Progressive surge protector

So after reading some horror stories about not having a voltage/surge protector, we bought Progressives Em's 50 amp hard wired unit. What we didn't think about was when we are at home we use our 30 amp generator. It would not allow the generator to come through. I called Progressive and I told them we had an E 2 which means it doesn't sense a ground. Seems it is very important how you plug in. Anybody else use one of these surge protectors?
Sewhappy is offline   Reply With Quote
Old 05-12-2014, 04:11 PM   #2
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
You need to make a neutral bonded plug and plug it into your gennie.
Run a wire from the ground to the neutral inside this plug.
Then plug it in .


TURBS

Sabre owners united!
Attached Thumbnails
Click image for larger version

Name:	1399929084860.jpg
Views:	160
Size:	40.2 KB
ID:	52260  
TURBS is offline   Reply With Quote
Old 05-12-2014, 04:17 PM   #3
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 4,167
Quote:
Originally Posted by f1100turbo View Post
You need to make a neutral bonded plug and plug it into your gennie.
Run a wire from the ground to the neutral inside this plug.
Then plug it in .


TURBS

Sabre owners united!
X2

Generator Ground-Neutral Bonding | No~Shock~Zone
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2019 F350 Ruby Red 6.7l diesel 3.31 axle electronic locker
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2014 (18) 2015 (18) 2016 (36) 2017 (32) 2018 (42) 2019 (28) 2020 (35)
fonzie is offline   Reply With Quote
Old 05-12-2014, 05:05 PM   #4
Senior Member
 
Sewhappy's Avatar
 
Join Date: Mar 2014
Posts: 117
Great info. Thanks!
Sewhappy is offline   Reply With Quote
Old 05-13-2014, 12:22 AM   #5
Plain Old Member
 
Join Date: Nov 2012
Location: Full Timing in South Louisiana
Posts: 1,938
Just curious, if running the 2 Honda EU2000's parallel, would you have to put a bonded plug on each genset, or just in 1?
__________________
John and Rebecca Dickson
Emma-7 / Little John-5 / Iva-1
Full Timing Again, Rev B
2013 Ford F-350 Lariat CC LB PSD
2015 SOB TT - With OC's Awning Poles (#8)
At least in Heaven, RVs will be perfect, and I won't have to keep fixing them.
BigJohnD is offline   Reply With Quote
Old 05-13-2014, 05:12 AM   #6
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 4,167
Since these are hook up in parallel, one should do it.
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2019 F350 Ruby Red 6.7l diesel 3.31 axle electronic locker
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2014 (18) 2015 (18) 2016 (36) 2017 (32) 2018 (42) 2019 (28) 2020 (35)
fonzie is offline   Reply With Quote
Old 05-13-2014, 05:48 AM   #7
Plain Old Member
 
Join Date: Nov 2012
Location: Full Timing in South Louisiana
Posts: 1,938
Ok. Guess if I still get the E2 code, I'll try to put one on each. Thanks.
__________________
John and Rebecca Dickson
Emma-7 / Little John-5 / Iva-1
Full Timing Again, Rev B
2013 Ford F-350 Lariat CC LB PSD
2015 SOB TT - With OC's Awning Poles (#8)
At least in Heaven, RVs will be perfect, and I won't have to keep fixing them.
BigJohnD is offline   Reply With Quote
Old 05-13-2014, 06:20 AM   #8
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
If in doubt plug it into the same gennie thats ok plugged into camper.

TURBS

Sabre owners united!
TURBS is offline   Reply With Quote
Old 05-13-2014, 06:39 AM   #9
Plain Old Member
 
Join Date: Nov 2012
Location: Full Timing in South Louisiana
Posts: 1,938
Will give it a shot. We very seldom use the Hondas. Pretty much for emergency only. But, when we have ran them, I just bypassed the EMS due to the E2.

You never quit learning. I'll make a few of those jumped plugs when I get home in a few days.
__________________
John and Rebecca Dickson
Emma-7 / Little John-5 / Iva-1
Full Timing Again, Rev B
2013 Ford F-350 Lariat CC LB PSD
2015 SOB TT - With OC's Awning Poles (#8)
At least in Heaven, RVs will be perfect, and I won't have to keep fixing them.
BigJohnD is offline   Reply With Quote
Old 05-13-2014, 12:55 PM   #10
Papi
 
Papicamper's Avatar
 
Join Date: Nov 2011
Location: Dade City, FL (TRR)
Posts: 241
Another thought: In addition to (the very necessary neutral): What type generator are you using? Some generators provide very "dirty" power that the surge doesn't tolerate well. Could be spikes, other transients that trigger it. This is the stuff that blows up electronics on line...or even off line anymore! If your genset is a Gen-Inverter type (Honda et al) it should be fine though.
__________________
PapiCamper
We're Fulltime in the Cedar Creek
and it ain't goin' nowhere. On 7 years
now in same place.
Papicamper is offline   Reply With Quote
Old 05-13-2014, 01:01 PM   #11
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Honeywell 6875

TURBS

Sabre owners united!
TURBS is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 07:19 AM.