (CRS is he$$). The DW keeps telling me our camping card is filling up fast this year...

Happy Trails,

B n D
__________________
His TV: 2014 RAM 3500 MC DRW 6.7 CTD AISIN
His RV: 2014 REDWOOD 38FL (House)
Her TV: 2013 RAM 1500 CC 5.7 Hemi
Her RV: 2010 VCross 20VFB (Camper)
--------------------------------------------------
Bill n Diana is offline   Reply With Quote
Reply

Tags
electric, electrical


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 12:28 PM.