Splitting the 30amp service

My wife and I have a side business that involves using a heat press to apply custom rhinestone designs to shirts.

We are looking at going to some local fairs / festivals to sell these. Since we will be there all day for 3 days in the heat of Aug I am considering taking the TT along.

They are able to provide a 30amp/120volt with RV connector for service.

I want to be able to run the A/C on the TT
I want to be able to run the fridge on the TT.
The heat press has ratings of: 120 volts, 1750 watts, 14.5 amps

My concern comes with plugging the press into the outside 110 outlet on the side of the camper. Would I be pulling to much electricity through the camper/outlet?

Can I split the 30amp service at the provided box and have the heat press run on a separate heavy duty cord?

I don't know the A/C amps but guessing it is a 13.5k unit so I figure to be under the total 30amp draw.
__________________
22 Forest River RPod 192
2019 Nissan Titan


vizsla owner is offline   Reply With Quote
Old 07-19-2013, 11:24 AM   #2
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,954
Quote:
Originally Posted by vizsla owner View Post
They are able to provide a 30amp/120volt with RV connector for service.

I want to be able to run the A/C on the TT
I want to be able to run the fridge on the TT.
The heat press has ratings of: 120 volts, 1750 watts, 14.5 amps

I don't know the A/C amps but guessing it is a 13.5k unit so I figure to be under the total 30amp draw.
Howdy. Different A/C brands/models can require different amps. One model might use 11 amps and another may use 15. They also require more amps starting up, but this is for a very short time.

Just taking an average of 12 amps for the AC, say 6 amps for the refrigerator, and 14.5 amps for your heat press, you can see you are over your 30 amp total.

Does the 30 amp outlet you are plugging into have it's own dedicated circuit breaker at the outlet?

I don't see how "splitting" the service accomplishes anything. You still only have 30 amps total available. If the 30 amp outlet doesn't have a 120 volt 15/20 amp receptacle in addition to the 30 amp RV receptacle.......you can always use an adapter that plugs into the 30 amp RV outlet, and then has a standard household 120 volt end to plug your heat press into.

Of course, when doing this, you won't be able to have your trailer plugged in to run the A/C and fridge. But you might could do this in short bursts and make it fine.

__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 07-19-2013, 11:34 AM   #3
Senior Member
 
avolnek's Avatar
 
Join Date: Jun 2013
Location: Nebraska
Posts: 630
You can sure try plugging the press into the outlet on the side of the camper but I don't think it will last long for you... Your best bet would be if they can provide you with the 30 amp rv plug as well as a 20 amp outlet. Most camp sites are set up this way, I am aware you wont be at a typical camp site but it's worth asking...
__________________

TV- 2015 Ram 2500 CCLB 6.7 Cummins 3.42 gears
Camper - 2015 Saber 322BHTS
avolnek is offline   Reply With Quote
Old 07-19-2013, 11:40 AM   #4
Member
 
vizsla owner's Avatar
 
Join Date: Aug 2012
Location: Texas
Posts: 90
I'll have to look what the A/C draw is. I saw on another post that a fridge is only about 2 amps.

A/C = 12
Fridge = 2
Press = 14.5
Total = 28.5 amps when everything is on.

My thought about splitting it means I can put an adapter on one side so the press doesn't have to run through the TT electrical but I still have enough AMPs for everything to run.
__________________
22 Forest River RPod 192
2019 Nissan Titan


vizsla owner is offline   Reply With Quote
Old 07-19-2013, 11:51 AM   #5
Senior Member
 
Join Date: Jul 2012
Posts: 1,258
If you have a spare spot for an extra breaker, I would install a dedicated outside plug for your press, with an appropriately-sized feed wire. That way you wouldn't have to worry about overloading anything.
And you could always check your voltage drop when the air is on and you are using the press, just to make sure it is ok.
And you can run your fridge on propane, as it doesn't use much at all.
bakken is offline   Reply With Quote
Old 07-19-2013, 12:00 PM   #6
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,954
Quote:
Originally Posted by vizsla owner View Post
I'll have to look what the A/C draw is. I saw on another post that a fridge is only about 2 amps.
Here again, different makes/models/sizes of refrigerators will use different amps...just like the air-conditioners. These numbers are just guestimations, and we would need more specifics to provide more specific answers.

2 amps could have possibly been DC (12 volt) draw, and not AC (120 volt) draw

Here is a chart that shows general averages of electrical draws from appliances.......but will always depend on other factors.

http://www.forestriverforums.com/for...aws-17300.html
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 07-19-2013, 12:03 PM   #7
Senior Member
 
avolnek's Avatar
 
Join Date: Jun 2013
Location: Nebraska
Posts: 630
Quote:
Originally Posted by vizsla owner View Post
I'll have to look what the A/C draw is. I saw on another post that a fridge is only about 2 amps.

A/C = 12
Fridge = 2
Press = 14.5
Total = 28.5 amps when everything is on.

My thought about splitting it means I can put an adapter on one side so the press doesn't have to run through the TT electrical but I still have enough AMPs for everything to run.

I would have to say that the fridge and A/C are probably a little low. Even if they weren't the issue wont be the running amps it will be the start up... You can pull as much as 75 amps on start up for the air conditioner...

I definitely see it worth trying... Worst case would be you trip a breaker... no big deal... then you know you need to break something off onto a separate circuit.
__________________

TV- 2015 Ram 2500 CCLB 6.7 Cummins 3.42 gears
Camper - 2015 Saber 322BHTS
avolnek is offline   Reply With Quote
Old 07-19-2013, 12:07 PM   #8
Member
 
jriddering's Avatar
 
Join Date: Feb 2012
Posts: 163
Refrigerator on gas is 2 amps at 12 volts? That is 24 watts. It would be .2 amps of AC power.
__________________
Jim and Carol

2012 Crusader 290RLT
2010 Ford F-250 King Cab Diesel
Harley Davidson Edition
jriddering is offline   Reply With Quote
Old 07-19-2013, 12:16 PM   #9
Senior Member
 
Dave Lyon's Avatar
 
Join Date: Aug 2012
Location: Oshawa, ON
Posts: 983
What is the chance that all three will be running at once? I would flip the fridge on propane when planning to use the heat press, or the entire three days for that matter.
__________________
Dave, Southern,ON



2017 GMC SLT HD All Terrain Crew Cab (6' 6" Box) 2012 Roo 23SS
E2 Trunnion WDH (1,000 lb / 10,000 lb)
Dave Lyon is offline   Reply With Quote
Old 07-19-2013, 12:16 PM   #10
Senior Member
 
Join Date: Jul 2012
Posts: 1,258
Quote:
Originally Posted by jriddering View Post
Refrigerator on gas is 2 amps at 12 volts? That is 24 watts. It would be .2 amps of AC power.
When the fridge is on gas, the propane does the cooling.
When on AC, the electricity powers the cooling.
So you can't compare the two.
bakken is offline   Reply With Quote
Old 07-19-2013, 01:00 PM   #11
Member
 
jriddering's Avatar
 
Join Date: Feb 2012
Posts: 163
Quote:
Originally Posted by bakken View Post
When the fridge is on gas, the propane does the cooling.
When on AC, the electricity powers the cooling.
So you can't compare the two.
I am showing how little power is used in propane mode. He has a lot of AC power he wants to use. I was showing that when in propane mode, his use of converted AC power won't affect rest of what he wants to run
__________________
Jim and Carol

2012 Crusader 290RLT
2010 Ford F-250 King Cab Diesel
Harley Davidson Edition
jriddering is offline   Reply With Quote
Old 07-19-2013, 01:09 PM   #12
Mod free 5er
 
Join Date: Mar 2008
Location: Concord, NC
Posts: 24,702
Quote:
Originally Posted by avolnek View Post
I would have to say that the fridge and A/C are probably a little low. Even if they weren't the issue wont be the running amps it will be the start up... You can pull as much as 75 amps on start up for the air conditioner...
75 Amps for a 13.5 AC?????
__________________
OldCoot is offline   Reply With Quote
Old 07-19-2013, 01:55 PM   #13
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 23,269
Quote:
Originally Posted by avolnek View Post
You can pull as much as 75 amps on start up for the air conditioner...
I believe you are using the Locked Rotor Amperage for both the compressor and the fan. (The LRA on my 15k is 53 amps).

However startup amps can be no higher then 1.56 times the running amps in order to get a UL rating.

Having said that, I recommend a small Honda EU2000i for the press unless 50 amps is available at the pedestal. Most 30 amp only services have the 20 amp duplex breaker pig-tailed off the 30 amp breaker and are not additive to the available 30 amp service.

If your camper is wired like mine, the outlet outside is circuit protected at 15 amps and the fridge is on that circuit. Blowing that breaker and not noticing it could be problematic. Additionally, having the iron on and having the compressor/fan start, could open your main breaker. (also problematic).
__________________
Lou & Freya the wonder dog
2008 GMC Sierra 3000HD Allison Duramax
2019 Flagstaff 8529FL
Herk7769 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 02:52 AM.