My generator stops running when going over bumps, rough roads
My 5.5 Onan genset cuts off on its own if I am driving on a rough road (hard to go around these), go over a rough railroad crossing, hit a pot hole, etc. On a previous trip, one of the two 30 amp breakers would trip, but on this last trip, both breakers are still on after the generator stops. I am running 1 A/C, and, per FR advice due to known problems, have the vent on the A/C open, as opposed to closed which would direct the cool air into the overhead ducts. I also experience what sounds like the A/C almost shutting off, but staying on, and then quickly getting back to full capacity as I am driving along. Any help on this issue so I can stay cool while driving? (sorry, I put this post into the general discussion first by accident).
Thanks.
__________________
2016 Georgetown 270S
2013 Ford C-Max Hybrid
2 Jamis Hybrid Bicycles
Not too serious about anything except what affects health and happiness.
|
|
|
09-12-2016, 09:59 AM
|
#2
|
Senior Member
Join Date: Jan 2015
Location: Englewood FL
Posts: 2,797
|
Make sure your oil is right up to the full mark. There is a low oil sensor that might be cutting it off.
__________________
2015 335DS
|
|
|
09-12-2016, 10:11 AM
|
#3
|
Back On The Go
Join Date: Dec 2015
Location: Central Texas
Posts: 272
|
Thanks. I check it regularly and it is maybe 1/4" below total full mark, but I'll put more in.
__________________
2016 Georgetown 270S
2013 Ford C-Max Hybrid
2 Jamis Hybrid Bicycles
Not too serious about anything except what affects health and happiness.
|
|
|
09-12-2016, 10:25 AM
|
#4
|
Member
Join Date: Jul 2016
Location: Mississippi
Posts: 41
|
Quote:
Originally Posted by salwolfe
My 5.5 Onan genset cuts off on its own if I am driving on a rough road (hard to go around these), go over a rough railroad crossing, hit a pot hole, etc. On a previous trip, one of the two 30 amp breakers would trip, but on this last trip, both breakers are still on after the generator stops. I am running 1 A/C, and, per FR advice due to known problems, have the vent on the A/C open, as opposed to closed which would direct the cool air into the overhead ducts. I also experience what sounds like the A/C almost shutting off, but staying on, and then quickly getting back to full capacity as I am driving along. Any help on this issue so I can stay cool while driving? (sorry, I put this post into the general discussion first by accident).
Thanks.
|
We have had the same problem with our new MH. Thanks in advance for all the helpful advice. Deb
__________________
Mitch & Debbie
Maggie, the Wonder Dog
2015 GeorgetownXL 352
2016 Jeep Wrangler Unlimited
|
|
|
09-12-2016, 12:40 PM
|
#5
|
Junior Member
Join Date: Oct 2010
Location: Kansas
Posts: 26
|
I have a Generac that shuts off going down the road also. It starts right up again but will shut down again for no apparent reason. Oil is full and breakers are not tripped. Runs fine when the unit is parked. Any ideas?
|
|
|
09-12-2016, 12:47 PM
|
#6
|
Pickin', Campin', Mason
Join Date: Aug 2015
Location: South Western PA
Posts: 19,051
|
Many generators use a spring loaded, coil activated contactor in the transfer switch to transfer the electrical power to the coach once started.
I've seen some of these that 'bumps/rough roads' would jar the contactor enough to disconnect.
Just a possibility.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2017 Ford F-Series SCREW 4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA
Days Camped ☼ '19=118 ☼ '20=116 ☼ '21=123 ☼ '22=134 ☼ '23=118☼ '24=64
|
|
|
09-12-2016, 01:00 PM
|
#7
|
Junior Member
Join Date: Oct 2010
Location: Kansas
Posts: 26
|
It's worth a shot.
|
|
|
09-12-2016, 01:07 PM
|
#8
|
Junior Member
Join Date: Nov 2015
Location: Lake Havasu City, Arizona
Posts: 21
|
Also, on the onan units they need a valve adjustment after the first 50 hours or so. The valves tighten up during breakin. That will cause a severe loss of compression.
|
|
|
09-12-2016, 01:33 PM
|
#9
|
Senior Member
Join Date: Jul 2011
Posts: 904
|
Maybe they are getting fuel starved - their fuel pickups are supposed to be at the 1/4 tank level, but maybe they aren't or the fuel was too low?
__________________
former 2017 Forest River Sunseeker 2250SLE owner - replaced by a Pleasure-Way Tofino and then an Ontour 2.0
|
|
|
09-12-2016, 03:12 PM
|
#10
|
Junior Member
Join Date: Oct 2010
Location: Kansas
Posts: 26
|
As for mine, the fuel has been at least 1/2 tank if not more. Thought it might be a fuel filter problem but it only quits going down the road.
|
|
|
09-12-2016, 06:06 PM
|
#11
|
Back On The Go
Join Date: Dec 2015
Location: Central Texas
Posts: 272
|
Yes, my fuel tank is over 3/4 full when the generator quits. Still might be fuel starved but not due to running with the tank too low for normal operation.
__________________
2016 Georgetown 270S
2013 Ford C-Max Hybrid
2 Jamis Hybrid Bicycles
Not too serious about anything except what affects health and happiness.
|
|
|
09-12-2016, 07:28 PM
|
#12
|
Junior Member
Join Date: Dec 2015
Location: florida
Posts: 16
|
We had the same issue. I don't know wat fixed it but when I changed the oil made sure it was completely full and I also realized that I was keeping my water heater on,so now heater is off and I run only one Ac plus residential refrigerator, no more problems.
|
|
|
09-12-2016, 07:32 PM
|
#13
|
Back On The Go
Join Date: Dec 2015
Location: Central Texas
Posts: 272
|
Thanks. I won't be out again for about 3 weeks and will ensure that oil is totally full and not just in the "acceptable" range. I turn water heater off on both propane and electric heat.
__________________
2016 Georgetown 270S
2013 Ford C-Max Hybrid
2 Jamis Hybrid Bicycles
Not too serious about anything except what affects health and happiness.
|
|
|
09-13-2016, 08:31 PM
|
#14
|
Junior Member
Join Date: Aug 2016
Location: Oklahoma
Posts: 19
|
Just another idea on your "bumpy road" Generator, Mine (Champion4000)
Did this after a ride on a very bumpy road in Colorado. Again, the Oil level Switch......has a wire coming from it. See if yours unplugs from another wire. M/F connection. Unplug this wire, Start the Generator......let it run 20 minutes, then reconnect. No problems Since learning this.
__________________
Carmwes54
Keystone Cougar 22 RBS
Forest River E Pro 15 TB
'17 Ford Super Duty F-250
|
|
|
09-14-2016, 08:27 AM
|
#15
|
Back On The Go
Join Date: Dec 2015
Location: Central Texas
Posts: 272
|
Thanks Carmwes.
__________________
2016 Georgetown 270S
2013 Ford C-Max Hybrid
2 Jamis Hybrid Bicycles
Not too serious about anything except what affects health and happiness.
|
|
|
10-24-2016, 12:00 AM
|
#16
|
Member
Join Date: Jun 2016
Posts: 85
|
Onan has a check engine light. If the Gen is shut down for a reason other than pushing the button it will flash the status light. No blink would lead me to belive you may have a pinched stop wire. If you open the outside access there is a remote pigtail on the left over the battery cable. If you unplug it you can only start and stop from outside but it will bypass the remote wiring. If it takes the bumps like that it is time to hunt the short.
|
|
|
10-24-2016, 07:48 AM
|
#17
|
Back On The Go
Join Date: Dec 2015
Location: Central Texas
Posts: 272
|
Thanks, Spaach. We just got back from a trip with a 95 degree day, and experienced the generator continuing to run, no particularly rough roads or large bumps, but power was lost into the coach while the generator was running. The genset had been running maybe 45 minutes or so at that point when we noticed the A/Cs were not running. Air conditioners had turned off and there was no power to microwave panel (didn't have it on; just saw that there was no power to the clock). No circuit breakers tripped inside or out.[Our first experience with problems on a previous trip had been the generator stopped running and one of the circuit breakers on the genset had tripped].
I heard a couple of loud noises outside on the driver side as I was standing in the bedroom. I went outside to listen better and experience the generator kind of coughing/sputtering while the generator was running before I went ahead and turned it off.
We had just stopped and filled up with gasoline prior to turning the generator on so the tank was filled close to capacity. I am scheduled to take the rig into a non-FR authorized service company maybe next week where I will have to pay them and get reimbursement from FR, so I'll talk to them about all of these issues/possibilities.
Would be nice to take it to a FR authorized servicer but there isn't one close by that will do warranty work since I bought it somewhere else.
__________________
2016 Georgetown 270S
2013 Ford C-Max Hybrid
2 Jamis Hybrid Bicycles
Not too serious about anything except what affects health and happiness.
|
|
|
10-24-2016, 07:52 AM
|
#18
|
Back On The Go
Join Date: Dec 2015
Location: Central Texas
Posts: 272
|
Quote:
Originally Posted by 5picker
Many generators use a spring loaded, coil activated contactor in the transfer switch to transfer the electrical power to the coach once started.
I've seen some of these that 'bumps/rough roads' would jar the contactor enough to disconnect.
Just a possibility.
|
Picker, with my latest experience, I'm thinking more about your idea. I will not be working on this myself but I want to help out the service guy as much as possible (if he is receptive to 'not invented here' ideas).
__________________
2016 Georgetown 270S
2013 Ford C-Max Hybrid
2 Jamis Hybrid Bicycles
Not too serious about anything except what affects health and happiness.
|
|
|
10-24-2016, 08:02 AM
|
#19
|
Member
Join Date: Jun 2016
Posts: 85
|
Quote:
Originally Posted by salwolfe
Picker, the transfer switch you are referring to is in the generator, not in the power bay separate from the generator? With my latest experience, I'm thinking more about your idea, too.
|
If the rig has a transfer switch it is in a separate location. If you plug your shore cord in to an outlet inside its own compartment you most likely do not have a transfer switch.
If this is a KY or hgjab model there are some fuel pump problems on both that will cause a fueling stall. If the Gen shuts down due to this it will cause the trouble light to blink. If it only shuts down while you are driving the gas cap could be bad as well causing the main engine to pull the fuel out of the generator instead of the gas cap venting.
As far as the fuel pump: If you run the Gen till that loping stall, you can immediately hold the stop to prime button and see if the pump is trying to pump. It is on the under side of the generator below the control/breaker box. It vibrates as it pumps and makes a happy fast little thump, thump, thump sound that you can feel if you put your hand around it.
|
|
|
10-24-2016, 09:30 AM
|
#20
|
Back On The Go
Join Date: Dec 2015
Location: Central Texas
Posts: 272
|
Quote:
Originally Posted by spaach
If the rig has a transfer switch it is in a separate location. If you plug your shore cord in to an outlet inside its own compartment you most likely do not have a transfer switch.
If this is a KY or hgjab model there are some fuel pump problems on both that will cause a fueling stall. If the Gen shuts down due to this it will cause the trouble light to blink. If it only shuts down while you are driving the gas cap could be bad as well causing the main engine to pull the fuel out of the generator instead of the gas cap venting.
As far as the fuel pump: If you run the Gen till that loping stall, you can immediately hold the stop to prime button and see if the pump is trying to pump. It is on the under side of the generator below the control/breaker box. It vibrates as it pumps and makes a happy fast little thump, thump, thump sound that you can feel if you put your hand around it.
|
Mine is a Cummins Onan 5.5HGJAB so perhaps the known fuel pump problem is the issue. Thanks.
__________________
2016 Georgetown 270S
2013 Ford C-Max Hybrid
2 Jamis Hybrid Bicycles
Not too serious about anything except what affects health and happiness.
|
|
|
|
|
Thread Tools |
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|