Help with propane furnace.

I have an issue with my furnace. It starts okay, but sometimes it does not turn off when it reaches its set temperature. Even if I turn the thermostat to the off position it will not turn off.
If I pull the fuse and reinsert it, it turns off.
It sounds like a suck relay.
I think it is a Suburban brand.
Does anybody know what might be causing my problem?
Thanks
__________________
2013 Georgetown XL 378
2008 Honda CR-V
wrapperman is offline   Reply With Quote
Old 11-29-2019, 06:36 PM   #2
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
The last few I remember with that type problem had a bad control board.

But, before you run off buying a new board, remove the thermostat wires going to the furnace once it gets up to temp and see if the furnace shuts down. If it does, it's the thermostat.

Can you tell us which thermostat you have?
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 11-29-2019, 07:03 PM   #3
Site Team
 
bikendan's Avatar
 
Join Date: Jan 2007
Location: Goodyear, Arizona
Posts: 33,604
Sounds like you have the cheap analog thermostat. Get a good digital thermostat.
__________________
Dan-Retired California Firefighter/EMT
Shawn-Musician/Entrepreneur/Wine Expert
and Zoe the Wonder Dog(R.I.P.)
2016 PrimeTime TracerAIR 255, pushing a 2014 Ford F150 SCREW XTR 4x4 3.5 Ecoboost w/Max Tow Package
4pt Equal-i-zer WDH and 1828lbs of payload capacity
bikendan is offline   Reply With Quote
Old 11-29-2019, 07:43 PM   #4
Senior Member
 
Join Date: May 2013
Location: Whitehouse, Texas
Posts: 1,275
This is my thermostat. Click image for larger version

Name:	1575074581951.jpeg
Views:	162
Size:	46.6 KB
ID:	220033
__________________
2013 Georgetown XL 378
2008 Honda CR-V
wrapperman is offline   Reply With Quote
Old 11-29-2019, 09:31 PM   #5
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
That's a Dometic Single Zone thermostat. Try to initialize it and see if that does any good.

Quote:
"A system initialization will need to be performed by the installer after
the system is installed.
Make sure the Single Zone LCD thermostat is in the Off condition.
Press the “+” button and, while holding it, also press and hold the On/Off Mode button for three seconds. LCD will show ― ― .
Press the On/Off Mode button again to turn system off.
This completes the initialization."
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 11-29-2019, 10:32 PM   #6
Senior Member
 
Join Date: May 2013
Location: Whitehouse, Texas
Posts: 1,275
Quote:
Originally Posted by Bama Rambler View Post
That's a Dometic Single Zone thermostat. Try to initialize it and see if that does any good.
I'll try that.
Thanks
__________________
2013 Georgetown XL 378
2008 Honda CR-V
wrapperman is offline   Reply With Quote
Old 11-30-2019, 01:28 PM   #7
Senior Member
 
Join Date: Feb 2018
Posts: 160
The furnace will run for a while after the burner shuts off to remove the residual heat. Even if you turn the thermostat off the furnace will run until the limit switch allows the blower to stop. Pulling the fuse to shut off the blower before it removes this heat could damage your furnace.
__________________
2016 Rockwood Windjammer 3001W
2016 F150 SCREW 3.5 EB
ProPride 3P 1400
Oafdawg is offline   Reply With Quote
Old 11-30-2019, 01:54 PM   #8
Global Nomad
 
Scheinin's Avatar
 
Join Date: Sep 2015
Location: In my 36CKTS 5th Wheel
Posts: 811
Quote:
Originally Posted by Oafdawg View Post
The furnace will run for a while after the burner shuts off to remove the residual heat. Even if you turn the thermostat off the furnace will run until the limit switch allows the blower to stop. Pulling the fuse to shut off the blower before it removes this heat could damage your furnace.
That is the case with my Suburban furnace. It might blow up to 5 minutes.
__________________
Steven J. Scheinin
2015 RAM 3500 4X4
6.7L CTD Dually pulling a
2016 Cedar Creek 36CKTS (Center Kitchen Three Slides)


Scheinin is offline   Reply With Quote
Old 11-30-2019, 02:04 PM   #9
Senior Member
 
Join Date: Jul 2017
Location: North of Seattle, WA
Posts: 17,285
Quote:
Originally Posted by Scheinin View Post
That is the case with my Suburban furnace. It might blow up to 5 minutes.
If the fan continues to run for what seems like an excessive amount of time check the ducting for restrictions.

I had a similar issue with a restricted duct, having a bunch of unnecessary 90 degree bends (one was actuually 180) and crushed duct at the furnace outlet.

My furnace would cycle against the upper limit, starting and stopping the flame, and then run for at least 5 or more minutes after the T-Stat said "enough".

I removed the lousy duct and replaced with better material that had fewer bends. No 90's, just sweeping bends that allow more air flow. Furnace shuts down completely after T-Stat is "happy" in 2-3 minutes.

TT also heats quicker with more air flow through the ductwork.
__________________
"A wise man can change his mind. A fool never will." (Japanese Proverb)

"You only grow old when you run out of new things to do"

2018 Flagstaff Micro Lite 25BDS
2023 f-150 SCREW XLT 3.5 Ecoboost (The result of a $68,000 oil change)
TitanMike is offline   Reply With Quote
Old 11-30-2019, 02:38 PM   #10
Junior Member
 
Join Date: Aug 2018
Location: Rochester, NY
Posts: 24
I had the same issue with my furnace a day after I picked it up from the dealer this past May 2019. set the thermostat to 69, we left for a couple of hours and when we returned it was 84 degrees and the furnace was still running. I called the dealer and was told to unplug from the pedestal and disconnect from the battery, wait a couple of minutes and then power up again, that should reset it. It worked and it has worked perfectly since.
Give it a try.
__________________
Jamesr7332
2022 Silverado 2500HD Crew Cab 4x4
2019 Rockwood Ultra Lite 2608BS
Jamesr7332 is offline   Reply With Quote
Old 11-30-2019, 05:23 PM   #11
Senior Member
 
Adrian Gordon's Avatar
 
Join Date: Mar 2018
Posts: 420
Quote:
Originally Posted by bikendan View Post
Sounds like you have the cheap analog thermostat. Get a good digital thermostat.
I'm still very much a newbie to analyzing my RV problems after two seasons and trying to learn how to approach problems that arise. Can you tell me what there was in the OP's post that led you to this possibility?
__________________
2018 Coachmen Leprachaun 210RS with DW, Nanuq the Samoyd puppy and the cat.
Adrian Gordon is offline   Reply With Quote
Old 11-30-2019, 05:27 PM   #12
Site Team
 
bikendan's Avatar
 
Join Date: Jan 2007
Location: Goodyear, Arizona
Posts: 33,604
Quote:
Originally Posted by Adrian Gordon View Post
I'm still very much a newbie to analyzing my RV problems after two seasons and trying to learn how to approach problems that arise. Can you tell me what there was in the OP's post that led you to this possibility?
This statement:

"It starts okay, but sometimes it does not turn off when it reaches its set temperature".
Analog thermostats often have inaccurate temperature swings. Digital thermostats have more accurate temperature settings. But the OP has a digital thermostat so it's likely not the issue.
__________________
Dan-Retired California Firefighter/EMT
Shawn-Musician/Entrepreneur/Wine Expert
and Zoe the Wonder Dog(R.I.P.)
2016 PrimeTime TracerAIR 255, pushing a 2014 Ford F150 SCREW XTR 4x4 3.5 Ecoboost w/Max Tow Package
4pt Equal-i-zer WDH and 1828lbs of payload capacity
bikendan is offline   Reply With Quote
Old 11-30-2019, 07:48 PM   #13
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,458
Anticipator

Quote:
Originally Posted by bikendan View Post
This statement:

"It starts okay, but sometimes it does not turn off when it reaches its set temperature".
Analog thermostats often have inaccurate temperature swings. Digital thermostats have more accurate temperature settings. But the OP has a digital thermostat so it's likely not the issue.
The hysteresis in an analog thermostat is adjustable via the anticipator on the back side of the thermostat base plate. Suburban recommends starting with a setting of 0.8. Given all the bad things we've heard about FR assembly, it's a good bet that this is never checked when the thermostats are installed.

I'd rather have a simple, mechanical thermostat than one where I have to remember to hold my nose, hold temp down and temp up while holding heat and cool at the same time, squinting my left eye, and hoping there's no full moon. I've never heard of anyone rebooting an analog thermostat.

I'm no Luddite. I was a computer designer for IBM for 45 years. But I do believe simpler is better--especially on a cold Sunday night 50 miles from the nearest RV supply.
__________________
Larry
"Everybody's RV is not like your RV."
"Always take pictures with the button on the right."
"Always bypass the water heater before opening the low-point drains."
Sticks and Bricks: Raleigh, NC
2008 Cherokee 38P: at Ivor, VA permanently
Larry-NC is offline   Reply With Quote
Old 11-30-2019, 08:57 PM   #14
Senior Member
 
Join Date: May 2013
Location: Whitehouse, Texas
Posts: 1,275
My issue is like what jamesr7332 was having. It only happens now and then. Never predictable.
I will try jamesr7332 approach.
I have a front and rear furnace, but only the front one is having this issue. They are both 6 1/2 years old and the front one just started this issue.
No sharp or 90* bends.
Turning off the thermostat or lowering the thermostat does not stop the furnace from blowing hot air, even after 2 hours.
My thinking is the control model may be going out. Getting to it won't be easy. It is under the oven.
__________________
2013 Georgetown XL 378
2008 Honda CR-V
wrapperman is offline   Reply With Quote
Old 11-30-2019, 09:15 PM   #15
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,458
Getting the furnace out

Quote:
Originally Posted by wrapperman View Post
My issue is like what jamesr7332 was having. It only happens now and then. Never predictable.
I will try jamesr7332 approach.
I have a front and rear furnace, but only the front one is having this issue. They are both 6 1/2 years old and the front one just started this issue.
No sharp or 90* bends.
Turning off the thermostat or lowering the thermostat does not stop the furnace from blowing hot air, even after 2 hours.
My thinking is the control model may be going out. Getting to it won't be easy. It is under the oven.
I'm assuming it's a Suburban SF series. I don't think there were any other options 6-1/2 years ago.

It's easy to find the troubleshooting guide for the SF-series furnaces. Click the "Library" link at the top of the page. Go through their steps before taking the furnace apart.

Getting the furnace out is really pretty easy.
1) Turn the propane off at the tanks
2) Take off the grille
3) Turn off the propane at the tanks
4) Disconnect the propane line at the upper right of the plenum. (Mine had an elbow which had a flare fitting on one side. I had to use a crowfoot socket to disconnect it there. I was able to leave the elbow on the furnace.)
5) Remove the plenum front cover. It's one or two sheet-metal screws at the top.
6) Remove the firebox anchor screw. It's a single sheet metal screw at the bottom center.
7) There should be enough slack in the four wires going to the furnace that you can pull the firebox straight out, while stuffing the wires into the plenum at the back--or there may be a connector on the four wires so you can unplug it.*
8) Pull the firebox out. The control board is on the back side.

*If the wires are too short and there's no connector, you can add one.Just buy this cord. Connect it to itself, pull the loop taut and cut the four wires so half remains on each connector. Now, one at a time, cut one of the four furnace wires and connect the two pieces to opposing pins on the connector. (Make sure the +12 supply is on a female contact, not male.)

Reassembly is the reverse. When sliding the firebox back into the plenum, you have to engage the intake and exhaust tubes into the mating tubes on the outside vent. The Suburban manuals advise you to take the vent off, and install it last. Some folks have been able to engage the firebox tubes to the vent tubes but I never have.

Be sure to get the propane flare nut really tight. You can check for leaks with a little soapsuds.
__________________
Larry
"Everybody's RV is not like your RV."
"Always take pictures with the button on the right."
"Always bypass the water heater before opening the low-point drains."
Sticks and Bricks: Raleigh, NC
2008 Cherokee 38P: at Ivor, VA permanently
Larry-NC is offline   Reply With Quote
Old 12-01-2019, 12:41 AM   #16
Always Learning
 
ependydad's Avatar
 
Join Date: Nov 2011
Location: Four Corners, FL
Posts: 21,890
Quote:
Originally Posted by Bama Rambler View Post
That's a Dometic Single Zone thermostat. Try to initialize it and see if that does any good.
Where did you find that? I need to do the same for our 3rd A/C in the garage but it’s the new capacitive touch thermostat by Dometic.
__________________
Officially a SOB with a 2022 Jayco Precept 36C
Checkout my site for RVing tips, tricks, and info | Was a Fulltime Family for 5 years, now we're part-timing on long trips
ependydad is offline   Reply With Quote
Old 12-01-2019, 07:57 AM   #17
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
Quote:
Originally Posted by ependydad View Post
Where did you find that? I need to do the same for our 3rd A/C in the garage but it’s the new capacitive touch thermostat by Dometic.
It's in the "manual" for the single zone thermostat.

Here's one version of the Operating Manual for the Capacitive Touch Thermostat that lists an initialization procedure.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 12-01-2019, 07:33 PM   #18
Senior Member
 
Join Date: May 2013
Location: Whitehouse, Texas
Posts: 1,275
Quote:
Originally Posted by Larry-NC View Post
I'm assuming it's a Suburban SF series. I don't think there were any other options 6-1/2 years ago.

It's easy to find the troubleshooting guide for the SF-series furnaces. Click the "Library" link at the top of the page. Go through their steps before taking the furnace apart.

Getting the furnace out is really pretty easy.
1) Turn the propane off at the tanks
2) Take off the grille
3) Turn off the propane at the tanks
4) Disconnect the propane line at the upper right of the plenum. (Mine had an elbow which had a flare fitting on one side. I had to use a crowfoot socket to disconnect it there. I was able to leave the elbow on the furnace.)
5) Remove the plenum front cover. It's one or two sheet-metal screws at the top.
6) Remove the firebox anchor screw. It's a single sheet metal screw at the bottom center.
7) There should be enough slack in the four wires going to the furnace that you can pull the firebox straight out, while stuffing the wires into the plenum at the back--or there may be a connector on the four wires so you can unplug it.*
8) Pull the firebox out. The control board is on the back side.

*If the wires are too short and there's no connector, you can add one.Just buy this cord. Connect it to itself, pull the loop taut and cut the four wires so half remains on each connector. Now, one at a time, cut one of the four furnace wires and connect the two pieces to opposing pins on the connector. (Make sure the +12 supply is on a female contact, not male.)

Reassembly is the reverse. When sliding the firebox back into the plenum, you have to engage the intake and exhaust tubes into the mating tubes on the outside vent. The Suburban manuals advise you to take the vent off, and install it last. Some folks have been able to engage the firebox tubes to the vent tubes but I never have.

Be sure to get the propane flare nut really tight. You can check for leaks with a little soapsuds.
Thanks Larry.
I'll try the troubleshooting section first. Sounds easier than it looked.
__________________
2013 Georgetown XL 378
2008 Honda CR-V
wrapperman is offline   Reply With Quote
Old 12-12-2019, 07:19 PM   #19
Member
 
Join Date: Jan 2018
Posts: 93
Same kind of stuff was happening to mine. The mobile RV guy come over changed out the thermostat and control board. Cost me $150.0
For everything.
Good luck
Jomo is offline   Reply With Quote
Old 12-12-2019, 08:58 PM   #20
Senior Member
 
MNtraveler's Avatar
 
Join Date: Oct 2015
Posts: 2,404
Quote:
Originally Posted by Oafdawg View Post
The furnace will run for a while after the burner shuts off to remove the residual heat. Even if you turn the thermostat off the furnace will run until the limit switch allows the blower to stop. Pulling the fuse to shut off the blower before it removes this heat could damage your furnace.
I agree with this comment. What the OP reported may actually be absolutely normal furnace behavior.

Only if the fan runs for a long time after reaching temperature or being turned off would there be a concern. If warm air is still coming out of the vents, it is still cooling down. If the fan continues to blow for some time after the air from the furnace is cool, then there could be a problem.
__________________
2016 FR Forester 2401R
Towing 2014 Honda CR-V
MNtraveler is offline   Reply With Quote
Reply

Tags
furnace, propane

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 06:22 PM.