Old 06-01-2015, 06:35 PM   #11
Senior Member
 
davel1971's Avatar
 
Join Date: Nov 2013
Location: Seaford, De
Posts: 2,317
I thought about doing that, but since I just put in a new ac unit the same day, wasn't taking any chance of frying anything.
__________________

__________________
David & Lynn
2014 Coachmen Chaparral Signature 327 RLKS
2016 Ford F350 Lariat CC Dually
davel1971 is offline   Reply With Quote
Old 06-01-2015, 06:54 PM   #12
Senior Member
 
northstar1960's Avatar
 
Join Date: Feb 2015
Location: in my new 29hfsxlr
Posts: 1,658
Quote:
Originally Posted by davel1971 View Post
I have a Coachman 5th wheel with a Progressive Industries EMS hardwired protection unit. Recently bought a Champion generator that has a 30 amp RV plug already on generator. Tried to use for first time Saturday, and get a E2 fault, open ground. Does the generator need any type of grounding or is there a possible problem with my new generator?

That's because the generator is not grounded . there is a place on the genset to add a ground wire . I use a solid piece of copper run it into the ground and then have a 8ga wire with a clip on it hooked into the generator .
__________________

__________________
northstar1960 is offline   Reply With Quote
Old 06-01-2015, 06:57 PM   #13
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,337
Quote:
Originally Posted by northstar1960 View Post
That's because the generator is not grounded . there is a place on the genset to add a ground wire . I use a solid piece of copper run it into the ground and then have a 8ga wire with a clip on it hooked into the generator .
Incorrect.
It needs a neutral bonded plug as suggested by fonzi.

TURBS
08 duramax tuned n modded
2011 32bhok Sabre
2015 camping "9 nights"
__________________
TURBS is offline   Reply With Quote
Old 06-01-2015, 07:10 PM   #14
Senior Member
 
HONDAMAN174's Avatar
 
Join Date: Jun 2011
Location: Big brown desert
Posts: 2,319
When I run a single honda 2000, I use the grounded plug. When both units are parrelled, I have to flip the bypass switch.
__________________
2014 Stealth Evo 2850- "Woodstock"
2011 Toyota Tundra Rock Crawler TRD 5.7- "Clifford"
2013 Honda Accord Coupe V6 w/Track Pack- "Julia"

Just glad to get away
HONDAMAN174 is offline   Reply With Quote
Old 06-01-2015, 10:42 PM   #15
Member
 
Join Date: Apr 2013
Posts: 81
Quote:
Originally Posted by northstar1960 View Post
That's because the generator is not grounded . there is a place on the genset to add a ground wire . I use a solid piece of copper run it into the ground and then have a 8ga wire with a clip on it hooked into the generator .
That's not true. You're confusing earth grounding with neutral bonding. The ground rod by itself doesn't provide the correct low impedance "ground" path back to the neutral, so many EMS protectors (Electrical Management Systems) will interpret it as an open "ground" and shut down the power.

Portable generators feeding a single load system such as an RV don't require a ground rod of any type to be Code compliant. However, they really should be Ground-Neutral bonded since a lot of modern electronics will behave badly without a ground plane tied to the neutral.

Mike Sokol
No Shock Zone
__________________
jmsokol is offline   Reply With Quote
Old 06-01-2015, 10:46 PM   #16
Member
 
Join Date: Apr 2013
Posts: 81
Quote:
Originally Posted by HONDAMAN174 View Post
When I run a single honda 2000, I use the grounded plug. When both units are parrelled, I have to flip the bypass switch.
I've encountered this before. It's caused because the interconnecting jumpers between the two gensets are not color coded, so there's a 50/50 chance of getting the one generator's polarity flipped. If you're using a companion generator, then that's the one that should have my G-N bonding plug installed. If you're using an aftermarket kit with a separate TT-30 outlet, then you should mark your jumper cables with colored electrical tape to be sure you connect them with proper polarity each time you hook up. There's no damage done to the generators if they're connected out of polarity, but it will make your EMS think that the Neutral and Hot have been reversed which is shutting you down.

Mike Sokol
No Shock Zone
__________________

__________________
jmsokol is offline   Reply With Quote
Reply

Tags
generator

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 11:27 PM.