Generator quits when using both ACs.

Hi,
I’m in an older RV (1999 Gulfstream Class A Scenic Cruiser). I have a dual A/C roof mounted system with Duo-Therm by Dometic branding.

Dry camping or driving running off my generator everything works fine for about 10-13 minutes with both units cooling nicely. Suddenly the generator shuts down and with it, both A/C units (naturally). I can leave off for 10 minutes or so then restart the gen. All works well again for about 10-13 minutes before gen again shuts down.

If I’m hooked up to 50 Amps service, no problems.

Anyone able to assist? Please PM me.

Thanks
RRTSCB is offline   Reply With Quote
Old 07-25-2019, 09:13 AM   #2
Senior Member
 
Join Date: Jun 2015
Location: Payson, AZ
Posts: 3,874
what generator? what size a/c's? is any other electric load on (converter, water heater, etc)? do they shut down when running or when a compressor tries to start?

i do not know how your generator responds if it is overloaded? perhaps it shuts down.
__________________
2015 cardinal model 3825fl
2015 dodge ram 3500 dually
CHICKDOE is offline   Reply With Quote
Old 07-25-2019, 09:18 AM   #3
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
How much fuel is in the fuel tank? I know on a lot of units, the low level cutoff for the generator is above the 1/4th tank level.

If you run the generator without running the A/C's does it run longer?
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 07-25-2019, 09:50 AM   #4
Senior Member
 
Daycruiser's Avatar
 
Join Date: Jul 2018
Location: Crossville,TN
Posts: 588
My take is fuel starvation at the Gen with a heavy load. Fuel pump on the Gen may have retired and it's not getting enough fuel when you really load it up to keep running. The fact that it restarts tells me the fuel gets replenished when it shuts down. Just my 3 cents worth.
__________________
Retired 2020.
46 Years RVing and no end in sight.
2018 Ram 3500 SB Limited, CC, 6.7/Aisin, 4X4, SRW. Comfort Ride Energy Absorbing Hitch.
2020 Cedar Creek Hathaway 34IK, Reese 19K Sidewinder PB.
Daycruiser is offline   Reply With Quote
Old 07-25-2019, 10:06 AM   #5
Senior Member
 
NMWildcat's Avatar
 
Join Date: Jun 2012
Location: Southern NM
Posts: 9,564
Quote:
Originally Posted by Daycruiser View Post
My take is fuel starvation at the Gen with a heavy load. Fuel pump on the Gen may have retired and it's not getting enough fuel when you really load it up to keep running. The fact that it restarts tells me the fuel gets replenished when it shuts down. Just my 3 cents worth.
X2, first guess is fuel problem. Check/change fuel filter first.
__________________
Scott and Liz - Southern NM
2012 Wildcat Sterling 32RL - w/level up (best option ever)
2007 Chevy 2500HD Duramax
Reese Fifth Airborne Sidewinder
NMWildcat is offline   Reply With Quote
Old 07-25-2019, 01:01 PM   #6
Senior Member
 
Join Date: Dec 2014
Posts: 279
My guess is that your 2 20 year old a/c units are drawing more power than your generator can continually provide.
ActionJackson is offline   Reply With Quote
Old 07-25-2019, 02:19 PM   #7
Member
 
Join Date: Jan 2017
Posts: 38
My best guess is the Gen to small for 2 AC's
wcrafter is offline   Reply With Quote
Old 07-25-2019, 02:34 PM   #8
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,149
Quote:
Originally Posted by ActionJackson View Post
My guess is that your 2 20 year old a/c units are drawing more power than your generator can continually provide.
Quote:
Originally Posted by wcrafter View Post
My best guess is the Gen to small for 2 AC's
I'm not going to say their two A/Cs aren't drawing too much current... BUT... that would make the generator shut down. It might trip the breaker but it wouldn't stop the engine.

Again, it sounds more like a fuel starvation issue under heavy load.

What happens if you only run one A/C? How long does it run?
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=90
5picker is offline   Reply With Quote
Old 07-25-2019, 02:35 PM   #9
Senior Member
 
Join Date: Nov 2015
Posts: 672
Might be oil level. Some generators will shut down when the oil gets to low. With a full load and hot weather the oil may be foaming up after a bit and then tripping the low oil sensor.
MtBiker is offline   Reply With Quote
Old 07-25-2019, 03:04 PM   #10
Senior Member
 
Join Date: Dec 2014
Posts: 279
Quote:
Originally Posted by 5picker View Post
I'm not going to say their two A/Cs aren't drawing too much current... BUT... that would make the generator shut down. It might trip the breaker but it wouldn't stop the engine.

Again, it sounds more like a fuel starvation issue under heavy load.

What happens if you only run one A/C? How long does it run?
Maybe my circuit breaker is not working correctly on my generator, but if I overload my Micro 4000 Onan, it will totally shut down. Relieve the load off of it and it starts right back up.

Good advice to the OP to just run one and see what happens. If no more issues, it would be a power overdraw scenario.
ActionJackson is offline   Reply With Quote
Old 07-25-2019, 04:09 PM   #11
Senior Member
 
Daycruiser's Avatar
 
Join Date: Jul 2018
Location: Crossville,TN
Posts: 588
Quote:
Originally Posted by Daycruiser View Post
My take is fuel starvation at the Gen with a heavy load. Fuel pump on the Gen may have retired and it's not getting enough fuel when you really load it up to keep running. The fact that it restarts tells me the fuel gets replenished when it shuts down. Just my 3 cents worth.

Here's what led me to fuel starvation: "Dry camping or driving running off my generator everything works fine for about 10-13 minutes with both units cooling nicely." If it were a overload condition I strongly doubt it would run both for 13 minutes. Startup inrush is the highest load on the Gen, Once the compressors are up and running the load drops considerably. Just my second 3 cents.
__________________
Retired 2020.
46 Years RVing and no end in sight.
2018 Ram 3500 SB Limited, CC, 6.7/Aisin, 4X4, SRW. Comfort Ride Energy Absorbing Hitch.
2020 Cedar Creek Hathaway 34IK, Reese 19K Sidewinder PB.
Daycruiser is offline   Reply With Quote
Old 07-25-2019, 05:10 PM   #12
Senior Member
 
Join Date: Mar 2019
Location: Nevada
Posts: 1,815
Try running one AC unit at a time.
ppine is offline   Reply With Quote
Old 07-25-2019, 05:47 PM   #13
Site Team
 
dcheatwood's Avatar
 
Join Date: Nov 2011
Posts: 4,499
Also, as in my recent experience. The gen can shut down if oil is too high. I had the shut down issue after first oil change and found a video on YouTube about it. Seems a little to much oil will cause shutdown as it warms up. After cool down, gen runs fine again for a little while.

The solution was to remove a little oil. I did that and the problem was gone. Seems more likely when gen is not level. Mine is an onan microquiet 4000.
Quote:
Originally Posted by MtBiker View Post
Might be oil level. Some generators will shut down when the oil gets to low. With a full load and hot weather the oil may be foaming up after a bit and then tripping the low oil sensor.
__________________
2018 Forester 3011 DS

dcheatwood is offline   Reply With Quote
Old 07-26-2019, 01:46 PM   #14
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,149
Quote:
Originally Posted by dcheatwood View Post
Also, as in my recent experience. The gen can shut down if oil is too high. I had the shut down issue after first oil change and found a video on YouTube about it. Seems a little to much oil will cause shutdown as it warms up. After cool down, gen runs fine again for a little while.

The solution was to remove a little oil. I did that and the problem was gone. Seems more likely when gen is not level. Mine is an onan microquiet 4000.
Interesting. Thanks for the post.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=90
5picker is offline   Reply With Quote
Old 07-26-2019, 04:01 PM   #15
Junior Member
 
Join Date: Jul 2019
Posts: 6
A/C shutting down (follow up)

For those who’ve asked, the fuel is propane and yes it’s full. In fact, it wasn’t until I refilled it that this problem started. Coincidence? Seems unlikely.

The only things running are the two roof-mounted A/C units; nothing else except those times when the Cummins diesel is running.

The generator is a GENERAC NP-66G.

DOMETIC DOU-THERM A/C units.

Thanks
RRTSCB is offline   Reply With Quote
Old 07-26-2019, 04:06 PM   #16
Junior Member
 
Join Date: Jul 2019
Posts: 6
The oil in the generator is just below the FULL mark; it’s probably 9/10 full. Not overfilled and not too low. Thanks for that info; someone said I should drain out some of the oil but the level hasn’t changed in the last 4 months that I’ve been checking it and this issue has just started (over 4th of July weekend trip) and continues every time I’ve tested it.
RRTSCB is offline   Reply With Quote
Old 07-26-2019, 04:38 PM   #17
Senior Member
 
Daycruiser's Avatar
 
Join Date: Jul 2018
Location: Crossville,TN
Posts: 588
Quote:
Originally Posted by RRTSCB View Post
fuel is propane and yes it’s full.

Ok now there's an important piece of information. LP. Would have been nice to know that in the beginning. I want my 6 cents back.
__________________
Retired 2020.
46 Years RVing and no end in sight.
2018 Ram 3500 SB Limited, CC, 6.7/Aisin, 4X4, SRW. Comfort Ride Energy Absorbing Hitch.
2020 Cedar Creek Hathaway 34IK, Reese 19K Sidewinder PB.
Daycruiser is offline   Reply With Quote
Old 07-26-2019, 05:39 PM   #18
Junior Member
 
Join Date: Jul 2019
Posts: 6
Sorry about that. ��
RRTSCB is offline   Reply With Quote
Old 07-26-2019, 05:52 PM   #19
Senior Member
 
Join Date: Jun 2015
Location: Payson, AZ
Posts: 3,874
i looked at the manual for this generator. i could only find two reasons for a shutdown. one is low oil pressure and the other is over temperature. i did not find any indication that it flashes an error code like the onans do. so your guess. i could make a case for over temperature as it restarts and runs after it cools down. but that is purely a guess.
__________________
2015 cardinal model 3825fl
2015 dodge ram 3500 dually
CHICKDOE is offline   Reply With Quote
Old 07-26-2019, 06:13 PM   #20
Junior Member
 
Join Date: Jul 2019
Posts: 6
Thank you!
RRTSCB is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 05:54 PM.