Old 06-08-2016, 06:20 AM   #11
Senior Member
 
Join Date: Jan 2015
Location: Englewood FL
Posts: 1,604
[QUOTE=Tom48;1219894]
Quote:
Originally Posted by friendofacatahoula View Post
Scott, so are you agreeing that a Pwm with two panels in parallel could possibly be better?

My tech guy did some test with a small system. (He is now at 3000 watts---not small) At 400 watts he found that series with the Mppt, most started charging in lower am and pm lighting, but found less loss and overall better production with PWM.
From everything that I can read, it is very hard to find any real proof that MPPT is of any advantage for smaller systems. I believe that the biggest advantage that it has is that it can handle higher voltages than PWM so it can be used in big systems supporting many series connected panels and the much higher voltages and lower feed currents that result. For a system that one would use in an RV those parameters are really not useful anyway.

Two to four 100 watt panels, parallel connected to PWM is the ticket, as is the really well executed design of the Bogart TM and SC pair.
__________________

__________________

2015 335DS
ScottBrownstein is online now   Reply With Quote
Old 06-09-2016, 07:38 PM   #12
Senior Member
 
PokerDealer's Avatar
 
Join Date: Feb 2012
Location: NowthWest
Posts: 126
So, I have a few questions. although my 55 amp stock Wafco appears to be working fine, I seem to thing it takes to long to charge the batteries (two T105's) I am going to install the SC 2030 in consort with the already installed TM 2030. First question, it all I need to do is share positive and have the negative go from the batteries to the large bolt on the far side of the shunt?
I'm looking at the upgrade that Progressive Dynamics offers, It's programmable with the Charge Wizard and pedant. Should I replace and controller because nothing get past the controller or will I be able to program the SC2030 to deliver power directly to the batteries? I'm going to install the temp sensor and SC 2030 do the cables that go out to the panels need any kind of special connection or will screwed in lugs work? I'm trying to order just the panels from Windy Nation most portable kits come with a charge controller pre-attached. your comments please.
__________________

__________________
2015 Wildwood 181 BHXL. 2005 1500 Ram Hemi 4x4 W/package
PokerDealer is offline   Reply With Quote
Old 06-09-2016, 09:01 PM   #13
Senior Member
 
Join Date: Jan 2015
Location: Englewood FL
Posts: 1,604
Quote:
Originally Posted by PokerDealer View Post
So, I have a few questions...
First, you can leave the WFCO or replace it with a PD unit as it has nothing to do with the SC2030 charge controller from Bogart. The 2030 positive lead goes to the battery positive and the negative lead goes to the chassis, just like the negative lead of the WFCO does. You can put the positive lug on the battery controller post that goes to the positive battery post, or you can run it directly to the battery positive post. Put a 30 amp fuse in the positive line from the SC2030 to the battery, since the 2030 cannot put out more than 20 amps anyway. The shunt goes between the battery common negative and the chassis ground. The sense wire to the TM goes on the battery side of the shunt and the two negative leads go on the shut post toward the chassis.

If you install the controller this way, the SC2030 will be able to charge your batteries regardless of whether the disconnect is on or off, unlike the WFCO which won't do anything with the disconnect off.

If you order the right length of #10 PV wire, you can run from the panels to the SC2030 directly, without the need for special connectors. However, most panels come with special solar connectors and you can get adaptors that will parallel both panels without any terminal strips. Many panels come with MC-4 solar connectors and you can just buy PV wire with the required connectors already attached. You can also get parallel adapters that will allow you to parallel two panels without resorting to 4 wires going down from the roof.

Take a look at Amazon https://www.amazon.com/HQRP-T-branch...=1&*entries*=0

Check what your panels have before you order the wire and connectors. Put a 30 amp fuse and fuse holder in the panel feed down from the roof to the SC2030.
__________________

2015 335DS
ScottBrownstein is online now   Reply With Quote
Old 06-10-2016, 07:32 PM   #14
Senior Member
 
PokerDealer's Avatar
 
Join Date: Feb 2012
Location: NowthWest
Posts: 126
I just purchased the SC 2030 it will act as the brains between the existing TM 2030 and the soon to be added solar panel(s). I am not going to replace my stock Wafco 55 amp stock controller. Will it suffice to just turn off the Main when I use solar power? All product is ordered and questions asked (almost). All I still need is the Solar panel(s) to add on the front side. I don't want to use roof mounts, I want to stay on the ground with adjustable stands. Storage, Quality, size are important, I'm looking for about 50 to 70 watts in 6+ hours. I think I'm looking for adding two 100 watt panels. Now open for panel suggestions
__________________
2015 Wildwood 181 BHXL. 2005 1500 Ram Hemi 4x4 W/package
PokerDealer is offline   Reply With Quote
Old 06-10-2016, 08:18 PM   #15
Senior Member
 
PokerDealer's Avatar
 
Join Date: Feb 2012
Location: NowthWest
Posts: 126
I'm going to install a positive battery cable from the positive post to the SC 2030, I'm going to install the temp sensor to the SC 2030 and connect the TM 2030 and the SC 2030 by the included phone line. I plan on installing cables that go from the SC 2030 to the solar panel(s) but I want to use an M4 connector or other connector so their is a pigtail so to speak on the way to the solar panel(s) that way I can connect and disconnect as needed when the panels(s) are deployed. Are you suggesting a stand alone 30 fuse on both sides?
__________________
2015 Wildwood 181 BHXL. 2005 1500 Ram Hemi 4x4 W/package
PokerDealer is offline   Reply With Quote
Old 06-12-2016, 09:38 PM   #16
Member
 
friendofacatahoula's Avatar
 
Join Date: Mar 2016
Location: Alberta
Posts: 86
Yes you can add a fuse or breaker on the power (+) side between the panels and controller and another between the controller and battery.

The Bogart installation diagrams are very straight forward and easy to follow. The only emissions are the placement of the fuses or breakers. I am currently using a 30 amp breaker on the panel side and a 40 on the battery side. I may swap those out for ANL or AGU type fuses as the breakers although functioning are not as easy to "view" a problem.


I installed my SC/TM combo this weekend while camping. The monitor is working flawlessly but I fear I have a bad controller. Neither LED light on the controller come on when the panels are hooked up. A little disappointed now.
__________________
friendofacatahoula is offline   Reply With Quote
Old 06-26-2016, 11:13 PM   #17
Junior Member
 
Join Date: Jun 2016
Posts: 22
Quote:
Originally Posted by friendofacatahoula View Post
Yes you can add a fuse or breaker on the power (+) side between the panels and controller and another between the controller and battery.

The Bogart installation diagrams are very straight forward and easy to follow. The only emissions are the placement of the fuses or breakers. I am currently using a 30 amp breaker on the panel side and a 40 on the battery side. I may swap those out for ANL or AGU type fuses as the breakers although functioning are not as easy to "view" a problem.


I installed my SC/TM combo this weekend while camping. The monitor is working flawlessly but I fear I have a bad controller. Neither LED light on the controller come on when the panels are hooked up. A little disappointed now.
Have you got it working yet?
My 2016 2504S mini lite has two 160 watt rigid mono panels (with another two panels awaiting install) I run the Bogart system and find the absorption voltage controllability superior. Guess what? "At 260lbs I did not fall though the roof " been on the freeway and dirt roads and the panels didn't fall off!
My father-in-law glued an 80 watt panel with just silicone been on for over 3000 miles. I sunk four screws per bracket.
Good luck with you're project!
__________________
Grizzzman is offline   Reply With Quote
Old 06-26-2016, 11:28 PM   #18
Senior Member
 
Blackhat6mike's Avatar
 
Join Date: Dec 2014
Location: St Simons Island, GA
Posts: 1,204
Fuses are good everywhere. I have 600 watts of panels into a 60amp controller and have a 30 amp breaker in between. A 63amp breaker between the controller and battery bank. Also have a 300amp ANL between the 5,000 watt inverter and the battery bank. I'm an electronics tech and believe in fuses big time.
__________________
Aviator Wright Flyer #1919
Army Pathfinder Vietnam, 3 tours
DAV, MOPH, VFW, NRA, 1stCav. ABN
Blackhat6mike is offline   Reply With Quote
Old 06-27-2016, 01:22 AM   #19
Senior Member
 
Tom48's Avatar
 
Join Date: Apr 2015
Location: Ontario, California
Posts: 1,007
[QUOTE=ScottBrownstein;1220668]
Quote:
Originally Posted by Tom48 View Post

From everything that I can read, it is very hard to find any real proof that MPPT is of any advantage for smaller systems. I believe that the biggest advantage that it has is that it can handle higher voltages than PWM so it can be used in big systems supporting many series connected panels and the much higher voltages and lower feed currents that result. For a system that one would use in an RV those parameters are really not useful anyway.

Two to four 100 watt panels, parallel connected to PWM is the ticket, as is the really well executed design of the Bogart TM and SC pair.
Our camping partners have put 4 100s on their roof and ran two pairs in parallel with each pair in series. claims his MPPT controller stats charging in marginal times like early am just after the barest edge of sunrise as when each panel gets up to about 7 volts in output the series makes that 14 and enough to start charging the batteries. Same thing in overcast conditions. He charges in more marginal conditions than my 100s in parallel with my PWM controller. Still if you have big enough wire coming from the roof to handle big amps our PWM system satisfies our needs.
__________________
Tom48 is offline   Reply With Quote
Old 06-28-2016, 07:06 AM   #20
Member
 
friendofacatahoula's Avatar
 
Join Date: Mar 2016
Location: Alberta
Posts: 86
Quote:
Originally Posted by Grizzzman View Post
Have you got it working yet?
My 2016 2504S mini lite has two 160 watt rigid mono panels (with another two panels awaiting install) I run the Bogart system and find the absorption voltage controllability superior. Guess what? "At 260lbs I did not fall though the roof " been on the freeway and dirt roads and the panels didn't fall off!
My father-in-law glued an 80 watt panel with just silicone been on for over 3000 miles. I sunk four screws per bracket.
Good luck with you're project!
Sorry I was away for a few days.

My bogart controller is sitting on the table either waiting to go back to the retailer or bogart. A new one was supposed to have been delivered to me last week and I still haven't seen it so a little disappointed in that.

My panels are all installed and I have the 100watt semi flex panels on there. I opted to use 3M VHB tape on the panels to secure them. I tried it on a few items at home prior to see how strong it way compared to the typical automotive 3M tape and the VHB is going to have no problems with the 3 pound panels. I then sealed the edges with Dicor just to prevent any water penetration or wind from catching a lip.

This is where I feel I should have used Eternabond tape around the edges of the panels. The Dicor mentions it may "wrinkle" the roof material but I didn't understand to what extreme. It bubbled more than I would like to see but I will keep an eye on it. Dicor is supposed to be approved by this roof type for sealing.
__________________

__________________
friendofacatahoula is offline   Reply With Quote
Reply

Tags
solar

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 06:04 PM.