Generator

I have a CC 34RLSA. We had a progressive control hard wired and we are not able to use our generator.
We did not get the generator prep done. Has anyone had this problem
__________________

__________________
Arc of the Sun is offline   Reply With Quote
Old 05-04-2015, 11:28 AM   #2
Senior Member
 
Join Date: Jul 2009
Location: Warsaw,NC
Posts: 4,284
You have a on board generator


Sent from my iPhone using Forest River Forums
__________________

__________________
2015 Cedar Creek 32RL
2012 Silverado 3500HD SRW
http://www.forestriverforums.com/for...ignhavefun.gif
spock123 is offline   Reply With Quote
Old 05-04-2015, 12:45 PM   #3
Junior Member
 
Join Date: Oct 2013
Posts: 22
No a 3000 Honda
__________________
Arc of the Sun is offline   Reply With Quote
Old 05-04-2015, 12:49 PM   #4
Senior Member
 
Join Date: Jun 2012
Location: Fulltimers
Posts: 234
You probably have a floating neutral generator and your Progressive unit is not allowing power to connect. I have read that you can fix that by a plug in the generator connecting the neutral to ground. But you'll need to research it further as I haven't actually done this. I'm sure someone who has will chime in.
__________________
F-350 Dually
Cedar Creek Silverback
Mazda Miata TOAD for sex appeal
danno2u is offline   Reply With Quote
Old 05-04-2015, 12:55 PM   #5
Senior Member
 
Broadway Joe's Avatar
 
Join Date: Oct 2011
Location: Fort Worth
Posts: 636
Are you getting a fault on your Progressive surge protector? See this article regarding open ground with Honda Generators.
Honda EU2000i open ground
__________________
Broadway Joe is offline   Reply With Quote
Old 05-04-2015, 12:56 PM   #6
Senior Member
 
Join Date: Jun 2012
Location: Fulltimers
Posts: 234
Here's another article I found that appears to address your problem:


Generator Ground-Neutral Bonding | No~Shock~Zone
__________________
F-350 Dually
Cedar Creek Silverback
Mazda Miata TOAD for sex appeal
danno2u is offline   Reply With Quote
Old 05-04-2015, 01:49 PM   #7
Junior Member
 
Join Date: Oct 2013
Posts: 22
Thank you
__________________
Arc of the Sun is offline   Reply With Quote
Old 05-04-2015, 04:56 PM   #8
Member
 
Join Date: Apr 2013
Posts: 81
Quote:
Originally Posted by danno2u View Post
Here's another article I found that appears to address your problem:


Generator Ground-Neutral Bonding | No~Shock~Zone
I'm Mike Sokol, author of this No~Shock~Zone article on bonding floating neutral generators with a G-N bonding plug. Thanks for posting the link here. This is indeed the fix per the engineers at Progressive Industries as well as my inside contacts at Honda.

There's lots more articles about RV electrical hookups and safety at No Shock Zone. Feel free to post any electrical questions there.

Mike Sokol
__________________

__________________
jmsokol is offline   Reply With Quote
Reply

Tags
generator

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 06:41 PM.