Furnace woes

We've got a 2015 FR3 28DS with the suburban propane heater. Is has a funky thermostat that looks like this:


Name:   IMG_4880.jpg
Views: 741
Size:  44.5 KB

Normally we have the rig connected to shore power and we find that the heat pump and propane furnace work together in conjunction to heat the coach. So far so good.

This past weekend, we tried to use only the furnace (without the heat pump) while boondocking. We turned the thermostat to "heat" mode and set the fan to "auto" and enabled the Furnace mode. We found that no matter how high we turned the setpoint, the furnace would not come on. Ambient temperature was 42 degrees.

To diagnose, we tested the red and white wires coming from the thermostat into the furnace. At all times we got 14V across those two wires, no matter what temperature the thermostat was set. We found that the furnace would start up if we connected the two blue wires from the board together.

Any ideas?
__________________
2015 FR3 28DS
boozedog is offline   Reply With Quote
Old 10-01-2018, 12:34 PM   #2
Member
 
Join Date: Jul 2016
Posts: 36
Also ... does anyone know what make and model of thermostat this is?
__________________
2015 FR3 28DS
boozedog is offline   Reply With Quote
Old 10-01-2018, 05:46 PM   #3
Senior Member
 
rk06382's Avatar
 
Join Date: Oct 2016
Location: Alaska
Posts: 1,831
Quote:
Originally Posted by boozedog View Post
We've got a 2015 FR3 28DS with the suburban propane heater. Is has a funky thermostat that looks like this:

Attachment 187978

Normally we have the rig connected to shore power and we find that the heat pump and propane furnace work together in conjunction to heat the coach. So far so good.

This past weekend, we tried to use only the furnace (without the heat pump) while boondocking. We turned the thermostat to "heat" mode and set the fan to "auto" and enabled the Furnace mode. We found that no matter how high we turned the setpoint, the furnace would not come on. Ambient temperature was 42 degrees.

To diagnose, we tested the red and white wires coming from the thermostat into the furnace. At all times we got 14V across those two wires, no matter what temperature the thermostat was set. We found that the furnace would start up if we connected the two blue wires from the board together.

Any ideas?
I turn off the A/C circuit breaker in the AC panel to prevent heat-pump from running.
__________________
Robert
2018 FR3 28DS | Boondock 99% of the time
Samlex EVO-3012 Inverter/Charger | 600ah Battle Born LiFePO4 | Victron BMV-712 & MPPT 100/50 | 800W Renogy Solar | Fan-Tastic Fans | Blue Ox TruCenter | SnapPads | SumoSprings | Koni Shocks | RVLock
Solar Power & Battle Born batteries
rk06382 is offline   Reply With Quote
Old 10-01-2018, 05:54 PM   #4
Member
 
Join Date: Jul 2016
Posts: 36
Quote:
Originally Posted by rk06382 View Post
I turn off the A/C circuit breaker in the AC panel to prevent heat-pump from running.
Thanks Robert -- but we were boondocking with the generator off ... so there was no 110V to disable
__________________
2015 FR3 28DS
boozedog is offline   Reply With Quote
Old 10-01-2018, 06:59 PM   #5
Senior Member
 
Kadiddle's Avatar
 
Join Date: Jan 2015
Location: Massachusetts
Posts: 138
I have the identical system on my 2015 30DS. Looks like your coach (mine is a 2015.2, second half of model year) has the Atwood A/C/Heat Pump system and the panel you show is from Atwood. The system has the moniker name "AirCommand".

Thought I had the manual for the panel but can't quickly locate. I think it's in my coach and is like one page in the A/C manual. I do know that if you hold down the 'sleep' button for several seconds, the display will tell you what temperature the panel thinks your coach is currently. (Normally the panel shows the set point and I certainly wish it would show the current temperature unless you are changing the set point!!!!! I know what I set it to!!!!!)

I had a short lived problem a couple weeks ago where the panel was showing a much higher current temperature and the furnace would not come on. Problem went away on its own. Not sure related but looking that the panel's sense of the current temperature (via holding sleep) might give you a clue about whether or not the panel is even thinking it should be calling for heat.

BTW, the fan mode does nothing to the propane furnace but rather only the speed of the A/C rooftop unit. But who knows for sure - that panel may care.

Make sure you are turning on the 'Furnace' mode of the panel. The heat pump mode will automatically switch to 'Furnace' when the temperature outside is too low. There's an outside possibility you've set the panel to use the heat pump ('heat' mode without 'furnace'). Without 110V, it may not be automatically switching to propane mode. In mine, pretty sure >>I<< have to push 'Furnace' to get the propane heater to run.

BTW, Atwood was bought by Dometic about two years ago. So getting help might be - blurred.
__________________
2015 FR3 30DS
2010 Ford Escape Toad -or- 2012 Ford Focus Toad
Kadiddle is offline   Reply With Quote
Old 10-01-2018, 07:15 PM   #6
Member
 
Join Date: Jul 2016
Posts: 36
Quote:
Originally Posted by Kadiddle View Post
I have the identical system on my 2015 30DS. Looks like your coach (mine is a 2015.2, second half of model year) has the Atwood A/C/Heat Pump system and the panel you show is from Atwood. The system has the moniker name "AirCommand".

Thought I had the manual for the panel but can't quickly locate. I think it's in my coach and is like one page in the A/C manual. I do know that if you hold down the 'sleep' button for several seconds, the display will tell you what temperature the panel thinks your coach is currently. (Normally the panel shows the set point and I certainly wish it would show the current temperature unless you are changing the set point!!!!! I know what I set it to!!!!!)

I had a short lived problem a couple weeks ago where the panel was showing a much higher current temperature and the furnace would not come on. Problem went away on its own. Not sure related but looking that the panel's sense of the current temperature (via holding sleep) might give you a clue about whether or not the panel is even thinking it should be calling for heat.

BTW, the fan mode does nothing to the propane furnace but rather only the speed of the A/C rooftop unit. But who knows for sure - that panel may care.

Make sure you are turning on the 'Furnace' mode of the panel. The heat pump mode will automatically switch to 'Furnace' when the temperature outside is too low. There's an outside possibility you've set the panel to use the heat pump ('heat' mode without 'furnace'). Without 110V, it may not be automatically switching to propane mode. In mine, pretty sure >>I<< have to push 'Furnace' to get the propane heater to run.

BTW, Atwood was bought by Dometic about two years ago. So getting help might be - blurred.
Thanks Kadiddle that's a great idea ... I will check the ambient reading tomorrow. I can confirm that I did have Furnace mode selected, the little LED next to the furnace button was lit.
__________________
2015 FR3 28DS
boozedog is offline   Reply With Quote
Old 10-01-2018, 07:16 PM   #7
Senior Member
 
Join Date: May 2017
Posts: 154
we had a similar problem. We turned it off and then removed the thermostat from the wall and then replace. Turn it back on and it worked for us.
Kentucky Bob is offline   Reply With Quote
Old 10-01-2018, 07:20 PM   #8
Senior Member
 
Kadiddle's Avatar
 
Join Date: Jan 2015
Location: Massachusetts
Posts: 138
Note the panel will light the Furnace LED itself if it detects the heat pump won't work at current temperatures. I'm sure you are pushing it but all should note that the LED might be on even though not pushed by user.
__________________
2015 FR3 30DS
2010 Ford Escape Toad -or- 2012 Ford Focus Toad
Kadiddle is offline   Reply With Quote
Old 10-01-2018, 07:24 PM   #9
Member
 
Join Date: Jul 2016
Posts: 36
Quote:
Originally Posted by Kentucky Bob View Post
we had a similar problem. We turned it off and then removed the thermostat from the wall and then replace. Turn it back on and it worked for us.
Thanks Kentucky Bob ... did you disconnect the plug on the thermostat or leave it connected when you removed it from the wall?
__________________
2015 FR3 28DS
boozedog is offline   Reply With Quote
Old 10-02-2018, 05:33 AM   #10
Senior Member
 
Join Date: May 2017
Posts: 154
We disconnected the plug,. It seemed to reset itself after that.
Kentucky Bob is offline   Reply With Quote
Old 10-02-2018, 11:34 AM   #11
Member
 
Join Date: Jul 2016
Posts: 36
Tried disconnecting the thermostat and reconnecting, also tried pulling both the furnace and heat pump fuses and replacing. No joy.

Checked ambient temperature on the thermostat, it was showing 74 degrees. But still doesn't seem to call for furnace heat even if I set the setpoint to 85 degrees.

I had Heat mode selected and the furnace button selected (LED was lit) and running only on 12V, no 110V.

Not hearing anything at all from the furnace.

Furnace does start up just fine if I connect the two blue wires from the controller board together.
__________________
2015 FR3 28DS
boozedog is offline   Reply With Quote
Old 10-03-2018, 02:53 PM   #12
Senior Member
 
Kadiddle's Avatar
 
Join Date: Jan 2015
Location: Massachusetts
Posts: 138
Sounds like tracing 12VDC wiring to the heater and finding a fuse might be the next step. Also assuming here that you have propane and the valve is open (but then you'd probably hear the furnace trying to light).
__________________
2015 FR3 30DS
2010 Ford Escape Toad -or- 2012 Ford Focus Toad
Kadiddle is offline   Reply With Quote
Old 10-03-2018, 03:01 PM   #13
Member
 
Join Date: Jul 2016
Posts: 36
Quote:
Originally Posted by Kadiddle View Post
Sounds like tracing 12VDC wiring to the heater and finding a fuse might be the next step. Also assuming here that you have propane and the valve is open (but then you'd probably hear the furnace trying to light).
We've confirmed 12V to the heater, the heater does run if we just connect the two blue wires from the control board together.

But for some reason the thermostat doesn't seem to be calling for heat
__________________
2015 FR3 28DS
boozedog is offline   Reply With Quote
Old 10-03-2018, 03:26 PM   #14
Senior Member
 
Join Date: Apr 2012
Posts: 3,253
It's a thermostat issue(either setting isn't correct or it's faulty). The thermostat's job is to connect those 2 wires when heat is needed. If you can manually connect the wires and all is good, then you do not have a furnace issue.
dustman_stx is offline   Reply With Quote
Old 10-03-2018, 03:28 PM   #15
Member
 
Join Date: Jul 2016
Posts: 36
Quote:
Originally Posted by dustman_stx View Post
It's a thermostat issue(either setting isn't correct or it's faulty). The thermostat's job is to connect those 2 wires when heat is needed. If you can manually connect the wires and all is good, then you do not have a furnace issue.
Having done some more research, it seems that there are some control boards up in the heat pump that handle the furnace. Right now our theory is that something's gone wrong in one of those control boards or in a connection up there. Received a pretty detailed manual from Atwood, I'm attaching it here in case it's of interest to anyone.

Air Conditioner Service Manual - Rev 11.pdf
__________________
2015 FR3 28DS
boozedog is offline   Reply With Quote
Old 10-19-2018, 10:24 PM   #16
Senior Member
 
Join Date: Feb 2017
Posts: 148
Quote:
Originally Posted by Kentucky Bob View Post
we had a similar problem. We turned it off and then removed the thermostat from the wall and then replace. Turn it back on and it worked for us.


What thermostat did you get to replace the old one as I am going to replace mine as it comes on once then never comes on again!....thanks in advance!
lazbo is offline   Reply With Quote
Old 10-21-2018, 09:51 PM   #17
Senior Member
 
Join Date: Feb 2017
Posts: 148
Quote:
Originally Posted by lazbo View Post
What thermostat did you get to replace the old one as I am going to replace mine as it comes on once then never comes on again!....thanks in advance!


Could you send me a picture of the one you replaced it with...thanks in advance
lazbo is offline   Reply With Quote
Old 11-21-2018, 02:22 AM   #18
Senior Member
 
Join Date: Feb 2017
Posts: 148
I am going to replace my thermostat but not sure if I need to replace the control box it came with....have four wires yellow,red,white and black and not sure where they go yellow and white are for the air conditioner I assume and red and black for the furnace...any help would be awesome
lazbo is offline   Reply With Quote
Reply

Tags
furnace


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 01:47 PM.