Quote:
Originally Posted by Herk7769 View Post
Start with the article in Big Baron's post and then go to the ground/Neutral lugs from the converter.

One or the other should fix it.
I flew through the thread and typed out a plea before I read the article. I will go with the suggestions.
thank-you.
__________________

__________________
Brother Les

2013 Forest River Salem Hemisphere SBT312QBUD

2001 CrewCab F-250 7.3 PowerStroke Diesel
SuperChip, BTS transmission, 6.0 Trans Cooler
Brother Les is offline   Reply With Quote
Old 08-15-2014, 11:25 AM   #22
Senior Member
 
B and B's Avatar
 
Join Date: Jun 2013
Location: Wilmot Twp, Ontario, Canada
Posts: 8,604
Having worked with tower grounding and AM transmitters the bonding of connections are important in both RF (Radio Frequency) and AC power. Often a compound called Penetrox is used.
PENA134 - Burndy - Electrical Joint Compounds | Galco Industrial Electronics

This will eliminate corrosion between dissimilar metals and provide a electrical connection between cleaned surfaces. This is available at Lowes or Home Depot. We used a lot of alumium connectors for high power 600 vac 500 amp services for UHF transmitters and always used penetrox to eliminate heating and damage.

One bigger question is code surrounding Neutral bonded to Ground. According to Ontario and Canadian Electrical code a sub panel can not have the neutral and ground bonded. The park service panel distribution is where they are bonded. The National electrical code in the US may be different and the trailer have CSA for Canadian Certification. There is the code that says no and the reality the Trailer is safe and meets code as per the CSA certification.

The outlets in the trailer are protected by GFCI so the bonding from a safety aspect might be a non issue but hot skin or what Lou had could still happen as the return ground path is on the neutral instead of the ground. With high power usage in a park, all being single phase, it is quite possible a lot of neutral current exists creating a AC potential between the bonded trailer ground and real earth ground. When I spec an install I always have double sized neutrals added to compensate for single phase loads.

Sorry for going all engineer on you with this

Brian
__________________

__________________
B and B is offline   Reply With Quote
Old 08-15-2014, 11:26 AM   #23
Senior Member
 
camaraderie's Avatar
 
Join Date: Feb 2014
Posts: 1,721
I just got one of these NON CONTACT VOLTAGE SENSORS (amazon) for 15 bucks to check the steps for hot skin after plugging in anywhere...but also useful for finding hot wires throughout the house and coach. I got this one because the adjustability makes it good for both 12 and 120V sensing and you can make it less sensitive to isolate THE wire with current in a bundle.
The ONLY thing I don't like about it is that you have to hold the on switch rather than there being a click on switch. Otherwise, highly recommended.
http://www.amazon.com/Sperry-Instruments-VD6505-Adjustable-Sensor/dp/B000GLAC5G/ref=sr_1_1?s=hi&ie=UTF8&qid=1408116681&sr=1-1
We also have a circuit tester like Herks above and give that a big DITTO too!
__________________
________
Cam
2015 Georgetown 280DS
2014 Vespa LX150 2014 StellaAuto 125
camaraderie is offline   Reply With Quote
Old 08-15-2014, 08:17 PM   #24
Senior Member
 
RPAspey's Avatar
 
Join Date: Jul 2008
Location: central PA
Posts: 973
Quote:
Originally Posted by B and B View Post
Having worked with tower grounding and AM transmitters the bonding of connections are important in both RF (Radio Frequency) and AC power. Often a compound called Penetrox is used.
PENA134 - Burndy - Electrical Joint Compounds | Galco Industrial Electronics

This will eliminate corrosion between dissimilar metals and provide a electrical connection between cleaned surfaces. This is available at Lowes or Home Depot. We used a lot of alumium connectors for high power 600 vac 500 amp services for UHF transmitters and always used penetrox to eliminate heating and damage.

One bigger question is code surrounding Neutral bonded to Ground. According to Ontario and Canadian Electrical code a sub panel can not have the neutral and ground bonded. The park service panel distribution is where they are bonded. The National electrical code in the US may be different and the trailer have CSA for Canadian Certification. There is the code that says no and the reality the Trailer is safe and meets code as per the CSA certification.

The outlets in the trailer are protected by GFCI so the bonding from a safety aspect might be a non issue but hot skin or what Lou had could still happen as the return ground path is on the neutral instead of the ground. With high power usage in a park, all being single phase, it is quite possible a lot of neutral current exists creating a AC potential between the bonded trailer ground and real earth ground. When I spec an install I always have double sized neutrals added to compensate for single phase loads.

Sorry for going all engineer on you with this

Brian
I think this is the same in the US. Neutral and ground are not to be bonded except at the service. I could be mistaken, as its been a while since studying the NEC. I know that in my TT they are separate.
__________________
2000 Cherokee 29BH with 6V batteries, LED lights & 400 watts of solar power, flipped axles and raised. 2007 Tundra 5.7L DC-LB with lots of mods. C-co, 8/158th AVN Maint.
RPAspey is offline   Reply With Quote
Old 08-15-2014, 09:12 PM   #25
Senior Member
 
bubbles's Avatar
 
Join Date: Dec 2012
Posts: 2,560
Quote:
Originally Posted by RPAspey View Post
I think this is the same in the US. Neutral and ground are not to be bonded except at the service. I could be mistaken, as its been a while since studying the NEC. I know that in my TT they are separate.
The words electrical bonding refers to the process of joining two metals together providing the least electrical resistance between the metals (this includes crimp on wire terminal lugs used to ground wires to wherever). Electrical ground (neutral returns included) circuits differing in function/type and amount of voltage/signal etc. should not be combined to a common ground point (stud) rather to its own dedicated ground point. Likewise identical function wiring may be combined on a common stud (point). Everyone probably knows this though so I'm done.
__________________
bubbles is offline   Reply With Quote
Old 08-16-2014, 09:26 AM   #26
Senior Member
 
Oaklevel's Avatar
 
Join Date: Sep 2012
Location: Virginia
Posts: 3,530
Quote:
Originally Posted by camaraderie View Post
I just got one of these NON CONTACT VOLTAGE SENSORS (amazon) for 15 bucks to check the steps for hot skin after plugging in anywhere...but also useful for finding hot wires throughout the house and coach. I got this one because the adjustability makes it good for both 12 and 120V sensing and you can make it less sensitive to isolate THE wire with current in a bundle.
The ONLY thing I don't like about it is that you have to hold the on switch rather than there being a click on switch. Otherwise, highly recommended.
http://www.amazon.com/Sperry-Instruments-VD6505-Adjustable-Sensor/dp/B000GLAC5G/ref=sr_1_1?s=hi&ie=UTF8&qid=1408116681&sr=1-1
We also have a circuit tester like Herks above and give that a big DITTO too!
Never tried this brand but know their limitations & always test them on a known source before using as the battery inside will eventually die. The ones I have used only check AC though not 12V.

__________________

2005 Dodge 3500 Cummins
2017 Wildwood Lodge 4092 BFL
1966 Mustang GT
1986 Mustang SVO
Sadie & Lillie Spoiled Rotten Boxers
Oaklevel is offline   Reply With Quote
Old 08-17-2014, 10:10 AM   #27
Member
 
Join Date: Jun 2012
Location: Central Wyoming
Posts: 72
Quote:
Originally Posted by Herk7769 View Post
It was directly under the converter at the frame.

The green wire went directly from the converter's ground buss to the frame (via a hole in the floor) and the Neutral from the converter's buss went to another Neutral buss screwed to the floor; and then to the frame via the same hole as the green ground wire.

Herk,
Are you sure the buss screwed to the floor is not the common buss for the DC side? The neutral and the equipment ground should NOT be bonded together in the trailer. The only place the neutral and ground should be bonded is at the main service disconnect in the home or campground electrical system. If they are tied together in the trailer, that creates a parallel path for neutral current through the ground conductor which is not good.

Brad
__________________
WY Husker Fan is online now   Reply With Quote
Old 08-17-2014, 01:03 PM   #28
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 21,169
Quote:
Originally Posted by WY Husker Fan View Post
Herk,
Are you sure the buss screwed to the floor is not the common buss for the DC side? The neutral and the equipment ground should NOT be bonded together in the trailer. The only place the neutral and ground should be bonded is at the main service disconnect in the home or campground electrical system. If they are tied together in the trailer, that creates a parallel path for neutral current through the ground conductor which is not good.

Brad
Gonna look again today, but that is what I recall finding.
Lou
__________________

Lou and Laura with Bella - German Short Hair Pointer
2008 GMC Sierra 2500HD Crewcab SB Allison Duramax
2010 Flagstaff 8526RLWS - Superglide 3300
HAM CALLSIGN - KC3FFW
Herk7769 is offline   Reply With Quote
Old 08-17-2014, 01:39 PM   #29
itch'n to road trip
 
campnqueen's Avatar
 
Join Date: Jun 2010
Location: North Georgia Mountains-Jasper GA.
Posts: 908
WOW I would have never thought about the battery. GREAT POINT Herk.
__________________
2012 Ford F-250 King Ranch Super Crew Cab 4x4 "Mae West"
2014 Work & Play 25ULA "Ula"
Paula Drake, Ken Cooksey, Sunny Delight & Valor
Jasper Ga.
campnqueen is offline   Reply With Quote
Old 08-21-2014, 01:52 PM   #30
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 21,169
So, just when I thought I had it all figured out ... Monkey Wrench.

The buss screwed to the floor is indeed the 12 volt DC "Ground Buss."

Unbonded the AC Ground and AC Neutral in the camper and my 30 volts AC is back; frame ground to Neutral.

Further troubleshooting is I have about 2 volts AC between the AC ground and AC Neutral with all breakers on except the L/R GFCI circuit/Converter (hots are soldered together and inserted at the breaker).

In process of trying to isolate which leg is the culprit. I am afraid the issue is in the converter. (Film at Eleven)
__________________

__________________

Lou and Laura with Bella - German Short Hair Pointer
2008 GMC Sierra 2500HD Crewcab SB Allison Duramax
2010 Flagstaff 8526RLWS - Superglide 3300
HAM CALLSIGN - KC3FFW
Herk7769 is offline   Reply With Quote
Reply

Tags
frame

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 09:34 PM.