As Scott stated, the current is shuttling between the L1 and L2. The neutral only carries the imbalance.

It's explained in the link I previously posted in post #8.

It's this load balancing between the L1 and L2, along with the shared neutral which confuses most.

It does take a little reading, but it will soak in.
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 04-12-2018, 04:35 PM   #22
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,953
Quote:
Originally Posted by cavie View Post
WMTIRE, correct me if I'm wrong. The panel in the blue background is not correct. The 50 amp main would have to be in the middle feeding a split buss panel L1 to the left and L2 to the right as shown in the photo below it. In the example in blue, you could indeed use 240 volts in your trailer. A 30 amp service panel would be a single buss feed and the 30 amp main single pole breaker could go anywhere. In the example in blue the 30 amp is only feeding 1/2 of the panel.
Cavie, the electrical panel in blue would be like your house panel or the campgrounds main panel, and it's feeding the OUTLET that you plug your RV's shore power cord into. It shows as such in the pic, and this would be the feed from the electric company to the outlet. (aka shore power). It shows the shore power feeds to a 50 amp and 30 amp outlet/receptacle.

The second pic is the feed from the outlet via the shore power cord, into the RV's electrical distribution panel as I hopefully explained above the pic..
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 04-12-2018, 04:42 PM   #23
Senior Member
 
Join Date: Apr 2016
Location: Port Charlotte Fl/Hinsdale Ma
Posts: 4,823
Quote:
Originally Posted by wmtire View Post
Cavie, the electrical panel in blue would be like your house panel or the campgrounds main panel, and it's feeding the OUTLET that you plug your RV's shore power cord into. It shows as such in the pic, and this would be the feed from the electric company to the outlet. (aka shore power)

The second pic is the feed from the outlet via the shore power cord, into the RV's electrical distribution panel as I hopefully explained above the pic..
I just realized you were showing the pedestal panel. not the RV panel
cavie is offline   Reply With Quote
Old 04-12-2018, 05:09 PM   #24
Member
 
Join Date: Oct 2015
Location: Las Vegas, NV
Posts: 85
Just like the Clothes Dryer in your house, just 110-120 per Leg.
__________________
David L Horton
2016 Georgetown 328
dphorton is offline   Reply With Quote
Old 04-12-2018, 05:50 PM   #25
Senior Member
 
Join Date: Apr 2016
Location: Port Charlotte Fl/Hinsdale Ma
Posts: 4,823
The differance being is your house uses line 1 and 2 at the same time to get 240 volts. Your Rv can't do that. 120 volts only.
cavie is offline   Reply With Quote
Old 04-12-2018, 08:11 PM   #26
Member
 
Join Date: Oct 2015
Location: Las Vegas, NV
Posts: 85
Well from L1 to Neutral it is 110-120. From L2 to Neutral it is also 110-120. So it is the same. You just have L1, L2, Neutral and Ground with a 50 Amp Hookup. Taking 110-120 from each Leg at max 50 Amp per Leg.
__________________
David L Horton
2016 Georgetown 328
dphorton is offline   Reply With Quote
Old 04-14-2018, 12:49 PM   #27
Senior Member
 
RVBuff's Avatar
 
Join Date: Jan 2013
Location: Charlotte, NC
Posts: 144
Quote:
Originally Posted by elind View Post
The RV 50 amp service is two 50 amps 120 volt circuits. Nothing runs on 240 volts in the RV. That way when you use a 30 to 50 amp dog leg adapter you only get 30 amps because both hot lines are tied together. In a 30 amp cable you 3-10 gauge wires feeding the RV and in a 50 amp cable there is 4-6 gauge wires (2 hot wires).
wmtire...Please clarify this--Are the two 50 amp legs tied together in a dogbone?
RVBuff is offline   Reply With Quote
Old 04-14-2018, 03:07 PM   #28
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,953
Quote:
Originally Posted by RVBuff View Post
wmtire...Please clarify this--Are the two 50 amp legs tied together in a dogbone?
If you are talking about a 50 amp female to 30 amp male adapter, that allows you to use a 50 amp rv, on a 30 amp outlet... Then yes the 30 amp L1(which is all a 30 amp has) is shared/jumped to both the L1 and L2 legs of the 50 amp cord.

This allows both the L1 and L2 inside the RV to have power, so half of your stuff wouldn't work otherwise.

Just remember, a 30 amp outlet ONLY had one leg at 120 volts, so sharing this one leg, is still only 120 volts.

It's just now you are limited to 30 amps inside your 50 amp RV when using this adapter.

I'm currently on the road or I would provide schematics of how the L1 and L2 share the only L1 of a 30 amp outlet. I've posted these many times. Maybe somebody can share such.

This link will show it.

http://www.dmbruss.com/zFullTimeLife...alAdapters.htm
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 04-14-2018, 06:53 PM   #29
Senior Member
 
bubbles's Avatar
 
Join Date: Dec 2012
Posts: 7,652
Actually it's probably better to look at it as being limited to 30 amps total on your 100 amps total rv. Makes you think about usage limit adjustments. Just a thought.
bubbles is offline   Reply With Quote
Old 04-14-2018, 07:19 PM   #30
Senior Member
 
Join Date: Jan 2017
Posts: 3,290
I'll simplify this '50amp RV electrical' answer even more:

no matter 'how much' electrical power you are connected to, either 50amp(100amps total), 30amp, 20amp, 15amp, or anything in between... the individual circuit breaker for each outlet(s) or device is the limiting factor.


travel, enjoy! ...and plug in!
__________________
The Turners...
'07 Rockwood Signature Ultralight...
two Campers and two Electric cars : )
formerFR is offline   Reply With Quote
Old 04-15-2018, 07:52 AM   #31
Senior Member
 
RVBuff's Avatar
 
Join Date: Jan 2013
Location: Charlotte, NC
Posts: 144
OK...I get it that you are talking about the 30-amp current as it enters your 50-amp RV. Obviously you would want to feed both legs inside the unit. I misunderstood, thinking he was referring to the L1 and L2 pins on the female receptacle at the pedestal. If you tied those together, I would expect some fireworks.
RVBuff is offline   Reply With Quote
Old 04-15-2018, 09:07 AM   #32
Senior Member
 
Join Date: Apr 2017
Posts: 175
Just quick nod to electricians. Those diagrams look exactly like what an electrician would wire up for you and what I would expect them to wire up. It's the standard. Nothing different for an RV. If you didn't get exactly that, you need a better electrician.
__________________
2017 Ford F350 LB SRW 4x4
2016 Cedar Creek Silverback 29RE
BigRockr is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 03:27 PM.