Old 09-24-2015, 11:47 AM   #1
Junior Member
 
Join Date: Sep 2015
Location: Maryland Eastern Shore
Posts: 20
Furnace wont run

I have a 2014 Sunseeker 2860 with a Suburban Furnace and a Dometic LCD Thermostat. A/C works great but when I turn it to Heat nothing happens except a faint click from the furnace area. Fan does not come on. Running on Shore power. Checked voltage at themostat and got 12.6 volts DC, 13.8 at coach battery. Stove runs fine with all three burners showing blue flame. Fridge runs fine on gas also. Is there a fuse somewhere other than the Panel which shows all fuses and breakers closed. Help, cooler weather is coming.
__________________

__________________
2014 Sunseeker 2860
Blue Ox Towbar and plate
Toad - 2015 Jeep Wrangler Unlimited
tjasick is offline   Reply With Quote
Old 09-24-2015, 12:09 PM   #2
Head Rambler
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 4,322
Has it worked up until now?

If so it sounds like it's not sensing the sail switch being open. If it senses the sail switch being closed when it's not running then it won't try to start. That's where I'd start looking.
__________________

__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 09-24-2015, 12:18 PM   #3
Junior Member
 
Join Date: Sep 2015
Location: Maryland Eastern Shore
Posts: 20
We got it late last June so we did not have a need for heat until now. During the walk through we were shown how to set the thermostat to heat but never saw the furnace run, it was in the mid 90's that day.
__________________
2014 Sunseeker 2860
Blue Ox Towbar and plate
Toad - 2015 Jeep Wrangler Unlimited
tjasick is offline   Reply With Quote
Old 09-24-2015, 12:19 PM   #4
Junior Member
 
Join Date: Sep 2015
Location: Maryland Eastern Shore
Posts: 20
Sail switch will not work since the fan never comes on.
__________________
2014 Sunseeker 2860
Blue Ox Towbar and plate
Toad - 2015 Jeep Wrangler Unlimited
tjasick is offline   Reply With Quote
Old 09-24-2015, 12:32 PM   #5
Senior Member
 
bubbles's Avatar
 
Join Date: Dec 2012
Posts: 2,562
Quote:
Originally Posted by Bama Rambler View Post
Has it worked up until now?

If so it sounds like it's not sensing the sail switch being open. If it senses the sail switch being closed when it's not running then it won't try to start. That's where I'd start looking.
Yes, it is the sail switch not being actuated but as said the sail switch is actuated by the fan blowing air on it. When there was the click sound the fan should have come on, I believe and then a short time later the heater should have fired up. The thermostat must be set to a high enough temperature setting for the furnace to come on. There is a delay from furnace on to hearing the fan.
__________________
bubbles is offline   Reply With Quote
Old 09-24-2015, 12:52 PM   #6
Senior Member
 
Toby's Avatar
 
Join Date: Sep 2011
Location: Western Iowa
Posts: 578
This happened to me a few years ago. My dealer told me to take the cover (cosmetic louvre) off and knock on the furnace a few times. I thought that sounded odd but I tried it anyway. Furnace kicked right off. A few weeks later they replaced the sail switch under warranty (you get two years on the furnace from the manufacturer). It's an easy test.


Sent from my iPhone using Forest River Forums
__________________
2012 Ford F-150 EB 3.73
2015 Forest River 25RR
2004 Honda GL1800
Toby is offline   Reply With Quote
Old 09-24-2015, 01:21 PM   #7
Junior Member
 
Join Date: Sep 2015
Location: Maryland Eastern Shore
Posts: 20
Thanks for the suggestions, I'll try tapping on the furnace and post results
__________________
2014 Sunseeker 2860
Blue Ox Towbar and plate
Toad - 2015 Jeep Wrangler Unlimited
tjasick is offline   Reply With Quote
Old 09-24-2015, 02:08 PM   #8
Head Rambler
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 4,322
Here's what's supposed to happen with the sail switch. When the t-stat calls for heat, the start relay engages and the control board checks the sail switch to make sure it's not on. If it's not on, then it starts the blower and checks to see that the sail switch closes. If that happens it then waits for the purge time to expire and then it energizes the igniter, opens the gas valve and then checks for a flame.

The reason it initially checks to see if the sail switch is open is for safety reasons. If the switch is closed when the blower isn't running then there's something is wrong with the switch and it can't let the unit start.

If it didn't check the position of that switch prior to starting the blower it could potentially start the igniter without airflow through the system and cause a possible explosion due to lack of purge.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 09-24-2015, 03:31 PM   #9
Senior Member
 
Join Date: Oct 2014
Location: Where ever the trailer is parked
Posts: 112
Mine had a problem not starting about a year go, it was getting cold and it did not work for about three days. I did not know what was going wrong, all it was is a air lock in the gas line and would not let it the furnace fire, it finely worked its way out and started firing.
__________________
Ditchdigger is offline   Reply With Quote
Old 09-24-2015, 03:40 PM   #10
Junior Member
 
Join Date: Sep 2015
Location: Maryland Eastern Shore
Posts: 20
Removed wood cover under fridge to gain access to furnace. Removed front metal cover of furnace, can't see anything but outside of burner chamber, blower and all wires are in back of furnace and not accessible without removing the furnace. Tapped on furnace as far back as I could reach. Still nothing when thermostat is set to heat.
__________________

__________________
2014 Sunseeker 2860
Blue Ox Towbar and plate
Toad - 2015 Jeep Wrangler Unlimited
tjasick is offline   Reply With Quote
Reply

Tags
furnace

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 07:18 AM.