Old 01-06-2013, 03:33 PM   #11
Member
 
Join Date: Jun 2012
Location: Central Wyoming
Posts: 72
Midwest RV Power Outlets with post will work we'll. Each pedestal can be configured for phase connection of receptacles. Service will be a 200 amp service with 5 pedestals on each phase. Maximum load would then be 150 amps per phase. You will need 4 wire feeder for supply to pedestals. I am not sure of the materials and methods used in your area but if I were doing this project in my area (Wyoming) I would use 4/0 aluminum direct burial cable for phase and neutral conductors and a #4 cu equipment grounding conductor. This feeder is then looped through each pedistal. The post has the terminal blocks for in and out wiring with movable jumpers to connect the circuit breakers to the correct phase conductor. I will check on demand factors that may be able to be applied once I get to my office tomorrow. PM me with details - layout etc. and I will be glad to help with layout and material spec. I am an electrical contractor and have done a couple of small RV parks.
__________________

__________________
WY Husker Fan is online now   Reply With Quote
Old 01-06-2013, 07:05 PM   #12
Senior Member
 
lindy's Avatar
 
Join Date: Jun 2011
Location: Jamestown NY
Posts: 588
Thanks WY Husker Fan, I'd figure to use 2/0 4 wire alum cable to be sure and on the safe side incase of furture additions to the system.
__________________

__________________

2012 Winnebago "Journey To Insanity" 40U
2008 Dakota Sport 4x4
2004 Subaru Baja - DW's
2006 Honda Shadow Aero - TOAD for now.
F.R.O.G. member
lindy is offline   Reply With Quote
Old 01-06-2013, 09:00 PM   #13
Senior Member
 
Twisty's Avatar
 
Join Date: Mar 2012
Posts: 1,138
"It will be for church members only for the most part."
If you intend to rent spots to anyone outside the church, you need to get an attorney involved.
What if someone sets up and refuses to leave? or gets hurt? or...?
__________________
FOR SALE 2014 BOSS 6.2L F350
2012 Surveyor SV264
NW Oregon
Twisty is offline   Reply With Quote
Old 01-06-2013, 09:27 PM   #14
Senior Member
 
caper's Avatar
 
Join Date: Jul 2010
Posts: 1,973
I wired the 25 new sites at our local KOA. We used 3/0 alum wire. The panels do come prewired for 50/30/20 amp with breakers for all three or if using a 30 amp post is wired for 30/20 amp. The length of run plus the amps will determine the wire size needed. The longer the run the heavier the gauge wire will be needed because of voltage drop.
__________________
Terry and Janet
2008 3001W Windjammer
2007 Ford F150
caper is offline   Reply With Quote
Old 01-06-2013, 09:40 PM   #15
Senior Member
 
fast murray's Avatar
 
Join Date: Jul 2011
Location: SD
Posts: 439
I've always been told to overdo these installations as RV's keep having more electrical load. We did a 5 unit setup last summer with a 200 amp service fed with 250-250-250-3/0 URD. If they add more sites down the road we'll add another 200 amp service and so the same thing. Steer clear of the people in the electrical isle for advice, they generally lead to more trouble than good.
__________________

__________________
2004 Wildcat 28BH
2012 Ram 2500 CCSB 6.7CTD
fast murray is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 06:27 PM.