Progressive surge protector
So after reading some horror stories about not having a voltage/surge protector, we bought Progressives Em's 50 amp hard wired unit. What we didn't think about was when we are at home we use our 30 amp generator. It would not allow the generator to come through. I called Progressive and I told them we had an E 2 which means it doesn't sense a ground. Seems it is very important how you plug in. Anybody else use one of these surge protectors?
|
|
|
05-12-2014, 04:11 PM
|
#2
|
Phat Phrog Stunt Team
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
|
You need to make a neutral bonded plug and plug it into your gennie.
Run a wire from the ground to the neutral inside this plug.
Then plug it in .
TURBS
Sabre owners united!
|
|
|
05-12-2014, 04:17 PM
|
#3
|
Senior Member
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 4,167
|
Quote:
Originally Posted by f1100turbo
You need to make a neutral bonded plug and plug it into your gennie.
Run a wire from the ground to the neutral inside this plug.
Then plug it in .
TURBS
Sabre owners united!
|
X2
Generator Ground-Neutral Bonding | No~Shock~Zone
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2019 F350 Ruby Red 6.7l diesel 3.31 axle electronic locker
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2014 (18) 2015 (18) 2016 (36) 2017 (32) 2018 (42) 2019 (28) 2020 (35)
|
|
|
05-12-2014, 05:05 PM
|
#4
|
Senior Member
Join Date: Mar 2014
Posts: 117
|
Great info. Thanks!
|
|
|
05-13-2014, 12:22 AM
|
#5
|
Plain Old Member
Join Date: Nov 2012
Location: Full Timing in South Louisiana
Posts: 1,938
|
Just curious, if running the 2 Honda EU2000's parallel, would you have to put a bonded plug on each genset, or just in 1?
__________________
John and Rebecca Dickson
Emma-7 / Little John-5 / Iva-1
Full Timing Again, Rev B
2013 Ford F-350 Lariat CC LB PSD
2015 SOB TT - With OC's Awning Poles (#8)
At least in Heaven, RVs will be perfect, and I won't have to keep fixing them.
|
|
|
05-13-2014, 05:12 AM
|
#6
|
Senior Member
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 4,167
|
Since these are hook up in parallel, one should do it.
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2019 F350 Ruby Red 6.7l diesel 3.31 axle electronic locker
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2014 (18) 2015 (18) 2016 (36) 2017 (32) 2018 (42) 2019 (28) 2020 (35)
|
|
|
05-13-2014, 05:48 AM
|
#7
|
Plain Old Member
Join Date: Nov 2012
Location: Full Timing in South Louisiana
Posts: 1,938
|
Ok. Guess if I still get the E2 code, I'll try to put one on each. Thanks.
__________________
John and Rebecca Dickson
Emma-7 / Little John-5 / Iva-1
Full Timing Again, Rev B
2013 Ford F-350 Lariat CC LB PSD
2015 SOB TT - With OC's Awning Poles (#8)
At least in Heaven, RVs will be perfect, and I won't have to keep fixing them.
|
|
|
05-13-2014, 06:20 AM
|
#8
|
Phat Phrog Stunt Team
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
|
If in doubt plug it into the same gennie thats ok plugged into camper.
TURBS
Sabre owners united!
|
|
|
05-13-2014, 06:39 AM
|
#9
|
Plain Old Member
Join Date: Nov 2012
Location: Full Timing in South Louisiana
Posts: 1,938
|
Will give it a shot. We very seldom use the Hondas. Pretty much for emergency only. But, when we have ran them, I just bypassed the EMS due to the E2.
You never quit learning. I'll make a few of those jumped plugs when I get home in a few days.
__________________
John and Rebecca Dickson
Emma-7 / Little John-5 / Iva-1
Full Timing Again, Rev B
2013 Ford F-350 Lariat CC LB PSD
2015 SOB TT - With OC's Awning Poles (#8)
At least in Heaven, RVs will be perfect, and I won't have to keep fixing them.
|
|
|
05-13-2014, 12:55 PM
|
#10
|
Papi
Join Date: Nov 2011
Location: Dade City, FL (TRR)
Posts: 241
|
Another thought: In addition to (the very necessary neutral): What type generator are you using? Some generators provide very "dirty" power that the surge doesn't tolerate well. Could be spikes, other transients that trigger it. This is the stuff that blows up electronics on line...or even off line anymore! If your genset is a Gen-Inverter type (Honda et al) it should be fine though.
__________________
PapiCamper
We're Fulltime in the Cedar Creek
and it ain't goin' nowhere. On 7 years
now in same place.
|
|
|
05-13-2014, 01:01 PM
|
#11
|
Phat Phrog Stunt Team
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
|
Honeywell 6875
TURBS
Sabre owners united!
|
|
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|