Generator won't Power A/C

Specifics:
Class C 2012 Lexington
A/C - Dometic Penguin II with Heat Pump
Generator - Onan RV QG 4000

When trying to start the A/C while under generator power, the generator bogs down and shuts off. The flashing light error code indicates too much load such as trying to run A/C while battery charger is running. I turned the house battery disconnect switch to off and tried again. Fan came on but the compressor won't kick over.

It seems unusual that the installed generator can't pull the load, but it can do everything else but the A/C. Is this normal?

Would a Micro-Air Easy Start be a possible solution?
__________________
2012 Lexington C Class
Toad: 2009 Honda Fit
Bob_K is offline   Reply With Quote
Old 05-30-2018, 01:18 PM   #2
Senior Member
 
A32Deuce's Avatar
 
Join Date: Nov 2012
Location: Mount Laurel, New Jersey
Posts: 9,230
That does help. Did that mod to mine.
__________________
2012 SunSeeker 3100SS Toad-1962 Futura Average 100 + days camping
A32Deuce is offline   Reply With Quote
Old 05-30-2018, 01:57 PM   #3
Senior Member
 
Join Date: Oct 2016
Location: SW PA
Posts: 909
Based on the info you provided I would say there is a issue with the generator. Your genny is rated to produce 4000 watts. Your rig being a 30 amp system has a max load of 3600 watts (30 amps @ 120 volts). If your A/C starts on shore power it should start on genny power.

It possible that the genny control is reading a higher peak load due to a internal malfunction. The only way to confirm would be to load test the genny, both continuous and peak. There also is the possibility that the locked rotor current draw from the A/C is excessive (possibly due to a bad start cap) and causing the shutdown. But I would expect that to trip the A/C’s 20 amp circuit breaker.

Also shuting off your battery disconnect may not disable your battery charger. Best bet to remove that load when testing would be to shut off the circuit breaker feeding the converter.

A easy start may help but something else is the root cause.
__________________


2021 Newmar Baystar 3401
2019 Jeep Cherokee Trailhawk toad
2017.5 Forester 3051S Traded 7/2020
Steve-W is offline   Reply With Quote
Reply

Tags
generator, power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 05:32 PM.