Old 10-11-2014, 04:53 PM   #1
Junior Member
 
Join Date: Aug 2014
Posts: 16
Portable Generator Breaker switch..

Here is my issue.. Fifth wheel that is 50 amp.. I am trying to use a portable generator .. Briggs and Stratt .. 8550 start .. 5550 continuous .. The 30 out is a NEMA L14-30 125/250VAC 120/240 outlet circuit breaker switch.. I attach the "4" Prong locking 30 amp adapter that is a 30 amp out.. use a 30 amp to 50 amp dogbone to attach my 50 amp cable to my RV.. I do not get any power to the RV.. No breakers pop.. etc.. I was afraid that something horrible happened but upon inspection .. no breakers within the unit popped .. Turned off generator.. disconnected it and switched on batteries.. Thankfully everything worked fine.. I checked the Generator and the 120/240 circuit breaker on the generator popped .. So I disconnected the 30amp to 50 amp dogbone and main cord to RV but left the "4" prong generator adapter plugged in.. Fired generator and the breaker didn't pop...? What would be making my Generator pop its breaker ..? I never used anything within the RV to draw any power..? Is there a switch/unit I am over looking ..? I don't want to damage my unit..
__________________

__________________
Vonner is offline   Reply With Quote
Old 10-11-2014, 08:31 PM   #2
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 3,237
From your description, I think it is your 30 amp to 50 amp dog bone adapter that is creating a short causing your generator breaker to open. Pictures of your set up and adapters would help.....

Also I think you would need one of these to connect to generator.

http://www.campingworld.com/shopping...-adapter/69592
__________________

__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2008 F250 Lariat CC SB 6.8L V10 4.10 axle ratio (NITTO TERRA GRAPLER G2 LT275/65R20E)
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2011(21) 2012(36) 2013 (17) 2014 (18) 2015 (18) 2016 (36) 2017 (32)
fonzie is online now   Reply With Quote
Old 10-12-2014, 11:01 AM   #3
Junior Member
 
Join Date: Aug 2014
Posts: 16
I have another quick question.. For its seems nobody from Home Depot and Camping World whom both of my Local locations advised me to make an appointment with their Service Dept.. This is the Simple question.. The Camping world advertise adapter specifies that it is a 125/250 ..

50 Amp 125/250V RV Female to 30 Amp 4-Prong Twist Lock Male Generator Adapter - Furrion FP52GEN4-SB - Generator Accessories - Camping World

I have found one from another Online Retailer

Electric Generator Depot - DuroMax 10/4 30 to 50 Amp RV Adapter (for all standard 50A RV's) That is able to ship it 2 day for we needed it by next Thursday for we are leaving on a 14 day .. Ok now the Question .. are they basically the same..? I have noticed that some specify 120/240 yet my Generator 4 prong outlet specifies 125/250 .. Thanks again Fonzie .. Cheer's
__________________
Vonner is offline   Reply With Quote
Old 10-12-2014, 11:19 AM   #4
Junior Member
 
Join Date: Aug 2014
Posts: 16
Fonzie.. If I may ask.. Why would the Generator circuit breaker pop with the configuration I mentioned..? I was explained that I would lose a leg .. I have basic knowledge I believe.. Going from the 4 prong 30 to another 30amp/50 dogbone to my 50 main cord that runs to my RV If I am understanding doesn't allow the full power .. How would it short the generator out..? I don't have any pics to show.. My trailer is in storage at the moment .. Thanks again ..
__________________
Vonner is offline   Reply With Quote
Old 10-12-2014, 07:06 PM   #5
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 3,237
That is why I'm asking for a picture of your dog bone adapter that you mentioned in your first post. (I attach the "4" Prong locking 30 amp adapter that is a 30 amp out.. use a 30 amp to 50 amp dogbone)

Is it like the ones you post above or is it like this one? ( a 3 straight blade to 4 straight adapter)

50 Amp 125/250V RV Female to 30 Amp RV Male Pigtail Adapter with Pull Handles - Furrion IP5431R-SB - Electrical Adapters - Camping World
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2008 F250 Lariat CC SB 6.8L V10 4.10 axle ratio (NITTO TERRA GRAPLER G2 LT275/65R20E)
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2011(21) 2012(36) 2013 (17) 2014 (18) 2015 (18) 2016 (36) 2017 (32)
fonzie is online now   Reply With Quote
Old 10-12-2014, 08:49 PM   #6
Senior Member
 
VinceU's Avatar
 
Join Date: Dec 2011
Posts: 3,502
Quote:
Originally Posted by Vonner View Post
Here is my issue.. Fifth wheel that is 50 amp.. I am trying to use a portable generator .. Briggs and Stratt .. 8550 start .. 5550 continuous .. The 30 out is a NEMA L14-30 125/250VAC 120/240 outlet circuit breaker switch.. I attach the "4" Prong locking 30 amp adapter that is a 30 amp out.. use a 30 amp to 50 amp dogbone to attach my 50 amp cable to my RV.. I do not get any power to the RV.. No breakers pop.. etc.. I was afraid that something horrible happened but upon inspection .. no breakers within the unit popped .. Turned off generator.. disconnected it and switched on batteries.. Thankfully everything worked fine.. I checked the Generator and the 120/240 circuit breaker on the generator popped .. So I disconnected the 30amp to 50 amp dogbone and main cord to RV but left the "4" prong generator adapter plugged in.. Fired generator and the breaker didn't pop...? What would be making my Generator pop its breaker ..? I never used anything within the RV to draw any power..? Is there a switch/unit I am over looking ..? I don't want to damage my unit..
I may have figured your connection problem. Your unit is delivering 220V. By using a std. 50-30 amp Y you are shorting L1 to L2 just as Fonzie guessed. Not a portable gen guy but gotta believe there is an accessory to convert the gen set to a 120 output.
__________________
VinceU is offline   Reply With Quote
Old 10-13-2014, 10:37 AM   #7
Junior Member
 
Join Date: Aug 2014
Posts: 16
Fonzie.. Correct .. these are my adapters/dogbone etc.. Again thanks for all your help.. I ordered the 4 prong direct to the 50 RV .. its being shipped.. But this is what I tried ..

#1 Power Grip 30-Amp Generator Adapter - Camco 55382 - Electrical Adapters - Camping World

#2 50 Amp 125/250V RV Female to 30 Amp RV Male Pigtail Adapter with Pull Handles - Furrion IP5431R-SB - Electrical Adapters - Camping World

#3 This is not the exact but the Furrion 50 amp that came with the Fifth wheel

50 Amp 125/250V RV Cordset with Power Smart LED - 25' - Furrion F50AR25-SB - Electrical Cords - Camping World
__________________
Vonner is offline   Reply With Quote
Old 10-13-2014, 11:00 AM   #8
Junior Member
 
Join Date: Aug 2014
Posts: 16
after reading Vince post .. I am concerned about damaging my unit.. here are a few pics that may help seeing what I am trying to do ..

710e6640-b37b-439e-9017-3f31953dfa06.jpg Photo by vonner1 | Photobucket

20141013_104648.jpg Photo by vonner1 | Photobucket

20141010_142903.jpg Photo by vonner1 | Photobucket
__________________
Vonner is offline   Reply With Quote
Old 10-13-2014, 11:20 AM   #9
Senior Member
 
VinceU's Avatar
 
Join Date: Dec 2011
Posts: 3,502
Portable Generator Breaker switch..

No damage yet, thank heavens for circuit breakers. Your original setup looked like you generator at 220Vac to deliver single phase 110. Now I see you can deliver two 110 circuits. For your 50 amp Rv. I noted a special (unusual) portable cord that has male end for gen set with L ground and 3 blades L 1-2 and neutral. Other end is a 50 amp female with round ground and 3 blades same power and neutral , that your coach will plug into. This is correctly not 220 volt but two 120 volt circuits at 30 amp capacity. Please use a meter to confirm L1 and L2 to neutral are 120 v each.


Sent from my iPhone using Forest River Forum.

I saw the connector on line at portable generator cords.
__________________
VinceU is offline   Reply With Quote
Old 10-13-2014, 11:41 AM   #10
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 3,237
Vonner, from what you posted in #7, you probably did not do any damage to your unit, but probably overloaded your generator 30 amp receptacle breaker as it was trying to feed all the load in the trailer on one leg of the 125/230 volt supply. With the new adapter you should have two circuits feeding your 50 amp RV plug with about 23.1 amps per leg. You still have to manage your load in the trailer not to exceed the generator breaker rating..... What is the rating of the generator breaker feeding the 30 amp receptacle?
__________________

__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2008 F250 Lariat CC SB 6.8L V10 4.10 axle ratio (NITTO TERRA GRAPLER G2 LT275/65R20E)
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2011(21) 2012(36) 2013 (17) 2014 (18) 2015 (18) 2016 (36) 2017 (32)
fonzie is online now   Reply With Quote
Reply

Tags
breaker, generator

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 06:47 PM.